Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 29-05-2022, 04:17   #1
Senior Cruiser
 
sneuman's Avatar

Cruisers Forum Supporter

Join Date: May 2003
Location: Chesapeake Bay
Boat: Sabre 28-2
Posts: 3,197
Images: 37
a/c breaker keeps tripping

I have a Marine Air Systems A/C aboard an older boat that is new to me. Experimenting with it, I find that I can get the pump primed and it will pump fine for about 10 minutes or so, after which time it trips the breaker and shuts off.

Any ideas on what might be going on? Thanks in advance.
__________________
Voyage of Symbiosis: https://svsymbiosis.blogspot.com/
sneuman is offline   Reply With Quote
Old 29-05-2022, 04:30   #2
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,586
Re: a/c breaker keeps tripping

bad breaker
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 29-05-2022, 04:44   #3
Registered User

Join Date: Mar 2022
Location: VESSEL IN JACKSONVILLE
Posts: 29
Re: a/c breaker keeps tripping

assuming the system was working previously. In oorder to trip a breaker you need to draw above it limits. Since is after 10 minutes I would check the wiring to make sure is not oxidated. this add resistance and increase current consumption. I would check with another breaker same current . If this dont work your pump is going dead soon.

another thing if you can check the pump consumption (make sure pump is not clog) with an AC meter and check against the spec. Normally if is not corrosion is the equipment pulling more to stay operational.
the Aviator is offline   Reply With Quote
Old 29-05-2022, 04:44   #4
Registered User

Join Date: May 2022
Posts: 760
Re: a/c breaker keeps tripping

Quote:
Originally Posted by sneuman View Post
I have a Marine Air Systems A/C aboard an older boat that is new to me. Experimenting with it, I find that I can get the pump primed and it will pump fine for about 10 minutes or so, after which time it trips the breaker and shuts off.

Any ideas on what might be going on? Thanks in advance.
Not a lot of information to go on there, for example, do you know if it EVER worked properly? There is a detail that is important.

You mention needing to "prime the pump." I assume you mean the seawater cooling pump. In a proper installation, this should never be needed. The pump should be below water level, and there should be no high points in the plumbing between the seacock and the pump. Even if it is not the cause of the blown breaker, a pump that losses prime will be an ongoing source of frustration with the system.

If the pump losses prime, or otherwise stops, the compressor _should_ shut down on its internal high pressure switch, but if that switch is faulty, or if the breaker and/or wiring is marginally sized the breaker might trip as the compresser power draw goes up.

It is also possible that the cooling circuit is clogged with debris or biogrowth.

It's a bit of a reach, but with no details onthe system, it's hard to say...
ItDepends is offline   Reply With Quote
Old 29-05-2022, 05:57   #5
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: a/c breaker keeps tripping

Is the breaker that’s popping only for the pump, or the whole AC?

If it’s for the whole mess, what’s the water flow look like?
Sailmonkey is offline   Reply With Quote
Old 29-05-2022, 08:47   #6
Senior Cruiser
 
sneuman's Avatar

Cruisers Forum Supporter

Join Date: May 2003
Location: Chesapeake Bay
Boat: Sabre 28-2
Posts: 3,197
Images: 37
Re: a/c breaker keeps tripping

Water flow is good when it's working and I checked for debris in the strainer and found none. I don't know much about the boat prior to me, but assume the A/C was working previously.
__________________
Voyage of Symbiosis: https://svsymbiosis.blogspot.com/
sneuman is offline   Reply With Quote
Old 29-05-2022, 17:44   #7
Registered User

Join Date: Apr 2016
Location: Schuylerville, NY
Boat: Wellcraft portofino 43’
Posts: 462
Re: a/c breaker keeps tripping

The pump may be a different brand than Marine Air. You should determine where the excess amperage is from, the pump or the ac. Marine Air has some of the best customer service in the marine industry. The phone number should be in your owner's manual. Call them. You'll be impressed.
David Mathis is offline   Reply With Quote
Old 29-05-2022, 17:49   #8
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,586
Re: a/c breaker keeps tripping

Quote:
Originally Posted by sailorboy1 View Post
bad breaker
Guess you want a more exoctic reason to chase
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 29-05-2022, 19:29   #9
TBW
Registered User

Join Date: Mar 2017
Location: Easton Maryland
Boat: LeBlanc trawler; 50 ft
Posts: 170
Re: a/c breaker keeps tripping

had this once; lots and lots of looking.
turned out to be not enough cooling water and tripping off on compressor overheat.
put a bucket under cooling water output and get some real numbers; gpm or whatever your ac needs
TBW is offline   Reply With Quote
Old 29-05-2022, 23:25   #10
Registered User

Join Date: May 2013
Location: Oregon to Alaska
Boat: Wheeler Shipyard 83' ex USCG
Posts: 3,560
Re: a/c breaker keeps tripping

Breakers that appear to trip for no reason is usually a bad breaker. Switch with another breaker and see if it still trips. Check the amp draw.
Lepke is offline   Reply With Quote
Old 30-05-2022, 04:06   #11
Registered User

Join Date: Aug 2017
Location: Yarmouth, ME
Boat: Amel 50
Posts: 336
Re: a/c breaker keeps tripping

In my experience, it’s the compressor that causes surges in power draw when it first goes on. In many systems, there’s a delay between turning on the overall AC system (seawater circuit) and the time the thermostat first causes the compressor to engage. We have two compressors onboard. They kick in and off according to separate thermostats but when they both coincidentally kick in at the same time, that sometimes trips the shore power circuit breaker.

Try to see if the circuit breaks coincidentally to your compressor turning on.
__________________
USCG master
Certified sailing instructor
Howler is offline   Reply With Quote
Old 30-05-2022, 05:10   #12
Registered User
 
Boatwright's Avatar

Join Date: Jul 2016
Location: Traverse City, Michigan
Boat: Hinterhoeller Niagara 35
Posts: 299
Re: a/c breaker keeps tripping

Quote:
Originally Posted by Howler View Post
Try to see if the circuit breaks coincidentally to your compressor turning on.
If it's not a bad breaker you likely have a voltage drop in the wiring feeding the unit: wire gauge to small, loose or corroded connections, etc..

AC motors are designed to run at a constant RPM determined by the frequency (50 or 60 cycle depending on the country). If the voltage is low from voltage drop in the circuit, an AC motor will draw more amps to maintain the fixed RPM. Too many amps = tripping breaker and/or an overheated motor.

One other possibility from past overheating is cooked motor windings leading to an internal short in the compressor motor. I don't know about the serviceability of your particular AC system, but the really bad news is if the motor is cooked you may end up having to replace the whole unit.
Boatwright is offline   Reply With Quote
Old 30-05-2022, 05:19   #13
Registered User
 
Boatwright's Avatar

Join Date: Jul 2016
Location: Traverse City, Michigan
Boat: Hinterhoeller Niagara 35
Posts: 299
Re: a/c breaker keeps tripping

I should add that since this is AC wiring, if you are not an experienced electrician, please hire someone who is before you hurt yourself or have an electrical fire.
Boatwright is offline   Reply With Quote
Old 30-05-2022, 05:29   #14
Registered User
 
Cuvee's Avatar

Join Date: Oct 2014
Location: Annapolis/St Thomas
Boat: Fountaine Pajot Saba 50
Posts: 100
Re: a/c breaker keeps tripping

Quote:
Originally Posted by sailorboy1 View Post
bad breaker
3rd5sm
Cuvee is offline   Reply With Quote
Old 30-05-2022, 09:14   #15
Registered User
 
OS2Dude's Avatar

Join Date: Nov 2014
Location: Atlanta, GA
Boat: Catalina 30
Posts: 689
Images: 5
Re: a/c breaker keeps tripping

How are you 'priming the pump'? Make sure your seacock is open all the way and check that your raw water filter is clear. (You DO have a filter, right?) One year our A/C pulled a lot of pine straw into the hose. Cleared the filter, but that did not help much. Took the hose off and it looked like a playdoh machine extruding the pine straw that was still stuck in it. After that it worked fine.
OS2Dude is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flex shaft coupling keeps "tripping" mattman Propellers & Drive Systems 3 02-09-2020 07:40
Quick Boiler B3 Keeps tripping my shorepower AFKASAP Plumbing Systems and Fixtures 4 12-09-2016 14:16
Windlass keeps tripping circuit breaker MinorI Electrical: Batteries, Generators & Solar 36 19-01-2015 19:32
My Refrigerator is Tripping its Breaker jonahmulski Plumbing Systems and Fixtures 15 17-04-2013 16:45
gas valve breaker tripping JusDreaming Plumbing Systems and Fixtures 4 25-10-2007 04:07

Advertise Here


All times are GMT -7. The time now is 13:21.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.