To all the tesla genies out there, if you want a common ground don't you want three wires, black -hot , white - neutral, and green - dedicated ground? Anyone who knows, please explain.
Nibiruwayne is offline   Reply With Quote
Old 13-02-2012, 18:29   #17
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: A/C Wiring Short ?

That's correct.

The AC main switch opens/closes both hot and neutral, each individual circuit has a breaker that opens/closes only the hot. Both neutral and grounds are common to all. The AC ground (in North America) is connected to the 12 volt negative bus, making all grounds, AC and DC common.
mitiempo is offline   Reply With Quote
Old 13-02-2012, 20:16   #18
Registered User
 
osirissail's Avatar

Join Date: Feb 2009
Location: A real life Zombie from FL
Boat: Gulfstar 53 - Osiris
Posts: 5,416
Images: 2
Re: A/C Wiring Short ?

Quote:
Originally Posted by Nibiruwayne View Post
To all the tesla genies out there, if you want a common ground don't you want three wires, black -hot , white - neutral, and green - dedicated ground? Anyone who knows, please explain.
Huh? - Basic electric 101 - North American style - black or red is Hot and comes from the power company into your house through a main disconnect (c/b or electric meter).

The white wire is the "neutral" which means it comes off the center tap of the transformer up there on the power pole. In your home electrical panel it is also tied to a grounding stake pounded down into the earth. It is the primary "ground."

The "green" wire is the "safety ground" and doesn't come from or go to the power pole. It goes to the same metal stake pounded into the ground as the "neutral." The green "safety" ground is there in case the white grounded neutral gets cut or disabled. Or if your appliance/whatever develops a short to its case or housing that a human can touch. It allows the line c/b or fuse to trip/blow in case of an overcurrent condition in the black hot supply wire.

In a boat, everything is the same - except - for shore power both the "Hot" and "Neutral" are disconnected by the shore power selector switch. This is done to prevent a reversed hot/neutral wiring problem from shorting out inside your boat possibly causing a fire. A reverse polarity light is normally installed beside the main shore power AC switch to warn you that the power is coming down the wrong wire - before you throw the switch.

In this system you have 2 grounds - the neutral and the green safety ground. In other electrical systems in use around the world they often do not use the "safety ground" wire and only wire things for a "hot" and a "neutral." For this reason, it is very important that your boat's AC green safety ground be connected to the boats grounding system that is in contact with the water/ocean. If it is not then your reverse polarity warning light would not operate and turning on the shore power switch could cause a fire at worst or blow the c/b on shore at best.
Attached Thumbnails
Click image for larger version

Name:	Corel010.JPG
Views:	185
Size:	71.6 KB
ID:	37367   Click image for larger version

Name:	Corel009.JPG
Views:	219
Size:	37.6 KB
ID:	37368  

osirissail is offline   Reply With Quote
Old 13-02-2012, 23:20   #19
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,895
Re: A/C Wiring Short ?

Quote:
Originally Posted by osirissail View Post
In this system you have 2 grounds - the neutral and the green safety ground. In other electrical systems in use around the world they often do not use the "safety ground" wire and only wire things for a "hot" and a "neutral." For this reason, it is very important that your boat's AC green safety ground be connected to the boats grounding system that is in contact with the water/ocean. If it is not then your reverse polarity warning light would not operate and turning on the shore power switch could cause a fire at worst or blow the c/b on shore at best.
You just failed Electricity 101.

1. All modern electrical systems use a green or green/yellow grounding wire.

2. The reverse polarity warning light is a bulb connected across the AC neutral and the AC ground wire. It will light if the neutral and hot wires are crossed in the dockpower system or extensions to the boat. It will operate if the AC ground wire is not connected to the boats grounding system.

3. Reversed polarity will not blow breakers or cause fires UNLESS there is a fault in your electrical system or appliances.

The issue of whether it is wise to connect the AC ground wire to the boats grounding system is contentious and evolving, and has been covered in other threads.

For the OP, the AC equivalent of DC resistance is called impedance, and includes inductance and capacitance, so something that might appear close to a dead short to DC will actually not pull that much AC current. One suggestion would be to energize the circuit and measure AC volts from each connection in the sockets to a known ground. Its hard to understand how your boat is wired, but you may also be able to clamp on the AC ammeter on a hot or neutral wire in various parts of the outlet circuit to see if and where the current is flowing.







the
donradcliffe is offline   Reply With Quote
Old 14-02-2012, 05:32   #20
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: A/C Wiring Short ?

Quote:
It will operate if the AC ground wire is not connected to the boats grounding system.
That is not correct. The operation of the reversed polarity light is independent of the presence or absence of a AC ground/vessel ground bond.
Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 14-02-2012, 05:36   #21
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,205
Re: A/C Wiring Short?

Quote:
Originally Posted by btrayfors View Post

Note: lightbulbs and motors and similar loads on the circuit could show a low ohm reading as well. Be sure there are none and/or they are switched off.
Been tricked by that one before. Breaker off, lamp turned on continuity between black & white.... Doh'.....

I would suggest unpluging all appliances in the outlet circuit and re-test..
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 14-02-2012, 05:37   #22
Registered User
 
sigmasailor's Avatar

Join Date: Jan 2010
Location: Netherlands, Holland
Boat: Sold Sigma 33 OOD some time ago, will be chartering in Turkey really soon
Posts: 361
Re: A/C Wiring Short ?

Quote:
Originally Posted by CharlieJ View Post
Don- Didn't you mean, "It will not operate if the AC ground wire is not connected to the boats grounding system."

Charlie
Guess not; you don't need ground to merely operate an AC circuit; hot and neutral are enough. Now; to operate it safely you do need ground and like other I would recommend ALS (aardlekschakelaar or earth protection switches) protected outlets.

Eric
__________________
Sailors do it with the wind...
sigmasailor is offline   Reply With Quote
Old 14-02-2012, 05:48   #23
Registered User
 
osirissail's Avatar

Join Date: Feb 2009
Location: A real life Zombie from FL
Boat: Gulfstar 53 - Osiris
Posts: 5,416
Images: 2
Re: A/C Wiring Short ?

Quote:
Originally Posted by donradcliffe View Post
. . .
3. Reversed polarity will not blow breakers or cause fires UNLESS there is a fault in your electrical system or appliances. . .
Let's see. the ship's neutral is connected to the ship's ground system.

You plug in your shore power cable and because of mis-wiring, the "hot" leg is now on the "neutral" leg wire which is directly connected to ground.

And you contend that when you connect a hot wire to ground you will not allow enough current to pass down the wire to either 1- trip the shore power circuit breaker - or, 2 - the dead short to ground cannot cause the wire to catch on fire?

Nah. don't think so. Give it a try - cross connect your shore power plug to feed "hot" down the neutral wire and turn on your shore power switch . . . just be careful to have a fire extinguisher nearby.
osirissail is offline   Reply With Quote
Old 14-02-2012, 08:14   #24
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: A/C Wiring Short ?

Quote:
Originally Posted by osirissail View Post
Let's see. the ship's neutral is connected to the ship's ground system.

You plug in your shore power cable and because of mis-wiring, the "hot" leg is now on the "neutral" leg wire which is directly connected to ground.

And you contend that when you connect a hot wire to ground you will not allow enough current to pass down the wire to either 1- trip the shore power circuit breaker - or, 2 - the dead short to ground cannot cause the wire to catch on fire?

Nah. don't think so. Give it a try - cross connect your shore power plug to feed "hot" down the neutral wire and turn on your shore power switch . . . just be careful to have a fire extinguisher nearby.

The ship's neutral is not connected to the ship's ground, with the exception of an internal connection in a generator or inverter. When on shorepower there is not a connection between AC ground and neutral on the boat.

As posted the reverse polarity light is wired between the incoming ground and neutral. Normally there is no current between these wires. If the shorepower is wired wrong (hot and neutral reversed) there will be 120 volts between the neutral and ground and the light will be on. The real danger is that since circuits downstream of the main switch only control the hot feed you will think a circuit is off but it will still be hot.

Reverse polarity is not good but appliances will run and a fire extinguisher is not required.
mitiempo is offline   Reply With Quote
Old 14-02-2012, 08:22   #25
Registered User

Join Date: Mar 2006
Posts: 1,594
Re: A/C Wiring Short ?

Are you 100% sure that you're NOT reading across devices on the AC line?
__________________
Randy

Cape Dory 25D Seraph
rtbates is offline   Reply With Quote
Old 14-02-2012, 08:27   #26
Registered User
 
gjberta's Avatar

Join Date: Jan 2010
Location: Margaritaville Ontario Canada
Boat: Wittholz 40
Posts: 36
Re: A/C Wiring Short ?

Just 2 cents worth re the cost of GFCIs; ideally, each AC receptacle is on it's own accessory breaker, but since this is not done very often, keep in mind that if you daisy-chain 2 or 3 receptacles on one breaker, only the first in line need to be GFCI (and downstream of it can be regular duplex).
If you are doing a complete rewire, consider an EFCI double pole main - well worth it for safety of swimmers around your boat if you are in fresh water regions.
__________________
Capt. Joe
https://www.cruisingdog.com
gjberta is offline   Reply With Quote
Old 14-02-2012, 08:59   #27
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,661
Re: A/C Wiring Short ?

Wow.... sounds like we have many conflicting "right" answers!
"The issue of whether it is wise to connect the AC ground wire to the boats grounding system is contentious and evolving, and has been covered in other threads" yeah, ran into this before. Some people steadfastly say it's dangerous to connect the neutral to ground. I tend to agree with them...
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 14-02-2012, 09:06   #28
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: A/C Wiring Short ?

Quote:
Originally Posted by Cheechako View Post
Wow.... sounds like we have many conflicting "right" answers!
"The issue of whether it is wise to connect the AC ground wire to the boats grounding system is contentious and evolving, and has been covered in other threads" yeah, ran into this before. Some people steadfastly say it's dangerous to connect the neutral to ground. I tend to agree with them...
Neutral should never be connected to ground aboard the boat except internally in a generator or inverter as they are sources. Neutral is connected to ground on shore.

Connecting the AC ground (green) to the boat's grounding system - 12 volt negative bus - is totally different and ABYC calls for it to be done. As you say it is contentious. It does however provide a safe path for a fault in the absence of a shore ground, which cannot always be depended on.
mitiempo is offline   Reply With Quote
Old 14-02-2012, 09:29   #29
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,924
Images: 241
Re: A/C Wiring Short ?

Quote:
Originally Posted by mitiempo View Post
The ship's neutral is not connected to the ship's ground, with the exception of an internal connection in a generator or inverter. When on shorepower there is not a connection between AC ground and neutral on the boat.

As posted the reverse polarity light is wired between the incoming ground and neutral [sic 25,000 Ohm resistance recommended]. Normally there is no current between these wires. If the shorepower is wired wrong (hot and neutral reversed) there will be 120 volts between the neutral and ground and the light will be on. The real danger is that since circuits downstream of the main switch only control the hot feed you will think a circuit is off but it will still be hot. ...
Indeed.
See also R.P.I. - Cruisers & Sailing Photo Gallery
Attached Thumbnails
Click image for larger version

Name:	79rev_polarity-med.jpg
Views:	185
Size:	249.1 KB
ID:	37386  
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 15-02-2012, 06:09   #30
Registered User
 
osirissail's Avatar

Join Date: Feb 2009
Location: A real life Zombie from FL
Boat: Gulfstar 53 - Osiris
Posts: 5,416
Images: 2
Re: A/C Wiring Short ?

Quote:
Originally Posted by mitiempo View Post
The ship's neutral is not connected to the ship's ground, with the exception of an internal connection in a generator or inverter. When on shorepower there is not a connection between AC ground and neutral on the boat. . .
Ah! You are making a dangerous assumption that "all" boats are wired in accordance with ABYC's current standards. Donradcliffe at least qualified his response with "All modern electrical systems . . ."

Lots of old boats follow neither ABYC or even any other world standard. I have encountered many old boats with "bonded" (grounded neutral) neutrals and many with no "reverse polarity" light. Quite a few had "reverse polarity" lights that were either disconnected or failed.

Likewise, the assumption that shore power supply systems conform to ABYC or any other system is also a dangerous assumption. From real world experience both inside the U.S.A. in ancient (a.k.a, decrepit or cheap marinas) and in many 3rd World countries you will find shore power supplies with no safety ground (green/green-yellow) wire and many with no bonding to ground on their neutral wiring system. Even some with reversed "hot/neutral" wiring that has been that way for years (especially in the "European" 220VAC, 50Hz 2 wire systems). In these circumstances there is nothing (short of using a portable VOM to test the shore power receptacle) that will alert you to a dangerous situation.

In my post the "Let's see. . ." was a "given" situation. The point being that making flat all-inclusive "book derived" answers can be dangerous in the real world of cruising where many "not-by-the-book" realities exist.
osirissail is offline   Reply With Quote
Reply

Tags
wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Boat Wiring jakegator Electrical: Batteries, Generators & Solar 7 01-02-2012 05:19
Shore Power and 110v Wiring TheScarab Electrical: Batteries, Generators & Solar 58 19-01-2012 07:16
Inverter Wiring CampDavid Electrical: Batteries, Generators & Solar 9 21-09-2011 17:59
Wiring Schematic for 1974 Pearson 28 boeing1 Electrical: Batteries, Generators & Solar 0 15-08-2011 13:31
Growth in Saltwater A/C Cooling System Conch Cruzer Plumbing Systems and Fixtures 7 13-08-2011 10:59

Advertise Here


All times are GMT -7. The time now is 06:20.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.