Re: AC DC common ground

The simplest, non-technical way to consider AC wiring on a boat is to think of the boat as a big extension cord with a power strip on the end. That is more or less what it is.

The wiring mistakes, especially the AC Neutral and Ground connection come because the boat is treated as a house, which it is not.

At home, would you connect the AC neutral and AC ground on the power strip? Probably not, so don't do it on a boat.

The AC Ground and DC negative should be connected at one point, usually on the engine block.
Dave Lochner is offline   Reply With Quote
Old 27-06-2021, 20:31   #17
Registered User

Join Date: Nov 2017
Posts: 459
Re: AC DC common ground

Quote:
Originally Posted by CharlieJ View Post
@roland_stockham #9


DC neutral?? If you truly meant DC ground or B-, than the latest version of ISO 13297 that I hold (2012) contradicts your statement.

ISO 13297-2012


roland_stockham #9


The "big copper stake" has nothing to do with fault clearance! Current is returned via the neutral in a USA 120V system. The safety ground (green wire) is a low impedance redundant conductive path back to the source, usually the secondary of the marina's transformer, to allow enough fault current to pass to trip a protective device somewhere in the circuit.

This is a seriously dangerous subject. Please, do not feel obligated to type something if you do not consider yourself well versed in the subject matter, as misinformation can do some actual harm if it is applied by a novice.

this is not to be taken lightly.
first, couple comments are discussing neutral and other "descriptions" . obviously these authors do not understand electricity- so emphasize, no comments unless you are certified.

the ground in the us' system is not a neutral. it is specifically a ground.

for the rest of the world- electricity does not concern itself with global boundaries.
It is simply physics.
research the principles and specifically the differences. Don't do it correct-
short term is sacrifice your underwater metals.
long term maybe sacrifice your friends.
boat driver is offline   Reply With Quote
Old 28-06-2021, 03:24   #18
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,577
Images: 22
Re: AC DC common ground

Quote:
Originally Posted by roland stockham View Post
Also depends where the boat was built. May have changed but in Europe it was forbidden to connect the A/C ground to the DC neutral. This seems sensible, D/C neutral is a 'floating ground' because ti is a closed loop on the boat it does not need a reference ground and does not care what voltage it is relative to the world outside the boat. The A/C side however must always have H2 or neutral joining the ground wire at the power source. If this is an onboard generator or inverter the ground and H2 or neutral should connect there. If A/C comes aboard from shore power then the H2 or neutral goes back ashore with the ground. This creates a ground that is reference to the outside world. The marina should have a big copper stake in the ground to maintain this reference.
The original wiring of my 1988 yacht has the A/C Earth (US Ground) connected to the D/C negative (US Neutral). When I recently installed a new inverter, I wired the case Earth connection to the D/C negative supply which connects to the anode etc via bus bars.

This is fairly standard in the UK, though it does provide some lengthy and lively discussions on UK forums.

Biggest problem in Europe is some marinas are wired the wrong way round so you hear of people making their own fly leads to reverse the positive and negative A/C supply.

Thank god for solar, we rarely plug in now unless we are out sailing in the depths of winter.
Pete7 is offline   Reply With Quote
Old 28-06-2021, 03:51   #19
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,262
Re: AC DC common ground

Quote:
Originally Posted by Pete7 View Post
The original wiring of my 1988 yacht has the A/C Earth (US Ground) connected to the D/C negative (US Neutral).
It must be a language or terminology thing ...
"D/C negative" is not "US neutral".
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 28-06-2021, 06:31   #20
Registered User

Join Date: Mar 2020
Location: NE Florida
Boat: CSY 44
Posts: 35
Re: AC DC common ground

Many thanks to everyone for the replies. I will be adding a connection for a common AC DC ground.
duetto is offline   Reply With Quote
Old 29-06-2021, 17:50   #21
Registered User

Join Date: Dec 2018
Location: Wichita/Pensacola
Boat: Lagoon TPI 37'
Posts: 560
Re: AC DC common ground

Quote:
Originally Posted by RigBig View Post
The shore power grounding bus (green wire) should be connected to the DC ground (Black or Yellow Wire). DO NOT connect the AC neutral (White Wire) to the DC ground (Black or Yellow Wire)/AC ground (Green Wire) together.
That was my problem. My inverter charger had green and whites connected together. My boat was blowing entire marina GFCI. I was not a popular dude that 98 degree day. Disconnected all my green wires to see which whites were shorted to greens. All three were in inverter charger. I removed the jumper in the invertor charger and no more problems.
sailingchiro is offline   Reply With Quote
Old 29-06-2021, 18:26   #22
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,262
Re: AC DC common ground

Quote:
Originally Posted by sailingchiro View Post
That was my problem. My inverter charger had green and whites connected together. My boat was blowing entire marina GFCI. I was not a popular dude that 98 degree day. Disconnected all my green wires to see which whites were shorted to greens. All three were in inverter charger. I removed the jumper in the invertor charger and no more problems.
You do know that the ground must be bonded to the neutral at the power source right ? ... and that the inverter is considered a "power source", right ?

A proper inverter does this switching/unswitching automatically. Did you leave this switching alone or just randomly disconnect ground/neutrals ?
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 02-07-2021, 09:10   #23
Registered User

Join Date: Apr 2015
Location: Vancouver, BC, Canada.
Boat: SeaClipper 38 Tri
Posts: 184
Re: AC DC common ground

As a former industrial electrician schooled in European technology but having worked mainly in North American, I can attest that we should be very careful about assumptions about the terminology used. Casual slang compounds the problem. What we assume can kill us. In this case a little knowledge can be a VERY dangerous thing!

One other important matter is that wiring itself is very rarely an issue unless overloaded or the insulation is damaged. Assuming the circuit is wired correctly in the first place, it is the terminations and connections that are the weak point and almost always the problem. Whether it is industrial, domestic or marine circumstances, poor connections are the primary reason for malfunction and fire. Ask your insurer!

Poor contacts - particularly from corrosion - allow arcing that creates heat that results in fires. Use of a thin smear of dialectic grease on terminations will help prevent this, even with non-tinned conductors. This is especially important in high-saline atmospheres near the equator.

I implore people to occasionally check connections so that this cannot happen. Just because it has worked for a month or a year or a decade, does not mean it is safe. In particular, AC systems, because the current is alternating 50 or 60 times a second, have a vibrating effect and tend to loosen over time. If you have a receptacle/plug, switch etc., that is hot to the touch when under load, check or replace it. Every year I check the tightness of the wiring in my home. Every year I find something not tight.

Check your connections!

Cheers, RR.
__________________
You don't have to be crazy to own a boat - but it helps! RR.
Rotten Ricky is offline   Reply With Quote
Old 03-07-2021, 14:25   #24
Registered User

Join Date: Sep 2009
Location: Mantua, Ohio- New Bern, N. Carolina
Posts: 9
Re: AC DC common ground

Will try to explain in as few as words as possible. In USA, Ac Colors- supply-Black wire, white wire- common, green wire-ground. Main panel you may have common and ground connected. Any sub panel off of main panel common and ground must not be connected. Main panel is where the panel is coming from marina. Correct ground at main panel to be properly grounded should have 1 or 2 8 ft min grounding rods driven into the earth or a water line or such that travels through the earth. Never a gas line. Most sub panels on a boat, common and ground should never be connected. Most sub panels depending on age have a green screw that should be removed. This screw connects the common and ground. As commented prevously GFI and GCFI look for an inbalance between black and white wires and trips.
Three888s is offline   Reply With Quote
Old 03-07-2021, 15:21   #25
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,262
Re: AC DC common ground

Quote:
Originally Posted by Three888s View Post
Will try to explain in as few as words as possible. In USA, Ac Colors- supply-Black wire, white wire- common, green wire-ground. Main panel you may have common and ground connected.
NO ! NO ! NO !

You must not have common and ground connected !
You are going to kill someone !

STOP offering electrical advice !
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 03-07-2021, 17:54   #26
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,000
Re: AC DC common ground

Quote:
Originally Posted by boatpoker View Post
NO ! NO ! NO !

You must not have common and ground connected !
You are going to kill someone !

STOP offering electrical advice !
Totally agree!
Common (AC neutral) and ground should only be connected at the SOURCE - your main panel or any other panels are NOT sources.
Unless you have M.E.N. arrangement which I have never seen or a boat - but never say never...
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is online now   Reply With Quote
Old 04-07-2021, 05:57   #27
Registered User

Join Date: Sep 2009
Location: Mantua, Ohio- New Bern, N. Carolina
Posts: 9
Re: AC DC common ground

I should have made my explanation more clear. Power lines come into building ( marina) are connected to a panel. (main panel.) They are not coming from grid to the dock. This is what i meant as main panel. Any panel that is fed power after that is a sub panel.
Three888s is offline   Reply With Quote
Old 04-07-2021, 06:29   #28
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
AC DC common ground

Personally no EU boat I’ve ever owned has AC protective earth bonded to DC ground. It’s a massive source of impressed corrosion

And you need to properly quote ISO 13297

“4.2 The protective conductor shall be connected to the craft's d.c. negative ground (earth) as close as practicable to the battery (d.c.) negative terminal.
NOTE If an RCD (whole-craft residual current device) or an isolation transformer is installed in the main supply circuit of the a.c. system (see 8.2), the negative ground terminal of the d.c. system need not be connected to the a.c. shore ground (protective conductor).


Since Eu boats always have RCD devices there is never any dc ac interconnection and in my view that’s an extremely good thing
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 04-07-2021, 09:03   #29
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: AC DC common ground

Quote:
Originally Posted by goboatingnow View Post
Personally no EU boat I’ve ever owned has AC protective earth bonded to DC ground. It’s a massive source of impressed corrosion

And you need to properly quote ISO 13297

“4.2 The protective conductor shall be connected to the craft's d.c. negative ground (earth) as close as practicable to the battery (d.c.) negative terminal.
NOTE If an RCD (whole-craft residual current device) or an isolation transformer is installed in the main supply circuit of the a.c. system (see 8.2), the negative ground terminal of the d.c. system need not be connected to the a.c. shore ground (protective conductor).


Since Eu boats always have RCD devices there is never any dc ac interconnection and in my view that’s an extremely good thing
In North America ABYC requires the AC-DC connection even if there is an ELCI (RCD).
mitiempo is offline   Reply With Quote
Old 04-07-2021, 09:09   #30
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
AC DC common ground

Quote:
Originally Posted by mitiempo View Post
In North America ABYC requires the AC-DC connection even if there is an ELCI (RCD).


Agreed but the point is major standards bodies disagree about the importance. ISO feels that whole boat RCD protection removes the need. As I mentioned I’ve never seen it such a connection in EU boats in the last 20 years.

Personally I don’t want any path for external current into my dc system and “ protective earths “ in marinas are often nothing of the sort.

It should be pointed that ISO standards are legal requirements in the EU. ABYC in the US is a recommendation
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Requirment to Connect To Common DC Ground Edward1960 Electrical: Batteries, Generators & Solar 41 18-03-2020 06:12
Common Neg. vs Common Pos. MPPT controllers pcmm Electrical: Batteries, Generators & Solar 0 12-11-2016 07:06
Ship's Common Ground zippy Electrical: Batteries, Generators & Solar 4 31-05-2006 09:12

Advertise Here


All times are GMT -7. The time now is 06:34.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.