Re: 1/0 wire

If a 1/0 cable became loose it would probably start a fire before it came off altogether. The fears about doubling cables are not born out by real life examples.

Paralleling cable of equal length is an acceptable practice. Make sure to terminate them correctly and secure the lugs properly. If you can properly crimp AWG 4 cable but not 1/0 then better to go with parallel smaller cables. Don't use the hammer crimpers.

It is not a good idea to put 2 wires into one crimp lug. The crimp lug probably will not crimp right as it is designed for a circular bundle of wires. Better to use the correct size lug on each wire IMO.
transmitterdan is offline   Reply With Quote
Old 09-02-2017, 22:52   #17
Registered User

Join Date: Jul 2016
Location: Anguilla
Boat: CheoyLee Offshore 33
Posts: 644
Images: 1
Send a message via Skype™ to masonc
Re: 1/0 wire

Quote:
Originally Posted by pcmm View Post
This is done all the time. I just finished doing a tour of a large data center (their generators are powered by V 16 diesels! ) and all 8 of their starter circuits are wired this way, but with 4/0 AWG cables. the stuff is just massive ( yeah I'm a nerd and notice that kind of stuff!!)
For clarity, although I'm reminded the National Electrical Code does not apply to boats, paralleled cabling is not just done all the time, there is no other way to wire large current applications. We commonly run 4 x 500mcm per phase. You can't easily bend cables above 750mcm, even with hydraulic bending and they wouldn't go through conduit.
However, code requires the smallest allowable parallel conductor set to be 1/0.
masonc is offline   Reply With Quote
Old 10-02-2017, 01:26   #18
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,137
Re: 1/0 wire

Quote:
Originally Posted by DotDun View Post
The REAL answer is YES! It's done generally to increase current carrying capacity of a circuit.

Without more information, one has to assume that 1/0 is what the application requires (~285a). (2) 4awg in parallel will yield ~320a. With that said, most would opt for the 1/0 cable due to ease of installation/management.

But contrary to what's been stated, there is nothing unsafe, temporary, or wrong about paralleling cables to gain ampacity.
Dot Dun and others who are happy with the practice of paralleling cable to gain ampacity, please consider some sample circuits below.

For this exercise, the load draws 30 amps when active. Cct A is safe, cct B is safe unless one cable goes open circuit, then it becomes very unsafe.

If the load is inactive (turned off) and low resistance fault develops on one cable as in cct C, the circuit is safe, the cables can carry the fault current until the breaker trips. But should a similar low resistance fault occur as in cct D, then the arrangement in unsafe, the single conductor will in likelihood fail (burn) before the breaker trips.

Now these are only sample circuits but they demonstrate why twin smaller conductors can't be considered safe in some scenarios.

To repeat an earlier post, it boils down to risk assessment and risk management.
Would I use parallel cables - yes in some circumstance and no in others.
Attached Files
File Type: pdf cct.pdf (222.8 KB, 56 views)
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 10-02-2017, 05:22   #19
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: 1/0 wire

I think cct D is unlikely to happen if the termination is good. However we are not taking about paralleling AWG 14 wire but AWG 4 wire. I think that makes the probability of a cct D scenario virtually nil. And the scenario ignores how cct D came to be in that state. One wire somehow worked itself loose and came all the way off but did not magically start a fire in the process.

Who has a real world documented example of paralleling larger wires that came to a bad end? Could that same thing happen on a boat?

If in doubt then it would be ok to parallel extra third wire for added redundancy.
transmitterdan is offline   Reply With Quote
Old 10-02-2017, 06:00   #20
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: 1/0 wire

Quote:
Originally Posted by smac999 View Post
as already mentioned there are reasons not too. if one cable breaks, or say is left disconnected by mistake. you'll now have 300a going through a single 4awg. and nobody would ever know or relize untill it burns. where as if the 1/0 comes off it won't work and you'd notice right away.
So, what is your recommendation for an application that requires more than 445a that the largest cable available (4/0) can deliver? Do your concerns disappear?

Like I stated, paralleling cables require extra 'management', your imagined concerns fall into that realm and must be dealt with.
DotDun is offline   Reply With Quote
Old 21-05-2017, 06:10   #21
Registered User
 
double u's Avatar

Join Date: Feb 2016
Location: forest city
Boat: no boat any more
Posts: 2,511
Re: 1/0 wire

"... if one cable breaks... you'll now have 300a going through a single 4awg. and nobody would ever know or relize untill it burns."

if this logic were true then one shouldn't have ANY wires at all on the boat: they might get chafed through halfway & now you have...
__________________
...not all who wander are lost!
double u is offline   Reply With Quote
Old 21-05-2017, 06:20   #22
Registered User
 
jonasaberg's Avatar

Join Date: Jul 2008
Location: Kristiansand, Norway
Boat: Wasa 410
Posts: 309
Re: 1/0 wire

I did not find this thread earlier today and started a new one where I got to know about this earlier thread.

I wrote a quick summary, and for those interested it is found here:
http://www.cruisersforum.com/forums/...ml#post2397121
jonasaberg is offline   Reply With Quote
Old 21-05-2017, 17:31   #23
Registered User
 
Leakie Marine's Avatar

Join Date: Jun 2014
Location: Melbourne, Australia
Boat: Beneteau First 45F5, Adams 12
Posts: 39
Re: 1/0 wire

If you are working with AC then doubling would help take advantage of skin effect because you have more surface area where the current tends to flow. I would still make sure the single conductor was capable of carrying the rating of the breaker.

https://en.wikipedia.org/wiki/Skin_effect
Leakie Marine is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
wire rigging dyform, compact wire, rod RDW Deck hardware: Rigging, Sails & Hoisting 4 12-11-2014 02:51
What's the Best Way to Connect a 4mm Wire to the Middle of a 6mm Wire? mischief Electrical: Batteries, Generators & Solar 11 07-11-2013 09:31
New wire being made 5 foot battery wire to terminal strip sdowney717 Electrical: Batteries, Generators & Solar 3 20-08-2012 08:27
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 12:47

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 19:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.