Re: I cut my fridge power by 75%. Really. No joke, no trick, no compromise.

Quote:
Originally Posted by FlyingScot View Post
The thin tubing is the high pressure liquid line (before expansion valve). The fatter tube is the low pressure liquid line (after expansion valve before evap plate).

Each evap plate has a line in and a line out. So if you see 3 lines, you need a 4th for the TXV sensing bulb. Real TXVs will have an additional line with a bulb attached to the outlet of evaporator plate, not leaving the box. This measures superheat (temp/pressure).

Sea Frost has other names for the valve, but they never use Thermal or TXV in the wording that I can find. They have a lot of documents on their website. Constant Pressure Valve is one of them you will see under the replacement parts section.
Please let us know what you find.
EDIT (complete delete of the post I just wrote....)
I thought there were 3 lines. Now, I'm not so sure. I need to go look at it again. Further, on re-reading the SeaFrost guidance that led me to making the adjustments I made, you are right -- they call it a "Constant Pressure Valve." In ways, it makes my changes make more sense, since it's not actually a TXV -- and if I was actually adjusting the low side pressure, it makes sense.



I need to go look at my system again.
sailingharry is offline   Reply With Quote
Old 25-04-2022, 19:19   #32
Registered User

Join Date: Nov 2015
Boat: R&C Leopard 40
Posts: 911
Re: I cut my fridge power by 75%. Really. No joke, no trick, no compromise.

Quote:
Originally Posted by sailingharry View Post
EDIT (complete delete of the post I just wrote....)
I thought there were 3 lines. Now, I'm not so sure. I need to go look at it again. Further, on re-reading the SeaFrost guidance that led me to making the adjustments I made, you are right -- they call it a "Constant Pressure Valve." In ways, it makes my changes make more sense, since it's not actually a TXV -- and if I was actually adjusting the low side pressure, it makes sense.



I need to go look at my system again.
Literally adjust low side pressure with that valve. It takes effect immediately too. I wish I could see my gauges from the valve location as it would have saved me a lot of running up and down.

Good luck.
__________________
-Chris
FlyingScot is offline   Reply With Quote
Old 26-04-2022, 04:45   #33
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,574
Re: I cut my fridge power by 75%. Really. No joke, no trick, no compromise.

It seems to me like that valve is basically an adjustable orifice / capillary tube. Might not be quite as good as a TXV, but when making changes to the system design it's definitely better than a fixed orifice.
rslifkin is offline   Reply With Quote
Old 27-04-2022, 18:49   #34
Registered User
 
sailingharry's Avatar

Join Date: Jun 2009
Location: Annapolis, MD
Boat: Sabre 34-1 (sold) and Saga 43
Posts: 2,388
Re: I cut my fridge power by 75%. Really. No joke, no trick, no compromise.

Mea Culpa

FlyingScot took issue with my understanding of the valve that I played with and discussed in my original post. He was right.

There are only 2 lines going to that valve -- high pressure, and low pressure. The third line, visible behind it, is the tie between two cold plates. With only 2 lines, it is impossible to be a TXV. It's just a set-able pressure relief valve.

Further, the behavior I witnessed is best explained by a pressure relief valve, and not a TXV. The TXV probably does NOT change the pressure (and boiling point) of the refrigerant -- as also pointed out by another poster upthread, it monitors superheat going into the compressor, another issue entirely.

The behavior and outcomes with the valve that I actually have match the explanation I was pontificating on. But the valve is most assuredly NOT a TXV as I initially thought.

I'm very content with the outcome of my fiddling. The temperatures and run times continue to be a huge improvement. But I am indebted to FlyingScot for accurately pointing out a significant error in my understanding of my system. In my days as a student at Navy Nuclear Power School, it would have been marked with a red "GCE" or Gross Conceptual Error.
sailingharry is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Island Packet 32 - Perfect Compromise? Dr. Moreau Monohull Sailboats 54 03-09-2018 19:12
To Cut or Not to Cut - Underseat Cabinets Jetexas Monohull Sailboats 9 25-02-2012 19:06
If I compromise will i ever know?! Thenaz007 Multihull Sailboats 140 29-08-2008 13:07
Do you compromise sailing enjoyment with a cat? isbolick Multihull Sailboats 22 21-07-2008 06:04

Advertise Here


All times are GMT -7. The time now is 04:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.