Old 17-04-2017, 07:29   #46
Registered User
 
jstevens's Avatar

Join Date: May 2006
Location: On board Sarah, currently lying in Jacksonville, FL
Boat: Pearson, 424, 42', Sarah
Posts: 674
Images: 4
Re: EU vs US electric

"Even rewiring the pedestal won't work. You just can't get 120V out of a single phase 240V supply just by swapping wires around."

I should have stopped writing before making that assertion. I assumed the power within the pedestal is 2-phase, just had a brain fart, forgetting with it would be 440VAC 2-phase. No way to get 120VAC out of that without some sort of a transformer.

John
jstevens is offline   Reply With Quote
Old 17-04-2017, 07:31   #47
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: EU vs US electric

Quote:
Originally Posted by carstenb View Post
Care to expand on this? Not sure why my boat would be wired for 15 amps? And if I plug into a 110 outlet, when this goes through my charger won't it be halved or more than halved to less than 15 amps
The normal EU boat is wired for 230v/16a. This means the shorepower cord needs to be protected with a 16a breaker at the pedestal. Downstream from the main breaker inside the boat, everything should be OK.
DotDun is offline   Reply With Quote
Old 17-04-2017, 07:36   #48
Moderator
 
carstenb's Avatar

Community Sponsor
Cruisers Forum Supporter

Join Date: May 2012
Location: At sea somewhere in the Caribbean
Boat: Jeanneau Sun Fast 40.3
Posts: 6,481
Images: 1
Re: EU vs US electric

Quote:
Originally Posted by DotDun View Post
The normal EU boat is wired for 230v/16a. This means the shorepower cord needs to be protected with a 16a breaker at the pedestal. Downstream from the main breaker inside the boat, everything should be OK.
Ok trying to un derstand (this is electricity for dummies).

So I buy a US plug and make an adapter wire with a US plug at one end and an EU at the other. But I have to intall a 16 amp fuse in this adapter wire somewhere.

Did I get that right?

carsten
__________________


https://www.amazon.co.uk/s?k=carsten...ref=nb_sb_noss

Our books have gotten 5 star reviews on Amazon. Several readers have written "I never thought I would go on a circumnavigation, but when I read these books, I was right there in the cockpit with Vinni and Carsten"
carstenb is offline   Reply With Quote
Old 17-04-2017, 07:37   #49
Registered User

Join Date: Jul 2012
Location: Switzerland
Boat: So many boats to choose from. Would prefer something that is not an AWB, and that is beachable...
Posts: 1,347
Re: EU vs US electric

Quote:
Originally Posted by jstevens View Post
I should have stopped writing before making that assertion. I assumed the power within the pedestal is 2-phase, just had a brain fart, forgetting with it would be 440VAC 2-phase.
No, in Europe you will not find 440VAC 2 phase anywhere. What you have is either 230V single phase, or 400V three phase...
K_V_B is offline   Reply With Quote
Old 17-04-2017, 07:53   #50
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: EU vs US electric

Quote:
Originally Posted by carstenb View Post
Ok trying to un derstand (this is electricity for dummies).

So I buy a US plug and make an adapter wire with a US plug at one end and an EU at the other. But I have to intall a 16 amp fuse in this adapter wire somewhere.

Did I get that right?

carsten
If you follow the "rules", yes the shorepower cord needs protected.

Technically, if nothing happens to the cord (i.e., gets chafed, cut, etc.) and assuming the main breaker inside the boat is 16a it will protect the cord by only allowing 16a to flow thru it.

I've seen a big variety of shorepower connections that were not exactly following the rules.
DotDun is offline   Reply With Quote
Old 17-04-2017, 08:09   #51
Registered User

Join Date: Apr 2012
Location: Currently in Spain
Boat: Island Packet 420
Posts: 419
Re: EU vs US electric

You need a transformer. I strongly suggest that you consult with a marine electrician before you do any of this. I worked with a marine electrical engineer who had sailed both US and Europe and lives in Europe for my setup. You cannot simply connect wires.
sailing_gal is offline   Reply With Quote
Old 17-04-2017, 08:10   #52
Moderator
 
carstenb's Avatar

Community Sponsor
Cruisers Forum Supporter

Join Date: May 2012
Location: At sea somewhere in the Caribbean
Boat: Jeanneau Sun Fast 40.3
Posts: 6,481
Images: 1
Re: EU vs US electric

Quote:
Originally Posted by DotDun View Post
If you follow the "rules", yes the shorepower cord needs protected.

Technically, if nothing happens to the cord (i.e., gets chafed, cut, etc.) and assuming the main breaker inside the boat is 16a it will protect the cord by only allowing 16a to flow thru it.

I've seen a big variety of shorepower connections that were not exactly following the rules.
well, so have I. I just don't want to fry my system.
__________________


https://www.amazon.co.uk/s?k=carsten...ref=nb_sb_noss

Our books have gotten 5 star reviews on Amazon. Several readers have written "I never thought I would go on a circumnavigation, but when I read these books, I was right there in the cockpit with Vinni and Carsten"
carstenb is offline   Reply With Quote
Old 17-04-2017, 08:33   #53
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,567
Re: EU vs US electric

Quote:
Originally Posted by DotDun View Post
If you follow the "rules", yes the shorepower cord needs protected.

Technically, if nothing happens to the cord (i.e., gets chafed, cut, etc.) and assuming the main breaker inside the boat is 16a it will protect the cord by only allowing 16a to flow thru it.

I've seen a big variety of shorepower connections that were not exactly following the rules.
I don't understand. The pedestal will have a breaker (30 amps in the U.S., usually).

Carsten's shore power inlet will have a breaker -- 16 amps, and probably an RCD.

What else is required?

I admit that I'm no longer much familiar with U.S. rules, so if there is something I'm not aware of, I will be grateful for the correction.
Dockhead is offline   Reply With Quote
Old 17-04-2017, 08:38   #54
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,567
Re: EU vs US electric

Quote:
Originally Posted by carstenb View Post
well, so have I. I just don't want to fry my system.
Your shore power cord, and your wiring between shore power inlet and main panel, may be rated to only 16 amps. I say "may be" because some French boats I've seen use the same wiring and sockets for both 230v and 110v boats.

If that's the case with your boat, then you do need to be sure that you won't put more than 16 amps through it. I would think that your main breaker/RCD will be enough.


Mine is 32 amps, by the way, but my whole shore power system is rated for 32 amps but only for the 16 amp blue plug on the end. If your main breaker, like mine, is 32 amps, then it is likely that your whole shore power system is good for 32 amps. Your boat manual may help you there, or just check the cross section of the wiring and the rating of the shore power inlet socket and plug.
Dockhead is offline   Reply With Quote
Old 17-04-2017, 09:02   #55
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: EU vs US electric

Quote:
Originally Posted by Dockhead View Post
I don't understand. The pedestal will have a breaker (30 amps in the U.S., usually).

Carsten's shore power inlet will have a breaker -- 16 amps, and probably an RCD.

What else is required?

I admit that I'm no longer much familiar with U.S. rules, so if there is something I'm not aware of, I will be grateful for the correction.
It's assumed that Carsten's shorepower cable is rated at 16a and plugged into a receptacle that has a 30a breaker. With the 16a RCD inside the boat, it would take a very rare fault to cause a problem. Personally, I would probably use it that way in a short term temporary situation, but I would not recommend it to others. Upgrading the wire size in the cord is the correct solution, assuming the physical connection part is handled via an adapter.

I was simply pointing out the discrepancy between the pedestal breaker size and the shorepower current carrying capacity. Per the rules, one should protect the wire with a breaker to match.
DotDun is offline   Reply With Quote
Old 17-04-2017, 09:09   #56
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,567
Re: EU vs US electric

Quote:
Originally Posted by DotDun View Post
It's assumed that Carsten's shorepower cable is rated at 16a and plugged into a receptacle that has a 30a breaker. With the 16a RCD inside the boat, it would take a very rare fault to cause a problem. Personally, I would probably use it that way in a short term temporary situation, but I would not recommend it to others. Upgrading the wire size in the cord is the correct solution, assuming the physical connection part is handled via an adapter.

I was simply pointing out the discrepancy between the pedestal breaker size and the shorepower current carrying capacity. Per the rules, one should protect the wire with a breaker to match.
Oh, I see. Thanks.

Note however that upgrading just the cable wouldn't be enough to fulfill this criterion -- the whole shore power system all the way to the 16 amp breaker on his panel would have to be rated 30 amps.

I would certainly not bother with it, myself.
Dockhead is offline   Reply With Quote
Old 17-04-2017, 10:10   #57
Moderator
 
carstenb's Avatar

Community Sponsor
Cruisers Forum Supporter

Join Date: May 2012
Location: At sea somewhere in the Caribbean
Boat: Jeanneau Sun Fast 40.3
Posts: 6,481
Images: 1
Re: EU vs US electric

I checked my Sterling charger manual - says it is good for 90-260V automatically - so I don't ahve to do anything there, also good for up to 60 amps so sounds like i'm ok there
__________________


https://www.amazon.co.uk/s?k=carsten...ref=nb_sb_noss

Our books have gotten 5 star reviews on Amazon. Several readers have written "I never thought I would go on a circumnavigation, but when I read these books, I was right there in the cockpit with Vinni and Carsten"
carstenb is offline   Reply With Quote
Old 17-04-2017, 10:19   #58
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,567
Re: EU vs US electric

Quote:
Originally Posted by carstenb View Post
I checked my Sterling charger manual - says it is good for 90-260V automatically - so I don't ahve to do anything there, also good for up to 60 amps so sounds like i'm ok there
60 amps is only 720 watts at 12v.

You can use a bigger inverter than that, but just keep in mind that you will be drawing down the batteries, if you use the inverter for long periods of time at max output.
Dockhead is offline   Reply With Quote
Old 17-04-2017, 10:53   #59
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: EU vs US electric

Quote:
Originally Posted by Dockhead View Post
Oh, I see. Thanks.

Note however that upgrading just the cable wouldn't be enough to fulfill this criterion -- the whole shore power system all the way to the 16 amp breaker on his panel would have to be rated 30 amps.

I would certainly not bother with it, myself.
Correct!
DotDun is offline   Reply With Quote
Old 20-04-2017, 06:38   #60
Registered User

Join Date: Sep 2016
Posts: 28
Re: EU vs US electric

Hi all,
I would set the boat up to be self sufficient. Install solar panels and don't hook up to any power. I have a lagoon 410 and have not had to hook up to shore power ever. If I go to a marina I don't bother to hook up, the solar takes care of the whole boat.
I hope this helps
dan swift is offline   Reply With Quote
Reply

Tags
electric


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: PAR Electric System Water Pump and JABSCO Electric Bilge Pump hanks Classifieds Archive 3 05-03-2014 19:03
For Sale: Electric Motors and hydraulic electric lifter arms 4 sale Sea Shoes Classifieds Archive 0 25-03-2012 07:46
The "Electric Wheel" ssullivan Engines and Propulsion Systems 3 06-04-2005 23:28
electric fence update tauras Health, Safety & Related Gear 12 22-03-2005 00:09
no electric water maker Jocelyne Plumbing Systems and Fixtures 1 28-10-2003 16:44

Advertise Here


All times are GMT -7. The time now is 00:57.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.