Old 30-07-2023, 06:00   #31
smj
Registered User

Join Date: Nov 2007
Boat: TRT 1200
Posts: 7,373
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by Chotu View Post
We did discuss this. Definitely. There was a thread.



By far is right.



It's one of those things (like marine heads/refrigeration) where the marine stuff is needlessly complicated and prone to breakdowns and requires a lot of maintenance.



I almost used standard window units carefully built in to be concealed, but one of them would have blocked my view aft from the helm, creating a hazard, so I went with the through-roof units.


We have 2 5,000btu window units on our current catamaran which do the job well, though we haven’t found the need to use them yet.
We had a 16,000 btu reverse cycle marine unit and a 8,000 btu window unit in our old boat. At the peak of summer when the water was above 90 degrees the reverse cycle unit was pretty much useless and the window unit did a much better job of cooling.
smj is offline   Reply With Quote
Old 30-07-2023, 06:06   #32
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by smj View Post
We have 2 5,000btu window units on our current catamaran which do the job well, though we haven’t found the need to use them yet.
We had a 16,000 btu reverse cycle marine unit and a 8,000 btu window unit in our old boat. At the peak of summer when the water was above 90 degrees the reverse cycle unit was pretty much useless and the window unit did a much better job of cooling.
how did you position them? I’m really curious. What I was going to do was put them on the aft wall or bulkhead where the salon doors are. In each far corner extremely outboard. Very far port and the other very far starboard. That way they would be hidden.

problem with mine is that you steer from the starboard side and the air conditioner was in the way for me to see aft properly
Chotu is offline   Reply With Quote
Old 30-07-2023, 06:27   #33
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,416
Images: 241
Re: Anyone having issues with water being too hot for your A/C to run?

Any AC has limits, no matter its age, how well it was installed, or its manufacturer, etc.
Generally speaking*, an air conditioning system [air to air] is designed to accommodate up to a 20°F difference [delta], between the outside air, and inside air while still keeping around a 55% humidity level, which is comfortable.

If you have your air conditioner set to a temperature that makes that differential more than 20 degrees, you’ll likely run your AC all day long, and still not reach those desired temperatures.

* The 20° Rule of Thumb applies to well insulated, modern buildings. A typical boat, with it’s poor insulation, single-pane glazing, and high infiltration, will [likely] have a much higher heat gain [than a house], so it’s A/C may only cool to a delta of ± 15°.

Most A/C techs will recommend an evaporator Delta T [difference between your supply air, and return air temperatures] of 16° to 22°F.
Experts generally recommend keeping a home’s relative humidity settings between 40% and 50%.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 30-07-2023, 06:43   #34
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,705
Re: Anyone having issues with water being too hot for your A/C to run?

On a lot of boats (mine included), I think the single biggest limitation with air cooled A/C units is "where the heck do I put the outside unit?"

I think it really comes down to a lot of the marine A/C units being less than ideally designed (such as condensers too small for high water temps) and the installations in many boats are less than great. It's definitely possible for most boat to have better A/C than they do.
rslifkin is online now   Reply With Quote
Old 30-07-2023, 09:28   #35
smj
Registered User

Join Date: Nov 2007
Boat: TRT 1200
Posts: 7,373
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by Chotu View Post
how did you position them? I’m really curious. What I was going to do was put them on the aft wall or bulkhead where the salon doors are. In each far corner extremely outboard. Very far port and the other very far starboard. That way they would be hidden.



problem with mine is that you steer from the starboard side and the air conditioner was in the way for me to see aft properly


They mount in the two rear hatches that open into the cockpit. They cool the queen size bunks on the bridgedeck and we use box fans to circulate the cool air into the hulls.
Click image for larger version

Name:	IMG_7201.jpg
Views:	139
Size:	96.3 KB
ID:	278939
smj is offline   Reply With Quote
Old 30-07-2023, 09:34   #36
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by smj View Post
They mount in the two rear hatches that open into the cockpit. They cool the queen size bunks on the bridgedeck and we use box fans to circulate the cool air into the hulls.
Attachment 278939
That is NICE! Great setup
Chotu is offline   Reply With Quote
Old 30-07-2023, 09:48   #37
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by GordMay View Post
Any AC has limits, no matter its age, how well it was installed, or its manufacturer, etc.
Generally speaking*, an air conditioning system [air to air] is designed to accommodate up to a 20°F difference [delta], between the outside air, and inside air while still keeping around a 55% humidity level, which is comfortable.

If you have your air conditioner set to a temperature that makes that differential more than 20 degrees, you’ll likely run your AC all day long, and still not reach those desired temperatures.

* The 20° Rule of Thumb applies to well insulated, modern buildings. A typical boat, with it’s poor insulation, single-pane glazing, and high infiltration, will [likely] have a much higher heat gain [than a house], so it’s A/C may only cool to a delta of ± 15°.

Most A/C techs will recommend an evaporator Delta T [difference between your supply air, and return air temperatures] of 16° to 22°F.
Experts generally recommend keeping a home’s relative humidity settings between 40% and 50%.

Wanted to point this out:

The 20 degree delta is measured between the *intake* air of the air conditioner and the output air, not the outdoor air and the indoor air.

So, you can cool an enclosed space down up to the point that the delta T of the air conditioner is equal to the heat gain of the enclosure. That is the point cooling stops.

Unless of course, you lose your delta T of the air conditioner because it can't cope from seawater being too hot, evaporator or condenser dirty, low refrigerant, compressor overload, etc.

So you can cool an enclosed space significantly more than 20 degrees from the outside temperature. In fact, you could make ice in your boat and freeze ice cubes on the settee with an ordinary air conditioner if you had great insulation properties. Might get a little dry inside however.

It's all about the ability of the air conditioner to remove heat vs the ability of any enclosure to let it back in.
Chotu is offline   Reply With Quote
Old 30-07-2023, 11:52   #38
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,416
Images: 241
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by Chotu View Post
Wanted to point this out:
The 20 degree delta is measured between the *intake* air of the air conditioner and the output air, not the outdoor air and the indoor air...
Yes, the 20°F [15° - 25°F ΔT] Delta T “Rule of Thumb” applies to the temperature differences, across the evaporator coil [or supply & return air],
AS WELL AS
the indoor outdoor temperature differences [ΔT].

Delta T [ΔT] is a change in temperature, typically displayed in the following equation:
T1 – T2 = ΔT
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 05-08-2023, 18:47   #39
Registered User

Join Date: Jul 2023
Posts: 39
Re: Anyone having issues with water being too hot for your A/C to run?

okay, had a professional come out, ran some strong (but not muratic) acid through it and it's currently working. Thank the heavens!!
MarinAirNoWorky is offline   Reply With Quote
Old 06-08-2023, 15:13   #40
Registered User

Join Date: Jul 2023
Posts: 39
Re: Anyone having issues with water being too hot for your A/C to run?

WELL, guess what.. it's still a no go. Seems like the timing was JUST right to have the water temp drop below 90..ran great all night... water temp 91 this afternoon and it's a no go again. Sigh.
MarinAirNoWorky is offline   Reply With Quote
Old 06-08-2023, 15:29   #41
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by MarinAirNoWorky View Post
WELL, guess what.. it's still a no go. Seems like the timing was JUST right to have the water temp drop below 90..ran great all night... water temp 91 this afternoon and it's a no go again. Sigh.
That is just awful. Sorry to hear it.

It’s just too hot for these types of problems to keep happening.

Can you do a stopgap measure and just get a cheap 5000 BTU air cooled AC set up through the companionway or hatch so the pressure is off and you get a little relief? That way you can think clearly and have less stress
Chotu is offline   Reply With Quote
Old 06-08-2023, 16:09   #42
Registered User

Join Date: Jul 2023
Posts: 39
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by Chotu View Post
That is just awful. Sorry to hear it.

It’s just too hot for these types of problems to keep happening.

Can you do a stopgap measure and just get a cheap 5000 BTU air cooled AC set up through the companionway or hatch so the pressure is off and you get a little relief? That way you can think clearly and have less stress
It's all good - I've got a place to stay with lots of cool air, hopefully till the water cools back down. Just annoying spending 1500 on something a couple years ago and having it not working when it's needed most. Will work on a hose to pickup water from deeper water... shouldn't be too hard.
MarinAirNoWorky is offline   Reply With Quote
Old 07-08-2023, 17:16   #43
Registered User

Join Date: Jul 2023
Posts: 39
Re: Anyone having issues with water being too hot for your A/C to run?

Called the company. They told me that the GPH is too fast for the AC.. 1200 gph pump came with the boat but they only want 350 gph on it.

Is there really a chance that the water is flowing too fast and it cant exchange the heat because of that?
MarinAirNoWorky is offline   Reply With Quote
Old 07-08-2023, 18:03   #44
Registered User
 
AKA-None's Avatar

Join Date: Oct 2013
Location: Lake City MN
Boat: C&C 27 Mk III
Posts: 2,647
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by MarinAirNoWorky View Post
Called the company. They told me that the GPH is too fast for the AC.. 1200 gph pump came with the boat but they only want 350 gph on it.

Is there really a chance that the water is flowing too fast and it cant exchange the heat because of that?


Ever see a river freeze, fast moving water takes a long time to remove heat

So yes based on the above it’s to fast
__________________
Special knowledge can be a terrible disadvantage if it leads you too far along a path that you cannot explain anymore.
Frank Herbert 'Dune'
AKA-None is offline   Reply With Quote
Old 07-08-2023, 18:29   #45
Registered User
 
CaptTom's Avatar

Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,270
Re: Anyone having issues with water being too hot for your A/C to run?

Quote:
Originally Posted by AKA-None View Post
Ever see a river freeze, fast moving water takes a long time to remove heat

So yes based on the above it’s to fast
Interesting. That's the opposite of what I would have thought.

Flowing air certainly removes heat more quickly than still air. That's why we have "wind chill" tables. In first aid classes I've also heard the same thing about cold water immersion. Moving around makes it worse.

When I want to cool down a cooking pot or something outdoors which has been in the sun, I don't just spray water on it. I run a stream of flowing water over it. Ditto for treatment of a first degree burn.

My understanding of icing on rivers is that it's the mechanical motion keeping ice crystals from forming, not that heat is being removed more slowly.

If this intuitive understanding is wrong, I'd love to learn the physics behind faster flowing water being a less effective heat sink than slower.
CaptTom is offline   Reply With Quote
Reply

Tags
water


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
HOT HOT HOT! running AC on Honda generator sailorboy1 Plumbing Systems and Fixtures 79 27-06-2019 07:21
I'm too lazy to use my lazy-bag? Anyone with experience of having a hard-shell? Privilege General Sailing Forum 8 27-09-2017 16:48
Having technical issues with your boat? here's some good advice. johnstone1959 Construction, Maintenance & Refit 0 30-06-2013 07:14
Hot water is TOO hot. By Invitation Construction, Maintenance & Refit 10 18-08-2007 06:02
Ohhhhh Hot! Hot! Hot! knottybuoyz Marine Electronics 6 01-06-2007 07:43

Advertise Here


All times are GMT -7. The time now is 11:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.