Refrigeration Troubleshooting

Here's the scenario: After having a suitable operating Technautics "Cool Blue" system for ten years, I found the need to replace the Compressor and associated modules as one unit (Danfloss w/fan, control module, etc.). This was a simple task requiring six connections (12VDC power +&-; thermostat +&-; and Aeroquip fittings for R134a to and from cold plate). Connections tested and secure,- coolant fully charged and not leaking; cold plate frosting and all apparently operating properly.

Here's the problem: The temperature remains suitable in the refrigeration section (ca 4cuft) vented from the freezer side (ca2cuft) as in the past. Most everything remains frozen in the freezer side; however, melt water does accumulate at the bottom of the box from added ice that partially melts)

Possible Solutions: 1- I'm sure I could alter and improve the the lid seal, but this remains the same as it was during the former good function of the freezer. 2- I'm considering that the insulation of the box has degraded due to water seeping from the box into the insulation. Access to the outside of the insulated box is very limited to check for temperature or condensation. I'm thinking of drilling a test hole to detect water and then plug and repair. 3- The newly replaced Technautics unit has a selection switch to control compressor speed that was not present on my older unit. I can increase the compressor speed and consume more amps that were formerly required. 4- My R134a volume is judged by looking for air bubbles in a sight glass which doesn't seem very accurate. Could I have too much or too little coolant. 5- I can't imagine any problems occurring on the cold plate side,- 'thermostat works, no leaks....

So, what are your thoughts? What other possibilities am I missing?
__________________
Take care and joy, Aythya crew
Hudson Force is offline   Reply With Quote
Old 04-01-2012, 13:34   #2
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Refrigeration Troubleshooting

Are you using the manual thermostats that comes with the unit or the optional elect tronic one? I have found it much easier to dial in the cold plate and the on/off range with the electronic one.
If you use the directions with the Coolblue the fill amount should be pretty accurate. Use a flashlight at an angle to get a good view of bubbles.
__________________
Paul
Paul L is offline   Reply With Quote
Old 04-01-2012, 13:45   #3
Moderator Emeritus
 
Hudson Force's Avatar

Cruisers Forum Supporter

Join Date: Nov 2008
Location: Lived aboard & cruised for 45 years,- now on a chair in my walk-in closet.
Boat: Morgan OI 413 1973 - Aythya
Posts: 8,481
Images: 1
Re: Refrigeration Troubleshooting

I do have the "manual" thermostat and was not aware of an option for an "electronic" thermostat. I have to admit that I don't understand the difference. I manually select the adjustment of my electrically connected thermostat. I'll need to look at the Technautics options. I don't have my manual with me, as I am away from my boat for this week, but I believe the directions stated that the R134a should be added to achieve "minimal" bubbles. Are you saying that the proper condition would be NO bubbles? Thanks for your reply.
__________________
Take care and joy, Aythya crew
Hudson Force is offline   Reply With Quote
Old 04-01-2012, 14:05   #4
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Refrigeration Troubleshooting

You fill till the bubbles stop, then wait something like 5 or 10 minutes and check for additional bubbles. Have measured the holding plate temp?
__________________
Paul
Paul L is offline   Reply With Quote
Old 04-01-2012, 18:31   #5
Moderator Emeritus
 
Hudson Force's Avatar

Cruisers Forum Supporter

Join Date: Nov 2008
Location: Lived aboard & cruised for 45 years,- now on a chair in my walk-in closet.
Boat: Morgan OI 413 1973 - Aythya
Posts: 8,481
Images: 1
Re: Refrigeration Troubleshooting

Quote:
Originally Posted by Paul L View Post
.......... Have measured the holding plate temp?
No I have not. Should a read the temperature from a frost removed area near the center of the cold plate? I also recall another complication to add to the mix. After installation I noticed the Schrader valve that is not the one designated for filling with the R134a had a minor leak. I poked at the center pin, with hope that it would seat properly, and tightened the brass cap. A soapy water spray indicated that it was not leaking. I do not know if this schrader valve leak was stopped at the valve or with the tightened cap. The cold plate is certainly below freezing due to it's frosted surface, but what temperature range should I expect?......and Paul, would you suggest that the final proper state would be infrequent small bubbles or absolutely no bubbles in the sight glass? Thanks...
__________________
Take care and joy, Aythya crew
Hudson Force is offline   Reply With Quote
Old 04-01-2012, 19:27   #6
Registered User

Join Date: Dec 2009
Posts: 2,959
Images: 4
Re: Refrigeration Troubleshooting

Check that the thermostat probe, if any, is attached the same as before. Mine goes to a clamp on the holding plate.

A few bubbles is okay. A sight glass is actually a fine way to judge the fill. The other is that after running for a while (normal temps and such) the frost line on the return tube should be somewhere after the holding plate, but before the compartment wall.
daddle is offline   Reply With Quote
Old 05-01-2012, 08:51   #7
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Refrigeration Troubleshooting

As said above, a few small bubbles os OK. You might call Tang at Technaitocs, he id Good at walking people through issues. There are small O ring gaskets in the Scchrader gable connections that cam get offset and damaged
I had a small that would leak out over 3 or 4 months. Replacing the O ring fixed it
My plate gets down to low double digits or bight single digits F.
__________________
Paul
Paul L is offline   Reply With Quote
Old 05-01-2012, 08:57   #8
Moderator Emeritus
 
Hudson Force's Avatar

Cruisers Forum Supporter

Join Date: Nov 2008
Location: Lived aboard & cruised for 45 years,- now on a chair in my walk-in closet.
Boat: Morgan OI 413 1973 - Aythya
Posts: 8,481
Images: 1
Re: Refrigeration Troubleshooting

Thanks for the ideas. This gives me some clear goals when I get back to my boat.
__________________
Take care and joy, Aythya crew
Hudson Force is offline   Reply With Quote
Old 06-01-2012, 15:11   #9
Registered User

Join Date: Dec 2011
Posts: 1
Re: Refrigeration Troubleshooting

Hi, I'm new to the forum and want to add my 2 pennies. When you were checking for bubbles in the sight glass was the compressor running on high speed? It not, run it on high speed and check the sight glass again, if you see lots of bubbles add refrigerant, if you don't see any bleed a little refrigerant out (slowly) until you see a few. You can fine tune the charge from there.

Good luck, Mike
Trish the Fish is offline   Reply With Quote
Old 06-01-2012, 15:24   #10
Moderator Emeritus
 
Hudson Force's Avatar

Cruisers Forum Supporter

Join Date: Nov 2008
Location: Lived aboard & cruised for 45 years,- now on a chair in my walk-in closet.
Boat: Morgan OI 413 1973 - Aythya
Posts: 8,481
Images: 1
Re: Refrigeration Troubleshooting

Quote:
Originally Posted by Trish the Fish View Post
............... When you were checking for bubbles in the sight glass was the compressor running on high speed? It not, run it on high speed and check the sight glass again, if you see lots of bubbles add refrigerant, if you don't see any bleed a little refrigerant out (slowly) until you see a few. You can fine tune the charge from there.

Good luck, Mike
I'm still not back to my boat to test these ideas, but "Trish the Fish" is confirming my earlier thought that too much refrigerant (no bubbles) can be a problem as well as too little (many bubbles). I had not considered that the view of the bubbles would be easier with the higher speed of the compressor. Maybe not "easier",- I'd assume the rate of flow would simply increase the number viewed over time. I'll be ready to test these ideas Sunday.
__________________
Take care and joy, Aythya crew
Hudson Force is offline   Reply With Quote
Old 06-01-2012, 16:08   #11
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Refrigeration Troubleshooting

On the Technautics I believe the flow control is done by the control value on the evaporator. This how it differs from tbr other vendors.
__________________
Paul
Paul L is offline   Reply With Quote
Old 05-07-2012, 14:42   #12
Registered User
 
sailalibi's Avatar

Join Date: Jul 2006
Location: Fla east coast/Bahamas
Boat: Schucker 436 motorsailor
Posts: 117
Re: Refrigeration Troubleshooting

I also have a cool blue with problems. My compressor runs all the time! It cools (and freezes stuff next to the holding plate) but I see NO bubbles in the sight glass. When I added 134a (about 1 can) still no bubbles but then I got 3 flashing led lights and a lout sounding compressor. I drained off some freon ant he flashing stopped as well as the noise but still no bubbles. Also when I push in the low side fill valve (shrader?) I hear no hissing. Any ideas?
sailalibi is offline   Reply With Quote
Old 06-07-2012, 04:36   #13
Marine Service Provider

Join Date: Aug 2004
Location: Ft. Lauderdale
Posts: 1,885
Re: Refrigeration Troubleshooting

Question: I drained off some Freon refrigerant the flashing stopped as well as the noise but still no bubbles. Also when I push in the low side fill valve (shrader?) I hear no hissing. Any ideas?

Yes, After sorting through several thousand emails and forum posts for my new forum the most expensive and extended boat refrigeration outages are caused by someone tampering with refrigerant. I just posted on my Forum sections on Too Much and Not Enough Refrigerant. Only one out of twenty so called service technicians know what they are doing on these small Danfoss compressor systems.

Depressing low pressure fill valve with compressor running is like shooting yourself in the foot as pain of no refrigeration may last throughout the cruising season. When someone says you need a new compressor 999 times they are wrong now the gun went off again and shot the other foot if compressor is replaced..

If you are positive compressor runs continuously problem of poor cooling is not electrical. On a Cool Blue a wide range of refrigerant volume is possible and still maintain good performance because of refrigerant receiver tank’s extra storage capacity. With a warm holding plate’s way oversized Thermo Expansion Valve (TEV) wide open to maximum flow large bubbles will be present in sight glass. When plate solution cools TEV will start reducing its orifice size and begin to reduce refrigerant flow. As refrigerant flow slows sight glass liquid will be more condensed with fewer and fewer bubbles. If compressor runs long enough plate solution will freeze hard like a rock and excessive liquid refrigerant will back up into receiver tank. It there is too much for receiver to hold excessive refrigerant will back up into condenser reducing systems overall performance. By tapping on froze plate with a large coin you can tell if plate is completely frozen. Now when condenser’s cooling medium’s air is warmest and plate is frozen will sight glass be completely clear. If condenser cooling air is cooler then small bubbles in glass will still indicate a correct charge.

There is a big difference in refrigerant charge volume between a TEV and a Capillary tube flow control device system that all other small refrigerators have. A Cool Blue unit can tolerate a variance of 3 to 5 ounces of refrigerant while ½ ounce change plus or minus will affect a Capillary tube system’s performance.
Richard Kollmann is offline   Reply With Quote
Old 06-07-2012, 05:23   #14
Registered User
 
Greggegner's Avatar

Join Date: Nov 2010
Posts: 406
My issue with cool blue was fixed when I got a programable thermostat and found the correct position for the thermocouple. It was to large in diameter to fix in the tube on the cold plate. If the plate is getting cold then the compressor is not the issue. Also make sure the box is not empty.
Greggegner is offline   Reply With Quote
Old 11-07-2012, 08:20   #15
Moderator Emeritus
 
Hudson Force's Avatar

Cruisers Forum Supporter

Join Date: Nov 2008
Location: Lived aboard & cruised for 45 years,- now on a chair in my walk-in closet.
Boat: Morgan OI 413 1973 - Aythya
Posts: 8,481
Images: 1
Re: Refrigeration Troubleshooting

'just a note for closure of my problem,- Technautics walked me through some diagnostics and then replaced my compressor unit under warranty. Now I'm back with a very cold, very quiet, and low amp use freezer/ refrig.
__________________
Take care and joy, Aythya crew
Hudson Force is offline   Reply With Quote
Reply

Tags
refrigeration


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help with Refrigeration Decisions . . . Beersmith Plumbing Systems and Fixtures 50 04-08-2023 15:53
For Sale: Drop-in 12vdc Refrigeration Unit aboutgone Classifieds Archive 3 18-11-2011 14:28
Refrigeration: 12vdc Holding Plate vs Evaporator malbert73 Electrical: Batteries, Generators & Solar 27 10-11-2011 10:03
Grunert Passagemaker Refrigeration Problem bstreep Construction, Maintenance & Refit 7 21-09-2011 17:56
Removing Engine Driven Refrigeration System cheoah Plumbing Systems and Fixtures 4 28-06-2011 20:37

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 07:14.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.