Old 16-08-2017, 01:47   #16
Registered User

Join Date: Sep 2016
Posts: 503
Re: Sizing the right air conditioner for your boat

Quote:
Originally Posted by CaptainJohn49 View Post
Great topic. I have a boat and an RV. The boat has no air but I'm interested. The RV I just removed the Coleman AC and replaced it with an AirCommand made in Australia and rated at 15,000 BTU's. I found both the Coleman 13,500 BTU unit and the AirCommand 15,000 BTU unit just reduced the temperature by a certain amount on the inside from what it was outside. The drop seems to be 12-15 degrees difference. So the point is, if it's 80 outside I can get it 70 inside no problem, if it's 90 outside it's 76 inside, if it's 100 outside then it's 84 inside. So what?

Well my point is that 15,000 BTU's is the max my generator can handle. I think you should be looking at the power you are willing to devote to the AC then figure if you are happy with a certain temperature drop from that setup. I know that I'm happy with 12-15 degree difference. Sure sometimes it's a little hotter than I like but it's still a big improvement. A larger AC unit means a larger generator, more fuel and larger wiring.

Maybe next year I'll look at AC for my boat.

Hope this helps
John
If I can get 80 when its 95 outside it would be very good, certainly more than good enough, I suspect a boat will not be as well insulated as an RV, but yeah, I will size it according to generator and see how it went.
Wckoek is offline   Reply With Quote
Old 16-08-2017, 02:37   #17
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,865
Images: 241
Re: Sizing the right air conditioner for your boat

Quote:
Originally Posted by Outlaw7 View Post
Take the cubic footage of the area you want to cool and multiply it by a factor of 14 if below decks and use 16 for above decks. Then add 200 BTU for every square foot of non vertical windows like a catamaran. If you have shades or tinted windows you may not have to account for the windows.
A rough "rule of thumb" for sizing marine air-conditioning (for use in sub-tropics) is between 14 (below decks) to 17 (above decks, glazed) BTU/H for each cubic foot of interior conditioned volume.

A (theoretically) perfectly-sized air conditioner will run continuously during the hottest 2.5% summer design (outdoor) temperatures.

Don't buy an oversized unit. An over-sized unit short-cycles (turns on & off too rapidly), so doesn’t properly de-humidify*, and uses more energy (starting currents).

Make sure any ducting and grillework is sized large enough to allow low-velocity air distribution.

http://www.cruisersforum.com/forums/...vac-37878.html
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 16-08-2017, 04:43   #18
Registered User

Join Date: Dec 2010
Location: W Carib
Boat: Wildcat 35, Hobie 33
Posts: 13,488
Re: Sizing the right air conditioner for your boat

Quote:
Originally Posted by thinwater View Post
Not really.

Variables include:
  • location
  • deck and topsides core construction
  • liner
  • window area
  • use of awnings and window covers to reduce solar gain
  • how quickly you want to cool
The down sides of over-size include:
  • additional electrical installation cost
  • power problems in some marinas
  • noise
  • poor humidification performance (cycles are too short)
Also...

Cat or Mono?

The big deck houses of cats can be a challenge to keep cool. Degree of challenge also depends on deckhouse window design. Similar challenge for pilot house/deck salon mono I expect.

Another consideration on cats is two hulls and widely separated cabin spaces. Getting air to all these spaces can be a big challenge. Depending on boat details, it may easier and cheaper to run coolant lines to radiators in each cabin rather than trying to route air around the constricted spaces of the hulls. Some opt to just put an AC unit in each cabin to avoid this problem.
belizesailor is offline   Reply With Quote
Old 16-08-2017, 04:53   #19
Registered User
 
TacomaSailor's Avatar

Join Date: Nov 2012
Location: Punta Gorda Isles, SW Florida
Boat: Caliber 40
Posts: 1,160
Re: Sizing the right air conditioner for your boat

Just did this exercise and not pleased with results!

Caliber 40 Sailboat
Interior space to cool is 25' long and an average of 11' wide with a ceiling height of 6' 7" (275 sq feet). There is one bulkhead that separates the galley/main salon from the forward sleeping area/head.

Boat is in SW Florida where water temperature is currently 88 degrees F. The daily temperature varies from 77 degrees F at 6 AM to 93 F from noon till 4 PM.

Prior to installing the A/C the boat interior was always above 90 F from mid-morning till late in the evening.

Installed a Haier 14,000 BTU portable A/C with a dual hose intake/exhaust system. A pair of 12V 6" fans run 100% of the time in the nav station and in the passage way to the forward compartment. There is also a Nicro solar powered 5" exhaust fan in the forward shower. There is great airflow thru the boat.

The boat interior is 87 F all day long with the A/C running continuously (9.5 Amps/120V) but the relative humidity is down to 55% rather than 80% without the A/C.

I calculated that there was 43,000 BTU/Hour heat gain thru the ceiling due to the direct sunlight on the boat deck. The main salon ceiling was always warmer than 98 F between 11 AM and 5 PM.

I mounted our full boat Sunbrella awning to eliminate 90% of the sun ondeck. The A/C can now keep the boat interior at 81 degrees F at all times but has to run 100% of the time from 10 AM until 6 PM. The runtime drops to 60% between midnight and 7 AM.

The boat interior is pleasant at 81 degrees F, probably because of the significant decrease in relative humidity.

I did not expect to have to run the A/C 20 hours a day in order to have a 81 degree F boat interior. Nor did I expect to run two big fans 100% of the time.

But, I am a Seattle native where 70 degrees is HOT and 80 degrees is noteworthy.
TacomaSailor is offline   Reply With Quote
Old 16-08-2017, 05:52   #20
Marine Service Provider
 
witzgall's Avatar

Join Date: Oct 2006
Location: Eastern Shore, MD
Boat: Camper Nicholson 44 Ketch
Posts: 2,060
Re: Sizing the right air conditioner for your boat

One item often overlooked when sizing ac/hat for a boat is the length and location of duct runs. If you have a 12k btu unit, you will not actually see all 12k in cooling, as there are losses, one of which is in the ducting. Simply put, you want to make the ducting runs as short, and as un-complicated as possible. If you very short (We have one with seven inches) you end up with significantly more noise, but high efficiency. You also run the risk of unbalanced air pressures, which can effect cooling ability negatively.

Chris
witzgall is offline   Reply With Quote
Old 16-08-2017, 06:15   #21
Registered User

Join Date: Dec 2015
Location: Fort Pierce Fl
Boat: Gulfstar 36 MS
Posts: 211
Re: Sizing the right air conditioner for your boat

The post on ductwork brings up another can of worms that goes well beyond sizing the unit. Static air pressure in ducting is a whole other science. Bad ducting can cause inefficiency and on the other end of the spectrum freeze ups.
Outlaw7 is offline   Reply With Quote
Old 16-08-2017, 06:36   #22
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Sizing the right air conditioner for your boat

Additionally, ducting can consume a lot of valuable storage space.

For any given size, 6' of duct =~ size of AC unit.

For a <35' mono, 2 x 5K BTU/Hr units can fit the bill. For <40', 2x8K, for <45', 3 x 8K, for < 50', 3x 12K.

This also allows flexibility for temp vs power available. If it's warm and only 30A available, run 12K or less. If hot and lots of power available, run everything flat out.

If one installs a 16K unit, they pretty much need a dedicated 30A connection just for Air Con.

Multiple units also allows redundancy when a unit fails.
ramblinrod is offline   Reply With Quote
Old 16-08-2017, 06:43   #23
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Sizing the right air conditioner for your boat

Quote:
Originally Posted by ramblinrod View Post

If one installs a 16K unit, they pretty much need a dedicated 30A connection just for Air Con.
Amen that was mentioned.....around here the sheer number of boats with a 16k unit, water heater, charger, outlets, etc...on a single 30A cord is amazing. They'll load these cords right up to 30 amps and wonder why they end up with melted/burnt ends!!

a 30A cord with a common twistlock connector is good for roughly 20A continous.
Sailmonkey is offline   Reply With Quote
Old 16-08-2017, 07:13   #24
Registered User

Join Date: Sep 2016
Posts: 503
Re: Sizing the right air conditioner for your boat

Quote:
Originally Posted by ramblinrod View Post
Additionally, ducting can consume a lot of valuable storage space.

For any given size, 6' of duct =~ size of AC unit.

For a <35' mono, 2 x 5K BTU/Hr units can fit the bill. For <40', 2x8K, for <45', 3 x 8K, for < 50', 3x 12K.

This also allows flexibility for temp vs power available. If it's warm and only 30A available, run 12K or less. If hot and lots of power available, run everything flat out.

If one installs a 16K unit, they pretty much need a dedicated 30A connection just for Air Con.

Multiple units also allows redundancy when a unit fails.
Good suggestion, or I can run a 6k for cabin and 10k for salon.
Easier to control usage too.
Wckoek is offline   Reply With Quote
Old 16-08-2017, 08:02   #25
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,788
Re: Sizing the right air conditioner for your boat

Quote:
Originally Posted by Wckoek View Post
The figure are still plenty high and use a lot more energy than I like.
I think I would have it configure in a way that is cold for the stateroom and merely enough for the saloon.

Remember that the load is MUCH lower at night. You also don't use the staterooms during the day. I think you will find that if you cool the salon during the day, cooling the staterooms once the sun goes down will be easy.
__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is online now   Reply With Quote
Old 17-08-2017, 07:50   #26
Registered User
 
SV Bacchus's Avatar

Join Date: Apr 2016
Location: Back on dirt in Florida
Boat: Currently in between
Posts: 1,338
Re: Sizing the right air conditioner for your boat

Forgot to mention earlier that I am sitting in a 36' 5th wheel RV about an hour north of Tampa. Been living here for 2 weeks now, since selling the house, while the contract on our new to us boat goes through all the steps.

Not a direct comparison as the RV has good insulation, not great but good, all the way around and double paned windows. It is 10:45AM and already 91, projected to go to 94 degrees today. Been pretty much the same all week.

The RV has the typical roof top A/C units but they are ducted. The front unit is the smaller and is 13K and ducted 1/2 way toward the back of the unit. The rear unit is larger at 16K and ducted running 1/2 way toward the front of the unit. Suffice to say the A/C units are sized by the factory and fairly well installed (duct work, not on every RV!).

I have them both set for approximately 84 degrees, best I can tell with the older, mercury bulb style slider thermostats. From about 10AM to 5:30 or 6PM They never shut off!
__________________
SV Bacchus - Living the good life!
SV Bacchus is offline   Reply With Quote
Old 17-08-2017, 10:25   #27
Registered User

Join Date: Sep 2016
Posts: 503
Re: Sizing the right air conditioner for your boat

I can only hope I can have as much power and good insulation in my boat.
Wckoek is offline   Reply With Quote
Old 17-08-2017, 17:55   #28
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Sizing the right air conditioner for your boat

I installed two AC's in my 38' IP. A 16K in the Salon and a 6K in the fwd Stateroom, I had no shade tent.
It takes all of both AC's running now in S Fl to keep the boat cool.
Both together pull 21 AC amps. You cannot run both AC's and the 1500 W water heater, but if it's Africa hot, we don't need hot water.
You do have to power manage things with a 30 amp boat.
Boat came with one 16K AC, and that just didn't cool it.

I say oversize a little, you don't have to run them on high, ideal is to have them work with the fans on low speed as they make a lot less noise that way.
Running them on high doesn't seem to really add much cooling, it only speeds up the fan not the compressor
a64pilot is offline   Reply With Quote
Reply

Tags
boat


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Marine Air Cabin Mate 16000btu air Conditioner formrteki Classifieds Archive 3 01-10-2012 08:52
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 03-09-2012 05:41
For Sale: Cruise Air Split Type Air Conditioner loowigi Classifieds Archive 1 23-08-2012 00:26
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 13-08-2012 04:28
For Sale: Cruise air split type air conditioner loowigi Classifieds Archive 2 14-07-2012 09:04

Advertise Here


All times are GMT -7. The time now is 07:27.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.