Ahhh, there you go... the Ham thing...
Cheechako is offline   Reply With Quote
Old 12-09-2009, 21:48   #17
Registered User

Join Date: Aug 2009
Location: oriental
Boat: crowther trimaran 33
Posts: 4,422
I just scored pounds of wire in the sf bay area for my boat various sizes on spools. There is a used building supplies Building REsources with wire, and they also have teak boards and other useful stuff for cheap. I even got 15 feet of 00 (double 0) gauge wire to connect the wind generator to the batteries.
seandepagnier is offline   Reply With Quote
Old 13-09-2009, 20:44   #18
Registered User

Join Date: Mar 2006
Location: Nevada City. CA
Boat: Sceptre 41
Posts: 3,857
Images: 9
Hi All here is a link to the wires that I pulled out pretty scary when I look at the fire they could have caused -- Picasa Web Albums - mckenzie.charlie - burnt wire
__________________
Fair Winds,

Charlie

Between us there was, as I have already said somewhere, the bond of the sea. Besides holding our hearts together through long periods of separation, it had the effect of making us tolerant of each other's yarns -- and even convictions. Heart of Darkness
Joseph Conrad
Charlie is offline   Reply With Quote
Old 14-09-2009, 03:31   #19
Registered User

Join Date: Sep 2009
Location: Onboard, cruising in Mexico
Boat: 45' Hunter CC "BABEEZE"
Posts: 23
The amperages for a given wire size in AC systems are correctly quoted as 15 amps for #14 awg, 20 amps for #12 awg and 30 amps for #10 awg. Voltage drop is not usually a factor in these short runs. However #8 awg might be a better choice for main runs to your breaker panel. Using a larger wire size than necessary does not save electricty. The wiring that appeared to be extension cord was likely marine cable. This cable is used on ships and devices such as sump pumps and float switches and is an approved wireing method. Marine grade wire is not only tinned but is constructed with finer wire strands, this reduces metal fatigue caused by vibration. Joints, splices and terminations are responsible for more fires than wire size when the wire is protected by the correct fuse or breaker. Improper crimping, loose screws and the wrong wire connectors are the usual culprits. Unless you are dealing with fixed resistance heating ( baseboard heaters etc.) devices can only be rated for 80% of rated breaker capacity or 12 amps (1440 watts). If you have a device rated at 15 amps or 1500 watts it must be plugged into a 20 amp recpticle on a 20 amp circuit. Not enough emphases is placed on the use of anti-corrosion compounds on splices, joints and terminals. These compounds help to exclude oxygen and salt controlling corrosion and overheating.The ball game is entirely different when dealing with DC circuits and a manual like the one by nigel calder is a major help even to a retired elecrtician like me. Marine wireing has many nuances not found in normal residential or industrial electrical applications.
Rene is offline   Reply With Quote
Old 14-09-2009, 05:26   #20
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,846
Images: 241
Quote:
Originally Posted by Rene View Post
... The wiring that appeared to be extension cord was likely marine cable. This cable is used on ships and devices such as sump pumps and float switches and is an approved wireing method...
Charlie’s picture seems (to me) to be depicting a (portable) Flexible Cord. Note the poly’ filler strands, a characteristic of flexible cords (and extension cord), not normally found on modern cables.

Extension cords are convenient ways to provide power to portable equipment. Extension cords are intended only for temporary use with portable equipment.

Flexible cords and cables are attached to appliances, and can be used as pendants, for the wiring of fixtures, for the connection of portable lamps and appliances, for the connection of stationary equipment that is frequently moved, and to prevent transmission of noise or vibration and allow movement. Flexible cords (& extension cords) are NOT an approved wiring method.

Most Codes, Standards, & Regulations prohibit the following uses of flexible cords (and extension cords):

- as a substitute for fixed wiring (i.e. permanent)

- when run through holes in walls, ceilings, or floors

- when run through doorways or windows

-when attached to building surfaces

- when concealed by walls, ceiling, or floors
Attached Thumbnails
Click image for larger version

Name:	Charlie's Cabtire.JPG
Views:	149
Size:	82.1 KB
ID:	9926  
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 14-09-2009, 07:50   #21
Registered User
 
senormechanico's Avatar

Join Date: Aug 2003
Boat: Dragonfly 1000 trimaran
Posts: 7,201
The "soot" seems to me to be oxidized black wire insulation. I don't see any evidence of overheating, just soot tracks. The plastic on the terminal ends looks ok and the polyester filler isn't damaged.

It's not approved wiring of course, but I don't think the boat was in danger of fire.

Steve B.
senormechanico is offline   Reply With Quote
Old 14-09-2009, 08:08   #22
Registered User

Join Date: Mar 2006
Location: Nevada City. CA
Boat: Sceptre 41
Posts: 3,857
Images: 9
Senor M:

I don't know enough about electrical fires to know for sure on this one but it sure looks like the wire was hot enough to leave a black stain on the yellow insulation of the extension cord. I am goign to replace the wire regardless of what happened but am curious as to whether this was a fire, overheating, or just oxidation.

Gord May is correct on this cable it says that it is extension cord right on the yellow jacket.
__________________
Fair Winds,

Charlie

Between us there was, as I have already said somewhere, the bond of the sea. Besides holding our hearts together through long periods of separation, it had the effect of making us tolerant of each other's yarns -- and even convictions. Heart of Darkness
Joseph Conrad
Charlie is offline   Reply With Quote
Old 14-09-2009, 09:55   #23
Registered User
 
Roy M's Avatar

Join Date: Feb 2007
Location: Southwestern Yacht Club, San Diego, CA
Boat: Searunner 40 trimaran, WILDERNESS
Posts: 3,175
Images: 4
Funny to have run into this thread, today. Over the weekend, I did some AC repairs on a friend's boat. It's a thirty-plus year old Islander that was exhibiting some failures of its AC circuits. I opened up the breaker panel and found several of the Marinetics (popular in those days) breakers, covered in black soot. All of the original wiring, basically a three wire zip cord, 14 gauge, untinned, red-black-green, was stiff, and green corroded at all the lugs. I replaced the entire panel with a new Blue Sea unit, added temporary pigtails to the existing wiring (I'll strip out all the original later) because the corrosion had capillaried back some ways, then replaced the Marinco shorepower plug with another, due to scorching of the terminals and some melting of the plastic. Miraculously, the water heater now works.

Old wiring systems should be replaced with newer, all-tinned stranded wires, such as Ancor. Old breakers do age as well, reducing their ability to conduct current and creating heat. All of the paper labels on the old breakers had charred. Moisture, salt and heat affect the older wiring over time, reducing their capacity to carry rated current, creating heat and mysterious failures to conduct.

I have completely replaced all of my original wiring and distribution system over the last couple years, upgrading in the process from a six-circuit DC system (enough in the 70's) to a sixteen circuit system for the 21st century's demands of nav electronics, saltwater washdown pumps, electric windlasses, refrigeration, and all those wonderful electric and electronic servants that make our cruising so special. If any of you have old AC or DC circuits, whether or not you ever leave the dock, they have been subjected to the abuse of time and the environment. Inspect the components, as well as the associated wiring and distribution, for signs of deterioration. Transplants are better than cardiac arrest. And if you are going to take shortcuts, as I am doing with my customer, make sure they are temporary, as in a couple months, at most.
Roy M is offline   Reply With Quote
Old 14-09-2009, 10:04   #24
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,648
Yeah, when you think about it, a wiring fire is probably more likely a cause to need to abandon ship than a weather problem.....
Cheechako is offline   Reply With Quote
Old 14-09-2009, 11:41   #25
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,846
Images: 241
Quote:
Originally Posted by senormechanico View Post
Current only travels on the surface of a conductor when it's at RF frequencies.
Steve B.
True, in a practical sense, for most applications. Not quite technically accurate, though.

The tendency of alternating current flow to crowd towards the external conductor surfaces is called Skin Effect. The higher the AC frequency, the more pronounced that tendency. These considerations become important for 60 Hz when conductor diameter exceeds about 1.25 inch (± 1500 MCM, where 1 MCM = 1000 Circular Mils).
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 14-09-2009, 19:46   #26
Registered User

Join Date: Sep 2009
Location: Onboard, cruising in Mexico
Boat: 45' Hunter CC "BABEEZE"
Posts: 23
Gord; The cable in the picture may be cabtire it isn't very clear. The code rules you allude to do apply to certain types of flexable cables in residential and industrial applications. The use of approved flexable cables in the mining code and shipboard codes is not only common but is the norm.
Rene is offline   Reply With Quote
Old 15-09-2009, 02:24   #27
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,846
Images: 241
Quote:
Originally Posted by Rene View Post
... The use of approved flexable cables in the mining code and shipboard codes is not only common but is the norm.
Most cruising boats don't have "festoons" or "pendants", where cabtire is most often used.
Are you Cdn? ("cabtire")

If you get stuck for a temporary repair, and must use a flexible cable (extension cord, or cabtire), try to get a cord with the letters “T” (high temperature) & “W” (wet locations) in the type designation.
Hence, for instance, type “STOW” as opposed to the cheaper “SO”.

__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 15-09-2009, 07:43   #28
S&S
Registered User
 
S&S's Avatar

Join Date: Jul 2009
Boat: 48' 1963 S&S yawl
Posts: 851
Images: 6
Stop reading the NEC Gord! You'll go blind!
S&S is offline   Reply With Quote
Old 15-09-2009, 09:18   #29
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,846
Images: 241
It’s been nearly a decade since I’ve studied the Canadian Electrical Code or the NEC, and I never even knew that the City of Chicago had it’s own Code; which (if the Ampacity Table is representative) certainly isn’t very stringent.
I don’t work in electrical design any more.
Even so, I am slowly going (slightly) blind.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 15-09-2009, 09:41   #30
S&S
Registered User
 
S&S's Avatar

Join Date: Jul 2009
Boat: 48' 1963 S&S yawl
Posts: 851
Images: 6
Quote:
Originally Posted by GordMay View Post
It’s been nearly a decade since I’ve studied the Canadian Electrical Code or the NEC, and I never even knew that the City of Chicago had it’s own Code; which (if the Ampacity Table is representative) certainly isn’t very stringent.
I don’t work in electrical design any more.
Even so, I am slowly going (slightly) blind.
That's quite a leap of logic going from an ampacity table to a comment about a whole code.

The Chicago Electrical Code is the strictest in the country. The table I posted is not from the CEC- just a representative sample off the net, In any event #12 AWG is standard wiring in THHN and the like for 20A free air circuits on shore and same for MTW in applications calling for it. Note I didn't post bundled conductors or length corrections
Come on, lighten up, I was just razzin' ya.

Say "festoon" 3 times.
S&S is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring sneuman Electrical: Batteries, Generators & Solar 10 05-05-2011 15:43
6v wiring Acadia Electrical: Batteries, Generators & Solar 17 16-11-2008 10:53
AC Wiring Charlie Electrical: Batteries, Generators & Solar 13 16-05-2007 03:39
dc wiring northerncat Electrical: Batteries, Generators & Solar 16 31-12-2006 21:11
Wiring.... ssullivan Electrical: Batteries, Generators & Solar 10 05-04-2006 02:26

Advertise Here


All times are GMT -7. The time now is 15:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.