Something that has always confused me?
What is the proper abbreviation for Air Conditioner..... A/C or AC?
Also How does you abbreviate and differentiate it from Alternating Current......A/C or AC?
Pelagic is offline   Reply With Quote
Old 30-10-2019, 06:43   #32
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Newer technology A/C systems

Quote:
Originally Posted by Pelagic View Post
I have 1040 Ah batteries @ 24v + 1673w of Solar

Seems to me that with a large 24v house bank and sufficient Solar a 24v Air Con unit like this would make optimum use of Solar, when your SOC is at 100% by noon

In eco mode it would seem many could run it as it only draws 200W, I’m sure that doesn’t include the waterpump but that ought to pull about 60?
I’m eco it’s a 3900 BTU system, but that’s still pretty good.
Click image for larger version

Name:	IMG_0120.jpg
Views:	95
Size:	208.4 KB
ID:	202344
a64pilot is offline   Reply With Quote
Old 30-10-2019, 07:09   #33
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Newer technology A/C systems

Best to use "aircon" when there is any chance the context could also imply mains style AC power
john61ct is offline   Reply With Quote
Old 30-10-2019, 07:11   #34
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Newer technology A/C systems

Using stored battery power to run aircon off grid accomplishes little but timeshifting, at maybe 100Ah added capacity per hour's usage.

Might as well run the genset concurrently.

Thousands of kW solar panels won't fit on most boats.
john61ct is offline   Reply With Quote
Old 30-10-2019, 07:28   #35
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Newer technology A/C systems

Quote:
Originally Posted by john61ct View Post
Using stored battery power to run aircon off grid accomplishes little but timeshifting, at maybe 100Ah added capacity per hour's usage.

Might as well run the genset concurrently.

Thousands of kW solar panels won't fit on most boats.


Well go back and look at the posters bank and array size.
I believe he could do it easily, I believe in Summer I could do it with the machine in eco mode, it’s only 200W and 3900 BTU would go a long way toward cooling our stateroom. I have a 6000 BTU in there now and it pulls 4.5 amps or 540 Watts and that’s more than is realistic for my Solar, but theoretically possible. But 200W I could manage.
a64pilot is offline   Reply With Quote
Old 30-10-2019, 08:01   #36
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Newer technology A/C systems

The greater efficiency and variability certainly help, as does LFP

Details to account for:

feeding directly off "excess free" solar is a very limited time window

banks need to get recharged concurrent with feeding the aircon

actual total consumption is likely higher, solar production lower than in theory, in each direction, Ah per 24hrs is the key

IMO 1200W of extra panelage just for the aircon loads, and at least 100Ah of extra bank per hour of timeshifting desired

realistic minimums, ballpark

So, entirely do-able for some, but not inexpensive.

Personally, aircon is a luxury, I would rather do without, just don't need it living out on the hook.
john61ct is offline   Reply With Quote
Old 30-10-2019, 08:16   #37
Registered User

Join Date: Mar 2019
Posts: 80
Re: Newer technology A/C systems

"Personally, aircon is a luxury, I would rather do without, just don't need it living out on the hook."

Not sure where you are but here on the the Gulf coast of South East Texas in the summer months, aircon is definitely a necessity and not just a luxury.
TCM1968 is offline   Reply With Quote
Old 30-10-2019, 08:30   #38
Registered User

Join Date: Mar 2019
Posts: 80
Re: Newer technology A/C systems

Quote:
Originally Posted by a64pilot View Post
Well it is off the top 32% more efficient as it draws 1000W as opposed to my 1320W.
However it’s also variable speed so as long as 16k BTU isn’t needed it can slow down and use less power where a standard shuts down and uses none.
Motor wise it’s a BLDC and they are extremely long lived motors, I’d be interested to know if the fan slows down with the compressor too to reduce noise.
I also wonder can you manually set lower outputs or is that only automatic, it has an eco mode, but can you set higher manually as eco is very low power. Probably be good for night though.
It’s weak link is the electronics, but nearly everything has electronics now.
It’s also apparently twice as expensive

On edit looking at the spec sheet again, it’s efficiency gain at 16kBTU is slight, it pulls 10 amps to mine pulling 11 and on mine that includes the water pump. So it would seem it pulls less power only when the cooling capacity is reduced, or it’s very inefficient running wide open or both.

The difference your not considering with this comparison is the variable speed ability. Yes it may be true that when both are at max output of 16000 BTU's then the amp draw is close to the same, but 16K BTU is only needed to bring the temp from temp A to temp B. Once temp B is achieved a significant less amount of BTU's is required to maintain that temp. These motors are way more efficient at slower speeds. You can't look at it as a straight give and take. Lets say the variable speed slows down to 8000 BTU speed but now runs twice as long to maintain the desired temp, the KWh's used will not be the same. The variable speed compressor may only be putting out half the BTU's but it can do that at at considerably less than half the wattage.
TCM1968 is offline   Reply With Quote
Old 30-10-2019, 08:57   #39
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Newer technology A/C systems

I understand that, but it’s really not just the motors efficiency, it’s more likely from oversized evaporators and condensers for the btu output of the compressor.
With the BD refrigerator compressors the slower speed let’s them operate at a much higher COP, or coefficient of performance, I’, sure the same is true here, it’s a matter of scale.
But it’s also $3,000 per unit or twice the cost, and for many like me, to run the AC’s means running the generator and pulling 15 amps instead of 25 amps from the generator is irrelevant, and when running from shore power the power savings will likely never pay for it.

Now if the fan slows way down and becomes quiet in eco mode and especially if the fan turns off when the unit is off like it’s done in a house, well then maybe it’s worth it for other reasons.

Now so far as start up surge, it doesn’t reduce it like a slow start does, it simply has no start up surge, if the literature is to e believed and I think it’s true, it starts at 2 amps and then ramps up to whatever running amperage is needed, so no surge at all.

But surge isn’t a problem for me on generator or shore power, my Nexgen 3.5 gen has a 6KW gen head so the generator can easily supply the surge and apparently the flywheel momentum of the motor can supply it for a short while.

However if surge is a problem, then it may well be worth it, and it may well be worth it in a new install.
But to tear out good operating units and replace them at $3,000 a pop to solve a surge problem as opposed to installing slow starts, I’m not so sure that is worthwhile, unless as I said it’s a much quieter unit fan noise wise or other appealing reason, but of course that has a lot to do with how often you need AC and well frankly how much money you have to spend.
For me, when my current units wear out, I’ll take a hard look at these, they are I believe the future of air conditioning
a64pilot is offline   Reply With Quote
Old 30-10-2019, 09:20   #40
Registered User
 
ranger58sb's Avatar

Join Date: Aug 2012
Location: Maryland, USA
Boat: 58' Sedan Bridge
Posts: 5,540
Re: Newer technology A/C systems

Quote:
Originally Posted by TCM1968 View Post
Compressor motors can a do draw 7 to 10 times the running amp draw during start up. They want to be at full speed and torque the instant you apply power. A soft start device will control the voltage and amperage during start up so that it builds up to full speed and power gradually.

Now as far as the new systems my OP is referring to not only to they already have a soft start but they are variable speed. This means that instead of the compressor running at either off or full speed that once your room temperature is reached instead of turning off and allowing room temperature to rise a couple of degrees and then starting up again it just slows down the compressor to a speed require to maintain the temp where required. It uses considerably less energy to maintain that slower speed than to continually start and stop from from full speed.
Ah. Got it. Guess it's been a non-issue, for us; I don't really notice the small temp swings, and apparently we have energy to spare...


Quote:
Originally Posted by a64pilot View Post
Most every boat AC’s fan runs continuously, moving air continuously across the coils and through the filter, so most of those advantages are diluted some.
That's just a setting on ours: continuous, cycle with compressor, reverse force on heat vs. AC, etc. I usually vary the continuous/cycle setting depending on time of year...

-Chris
__________________
Chesapeake Bay, USA.
ranger58sb is offline   Reply With Quote
Old 30-10-2019, 09:26   #41
Registered User

Join Date: Mar 2019
Posts: 80
Re: Newer technology A/C systems

Quote:
Originally Posted by a64pilot View Post
I understand that, but it’s really not just the motors efficiency, it’s more likely from oversized evaporators and condensers for the btu output of the compressor.
With the BD refrigerator compressors the slower speed let’s them operate at a much higher COP, or coefficient of performance, I’, sure the same is true here, it’s a matter of scale.
But it’s also $3,000 per unit or twice the cost, and for many like me, to run the AC’s means running the generator and pulling 15 amps instead of 25 amps from the generator is irrelevant, and when running from shore power the power savings will likely never pay for it.

Now if the fan slows way down and becomes quiet in eco mode and especially if the fan turns off when the unit is off like it’s done in a house, well then maybe it’s worth it for other reasons.

Now so far as start up surge, it doesn’t reduce it like a slow start does, it simply has no start up surge, if the literature is to e believed and I think it’s true, it starts at 2 amps and then ramps up to whatever running amperage is needed, so no surge at all.

But surge isn’t a problem for me on generator or shore power, my Nexgen 3.5 gen has a 6KW gen head so the generator can easily supply the surge and apparently the flywheel momentum of the motor can supply it for a short while.

However if surge is a problem, then it may well be worth it, and it may well be worth it in a new install.
But to tear out good operating units and replace them at $3,000 a pop to solve a surge problem as opposed to installing slow starts, I’m not so sure that is worthwhile, unless as I said it’s a much quieter unit fan noise wise or other appealing reason, but of course that has a lot to do with how often you need AC and well frankly how much money you have to spend.
For me, when my current units wear out, I’ll take a hard look at these, they are I believe the future of air conditioning
Now I think we are on the same page I think this assessment is spot on. Surge is an issue for me as I have five 16K BTU units on my boat that at some times of the year need to all run at the same time and although possible on my current 100amp shore power pedestal not so much for my 12.5kw gen or most 50amp marina setups where a y-adapter is used. And I also agree not worth the cost if present units are all working fine, but I have 2 that need replaced before summer next year. It would also be nice if they are quieter. So a cheaper electric bill would be a nice bonus to offset the cost but that is not my main driving factor for considering these.
TCM1968 is offline   Reply With Quote
Old 30-10-2019, 09:26   #42
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Newer technology A/C systems

I wish my fan cut off with the compressor but it doesn’t, it runs continuously.
The reason for that is the same as a window unit AC, that is the air temp sensor is in the return air path, so to sense room air temp air flow is required.
A home AC of course has a remote mounted thermostat, if my Webasto’s had that, then the fan could turn off with the compressor.
It has a remote mounted control box of course. But I guess a remote temp sensor would have been another dollar or two.
Soft start wise, I bet there is less than $10 of electronics in one, I don’t know why it’s not a $100 option?
a64pilot is offline   Reply With Quote
Old 30-10-2019, 09:33   #43
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Newer technology A/C systems

Quote:
Originally Posted by TCM1968 View Post
Not sure where you are but here on the the Gulf coast of South East Texas in the summer months, aircon is definitely a necessity and not just a luxury.
Tens of thousands of years, billions and billions of humans say otherwise. Words really need to mean things.

You just have high expectations, habituation to a certain level of comfort and cheap access to unsustainable energy resources.

In my case, I prefer to acclimate my body to the heat, and have lived many decades without aircon in places where 35°C is a normal day, dozens of days in a row over 40 are common, including "concrete jungle" cities near the equator with millions of residents packed into a small area.

There is always the option of moving too.

Clean water is a necessity, but having large quantities of it available on tap inside your living space is a luxury.
john61ct is offline   Reply With Quote
Old 30-10-2019, 09:48   #44
Registered User

Join Date: Feb 2017
Location: Panama, Central America
Boat: CT 49, 1989
Posts: 969
Re: Newer technology A/C systems

Quote:
Originally Posted by john61ct View Post
The greater efficiency and variability certainly help, as does LFP

Details to account for:

feeding directly off "excess free" solar is a very limited time window

banks need to get recharged concurrent with feeding the aircon

actual total consumption is likely higher, solar production lower than in theory, in each direction, Ah per 24hrs is the key

IMO 1200W of extra panelage just for the aircon loads, and at least 100Ah of extra bank per hour of timeshifting desired

realistic minimums, ballpark

So, entirely do-able for some, but not inexpensive.

Personally, aircon is a luxury, I would rather do without, just don't need it living out on the hook.
As previously mentioned last time you said this, '1,000 W's' of solar arent required. This was true 10 years ago.
I posted some figures of currently running systems. Do you have any specifics you care to share?
The typical window or portables use in the magnitude of 8 times the power of some of the current generation units.
However these efficient units are not the cheaper ones, and mostly 230v not 110v.
The big efficiency gains are from as mentioned the compressor variable speed motors, and big condensors etc.
Time shifting, Im not sure what your point is? This is what battery banks do.
Running a generator, some of us would rather avoid it where possible. How to not be popular in the anchorage.
Q Xopa is offline   Reply With Quote
Old 30-10-2019, 09:51   #45
Registered User

Join Date: Dec 2009
Location: Port Arthur, TX
Boat: Beneteau 36cc - Pura Vida
Posts: 76
Re: Newer technology A/C systems

TCM. I hope you'll keep us informed of your progress, especially if you go ahead with the frigomar system. I've been watching it a while waiting for my current Dometic to die. I'd love to have a system I can run, dependably, with my honda 2000.
galynd is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Solar Cell technology!! shadow Flotsam & Sailing Miscellany 14 05-11-2008 15:12
New solar technology on the way NoTies Electrical: Batteries, Generators & Solar 14 07-04-2007 13:00
battery technology northerncat Electrical: Batteries, Generators & Solar 16 17-02-2007 11:17
Anchoring Technology - Yale Cordage GordMay Seamanship & Boat Handling 27 29-10-2005 16:00

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 15:28.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.