Acceptable leakage on shore power ground wire

I have measured the AC and DC current on the green earth wire in my shore power cable.


DC - 0.5 microamps


AC - 230 microamps everything plugged in
130 uA with nothing but the isolation transformer connected
45 uA with the main breaker off


Are these figures considered acceptable please?
__________________
Twits twitter
MikadoII is offline   Reply With Quote
Old 31-03-2023, 20:15   #2
Registered User
 
Orin's Avatar

Join Date: Oct 2017
Location: Anacortes, Washington
Boat: Ta Shing - Baba 35
Posts: 163
Re: Acceptable leakage on shore power ground wire

Interesting. Truth be told I have no idea. Given a while I could probably calculate something or get ahold of one of my boat corrosion and preservation experts… but what I would ask…
Any leakage means some amount of corrosion. That said some amount of corrosion is going to occur no matter what…. And those current values are below many peoples instruments ability to accurately measure given natural phenomena become measureable at those scales.
Do you have any current problems or is this academic?
Do you currently have a galvanic isolator onboard? It’s my preferred method for addressing issues like this if you’re experiencing faster than normal corrosion.
__________________
- Hoping for filled sails and an empty calendar.
Cheers to the day I see your sails on the horizon!
Orin is offline   Reply With Quote
Old 31-03-2023, 20:32   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,713
Re: Acceptable leakage on shore power ground wire

Are you using a $10,000 piece of lab equipment?

A gfi trips at 5ma. An elci trips at 30ma. 0.045ma Is nothing…. And if using a regular meter I’d call that 0 anyways.
smac999 is offline   Reply With Quote
Old 01-04-2023, 01:01   #4
Registered User
 
MikadoII's Avatar

Join Date: Jul 2012
Location: Mount Dandenong Vic Australia
Boat: S&S Defiance 30 ft.
Posts: 40
Re: Acceptable leakage on shore power ground wire

My normal Fluke cannot get anywhere near uA. I used an el cheapo Jaycar Digitech meter that claims a range of 200uA AC or DC. The readings appeared to be quite repeatable.



Some time ago I did have a corrosion problem of the prop. It appears that the installation of an isolating transformer has at least alleviated that.


My feeling is that the DC reading is probably of no concern and that the AC reading could be capacitative coupling.
__________________
Twits twitter
MikadoII is offline   Reply With Quote
Old 01-04-2023, 09:29   #5
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: Acceptable leakage on shore power ground wire

OP:
You do not have an electrical leakage problem as your isolation transformer eliminates the return path to the shore power source via the safety ground. Note that you could develop an indicated leakage issue if you had a partial N>G in the shore cord/shore power inlet system.

BTW, on boats without isolation xfmrs, I rarely find <5mAAC leakage (and have found as much as 13A!!!) when clamping the L and N (120VAC service) or L1, L2 and N (240VAC service).
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 01-04-2023, 14:02   #6
Moderator
 
Jammer's Avatar

Join Date: Jan 2010
Location: Minnesota
Boat: Tartan 3800
Posts: 5,165
Re: Acceptable leakage on shore power ground wire

Quote:
Originally Posted by MikadoII View Post
Are these figures considered acceptable please?

They are acceptable, very good in fact. AC, anything under 5 mA is OK. Anything under 0.5 mA is fantastic.


On the DC side, one mol is 9.648×104 Coulombs.


You state that you have 0.5 microamperes, or 0.5×10-6 Amperes, of DC leakage. An Ampere is one Coulomb per second. This gives you, with some basic arithmetic, 16 Coulombs of galvanic corrosion per year or 1.6e-4 mols. I'm a little fuzzy on the electrochemistry of galvanic corrosion but a zinc anode has an atomic number of 30 and a typical ionization state of +2, so each mol of electrons will ionize 15 grams of zinc. Total of 2 mg of zinc. Basically nothing.


My math is probably wrong...
__________________
The best part of an adventure is the people you meet.
Jammer is offline   Reply With Quote
Old 01-04-2023, 14:40   #7
Registered User

Join Date: Aug 2021
Location: PNW
Boat: 35 Ft. cutter, custom
Posts: 2,546
Re: Acceptable leakage on shore power ground wire

Quote:
Originally Posted by Jammer View Post
An Ampere is one Coulomb per second.
I thought that one Coulomb per second = 1 Watt/Second.
One Amp at one Volt.
Anyway, the figures for Zinc erosion are quite interesting, but I know electrons don't weigh very much.
__________________
Beginning to Prepare to Commence
Bowdrie is offline   Reply With Quote
Old 01-04-2023, 17:44   #8
Registered User
 
MikadoII's Avatar

Join Date: Jul 2012
Location: Mount Dandenong Vic Australia
Boat: S&S Defiance 30 ft.
Posts: 40
Re: Acceptable leakage on shore power ground wire

Thanks everyone for your thoughts and comments.
__________________
Twits twitter
MikadoII is offline   Reply With Quote
Old 01-04-2023, 19:24   #9
Registered User
 
AKA-None's Avatar

Join Date: Oct 2013
Location: Lake City MN
Boat: C&C 27 Mk III
Posts: 2,647
Re: Acceptable leakage on shore power ground wire

Just to note
Repeatable does not equal accurate
__________________
Special knowledge can be a terrible disadvantage if it leads you too far along a path that you cannot explain anymore.
Frank Herbert 'Dune'
AKA-None is offline   Reply With Quote
Old 01-04-2023, 19:55   #10
Registered User
 
MikadoII's Avatar

Join Date: Jul 2012
Location: Mount Dandenong Vic Australia
Boat: S&S Defiance 30 ft.
Posts: 40
Re: Acceptable leakage on shore power ground wire

Quote:
Originally Posted by AKA-None View Post
Just to note
Repeatable does not equal accurate

Of cause not. At least, the dvm is not reacting to a passing seagull.
__________________
Twits twitter
MikadoII is offline   Reply With Quote
Old 03-04-2023, 08:54   #11
Registered User

Join Date: Feb 2015
Posts: 1,242
Images: 1
Re: Acceptable leakage on shore power ground wire

Quote:
Originally Posted by smac999 View Post
Are you using a $10,000 piece of lab equipment?

A gfi trips at 5ma. An elci trips at 30ma. 0.045ma Is nothing…. And if using a regular meter I’d call that 0 anyways.

I think the tongue-in-cheek in this comment was missed.


Are the numbers you are reporting micro-amps, or milli-amps? There is a thousand times difference. I *think* you mean milli-amps which is what most decent meters will read.


Are you really reporting uA, or is it mA?
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 03-04-2023, 17:54   #12
Registered User
 
MikadoII's Avatar

Join Date: Jul 2012
Location: Mount Dandenong Vic Australia
Boat: S&S Defiance 30 ft.
Posts: 40
Re: Acceptable leakage on shore power ground wire

Quote:
Originally Posted by tanglewood View Post
I think the tongue-in-cheek in this comment was missed.


Are the numbers you are reporting micro-amps, or milli-amps? There is a thousand times difference. I *think* you mean milli-amps which is what most decent meters will read.


Are you really reporting uA, or is it mA?

uA. The meter is an el cheapo but claims a 200 uA range. (My normal Fluke will not go anywhere near uA)


The general consensus is that I do not have a problem.


Thanks.
__________________
Twits twitter
MikadoII is offline   Reply With Quote
Old 14-04-2023, 08:41   #13
Registered User

Join Date: Jun 2014
Location: Chesapeake
Boat: Catalina 22 Sport
Posts: 1,239
Re: Acceptable leakage on shore power ground wire

Quote:
Originally Posted by AKA-None View Post
Just to note
Repeatable does not equal accurate
Agree!
Click image for larger version

Name:	Cartoon-showing-difference-between-precision-and-accuracy-A-new-cardiac-output-technique (1).png
Views:	38
Size:	151.3 KB
ID:	274017
lestersails is offline   Reply With Quote
Reply

Tags
power, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Leakage current on shore power cord question jackrabbit59 Electrical: Batteries, Generators & Solar 31 10-09-2021 15:02
AC ground current leakage smac999 Electrical: Batteries, Generators & Solar 22 04-11-2019 06:47
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
How Much Electrical Leakage is Acceptable? YPSILANTI Marine Electronics 7 30-08-2016 08:23
Not Talking Big Waves Here-Is It Acceptable Seamanship to be Anchored on a Lee Shore? Fuss Anchoring & Mooring 15 23-07-2010 05:29

Advertise Here


All times are GMT -7. The time now is 04:49.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.