Originally Posted by cfarrar View Post
As I understand it, if you connect your panels to the battery bus terminal posts, then there's no need to connect your battery monitor to the panels themselves. Your battery monitor should continue to operate as before. While the panels are providing charge, the battery monitor will display the resulting voltage and current flow into the batteries. That's what my monitor does.
Actually, with the panels connected directly to the battery terminals, the monitor will not display the panel charging output.

The battery monitor usually has a shunt resistor between the house ground point and the battery negative terminal, and this is how the battery current is measured. You should connect all loads and charging sources to the house ground, not to the battery negative terminal post. Some people argue that the SSB radio (if you have one) should connect directly to the batteries, but if this is done the radio may work better but the radio's current drain will not be monitored.

MPPT controllers do work, but if you have more money to spend you should first get all the panels you can afford (or can find a place for) and use a cheap controller. Then, if you still need more juice the MPPT controller may be a good upgrade.
__________________
Paul Elliott, S/V VALIS - Pacific Seacraft 44 #16 - Friday Harbor, WA
www.sailvalis.com
Paul Elliott is offline   Reply With Quote
Old 24-09-2010, 18:00   #17
Registered User
 
cfarrar's Avatar

Join Date: Apr 2008
Location: Brooklin, Maine U.S.A
Boat: Allures 44
Posts: 734
Images: 2
Quote:
You should connect all loads and charging sources to the house ground, not to the battery negative terminal post.
Sorry, poor word choice on my part. When I wrote "battery bus terminal post," I meant "battery bus power post." Ie, the DC positive post behind your electrical panel to which your battery cable(s) are attached, not the batteries themselves. The point is that you want the solar charger output charging all your batts even when the house battery selector switch is in the "off" position. As Paul writes, the charger's negative output goes to the house ground, which is probably the only large DC negative post in the panel.

To me the MMPT is a no brainer - it's no more expensive than the wattage equivalent of another solar panel, and it takes up zero space on top of my bimini.
cfarrar is offline   Reply With Quote
Old 24-09-2010, 18:13   #18
Moderator Emeritus
 
Paul Elliott's Avatar

Cruisers Forum Supporter

Join Date: Sep 2006
Posts: 4,663
Images: 4
Quote:
Originally Posted by cfarrar View Post
Your suggestion about maxing out your panels first, and using a cheap controller, makes perfect sense if you have plenty of real estate to put up panels, and you don't mind the weight and windage.
Exactly. Put up panels as many panels as you can stand, then go for the MPPT controller. Of course, you don't need to get the cheap controller if you think you will eventually want the MPPT.

By the way, I've had poor reliability from the Blue Sky MPPT controller. It seems that it only takes a few drips and the thing stops working. I've had two of them fail, with honestly only a tiny drip of salt water hitting it. I know I should have it better protected, but has anyone else had similar difficulties?
__________________
Paul Elliott, S/V VALIS - Pacific Seacraft 44 #16 - Friday Harbor, WA
www.sailvalis.com
Paul Elliott is offline   Reply With Quote
Old 29-09-2010, 06:56   #19
Registered User

Join Date: Sep 2010
Location: Mattaponi, VA
Boat: None yet!
Posts: 18
Quote:
Originally Posted by witzgall View Post
MPPT controllers also have the added benefit of using a pulse charging method that will top off your batteries a bit higher than conventional charging. This means more amps are available from your battery bank, and if they are wet cells, you will get longer life as they do not need equalization as much.

Chris
Cite please?

Batteries act as huge capacitors. Pulse charging seems useless.
Joe Simmons is offline   Reply With Quote
Old 29-09-2010, 18:57   #20
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Pulse charging is not a standard feature of mppt controllers. Pulse width modulated charging of lead acid batteries is generally not recommended or supported by battery manufacturers. IUI or IUU charging regimes are.
goboatingnow is offline   Reply With Quote
Old 30-09-2010, 05:55   #21
Marine Service Provider
 
witzgall's Avatar

Join Date: Oct 2006
Location: Eastern Shore, MD
Boat: Camper Nicholson 44 Ketch
Posts: 2,060
It is quite possible I got some bad info, or confused things myself. I retract my statement until such time as I can find some hard facts to back it up.

Chris


Quote:
Originally Posted by goboatingnow View Post
Pulse charging is not a standard feature of mppt controllers. Pulse width modulated charging of lead acid batteries is generally not recommended or supported by battery manufacturers. IUI or IUU charging regimes are.
witzgall is offline   Reply With Quote
Old 30-09-2010, 08:01   #22
Moderator Emeritus
 
Paul Elliott's Avatar

Cruisers Forum Supporter

Join Date: Sep 2006
Posts: 4,663
Images: 4
I don't recall the source, but I did see a claim in a catalog somewhere that the (non-MPPT) duty-cycle style charge-controllers would reduce battery sulfation because of the high-current pulses.

I don't believe it though. While these controllers do generate pulses (they merely connect and disconnect the solar panel to control the average current sent to the battery), the current in the pulse is limited by the panel and isn't very high. And, even if the current pulses were higher, the efficacy of pulsed charging to reduce sulfation is questionable.
__________________
Paul Elliott, S/V VALIS - Pacific Seacraft 44 #16 - Friday Harbor, WA
www.sailvalis.com
Paul Elliott is offline   Reply With Quote
Old 02-10-2010, 04:07   #23
Registered User

Join Date: Sep 2010
Location: Currently Algarve Portugal
Boat: Moody 42 Ketch 1977
Posts: 14
Panels Installed BUT....

Hi guys, please help again,
I have now installed the panels in series and are currently giving about 3 amps at 24volt, however should one panel go into shade I get nothing at all,
absolutely zero although the other panel is in full sun.
Is there any way to avoid this as it is difficult on the boat to keep both permanently in full sun.
Cheers,
John.
nostramo.moody is offline   Reply With Quote
Old 02-10-2010, 06:30   #24
Registered User
 
cfarrar's Avatar

Join Date: Apr 2008
Location: Brooklin, Maine U.S.A
Boat: Allures 44
Posts: 734
Images: 2
John,

From what I understand, this is the disadvantage of wiring solar panels in series. If you had four panels - each paired to create 24V, and then the pairs wired in parallel to double your amperage - you would only suffer a 50% loss if one panel was shaded. If you want to stick with two panels, however, I don't know of any solutions, aside from mounting them to minimize shading. Hopefully someone else has a better idea for you.
cfarrar is offline   Reply With Quote
Old 02-10-2010, 11:34   #25
Moderator Emeritus
 
Paul Elliott's Avatar

Cruisers Forum Supporter

Join Date: Sep 2006
Posts: 4,663
Images: 4
There are MPPT controllers that will boost the output of the "12V" panels to match John's 24V battery. With one of these he could then wire the panels in parallel. One likely controller is from Genasun, the GVB series. I've not used these, merely looked at the specs.

As to whether it's worth spending a couple of hundred dollars on the controller, thats another question.
__________________
Paul Elliott, S/V VALIS - Pacific Seacraft 44 #16 - Friday Harbor, WA
www.sailvalis.com
Paul Elliott is offline   Reply With Quote
Reply

Tags
battery


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
24vdc Solar to 12vdc Battery Bank hummingway Electrical: Batteries, Generators & Solar 56 13-09-2011 09:43
24vdc Battery Bank ArmyChief Electrical: Batteries, Generators & Solar 9 21-07-2010 01:28
How to Set Up 3 x 130w 12vdc Solar Panels for 24vdc with the Most Amps ? Fuss Electrical: Batteries, Generators & Solar 3 06-04-2010 00:25
36vdc Motor Bank and 12vdc House Bank bobola Electrical: Batteries, Generators & Solar 24 22-12-2009 20:30
Charging 48v battery bank with solar panels Hankthelank Electrical: Batteries, Generators & Solar 3 05-10-2008 13:55

Advertise Here


All times are GMT -7. The time now is 11:27.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.