Refrigeration Problem

I have been fighting refrigeration problems for the last 4 years but this problem has me stumped. I have a separate freezer unit with two large holding plates run by a Danfoss compressor with a capillary tube. The plates run in series first to the plate with the capillary tube then out of the box to the plate on the other side of the box then back to the compressor (Normal). The unit was working properly with both plates frosting and the temp of the box freezing things properly. Then the first plate (the one with the capillary tube refused to frost up and went to box temp.. I assumed that I had too much Freon and over a couple of day reduce the charge until I was down to 2 psi and the second plate would not freeze. I was in the middle of nowhere so I increase the Freon to about 14 psi froze the second plate and a length of the return tube and reduced the box size This got me through the season. Now I am In the Rio Dulce try to figure it out. I checked and the plate is full of “antifreeze”. Does anyone have any subjection as to where I should go from here?
Some history the last thing done to this unit was the installation of a dryer, vacuumed and Freon. This was two weeks before the problem.
Steve
lions paw is offline   Reply With Quote
Old 22-05-2014, 08:30   #2
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,921
Re: Refrigeration Problem

Hola Lions Paw...
It could be helpful for us to know the system type, is it a home brew system or one from a manufacturer?

With two holding plates plumbed in series, the system "sees" the two plates as one big evaporator along with the copper tubing connecting the two plates. So it's odd to see them behaving differently. It the compressor is running, most of the time it boils down to a charge issue and from the data that your return tube is now frosty...it sounds like you are now over-charged. Does the manufacturer give any charge data at to the amount of refrigerant designed for the system?
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Old 22-05-2014, 08:40   #3
Registered User
 
Cavalier's Avatar

Join Date: Dec 2010
Location: Houston, TX
Boat: Beneteau 461 47'
Posts: 927
Images: 1
Re: Refrigeration Problem

Quote:
Originally Posted by lions paw View Post
Then the first plate (the one with the capillary tube refused to frost up and went to box temp.. I assumed that I had too much Freon and over a couple of day reduce the charge until I was down to 2 psi and the second plate would not freeze.
Some plates are designed with an inbuilt passive bypass. i.e. there'll be a very small diameter cavity that runs from the inlet to the outlet. Most of the time the majority of the coolant will evaporate throughout the main bore of the system. In the event that the main bore becomes blocked, or restricted etc. (due to internal corrosion or foreign particles), then the Freon will bypass most of the plate and transfer to the outlet at a much lower rate.

This may explain why your second plate still works (down to a low pressure) but the first plate in series has stopped functioning. If this is the case then you're unlikely to notice any change in the performance of the compressor, as the blockage would only have affected the

If you have a vacuum and Freon charging system available (sounds like it). You could consider removing the blocked plate from the system to see how well the second (functioning) plate works. Alternatively, you could remove the functioning plate and confirm that the first plate is blocked.
__________________
"By day the hot sun fermented us; and we were dizzied by the beating wind. At night we were stained by dew, and shamed into pettiness by the innumerable silences of stars."
Cavalier is offline   Reply With Quote
Old 22-05-2014, 09:07   #4
Marine Service Provider
 
SV THIRD DAY's Avatar

Cruisers Forum Supporter

Join Date: Aug 2006
Location: La Paz, Mexico
Boat: 1978 Hudson Force 50 Ketch
Posts: 3,921
Re: Refrigeration Problem

Quote:
Originally Posted by Cavalier View Post
Some plates are designed with an inbuilt passive bypass. i.e. there'll be a very small diameter cavity that runs from the inlet to the outlet. Most of the time the majority of the coolant will evaporate throughout the main bore of the system. In the event that the main bore becomes blocked, or restricted etc. (due to internal corrosion or foreign particles), then the Freon will bypass most of the plate and transfer to the outlet at a much lower rate. .
Cavalier's good point highlights the need to know what type of system you have so we can give the right advice.
__________________
Rich Boren
Cruise RO & Schenker Water Makers
Technautics CoolBlue Refrigeration
SV THIRD DAY is offline   Reply With Quote
Reply

Tags
refrigeration


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need help with odd refrigeration problem brankin Electrical: Batteries, Generators & Solar 8 14-07-2013 22:18
Refrigeration problem sneuman Construction, Maintenance & Refit 0 16-10-2012 11:57
Xantrex Monitor Problem OR Battery bank problem? svstrider Electrical: Batteries, Generators & Solar 4 26-12-2011 20:08
Battery-Charging Regulator Problem ? MasterVolt Problem ? RJV Electrical: Batteries, Generators & Solar 18 06-11-2011 22:53
Grunert Passagemaker Refrigeration Problem bstreep Construction, Maintenance & Refit 7 21-09-2011 17:56

Advertise Here


All times are GMT -7. The time now is 04:43.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.