FYI: New Danfoss BD35/50 Control Module

Secop In their literature says their compressor is not cooled by return refrigerant but by oil.
However I can’t find a max temp allowed, I would think that would be a spec.
a64pilot is offline   Reply With Quote
Old 08-06-2018, 06:09   #77
cruiser

Join Date: Dec 2006
Posts: 405
Re: FYI: New Danfoss BD35/50 Control Module

Quote:
Originally Posted by a64pilot View Post
Secop In their literature says their compressor is not cooled by return refrigerant but by oil.
However I can’t find a max temp allowed, I would think that would be a spec.
That is not correct. Oil in the compressor plays a very minor role in cooling the compressor.

Like Missourisailor said earlier, the compressor is mostly cooled by refrigerant gas passing through. The cool but heat laden return gas (suction) enters the compressor cavity (like air into a 2 stroke petrol motor) and collects heat from the motor windings etc. This now hotter gas is pumped out of the compressor, carrying this heat along with heat collected from the evaporator, into the condenser where it is absorbed into the air or water.
As much as approx 20% of the heat the condenser disposes of, is heat from the compressor itself.

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems
OzePete is offline   Reply With Quote
Old 08-06-2018, 07:15   #78
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: FYI: New Danfoss BD35/50 Control Module

[QUOTE=missourisailor;2647388]
Quote:
Originally Posted by a64pilot View Post
... the condenser fan may help cool the compressor even if it is blowing heated air from the condenser, or maybe a compressor isn’t cooled by air very well, it’s not like it has cooling fins.
QUOTE]

The returning refrigerant plays a larger part in compressor cooling than air circulation. Hence, one of the reasons the return lines (low pressure lines) are insulated on almost every other system made...except marine refrigeration!
You are correct the general excepted rule for hermetically sealed electrical refrigeration compressors is, compressor cooling relies on sub cooled returning refrigerant and its flow. The job shop that designs and builds pleasure boat refrigeration is responsible for degree of compressor cooling. The recognized standard for returned cooling gas temperature is 60 degrees F although normal temperatures are slightly warmer than this.

These small compressors used in mobile marine refrigeration are each exposed to a number of temperature and installation applications where poor compressor cooling over time can destroy a complete system. The Italian refrigeration companies that use the Danfoss DB compressor use a small fan with heat sink attached to compressor for additional cooling. Adler Barbour, Isothern Nova Cold, Seafrost and others rely on condenser fan air to remove the mass metal heat of compressor. AC compressors ¼ HP and larger are available with an oil cooler coil inside compressor to assist in compressor heat removal.

It is the water cooled Danfoss BD compressor systems that are most likely to fail do to extended operation with compressor temperatures over 130 degree F. These are not mechanical failures they result from piston head gasket heat damage or oil heat contamination.

For those that say oil cools compressor, What do they say cools the oil? The maybe one drop of oil per minute returning with refrigerant gas vapor is not going to dispose of much heat.
Richard Kollmann is offline   Reply With Quote
Old 08-06-2018, 07:19   #79
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: FYI: New Danfoss BD35/50 Control Module

It apparently was Secop making that false claim, not a member here.
john61ct is offline   Reply With Quote
Old 10-06-2018, 07:47   #80
Registered User

Join Date: May 2008
Posts: 439
Re: FYI: New Danfoss BD35/50 Control Module

My old C-200 Cold Machine has the two control panels (?). The secondary one, shown at left, is giving me fits. Have to wiggle it and push on the components to get it to work and now has stopped altogether.
Have been advised to remove it and wire direct to the base panel at the right below but that appears to eliminate the power fuse and some resistors in the thermostat lines. Any advice on this process?
Does this new controller described above replace them both or the first one or the secondary one or.....??
Thanks!!
Attached Thumbnails
Click image for larger version

Name:	Bad Panel.jpg
Views:	265
Size:	428.5 KB
ID:	171394   Click image for larger version

Name:	Base Panel.jpg
Views:	123
Size:	401.5 KB
ID:	171395  

Flyingriki is offline   Reply With Quote
Old 10-06-2018, 08:20   #81
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,215
Re: FYI: New Danfoss BD35/50 Control Module

I would bet you have bad solder connections on the circuit board.
It's not rocket science to resolder them, but get someone who is good at it.
NO accidental solder bridges where they don't belong or you could kill it dead.
__________________
'You only live once, but if you do it right, once is enough.

Mae West
senormechanico is offline   Reply With Quote
Old 10-06-2018, 09:03   #82
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: FYI: New Danfoss BD35/50 Control Module

Quote:
Originally Posted by Flyingriki View Post
My old C-200 Cold Machine has the two control panels (?). The secondary one, shown at left, is giving me fits. Have to wiggle it and push on the components to get it to work and now has stopped altogether.
Have been advised to remove it and wire direct to the base panel at the right below but that appears to eliminate the power fuse and some resistors in the thermostat lines. Any advice on this process?
Does this new controller described above replace them both or the first one or the secondary one or.....??
Thanks!!
Klyingriki, From time to time we find design flaws in Pleasure boat refrigeration and attempt to notify the manufacture. Adler Barbour added an unnecessary circuit board to the CU model cold machines. There are three failures occurring with this printed circuit board; crack on copper ground, 15 amp fuse mounting and telephone thermostat jack. See TECH TIP #1 on my forum for information on by passing this circuit board and a picture of a failed board. If a replacement board is ordered it must be a improved structurally.


I represent no favored refrigeration company or job shop that assemblies Ice box conversion refrigeration. No one should infer I am referring to their product unless I mention the product by name.
Richard Kollmann is offline   Reply With Quote
Old 10-06-2018, 12:10   #83
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
FYI: New Danfoss BD35/50 Control Module

Quote:
Originally Posted by OzePete View Post
That is not correct. Oil in the compressor plays a very minor role in cooling the compressor.

Like Missourisailor said earlier, the compressor is mostly cooled by refrigerant gas passing through. The cool but heat laden return gas (suction) enters the compressor cavity (like air into a 2 stroke petrol motor) and collects heat from the motor windings etc. This now hotter gas is pumped out of the compressor, carrying this heat along with heat collected from the evaporator, into the condenser where it is absorbed into the air or water.
As much as approx 20% of the heat the condenser disposes of, is heat from the compressor itself.

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems


I understand how compressors are normally cooled, yet this is from Danfoss / Secop. How do you explain this?Click image for larger version

Name:	IMG_0383.jpg
Views:	209
Size:	188.3 KB
ID:	171415
Click on picture to expand it, read the explanation of why the outside of the compressor is hot.
a64pilot is offline   Reply With Quote
Old 10-06-2018, 12:59   #84
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: FYI: New Danfoss BD35/50 Control Module

Seems like a different oil system than the few drops in the coolant Richard was talking about?
john61ct is offline   Reply With Quote
Old 10-06-2018, 13:15   #85
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: FYI: New Danfoss BD35/50 Control Module

Quote:
Originally Posted by a64pilot View Post
I understand how compressors are normally cooled, yet this is from Danfoss / Secop. How do you explain this?Attachment 171415
Click on picture to expand it, read the explanation of why the outside of the compressor is hot.
The facts about a refrigeration system that differ from conventional systems are generally found on manufactures web site or in the installation and maintenance manual. There are links to this manual. Has anyone seen this manual?
Richard Kollmann is offline   Reply With Quote
Old 10-06-2018, 13:34   #86
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: FYI: New Danfoss BD35/50 Control Module

For someone who does not like Danfoss/Secop compressors because they are made in Chaina he spend time keeping the compressor he uses a secret.

If you are really interested in what true experts say about this type compressor cooling
https://www.achrnews.com/articles/10...ressor-cooling
Richard Kollmann is offline   Reply With Quote
Old 10-06-2018, 14:02   #87
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: FYI: New Danfoss BD35/50 Control Module

I did not detect any dislike of Danfoss in that line of questioning, and the "true experts" dig is childish at best.

I would personally like to know if their advertised internally circulating cooling-oil is a thing or not.

And if that issue makes a difference compared to the other three to four (?) major compressor brands out there.

Yes I agree it "would be nice" for every maker to be fully transparent about their design and components' sourcing, but I think it's their right to choose what to reveal or not as they see fit.

I was under the impression the only non-Chinese ones left were Italian owned by Webasto?
john61ct is offline   Reply With Quote
Old 10-06-2018, 14:36   #88
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
FYI: New Danfoss BD35/50 Control Module

I think the ones Cool Blue usually use are Spanish?
On edit, this is Cubigel I think in Barcelona
https://www.huayicompressor.es
There are I think several Chinese clones, the little icemakers and dorm fridges for example.
a64pilot is offline   Reply With Quote
Old 10-06-2018, 14:41   #89
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: FYI: New Danfoss BD35/50 Control Module

Seems odd Secop is either distributing false information, which is illogical, if they were hiding something, just keep quiet.
Their statement that they are a DC driven compressor, BD means battery driven by the way, and now they say the compressor is not cooled by return refrigerant, but by oil.
Meaning as I see it that the oil carries the heat to the case, where it’s cooled by air.

So either Secop is deliberately distributing false information, or they are a different animal so to speak, a different way to skin the cat.
a64pilot is offline   Reply With Quote
Old 10-06-2018, 14:45   #90
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
FYI: New Danfoss BD35/50 Control Module

Quote:
Originally Posted by john61ct View Post
I would personally like to know if their advertised internally circulating cooling-oil is a thing or not.
?

According to Richard’s link, it is. At least his link speaks to air cooled and the Secop verbiage said the oil carried the heat to the case, meaning in my opinion air cooled, oil is the medium by which the heat is transmitted to the case.
a64pilot is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Danfoss Electronic Module - Help Needed ericoh88 Plumbing Systems and Fixtures 53 14-04-2017 22:35
Troubleshooting a Danfoss BD35 Sonosailor Plumbing Systems and Fixtures 2 28-11-2015 12:23
Danfoss bd35 compressor economy mode Dod42 Electrical: Batteries, Generators & Solar 14 10-07-2014 06:18
Danfoss BD35/Frigoboat problem hoaga Plumbing Systems and Fixtures 87 27-02-2014 19:57
Danfoss BD35 Celestialsailor Plumbing Systems and Fixtures 2 24-11-2006 14:16

Advertise Here


All times are GMT -7. The time now is 11:18.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.