Old 12-05-2018, 05:19   #1
Registered User
 
Troutslayer's Avatar

Join Date: May 2018
Location: New Orleans, LA
Boat: Baba 35'
Posts: 15
Marine AC Sizing, Pump, Seacock Questions

Newbie here but longtime lurker. I am purchasing a 30' Allied Seawind Ketch and bringing her down to New Orleans from Maine. The heat is well, hot and the humidity here is brutal to yacht interiors so I am installing marine AC. I will preface by saying I believe in doing things the right way the first time in all cases.

I have been talking to manufacturers, using online calculators, etc and although I would like use a smaller unit it seems that 12-14k BTU is the smallest I can specify. I calculate about 920 cubic feet of interior space and am factoring 15btu per cu/ft. Any feedback on this would be greatly sppreciated!

The next problem is seacock sizing and seawater pump size. There is less information on the interwebs on how to get this right. Is a 250gph March pump an adequate choice?

On Seacocks I am going to use Groco BV series seacocks. I am manufacturing backing plates from G10 sheet bonded to the hull with bronze studs rather than going through the hull.

3/4" seems to be large enough but I read that a larger size will help reduce fouling from sealife. Should I go to a 1" BV-1000 and scoop intake? Will this affect pump priming (will be self priming)

On the discharge side is it OK to use a smaller 3/4" seacock? Can I plumb in a condensate discharge line with inline check valve?

And finally am I right going with real bronze or should I be looking at Maralon?

Many thanks for any feedback! I will document and share the project once I get started.
Troutslayer is offline   Reply With Quote
Old 12-05-2018, 05:34   #2
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Marine AC Sizing, Pump, Seacock Questions

Do NOT go smaller with an AC unit. Go with a 16K, also by far the most available, and common size
If it’s slightly oversized, well then you can enjoy it being on low fan and not having to listen to the thing so much.
These things depending on installation can be louder than house units.
Why go smaller, money saving is insignificant.
I bought a complete install kit from Defender, yes there were parts I didn’t need, but having the kit saved having to source little pieces that I may have forgotten if I didn’t have it, and I think I may have saved some money too.


I have never heard someone complain that their AC was too big, but I have seen many that cover windows, and wet the outside of the boat etc cause theirs isn’t quite as big as it should be.
a64pilot is offline   Reply With Quote
Old 12-05-2018, 06:19   #3
Marine Service Provider
 
rourkeh's Avatar

Join Date: Jun 2010
Location: Northern Caribbean
Boat: Cheoy Lee, 44 Cutter. Dolce Far Niente
Posts: 564
Re: Marine AC Sizing, Pump, Seacock Questions

I have lived in New Orleans so I understand the summer heat and crazy humidity
I would not even consider a unit less than 16,500 btu as you will be surprised at the amount of radiant heat your boat creates in direct sunlight. All the normal calculations for the number of btu you require are great if your boat is in the shade, and had any kind of insulating properties. I live in the Caribbean and run my A/C full time year round and have a lot of practical experience with installing A/C in my boat. I bought units from Flagship Marine in Florida and have run them non stop for years and have been very pleased with the simplicity and ease of repair. Their customer service is the best in the industry and replacement parts are cheap, probably 50% less than other manufacturers.. At some point you are going to need a new compressor or blower and you will be glad you did not buy marineair or wabasto, or similar. Also the unit comes with everything you need for the installation, sized correctly which makes it easy to install.. Try and make sure you have easy access to the sea strainer and through hull. And do your hose runs as short as possible. DO NOT use a pick up scoop on the outside of the hull.
rourkeh is offline   Reply With Quote
Old 12-05-2018, 06:26   #4
Registered User
 
Troutslayer's Avatar

Join Date: May 2018
Location: New Orleans, LA
Boat: Baba 35'
Posts: 15
Re: Marine AC Sizing, Pump, Seacock Questions

Ok, Thanks for the feedback everyone!
Troutslayer is offline   Reply With Quote
Old 12-05-2018, 08:20   #5
Registered User

Join Date: Jan 2011
Location: Montreal, Canada or St Maarten
Boat: Bavaria, 12.3m
Posts: 150
Send a message via Skype™ to Otia
Re: Marine AC Sizing, Pump, Seacock Questions

I guess it is a question of YMMV
I installed a Dometic 12k BTU on my 40ft boat last summer; I sail in the Antilles which is a more temperate climate than eastern US, max temperature here is 32C but the sun in intense. It cools the boat easily in the galley and v-berth. I did not run ducks to the aft cabin.
I used a 1/2 in seacock.
I wish my boat was made like an Amel, with one single seacock for all systems (engine, genset, a/c...)
Do plan a slowstart if you intend to use a/c with a genset.
__________________
Otia: Latin denominative plural for leisure, free time and peace
Otia is offline   Reply With Quote
Old 12-05-2018, 09:02   #6
Registered User

Cruisers Forum Supporter

Join Date: May 2011
Location: Miami Florida
Boat: Ellis Flybridge 28
Posts: 4,071
Re: Marine AC Sizing, Pump, Seacock Questions

I rarely disagree with A64Pilot, he is one smart dude. The problem is that if you go oversize with an air conditioner, it might not run long enough to remove the humidity before the temperature drops low enough to shut it off. My 28 Ft power boat did great with a 5K btu air conditioner. My gut feeling is that a 12K unit would be right for a 30 Ft sailboat. I’m sure there must be a company that specializes in marine refrigeration in New Orleans. Talk to them.

I don’t think you want to use an external scoop strainer on an AC intake. I recommend the Groco RSC series strainer to keep the big stuff out. It is a round strainer that is hinged so you can open it to clean out any growth inside.

Good choice on the seacocks. I suggest you just buy the matching Groco fiberglass backing plates. Much easier than making your own. By the time you pay for the G10, not much more expensive.

As to the pump, follow the AC manufactures recommendation. I think the Depco website has a table where you can figure out how much water you need for the btu of cooling.

The March pumps are excellent. I’m guessing you’re going to need the 500 gph pump, LC-3C-MD. It’s not self priming but I like to mount AC pumps below the waterline anyway.
__________________
Retired from Hopkins-Carter Marine Supplies
HopCar is offline   Reply With Quote
Old 12-05-2018, 09:28   #7
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Marine AC Sizing, Pump, Seacock Questions

I tend to agree with Hopcar. The AC needs to run long enough to pull the humidly out of the air. Too large a unit will short cycle on cooling and not do as good a job on reduction of humidity.

Also agree on a inline strainer. AC water inlets have a nasty habit of sucking "stuff" up into the line. An inside filter will be easier to clean.

As to water flow, allowing for additional compressor heat rejection on the condenser loop, A 12k btuh unit would need 3.2 gpm or 200 gph for a 10 degree F delta on discharge temp. A very common approach is to allow no more then 10 degree F rise on cooling water temperature on the condenser loop. I'm allowing for an additional 3000 btu's of heat rejection to account for compressor cooling (common on 200 to 2000 ton units scaled up of course.

Engineering Formula is GPM=BTUH/500/DeltaT rise.

Where GPM = gallons per minute
BTUH = British thermal units per hour
Delta T = difference between entering water temp and discharge water temp. For a condenser loop, conservative number is 10 degrees F.
500 = 60 minutes x 8.33 (weight of a gallon of water in pounds)

One Note: for areas with very hot sea surface water, over 80 degrees (say the forida keys), Use 5 or 7 degrees F Delta.

For a 18k btu, 4.2 gpm wound be the minimum. In either case, a 500 gph pump would be more then adequate for the dinky heat rejection.
sailorchic34 is offline   Reply With Quote
Old 12-05-2018, 10:18   #8
Registered User

Join Date: Jun 2012
Location: Port Aransas, Texas
Boat: 2019 Seawind 1160 Lite
Posts: 2,126
Re: Marine AC Sizing, Pump, Seacock Questions

Yep, my AC was oversized for the sleeping compartment and head at 8k BTU. It would get temp down to 65 deg. But then not run long enough to really get humidity and moisture level down. That's in Texas, and it gets hot here on southern coast. Don't oversize.
sailjumanji is offline   Reply With Quote
Old 12-05-2018, 10:20   #9
Registered User

Join Date: Feb 2010
Location: East shore Mobile Bay AL
Boat: ODAY 28
Posts: 425
Re: Marine AC Sizing, Pump, Seacock Questions

also agree with not over sizing unit,
boeing1 is offline   Reply With Quote
Old 12-05-2018, 10:53   #10
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Marine AC Sizing, Pump, Seacock Questions

We have an allied seawind II, so more volume than the original.

We installed a 5k btu unit, during the day it’s a great dehumidifier and keeps the cabin cooler than it would otherwise be. At night it is perfect.

Do not oversized the unit, it will short cycle and make the cabin cold and wet.

3/4” throughhull is fine for this, I would not install a scoop. The constant flow of water breeds sea life.

What are you hoping to accomplish with the AC? Comfortable sleep?
Ice box temps in the cabin in August?

I would also not recommend running it all the time. Use a dehumidifier for the times you’re not aboard. It’ll save the AC and you from constant line and strainer cleaning.
Sailmonkey is offline   Reply With Quote
Old 12-05-2018, 11:05   #11
Registered User
 
Troutslayer's Avatar

Join Date: May 2018
Location: New Orleans, LA
Boat: Baba 35'
Posts: 15
Re: Marine AC Sizing, Pump, Seacock Questions

Many thanks to everyone. Good to hear from someone with a Seawind also. I was afraid of oversizing as well as I have seen the effects of short cycling in homes with humidity problems. I am going to with a smaller unit and seacocks.
Troutslayer is offline   Reply With Quote
Old 12-05-2018, 12:11   #12
Registered User
 
OS2Dude's Avatar

Join Date: Nov 2014
Location: Atlanta, GA
Boat: Catalina 30
Posts: 692
Images: 5
Re: Marine AC Sizing, Pump, Seacock Questions

Too big is worse than too small. Too large will cycle really fast, aand besixes ot pullig the humidity out will harm the unit. That said, when we were sizing one for our 1985 Catalina 30 the best size would have been 20 BTU. The issue was they did not have a 20, just a 24 or 16. We wet with the 24 since it had dual fans.
OS2Dude is offline   Reply With Quote
Old 12-05-2018, 12:21   #13
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Marine AC Sizing, Pump, Seacock Questions

I have a 38’ Boat, with a 16K and a 6K.
For us it takes both in the heat of Summer to Cool the boat, and then it’s a just barely thing.
Boat came with one 16,and that didn’t cut it, worked great at night, but by 2 PM it was overwhelmed until after dark.

Then remember a boat AC fan runs continuously, as long as the evaporator is cold there is dehumidifying going on. I don’t think you will shock Cool a boat in the middle of Summer, no matter how big the AC, cause if you could, then all of us with proper sized ACs would have high humidity in the boat every night, when the heat loss is way less than half.


Plus he was saying he was going with a 12 or 14,a 16 is not all that much larger, and I bet on low fan with duct losses etc you would be doing very good to get 12K.
a64pilot is offline   Reply With Quote
Old 12-05-2018, 12:25   #14
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Marine AC Sizing, Pump, Seacock Questions

Oh and 12and 14 K but are not the smallest, I have a 6K Webasto in our forward Stateroom. I think that is about the smallest.
I treat the Webasto’s as throwaway systems, they are inexpensive enough and seem to last long enough so I don’t worry about replacing a compressor etc. I doubt that would make economic sense.
a64pilot is offline   Reply With Quote
Old 12-05-2018, 13:12   #15
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Marine AC Sizing, Pump, Seacock Questions

Quote:
Originally Posted by a64pilot View Post
Oh and 12and 14 K but are not the smallest, I have a 6K Webasto in our forward Stateroom. I think that is about the smallest.
I treat the Webasto’s as throwaway systems, they are inexpensive enough and seem to last long enough so I don’t worry about replacing a compressor etc. I doubt that would make economic sense.


Don’t forget the OP has a 30’ boat with a 9’ beam. Half the cockpit is long so the cabin is quite small.
Sailmonkey is offline   Reply With Quote
Reply

Tags
marine


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Freshwater Pressure Pump replacement sizing jasonquick Plumbing Systems and Fixtures 12 04-08-2016 08:38
Alternator sizing and water pump side loads? sailingca Electrical: Batteries, Generators & Solar 18 11-10-2015 21:50
For Sale: Groco SBV 1250 Marine Bronze Seacock (sells for over $320.00) jdecris Classifieds Archive 1 15-01-2013 05:05
Thru-Hull / Seacock Install Questions Skipjack20 Construction, Maintenance & Refit 10 12-08-2012 18:09
Unable to reach cruising speed- prop sizing questions Kindle Propellers & Drive Systems 28 10-04-2012 17:47

Advertise Here


All times are GMT -7. The time now is 15:14.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.