a/c main breaker

I am re-installing the original electrical panel in my Endeavour 40.
The panel is designed for 30A service but I am going to upgrade to 50A.
The original main breaker is 30A 3 pole.What is the 3rd pole for?


Any ideas?


There was originally a genset installed but it has been removed, may be replaced by solar depending on the coin toss.
The only thing I can think of is the 3rd pole was ground possibly related to genset usage.
Dunstaffnage is offline   Reply With Quote
Old 10-05-2023, 01:00   #2
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,425
Re: a/c main breaker

Quote:
Originally Posted by Dunstaffnage View Post
I am re-installing the original electrical panel in my Endeavour 40.
The panel is designed for 30A service but I am going to upgrade to 50A.
The original main breaker is 30A 3 pole.What is the 3rd pole for?


Any ideas?


There was originally a genset installed but it has been removed, may be replaced by solar depending on the coin toss.
The only thing I can think of is the 3rd pole was ground possibly related to genset usage.
You will need to post a picture or a link to the exact breaker you have.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 10-05-2023, 04:47   #3
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Hunter 340
Posts: 1,471
Re: a/c main breaker

Quote:
Originally Posted by Dunstaffnage View Post
I am re-installing the original electrical panel in my Endeavour 40.
The panel is designed for 30A service but I am going to upgrade to 50A.
The original main breaker is 30A 3 pole.What is the 3rd pole for?


Any ideas?


There was originally a genset installed but it has been removed, may be replaced by solar depending on the coin toss.
The only thing I can think of is the 3rd pole was ground possibly related to genset usage.
Ground should never be switched. Entirely possible that was done because a lot of wrong stuff are done on boats but you should not repeat it when cleaning things up.

Was your connection 120V or 120V/240V?

If it was 120V/240V then you will have 3 lines (hot1, hot2, and neutral). There is nothing wrong with switching all three although I am unsure if ABYC requires it. While only the two hots "should" be energized having 3 pole for 120V/240V ensures that if you have reverse polarity due to bad dock wiring and the neutral is hot that it is switched off too. Three pole breaker will completely isolate your main panel from shorepower with the exception of safety ground.

If it is just 120V 30A now being upgraded to 120V 50A then there is no point to a 3 pole breaker. Replace it with a 50A 2 pole breaker.

Since you are redoing everything anyways and will need to redo the inlet do the right thing and protect your boat and crew and put into an ELCI as close to the shore power inlet as possible. They are available in both 2 & 3 poles at 50A. Again ground is never switched. There should be a connection unbroken by switches/fuses/breakers from the shorepower pedestal ground to your main ground busbar. For completeness although it doesn't apply the only exception would be if using an isolation transformer.
Statistical is offline   Reply With Quote
Old 10-05-2023, 06:46   #4
Registered User

Join Date: Nov 2018
Location: Panama
Boat: Norseman 447
Posts: 1,628
Re: a/c main breaker

I worked on an Island Packet once that had a burned. 3-pole AC breaker. The third "pole" was actually connected between the neutral wire and earth ground. If you had "reversed polarity" it would trip the circuit breaker. We had to buy the breaker from IP.
Bycrick is offline   Reply With Quote
Old 13-05-2023, 23:48   #5
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,744
Re: a/c main breaker

some old boats had a 3rd "pole" for the ground wire to measure and trip on reverse polarity. it didn't actually break the ground though, and tripped on voltage not amps.
smac999 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage Drop From Battery To Main Breaker Panel marina.alex Electrical: Batteries, Generators & Solar 17 11-11-2021 15:16
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
AC Main Circuit Breaker EggHrbrGuy Electrical: Batteries, Generators & Solar 11 28-06-2015 06:12
Why does my main AC breaker keep tripping? Toubab Electrical: Batteries, Generators & Solar 19 10-10-2013 13:31
30A 110V Main Breaker Not Working boto Electrical: Batteries, Generators & Solar 10 19-08-2008 15:25

Advertise Here


All times are GMT -7. The time now is 03:09.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.