Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

One of the three 2008-era Cruisair 18k Stowaway units (SXUF18/1-HV-RMT -- 115VAC version) on our boat has been tripping the breaker periodically for a few weeks now, running the heat nearly constantly in the Baltimore weather. It would always trip during compressor start, the standard problem. A couple days ago, it tripped for its last time, and no amount of waiting was letting it come back to life. So today I dug in a bit.

When the compressor cuts in, my clamp ammeter shows a rapid climb up to ~72 amps peak draw before the breaker (25A) trips. The LRA/RLA on the unit is listing 79 amps, so I'm guessing we're real close to locked rotor status.

I pulled apart the wiring box and checked the start/run capacitors. The caps check out okay -- with my Fluke 115, the run capacitor checks at 57 uF, rated at 60 +/- 6%, the start capacitor checks at 51 uF, and I can't figure out what the rating is supposed to be (model # for the cap isn't pulling anything up either).

I checked resistance on the three compressor wires (at the wiring panel, so past a few feet of wiring) and got around 2.1 ohm, 1.8 ohm, and 0.8 ohm between the three pairs, which seems pretty low based on what I'm reading online, but it's not zero. The compressor is a Matsushita 2K21C126B, and I can't find specs on what the resistances should be.

If it had just flicked into this LRA mode all of a sudden after working perfectly, I'd suspect that the compressor had just shat the bed, but the slow buildup implies to me that something else is awry here, and my knowledge of A/C units is still pretty weak at this point.

Anything else I can check out? Or try beating on things with hammers?

I'm trying to extend life out of this stuff for another 3ish months while I design and build out a full chiller/boiler setup, so if this unit is dead, I'll just swap our helm unit (least used) out for it in the meantime, that's just going to be a fairly exhausting swap to deal with. I'm coming out of hernia surgery last week so I'm not supposed to lift anything, so this timing sucks pretty good.
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 07-01-2023, 20:57   #2
Registered User
 
pesarsten's Avatar

Join Date: Jan 2012
Location: St Pete
Boat: Sabre 34 , Island Packet 38
Posts: 739
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Are there any Schraeder valves on the refrigerant lines? I was wondering if you could get a drop of oil out so you can smell it and check if it's burnt?
__________________
All that is necessary for the triumph of evil is that good men do nothing. Edmund Burke
pesarsten is offline   Reply With Quote
Old 07-01-2023, 20:59   #3
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Two last checks I did after trying to read a bunch more online:
* I tried starting it with measuring current across specifically the start and run windings. Start winding was ~5 amps, run winding was ~71 amps. I checked voltage at run winding (to common) during this, and it was at 105VAC, a ~12% drop, but also it's pulling 71 amps, so that's not too surprising.
* I pulled the cap off the wiring at the compressor to check resistance there. Start to common was 1.8O, run to common was 0.6O, start to run was 2.4O. So, right at the compressor, run to common seems pretty damn low... But still significantly more than the 0.0-0.1Ohm I'd expect to see for a true short.
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 07-01-2023, 21:12   #4
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Quote:
Originally Posted by pesarsten View Post
Are there any Schraeder valves on the refrigerant lines? I was wondering if you could get a drop of oil out so you can smell it and check if it's burnt?
I tried briefly pressing in on the schraeder valves, but just gas came out, no oil of any trace that I could check for an appreciable smell. Didn't want to keep pouring R-22 out so only did a couple brief taps on each of the two valves tho.
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 07-01-2023, 21:12   #5
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Tried one last thing also of reversing start and run leads at the compressor, which made a different humming sound but did not seem to dislodge it at all. That kinda points to pretty seized compressor, it seems like.
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 08-01-2023, 09:44   #6
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,517
Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

How do the other two read? Does that meter measure inductance? That goes down quickly with shorted winding.
team karst is offline   Reply With Quote
Old 08-01-2023, 09:57   #7
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Unfortunately my meter only reads resistance/voltage/current/capacitance/frequency.

What other two readings are you asking about to check?
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 08-01-2023, 11:35   #8
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,517
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

U mentioned three units total? A compare should be easy.
team karst is offline   Reply With Quote
Old 16-01-2023, 10:29   #9
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Been a super cold and also super busy week, so didn't get around to checking this until today when it finally warmed up on the holiday.

Interestingly, and surprisingly, the resistances on a working unit are right about the same -- 2.4/0.6/1.8. So it doesn't appear that the rotor has welded itself open/closed, it might just be physically stuck, not that that helps. But I tried running it again today and same result -- locked rotor hum, high current pull, and breaker blow.

Any other ideas anyone?
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 16-01-2023, 21:10   #10
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,559
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Quote:
Originally Posted by codingparadox View Post
Any other ideas anyone?
Perhaps have a tech hook-up the gages and also check the operation of the reversing valve.
__________________
Beginning to Prepare to Commence
Bowdrie is online now   Reply With Quote
Old 16-01-2023, 22:16   #11
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

The problem is that by the time I pay the fee for a tech to come out and look, when they're free 3 months from now, I'm a long way towards just buying a new unit. This unit can just be turned off forever and it will be a minor annoyance but only that. I'll just replace it all with a chiller unit sometime this year.
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 16-01-2023, 23:00   #12
Registered User

Join Date: Jan 2020
Location: EC
Boat: Cruising Catamaran
Posts: 1,239
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

I did not read all the stuff, but did you trying running it in cooling mode?
Tin Tin is offline   Reply With Quote
Old 16-01-2023, 23:37   #13
Registered User

Join Date: Jun 2020
Location: On Our Boat
Boat: Endeavour TrawlerCat 48
Posts: 210
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Yeah, it blows there too.
__________________
David and Hannah de Regt
2008 Endeavour TrawlerCat 48 - Gold Loopers, Now East Coast Cruisers - Blog: https://highwind.fun/
codingparadox is offline   Reply With Quote
Old 17-01-2023, 06:41   #14
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,559
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Quote:
Originally Posted by codingparadox View Post
The problem is that by the time I pay the fee for a tech to come out and look, when they're free 3 months from now, I'm a long way towards just buying a new unit.
Understandable.
__________________
Beginning to Prepare to Commence
Bowdrie is online now   Reply With Quote
Old 17-01-2023, 15:26   #15
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,517
Re: Cruisair Stowaway near LRA/RLA amps and popping breaker at startup

Well, there is definitely a way to stop the breaker from tripping!
team karst is offline   Reply With Quote
Reply

Tags
cruisair


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main breaker popping at 10A Korvessa Electrical: Batteries, Generators & Solar 26 21-02-2018 11:41
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
My 20 Amp Breaker Keeps Popping and Shutting Down Genset Turtlep Electrical: Batteries, Generators & Solar 4 26-07-2012 13:23
Cruisair Stowaway 7K BTU markpj23 Classifieds Archive 2 27-05-2009 05:27

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 09:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.