dometic air conditioner recharge guidance

I have a 11 year old VCD18k-hv-410a air conditioner that cools poorly.
The temperature differential between the return and supply is about
11 degrees F and the water flow is normal. Loss of performance
seems to be slow over time. All filters are clean
I plan on adding some 410A refrigerant to the low pressure line.
Dometic recommends vacuuming out all of the coolant, then fully recharging the system by weight (18oz). I don't have a vacuum pump, and thought
I would simply add very small amounts of coolant and monitor the return and supply temperatures, but I'm not sure what to use as a target temperature differential and don't want to risk overcharging the system. Any guidance on this? Is it possible to recharge a unit like this using a superheat or subcooling method?
marcz is offline   Reply With Quote
Old 03-08-2023, 09:48   #2
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,528
Re: dometic air conditioner recharge guidance

Quote:
Originally Posted by marcz View Post
Is it possible to recharge a unit like this using a superheat or subcooling method?
Not sure what you mean by a "subcooling" method of charging.
I believe that your unit is a "cap tube" system, as such there really isn't a "superheat" adjustment, that's for TXV valves.
Units that use cap-tubes are charge critical, and Dometic is correct.
For ~200 bucks or so, you can get a vacuum pump/gages/leak detector at Harbor Freight.
You'll want a pressure/temperature chart for the 410A refrigerant.
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Old 03-08-2023, 12:40   #3
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,528
Re: dometic air conditioner recharge guidance

Addendum; hook-up your gage set to both the high and low sides and confirm that there is pressure on both sides.
All the components in that system are silver brazed together, as such, unless there has been physical damage the chance of leaks are very small.
The device most likely to suffer a refrigerant leak is the condenser.
While the CuNi condenser is highly corrosion resistant it can develop a tiny leak between the water side and the refrigerant side, especially if any stray current is present.
With pressure in the system disconnect the water and drain the condenser, then with the detector you can find out if refrigerant is leaking thru the condenser.
Don't just automatically hook-up a vacuum pump at first, if there is a condenser leak the pump will try to suck water thru the leak and that is disaster for the system.
Of course you'll check everything else for any leaks also.
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Old 03-08-2023, 14:12   #4
Registered User

Join Date: Jan 2023
Posts: 1,711
Re: dometic air conditioner recharge guidance

Quote:
Originally Posted by Bowdrie View Post
Not sure what you mean by a "subcooling" method of charging.
I believe that your unit is a "cap tube" system, as such there really isn't a "superheat" adjustment, that's for TXV valves.
Units that use cap-tubes are charge critical, and Dometic is correct.
For ~200 bucks or so, you can get a vacuum pump/gages/leak detector at Harbor Freight.
You'll want a pressure/temperature chart for the 410A refrigerant.
I would be really surprised if an 18K air conditioner was a capillary tube unit. But it is possible, I guess... But IF it is, trying to add refrigerant to a cap unit by pressure rarely is successful.

In an AC unit one of the possible symptoms of low charge is icing on the evaporator. The lower pressure from the reduced gas quantity results in lower evaporator pressure, which leads to icing on the bottom of the evaporator, and no cooling from the top.

Arbitrarily adding refrigerant to a machine is not likely to end well. You can get a vacuum pump on Amazon for <$100. I would strongly suggest you go that route, or else hire someone who actually knows what they are doing.
SailingHarmonie is offline   Reply With Quote
Old 03-08-2023, 20:59   #5
Registered User

Join Date: Sep 2016
Posts: 4
Images: 1
Re: dometic air conditioner recharge guidance

Quote:
Originally Posted by SailingHarmonie View Post
I would be really surprised if an 18K air conditioner was a capillary tube unit. But it is possible, I guess... But IF it is, trying to add refrigerant to a cap unit by pressure rarely is successful.

In an AC unit one of the possible symptoms of low charge is icing on the evaporator. The lower pressure from the reduced gas quantity results in lower evaporator pressure, which leads to icing on the bottom of the evaporator, and no cooling from the top.

Arbitrarily adding refrigerant to a machine is not likely to end well. You can get a vacuum pump on Amazon for <$100. I would strongly suggest you go that route, or else hire someone who actually knows what they are doing.

SailingHarmonie and Bowdrie, thanks!
I know I'm over my head in this matter, but the service guy can't check out the boat for 2 months and it will be a moot point by then. I didn't think a trial of slowly adding a few ounces of refrigerant would likely cause a problem.
Yes, the evaporator does freeze, but it has done so for years and opening the cover
to the settee that the unit is installed in fixed that until recently. I had come to the
conclusion that the original installation was suboptimal and that airflow restriction was responsible for the evaporator icing. Likely it was. Until last year, I would measure a much greater differential between the return and supply air temperatures (Wish I had
recorded that data, but I did not).


With respect to leak testing, I'm not sure I understand the suggested testing method. Is it to operate the A/C for a period of time, turn it off, remove the water supply hose from the thruhull, drain the water, and then check for leaks? I did not think the compressor would run if the system does not have water flow....
marcz is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Dometic Turbo DTU 16,000 BTU 115V 60HZ HVAC Air Conditioner / Heater Boater3 General Classifieds (no boats) 7 26-07-2019 05:28
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 03-09-2012 05:41
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 23-08-2012 00:26
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 13-08-2012 04:28
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 14-07-2012 09:04

Advertise Here


All times are GMT -7. The time now is 04:14.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.