A/C causes genset to go offline momentarily

Looking for suggestions-

We have a Kohler 8k marune genset and while running our 16k dometic AC pack, (when at anchor,) i notice that each time the compressor kicks on, our Victron touch screen GUI indicates that our shorepower/Genset feed drops out for about 10 seconds and then comes back online.

The shorepower and/or generator feeds go thought the Victron Multuplus 3k Inverter/Charger as it normally is designed..

This "trip" seems to follow when the compressor cycles from off to on.

Is this an indication that the capacitors on out genset are going out?

Not really sure if these capacitors are used in a way to buffer a spike or not.

I'm not really to sure of I'm close on my thought pattern here but just wanted to ask for suggestions.

Would be glad to hear ideas.

Maybe its the water pump cycling on that doing this?

PS, Our Air Conditioning system is 240vac

Thanks,
Jeff
jefndeb is offline   Reply With Quote
Old 22-08-2022, 20:23   #2
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,294
Re: A/C causes genset to go offline momentarily

There isn’t a problem, it’s a setting. Let me think a bit about which one…
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 22-08-2022, 20:26   #3
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,294
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by s/v Jedi View Post
There isn’t a problem, it’s a setting. Let me think a bit about which one…
Found it: Dynamic Current Limiter, set it to ON.
Attached Thumbnails
Click image for larger version

Name:	3FC0C212-4E12-4B11-9DE6-D023B80FCF43.jpg
Views:	68
Size:	434.7 KB
ID:	263272  
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 22-08-2022, 20:33   #4
Registered User
 
wingssail's Avatar

Join Date: Jan 2010
Location: On Vessel WINGS, wherever there's an ocean, currently in Mexico
Boat: Serendipity 43
Posts: 5,525
Send a message via AIM to wingssail Send a message via Skype™ to wingssail
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by jefndeb View Post
Looking for suggestions-

We have a Kohler 8k marune genset and while running our 16k dometic AC pack, (when at anchor,) i notice that each time the compressor kicks on, our Victron touch screen GUI indicates that our shorepower/Genset feed drops out for about 10 seconds and then comes back online.

The shorepower and/or generator feeds go thought the Victron Multuplus 3k Inverter/Charger as it normally is designed..

This "trip" seems to follow when the compressor cycles from off to on.

Is this an indication that the capacitors on out genset are going out?

Not really sure if these capacitors are used in a way to buffer a spike or not.

I'm not really to sure of I'm close on my thought pattern here but just wanted to ask for suggestions.

Would be glad to hear ideas.

Maybe its the water pump cycling on that doing this?

PS, Our Air Conditioning system is 240vac

Thanks,
Jeff
From what I read that 16KBTU AC will draw about 1500 watts but the start-up inrush can be several times that, which might exceed the pass-through of the Victron Inverter/Charger. It seems like the current is getting through but the Victron is complaining.
__________________
These lines upon my face tell you the story of who I am but these stories don't mean anything
when you've got no one to tell them to Fred Roswold Wings https://wingssail.blogspot.com/
wingssail is offline   Reply With Quote
Old 22-08-2022, 21:05   #5
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,711
Re: A/C causes genset to go offline momentarily

It’s possible the voltage or freq is going out of range when it serges. Causing the charger to stop passthrough

Is the ac connected to the inverter output or non inverter output? When it cuts out is the a/c getting inverted?
smac999 is offline   Reply With Quote
Old 23-08-2022, 05:32   #6
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,611
Re: A/C causes genset to go offline momentarily

I see the same on my boat (A/C is not fed through the inverter). Basically, the dip in the generator voltage and frequency caused by the A/C starting happens so quickly that the Victron gear sees it as a power problem and flips to inverting for a moment, then decides the power is suitable and switches back. I don't run A/C on generator power very often, so I haven't really hunted for a fix.
rslifkin is offline   Reply With Quote
Old 23-08-2022, 09:30   #7
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,294
Re: A/C causes genset to go offline momentarily

No need to hunt for fixes, I posted the fix right above in the thread. I have confirmed this on multiple installations.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 23-08-2022, 11:21   #8
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,611
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by s/v Jedi View Post
No need to hunt for fixes, I posted the fix right above in the thread. I have confirmed this on multiple installations.
Dynamic current limiter will help if you're running the A/C through the Multiplus. But for a setup like mine where the A/C doesn't go through the Multiplus (and I have power assist disabled as well) I can't see how it would make any difference.
rslifkin is offline   Reply With Quote
Old 23-08-2022, 13:38   #9
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,294
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by rslifkin View Post
Dynamic current limiter will help if you're running the A/C through the Multiplus. But for a setup like mine where the A/C doesn't go through the Multiplus (and I have power assist disabled as well) I can't see how it would make any difference.
The solution is for the OP. I read your post saying you have the same problem but now that I check it again, I see that it also says you don’t have the Multiplus between genset and A/C.

Yes, the surge from the A/C will be detected as an unsuitable power source. You can fix this by moving loads like A/C that you don’t want to power from battery to the OUT2 terminals on the Multiplus and changing the setting I mentioned.

The good thing about that change is that the Multiplus knows about the load of the A/C and it knows the maximum allowable load of the genset. It will reduce battery charging real quick during these events instead of overloading the genset, which is better for the systems.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 23-08-2022, 15:47   #10
Marine Service Provider
 
jefndeb's Avatar

Join Date: Mar 2016
Location: Annapolis, Maryland
Boat: Oday 28
Posts: 479
Images: 4
Re: A/C causes genset to go offline momentarily

Thanks very much for your suggestion, I just checked and I do have that option selected to on....

Also, it doesn't cycle when we are connected to dock power, so seems its something to do with the generator feed only...

Jeff
jefndeb is offline   Reply With Quote
Old 23-08-2022, 17:49   #11
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,294
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by jefndeb View Post
Thanks very much for your suggestion, I just checked and I do have that option selected to on....

Also, it doesn't cycle when we are connected to dock power, so seems its something to do with the generator feed only...

Jeff
Shore power has an ample supply so it’s normal that it doesn’t show the problem.

So you have an 8kW genset. How many BTU is the A/C? I have an 18kBTU A/C on a 6kW Northern Lights genset and the setting fixes it.

The age of the genset, as well as what type of voltage regulator it has come into play. I have an electronic voltage regulator. You could observe voltage and current during the compressor start surge.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 24-08-2022, 04:58   #12
Marine Service Provider
 
jefndeb's Avatar

Join Date: Mar 2016
Location: Annapolis, Maryland
Boat: Oday 28
Posts: 479
Images: 4
Re: A/C causes genset to go offline momentarily

Ok,, yes the genset has 1030 hrs and its a 2005 model.
I was wondering if I don't see it drop offline on the 120v leg, seems to only be 240....or am I misunderstanding what I am seeing as the analog 120 v needle only bumps a little (when the ac cycles) but the victron shows that it got dropped momentarily ...
jefndeb is offline   Reply With Quote
Old 24-08-2022, 05:19   #13
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,611
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by jefndeb View Post
Ok,, yes the genset has 1030 hrs and its a 2005 model.
I was wondering if I don't see it drop offline on the 120v leg, seems to only be 240....or am I misunderstanding what I am seeing as the analog 120 v needle only bumps a little (when the ac cycles) but the victron shows that it got dropped momentarily ...

That sounds like what I see as well. A quick flick, but enough to make the Multiplus drop off generator power for a moment. It's not that it goes out of range for long, but it's just enough (and happens very suddenly) that it thinks there's a power problem.
rslifkin is offline   Reply With Quote
Old 24-08-2022, 05:37   #14
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,294
Re: A/C causes genset to go offline momentarily

Quote:
Originally Posted by rslifkin View Post
That sounds like what I see as well. A quick flick, but enough to make the Multiplus drop off generator power for a moment. It's not that it goes out of range for long, but it's just enough (and happens very suddenly) that it thinks there's a power problem.
Exactly. When you have the UPS option enabled, this will be even more sensitive.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Reply

Tags
men


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Common causes of cruising boats being lost at sea? philaw Health, Safety & Related Gear 13 05-11-2008 15:38
boat list potential causes? Buddy_Y Monohull Sailboats 12 20-06-2008 20:14
Oil change causes oil pressure change. theonecalledtom Engines and Propulsion Systems 9 16-06-2008 14:10
New theory (and old equations) may explain causes of ship-sinking freak waves learningcurve Flotsam & Sailing Miscellany 0 14-09-2006 06:07
BLISTERS - Causes, Types, & Prevention GordMay Construction, Maintenance & Refit 0 31-05-2004 08:49

Advertise Here


All times are GMT -7. The time now is 12:15.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.