Burned out air conditioner circulation pump

I installed this air conditioner and everything myself about 2 years ago and it's more or less been running great until last night. I woke up with the air conditioner off and found that it had shut itself down because the circulation pump was not running.

I smacked it a couple of times with a wrench and it started moving around but it wouldn't pump. I did get a quick wiff of burning plastic smell. Not strong and didn't last very long.

I disassembled the pump and checked the diaphragm and everything and it all looked good so I reassembled it and reinstalled it and it started working just fine.

After running for about 20 minutes the breaker for my air conditioner circuit tripped at the panel and when I went to look at the air conditioner area I could smell a strong burning plastic smell.

With that all out of the way I'm pretty sure I know what's going on I just want to run it by y'all and see if there's something I'm missing. When I first installed the circulation pump I was supposed to put a 1.5 amp fuse for the pump but I completely forgot. At this point what I think happened is that as the strainer would clog the amps would rise and as it wasn't being protected this continued for a while every time the strainer would clog and eventually it burned out the wiring inside the pump or the windings themselves.

The motor is surely toast.

Basically my theory is that this happened because I forgot to install the 1.5 amp fuse. Does anyone disagree?
ttex is offline   Reply With Quote
Old 05-10-2023, 07:51   #2
Registered User

Join Date: May 2013
Location: Potomac/Chesapeake
Boat: Hunter 36
Posts: 694
Re: Burned out air conditioner circulation pump

What type of A/C was it? What brand?
Rohan is offline   Reply With Quote
Old 05-10-2023, 07:55   #3
Registered User

Join Date: Jun 2011
Location: Texas
Boat: Baba 35
Posts: 385
Re: Burned out air conditioner circulation pump

Webasto Platinum 12k btu

Circulation pump is a Shurflo AC circ pump 4.5 gpm

Circulation pump runs off of a relay that is activated by the Webasto system.
ttex is offline   Reply With Quote
Old 05-10-2023, 07:56   #4
Registered User

Join Date: Jun 2011
Location: Texas
Boat: Baba 35
Posts: 385
Re: Burned out air conditioner circulation pump

Wiring is 10 gauge. The circuit breaker for the air conditioner is 20 amp
ttex is offline   Reply With Quote
Old 05-10-2023, 07:58   #5
Registered User

Join Date: Jun 2011
Location: Texas
Boat: Baba 35
Posts: 385
Re: Burned out air conditioner circulation pump

I disconnected the circulation pump and the air conditioner will start up and run. I turned it off before it errors out because the circulation pump is not on. As soon as I reattach the circulation pump and turn it on it trips the breaker
ttex is offline   Reply With Quote
Old 05-10-2023, 11:14   #6
Senior Cruiser

Cruisers Forum Supporter

Join Date: Jun 2018
Location: Rock Hall, MD
Boat: Mariner 39
Posts: 724
Re: Burned out air conditioner circulation pump

Quote:
Originally Posted by ttex View Post
...The motor is surely toast.

Basically my theory is that this happened because I forgot to install the 1.5 amp fuse. Does anyone disagree?
Hi, ttex,
Your theory sounds completely reasonable to me - that a fuse might have prevented the windings from overheating when the pump became heavily loaded. Lousy situation, but experience makes us wiser. I am installing a pump myself and making sure I include the 3-5A fuse spec'd by the manufacturer. I'll start with a 3A and see what happens. I'll also put a label on the fuse holder as a reminder to my future self.
JoeRobertJr is offline   Reply With Quote
Old 05-10-2023, 12:50   #7
Senior Cruiser
 
Madehn's Avatar

Cruisers Forum Supporter

Join Date: Nov 2014
Location: Kemah Tx
Boat: Gulfstar 51
Posts: 646
Re: Burned out air conditioner circulation pump

No this does not sound right. Your pump would not be protected by a 1.5 amp fuse. They draw more power than that on a normal basis. The contro circuitry in your AC box may have needed that fuse. If something fried it is more likely that it is in your ac box than in the pump itself. The pump might draw more amps as flow became restricted but more likely your control circuit was called upon more often as flow became restricted then went into staying on continuously as the AC unit was continuously asked for cooling Normally the AC unit would then shut down if that cooling did not happen and show a high pressure fault code. Guessing that something in your ac control box fried. Just my best guess. Good luck with it. You can swap out pumps on a temporary basis and see if pump is the issue but my guess is that your fault will be in the control board for the AC unit.
Madehn is offline   Reply With Quote
Old 05-10-2023, 17:07   #8
Registered User

Join Date: Jun 2011
Location: Texas
Boat: Baba 35
Posts: 385
Re: Burned out air conditioner circulation pump

Quote:
Originally Posted by Madehn View Post
No this does not sound right. Your pump would not be protected by a 1.5 amp fuse. They draw more power than that on a normal basis. The contro circuitry in your AC box may have needed that fuse. If something fried it is more likely that it is in your ac box than in the pump itself. The pump might draw more amps as flow became restricted but more likely your control circuit was called upon more often as flow became restricted then went into staying on continuously as the AC unit was continuously asked for cooling Normally the AC unit would then shut down if that cooling did not happen and show a high pressure fault code. Guessing that something in your ac control box fried. Just my best guess. Good luck with it. You can swap out pumps on a temporary basis and see if pump is the issue but my guess is that your fault will be in the control board for the AC unit.
The pump is definitely the issue. That is not in doubt. I just now replaced the pump and everything's working fine. The pump does call for a 1.5 amp fuse for protection and these fuses do protect the pumps. This is 120 volt so that may be why you're confused with the 1.5 amp.

Also, this 120 volt circuit does not touch the boards and sensitive stuff in the air conditioner. Those are powered off of a transformer that goes down to 24 volts. Which is of course protected by their fuses inside the unit itself.
ttex is offline   Reply With Quote
Old 05-10-2023, 18:15   #9
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,069
Re: Burned out air conditioner circulation pump

I curious about the pump. I don’t think ShurFlo makes a suitable pump for AC use. The one you are using is way too small for a 12K BTU AC. Webasto recommends a 1000 gallon per hour pump for that AC. Take a look at the March AC-5C-MD. It’s not self priming so it would need to be mounted below the waterline.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 05-10-2023, 19:53   #10
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,787
Re: Burned out air conditioner circulation pump

I kinna doubt the fuse would have made a difference. Centrifugal pump amps typically do not go up that much with restriction. In fact, often they go down (higher head, but less flow). Haven't you heard a vacuum cleaner or fan speed up when the suction is blocked? It's not like a gear or diaphragm pump. The fuse only helps if there is a locked rotor (something jamming the impeller). More likely just poor quality on that unit. Maybe a seal failure.

__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is offline   Reply With Quote
Old 05-10-2023, 21:48   #11
Senior Cruiser

Cruisers Forum Supporter

Join Date: Dec 2019
Location: Miami Beach
Boat: Prout Snowgoose 37
Posts: 192
Re: Burned out air conditioner circulation pump

Quote:
Originally Posted by HopCar View Post
I curious about the pump. I don’t think ShurFlo makes a suitable pump for AC use. The one you are using is way too small for a 12K BTU AC. Webasto recommends a 1000 gallon per hour pump for that AC. Take a look at the March AC-5C-MD. It’s not self priming so it would need to be mounted below the waterline.
A real Hopkins Carter guy would recommend the better March pump…. the
LC-5C-MD. Especially if it’s installed in the engine room.
Capt Clark is offline   Reply With Quote
Old 05-10-2023, 22:29   #12
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,069
Re: Burned out air conditioner circulation pump

Quote:
Originally Posted by Capt Clark View Post
A real Hopkins Carter guy would recommend the better March pump…. the
LC-5C-MD. Especially if it’s installed in the engine room.
You’re right, just seemed the guy was working on a budget.

For those who are curious, the AC-5C-MD is an air cooled pump.
The LC-5C-Md is a liquid cooled pump. I believe it is also submersible.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 06-10-2023, 07:58   #13
Registered User

Join Date: Jun 2009
Location: Annapolis, MD
Boat: Gozzard, 44CC, 50'
Posts: 561
Re: Burned out air conditioner circulation pump

Just 5 weeks ago I had a "Nettle" aka Jelly Fish clog my AC's strainer. Not only did the March Pump burn up, it also took out the relay control board because a fuse was not installed between the two! Apparently when it was installed it was believed that the pump had it's own internal shutdown protection. Mine was the liquid cooled model and yes all their magetic drive centrifical pumps not self priming so they have to be installed below the waterline. There's a fuse there now!
Scrimshaw4 is offline   Reply With Quote
Reply

Tags
pump


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Marine Air Cabin Mate 16000btu air Conditioner formrteki Classifieds Archive 3 01-10-2012 08:52
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 03-09-2012 05:41
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 23-08-2012 00:26
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 13-08-2012 04:28
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 14-07-2012 09:04

Advertise Here


All times are GMT -7. The time now is 01:24.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.