Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by Richard Kollmann View Post
Adding too much refrigerant will always increase load on compressor. If too much refrigerant is added the high amperage load on compressor will stop compressor.
The EZKoll two plate system's refrigerant flow are normally controlled by an expansion valve. Did you locate this valve? If you can not find this valve your problem is going to be a little more difficult to solve.
I haven't found it yet but its a little tight in there, I'll probably find it once I remove the baffle.
sailingunity is offline   Reply With Quote
Old 19-10-2018, 08:46   #17
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by sailingunity View Post
I haven't found it yet but its a little tight in there, I'll probably find it once I remove the baffle.
We need to start over EZkold did sell systems with both types of refrigerant flow control devices Capillary tube and expansion valve.

The correct refrigerant charge on that two plate system after compressor has run more than 45 minutes will display a low side pressure of 12 to 14 psi. and hopefully amperage of no more than 5 1/2 amps. EZ Kold because of their additional water condenser has produced contaminants restricting refrigerant flow. So if low pressures are correct and amperage is too high we can assume refrigerant flow is restricted.


Report back after adjusting low pressure. When compressor stops then wait more than five minutes before restarting it.
Richard Kollmann is offline   Reply With Quote
Old 19-10-2018, 17:03   #18
cruiser

Join Date: Dec 2006
Posts: 405
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

[QUOTE=Richard Kollmann;2744639]We need to start over EZkold did sell systems with both types of refrigerant flow control devices Capillary tube and expansion valve.

The correct refrigerant charge on that two plate system after compressor has run more than 45 minutes will display a low side pressure of 12 to 14 psi. and hopefully amperage of no more than 5 1/2 amps. Correct.

EZ Kold because of their additional water condenser has produced contaminants restricting refrigerant flow. ?? Please explain!

So if low pressures are correct and amperage is too high we can assume refrigerant flow is restricted. Wrong information, if there is a restriction or blockage the suction pressure will be lower and most likely the amperage will also be lower. This is unless the blockage is in the compressor discharge which is extremely unlikely

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems
OzePete is offline   Reply With Quote
Old 20-10-2018, 09:46   #19
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

[QUOTE=OzePete;2744977]
Quote:
Originally Posted by Richard Kollmann View Post
We need to start over EZkold did sell systems with both types of refrigerant flow control devices Capillary tube and expansion valve.

The correct refrigerant charge on that two plate system after compressor has run more than 45 minutes will display a low side pressure of 12 to 14 psi. and hopefully amperage of no more than 5 1/2 amps. Correct.

EZ Kold because of their additional water condenser has produced contaminants restricting refrigerant flow. ?? Please explain!

So if low pressures are correct and amperage is too high we can assume refrigerant flow is restricted. Wrong information, if there is a restriction or blockage the suction pressure will be lower and most likely the amperage will also be lower. This is unless the blockage is in the compressor discharge which is extremely unlikely

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems
Pete, show the E Z Kold boater’s complete comments posted to your own qualified technician he or she will explain Non Destructive methods on identifying refrigerant flow problems from incorrect refrigerant charge. We know it is not complete refrigerant blockage. The test I suggested will help rule out oxide corrosion oil sludge restrictions that I believe caused E Z Kold to stop the boat refrigeration production.
Richard Kollmann is offline   Reply With Quote
Old 20-10-2018, 16:32   #20
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Just state your believed-true facts and opinions, and hopefully one day we fridge noobs will figure out who's right.

Insults are still insults even if you try to word them "subtly".
john61ct is offline   Reply With Quote
Old 20-10-2018, 17:14   #21
cruiser

Join Date: Dec 2006
Posts: 405
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

[QUOTE=Richard Kollmann;2745368]
Quote:
Originally Posted by OzePete View Post

Pete, show the E Z Kold boater’s complete comments posted to your own qualified technician he or she will explain Non Destructive methods on identifying refrigerant flow problems from incorrect refrigerant charge. We know it is not complete refrigerant blockage. The test I suggested will help rule out oxide corrosion oil sludge restrictions that I believe caused E Z Kold to stop the boat refrigeration production.
Thanks for the (belittling) tip Richard but with over 57 years actually hands on experience in the refrigeration industry and 50 years of engineering refrigeration systems, I am more qualified than any of my qualified refrigeration staff.

And if any of my staff advised a client, quote: "So if low pressures are correct and amperage is too high we can assume refrigerant flow is restricted." or " High side pressure should never exceed 120PSI" they would not have a job.. simple.

Your highlighted advice that I corrected, was completely wrong Richard, regardless of how you try spin it!

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems
OzePete is offline   Reply With Quote
Old 20-10-2018, 20:19   #22
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Pete, I do not know what high side pressure has to do with your employee keeping their job. High refrigerant pressure is controlled by the design of each system. High Back Pressure systems operate with pressures over 250 psi.

This thread deals with relation between amperage and low refrigerant pressure the actual high pressure is not known.
Richard Kollmann is offline   Reply With Quote
Old 22-10-2018, 10:03   #23
Marine Service Provider

Join Date: Dec 2016
Location: Toronto On Canada
Boat: Bristol 45.5
Posts: 736
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by Richard Kollmann View Post
We need to start over EZkold did sell systems with both types of refrigerant flow control devices Capillary tube and expansion valve.

The correct refrigerant charge on that two plate system after compressor has run more than 45 minutes will display a low side pressure of 12 to 14 psi. and hopefully amperage of no more than 5 1/2 amps. EZ Kold because of their additional water condenser has produced contaminants restricting refrigerant flow. So if low pressures are correct and amperage is too high we can assume refrigerant flow is restricted.


Report back after adjusting low pressure. When compressor stops then wait more than five minutes before restarting it.
I have serviced quite a few of these EZKold systems lately and have not yet seen one with a TXV or TEV yet.

I did find that they used all sorts of different parts and that not two of these systems were ever the same . I also noted some innovative evaporator box designs. The quick connect couplers they used were prone to leakage. I had to remove them on a few systems and solder the connectors together .

Regards John.
Typhoon is offline   Reply With Quote
Old 22-10-2018, 10:33   #24
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

I take it use of "innovative" there is in a negative sense?
john61ct is offline   Reply With Quote
Old 22-10-2018, 11:41   #25
Marine Service Provider

Join Date: Dec 2016
Location: Toronto On Canada
Boat: Bristol 45.5
Posts: 736
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by john61ct View Post
I take it use of "innovative" there is in a negative sense?
No, not at all. The stainless work I have seen is pretty good.

Regards John.
Typhoon is offline   Reply With Quote
Old 22-10-2018, 11:53   #26
Registered User

Join Date: Jun 2016
Posts: 850
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by ColdEh Marine View Post
I have serviced quite a few of these EZKold systems lately and have not yet seen one with a TXV or TEV yet.

I did find that they used all sorts of different parts and that not two of these systems were ever the same . I also noted some innovative evaporator box designs. The quick connect couplers they used were prone to leakage. I had to remove them on a few systems and solder the connectors together .

Regards John.
IIRC that is the reason the PO selected EZKold, because the cold plates were sort of custom designed for the space. I'm not near the boat, but last time I looked in there I don't recall seeing anything but the refrigerant lines, and the thermostat wire - however I can't rule out that there might be a TXV in there. The PO bought the water / air cooled system and within a year or two removed the water cooled part because of the aforementioned issues. However to my knowledge it worked for him for the remaining 5 years he owned the boat, and for 6 months while I lived aboard until I tried to tweak the refrigerant to get both plates to frost over. Then things went south. It sounds to me like it might be wishful thinking to get both plates completely frosted over?
sailingunity is offline   Reply With Quote
Old 22-10-2018, 13:25   #27
Marine Service Provider

Join Date: Dec 2016
Location: Toronto On Canada
Boat: Bristol 45.5
Posts: 736
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by sailingunity View Post
IIRC that is the reason the PO selected EZKold, because the cold plates were sort of custom designed for the space. I'm not near the boat, but last time I looked in there I don't recall seeing anything but the refrigerant lines, and the thermostat wire - however I can't rule out that there might be a TXV in there. The PO bought the water / air cooled system and within a year or two removed the water cooled part because of the aforementioned issues. However to my knowledge it worked for him for the remaining 5 years he owned the boat, and for 6 months while I lived aboard until I tried to tweak the refrigerant to get both plates to frost over. Then things went south. It sounds to me like it might be wishful thinking to get both plates completely frosted over?
As Richard has said before , there may not be enough reserve capacity in the system to get those plates completely frozen . If this system is based on a BD35 or 50 with two holding plates and the insulation is old there may be more heat coming into the box then the compressor can remove and the system reaches an equilibrium. The next question is , does the system cycle off ?

Regards John.
Typhoon is offline   Reply With Quote
Old 23-10-2018, 06:56   #28
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by ColdEh Marine View Post
As Richard has said before , there may not be enough reserve capacity in the system to get those plates completely frozen . If this system is based on a BD35 or 50 with two holding plates and the insulation is old there may be more heat coming into the box then the compressor can remove and the system reaches an equilibrium. The next question is , does the system cycle off ?

Regards John.
I do not know if capacity is of issue here as refrigerant flow control seams to be where the problem is. Using capillary tube refrigerant flow is too limited for the wide temperature range of a eutectic plate especially with dual plates. The fixed temperature range of a capillary tube is set by its length and its interior inside full length orifice diameter. As high pressure liquid refrigerant is expanded into low pressure evaporator it only absorbs heat efficiently during the phase change to a vapor. If phase change does not extend through the full length of evaporator coil tubing evaporator/eutectic plate has greater negative COP. The problem with capillary tube refrigerant flow it is predetermined by tube selection, the small volume of refrigerant in system, compressor speed, and the variable of condenser cooling temperatures. Add a second plate to a cap tube flow control system will require correct refrigerant charge and longer compressor running time.

Eutectic plates in series and large single eutectics should not use Capillary Tube refrigerant flow control devices. Thermostatic Expansion Valves (TXV) and a refrigerant receiver tank allow the installation engineer to set the heat absorption phase change to cover complete evaporator without overloading compressor.
Richard Kollmann is offline   Reply With Quote
Old 19-08-2020, 15:02   #29
Registered User
 
Tbaker's Avatar

Join Date: Jan 2013
Location: Birch Bay Washington
Boat: Hylas 44
Posts: 29
Send a message via Skype™ to Tbaker
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

I have a Frigaboat Keel Cooler system that has been slowly showing signs of needing a recharge. I installed it myself in 2004 and it has taken us halfway around the world with no issues. Signs are evaporator box not chilling up more than one inch and unit running continually. I only hear the tinny refrigerant sounds for about 30 minutes then nothing. My Frigaboat has a service port on a horizontal tube attached near the top of the compressor and another mounted on a vertical tube that is attached to one of the tubes coming into/out of the unit. Can someone please tell me which one is the low pressure service port? I'd also like to know what the ballpark charge PSI should be so I don't overcharge. I have attached a picture of a Frigaboat that unit looks like mine.
Thanks in advance,
Tom
Attached Thumbnails
Click image for larger version

Name:	Frigaboat compressor.jpg
Views:	137
Size:	78.9 KB
ID:	221625  
Tbaker is offline   Reply With Quote
Old 20-08-2020, 09:37   #30
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: 12/24 Volt Boat Refrigerator’s Poor Performance Possible Causes

Quote:
Originally Posted by Tbaker View Post
I have a Frigaboat Keel Cooler system that has been slowly showing signs of needing a recharge. I installed it myself in 2004 and it has taken us halfway around the world with no issues. Signs are evaporator box not chilling up more than one inch and unit running continually. I only hear the tinny refrigerant sounds for about 30 minutes then nothing. My Frigaboat has a service port on a horizontal tube attached near the top of the compressor and another mounted on a vertical tube that is attached to one of the tubes coming into/out of the unit. Can someone please tell me which one is the low pressure service port? I'd also like to know what the ballpark charge PSI should be so I don't overcharge. I have attached a picture of a Frigaboat that unit looks like mine.
Thanks in advance,
Tom
Without knowing what your compressor's preset speed is set for I would recommend adding Pure R134a refrigerant slowly until unit is drawing 5 amps and no more. Very slow leaks on Frigoboat units are do to using an actual flow moving Oring seal in each of the line connectors. See Frigoboat web site to obtain correct special seal.

Refrigerant low pressure in picture is the black or green cap above compressor dome. If after adding refrigerant and waiting a while evaporator's surface area does not display frost over 85% of its surface add a small amount of refrigerant. Too much refrigerant in system will display frost on return line towards compressor and compressor may not run the next time it tries to start.

Hopefully you did not add any moisture when servicing system, if so the hissing sound in evaporator will stop and the frost cover will disappear.
Richard Kollmann is offline   Reply With Quote
Reply

Tags
boat, refrigerator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Skips new Seafrost poor performance problem Richard Kollmann Plumbing Systems and Fixtures 87 19-07-2019 16:08
Max Prop Issues -cavitation and poor performance epoxyman Engines and Propulsion Systems 58 02-02-2019 02:41
outboard poor performance mestrezat Auxiliary Equipment & Dinghy 4 12-10-2017 06:29
New Boat , Poor Battery Performance PhilDuhs Electrical: Batteries, Generators & Solar 16 08-07-2011 12:09

Advertise Here


All times are GMT -7. The time now is 10:38.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.