Am I pushing my bank too hard?

I have four Fullriver DC400-6 deep cycle AGM batteries for my house bank. I recently upgraded my solar so we have been using the house bank for more energy intensive uses such as using the convection oven instead of the gas oven, etc. I never worried about using the microwave before as even though it was a very high current draw on the house bank it only lasted minutes. Now we may be drawing 140 amps for an hour. We never discharge more than 250 Amp-hours so have good safety margin as far as energy used, and with our solar we reliably get back to a 100% state of charge daily unless we have extended heavy overcast weather. Even with 50% cloud cover all day we will be at 100% at 5 PM.

I'm curious to hear what any AGM experts think about the practice of pulling larger currents for substantial times. From Fullriver's data sheet it would appear this should be OK. They have a table for constant current discharge rate and I'd be only at a 0.20CA rate and only going 20% of the discharge time (granted the discharge time is 100 SoC, but I'm only 40% for a 50% SoC).

Is this practice shortening the bank's life? If so is it a substantial change? If I'd be getting 1000 cycles and will only get 800, I'm fine with that.
dougweibel is offline   Reply With Quote
Old 09-03-2021, 18:10   #2
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,541
Re: Am I pushing my bank too hard?

well hard cycling always reduces life, but I would guess that it isn't as important as the impact of getting fully charged
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 09-03-2021, 20:07   #3
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Am I pushing my bank too hard?

A convection oven for an hour is not the most practical item for a boat. Are you really able to get these batteries back to a true 100% state of charge? If not, you will slowly kill them.
__________________
Paul
Paul L is offline   Reply With Quote
Old 10-03-2021, 04:26   #4
Registered User

Join Date: Feb 2017
Location: Occasionally in Colorado. Generally live-aboard. Eastern Caribbean last winter. Nova Scotia and Newfoundland hopefully this summer.
Boat: Antares 44i
Posts: 789
Re: Am I pushing my bank too hard?

Quote:
Originally Posted by Paul L View Post
Are you really able to get these batteries back to a true 100% state of charge?
Well, by the normal methods of measuring state of charge I'd say yes. My Victron battery monitor shows we reach 100% charge AND my Victron solar controller goes through bulk and absorption phases and reaches float.

By what other criteria could I judge a true 100% SoC?
dougweibel is offline   Reply With Quote
Old 10-03-2021, 04:32   #5
Registered User

Join Date: Feb 2017
Location: Occasionally in Colorado. Generally live-aboard. Eastern Caribbean last winter. Nova Scotia and Newfoundland hopefully this summer.
Boat: Antares 44i
Posts: 789
Re: Am I pushing my bank too hard?

I would agree that a convection oven is not the most practical, though I see more people with large wind and solar capacity going to all electric galleys. However for us it is more a matter of baking bread twice a week and wanting to run some laundry every week or so and having free energy with our added solar. Why burn the diesel and propane unnecessarily?
dougweibel is offline   Reply With Quote
Old 10-03-2021, 05:20   #6
Registered User

Join Date: Jul 2005
Location: Bellingham
Boat: Outbound 44
Posts: 9,319
Re: Am I pushing my bank too hard?

Quote:
Originally Posted by dougweibel View Post
Well, by the normal methods of measuring state of charge I'd say yes. My Victron battery monitor shows we reach 100% charge AND my Victron solar controller goes through bulk and absorption phases and reaches float.

By what other criteria could I judge a true 100% SoC?
The current at absorption voltage is between 1% and .05% of the bank capacity. Most chargers and monitors claim 100% sognificantly before this state.
Paul L is offline   Reply With Quote
Old 10-03-2021, 05:42   #7
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: Am I pushing my bank too hard?

I reviewed the FR spec sheet and it looks to me like you are operating well within the published parameters. With a normal DOD of about 30%, the service life plot shows that you should achieve about 1700 cycles.

Note that on the constant current plot discharging at the C20 rate (20.8A) or at the C5 rate (68A), the voltage profile is flat at the 1 hour mark.

Three very important ways to improve the service life of AGM batteries:
1. Use them; don't abuse them. LA batteries need to be exercised to be healthy.
2. Use temperature compensation for all of your charging sources.
3. Fully charge the batteries after use or as frequently as is possible.

BTW, the Full River spec sheet is one of the best spec sheets that I have seen.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 10-03-2021, 05:43   #8
Registered User

Join Date: Feb 2017
Location: Occasionally in Colorado. Generally live-aboard. Eastern Caribbean last winter. Nova Scotia and Newfoundland hopefully this summer.
Boat: Antares 44i
Posts: 789
Re: Am I pushing my bank too hard?

That doesn't seem like useful information. How can one get current at 0.5% of bank capacity at absorption voltage if all chargers have already switched to float voltage before that low current is reached.

That criteria doesn't even seem relevant to my situation as it would not matter if I pulled another 100Ah out of the bank a given day or not. That energy gets put back in the bank in the bulk phase and only delays the time in the other phases by a couple hours. If you want some extended low current charging time it won't happen either way as the refrigerator runs at night but the sun does not shine.
dougweibel is offline   Reply With Quote
Old 10-03-2021, 05:44   #9
Registered User
 
OneKoolCat's Avatar

Join Date: Jan 2019
Location: Newburyport, MA
Boat: FP, Lavezzi, 40
Posts: 71
Re: Am I pushing my bank too hard?

I also use the Victron to get me all charged up. I think that if your Victron charge controller is programmed for your battery then I think you are ok on the charging end. They have some good products that do a good job charging.

I am assuming you have a 12v system. That would mean that you have 2 battery blocks pulling 70 amps each. (each of those made of 2 batteries each pulling 70 amps at 6v) From their sheet 68 amps is 0.20CA. 5 hours until dead. As long as you are not cheating too much I think you are ok. Personally, I would rather use a battery than keep it as a decoration.

I also feel that cooking with electricity works well on a boat, but I also have an electric outboard on my dinghy. If you can make some low carb bread I will swing by later.
OneKoolCat is offline   Reply With Quote
Old 10-03-2021, 05:44   #10
Registered User

Join Date: Feb 2017
Location: Occasionally in Colorado. Generally live-aboard. Eastern Caribbean last winter. Nova Scotia and Newfoundland hopefully this summer.
Boat: Antares 44i
Posts: 789
Re: Am I pushing my bank too hard?

Quote:
Originally Posted by CharlieJ View Post
BTW, the Full River spec sheet is one of the best spec sheets that I have seen.
Thanks Charlie,

It seems battery spec sheets never have exactly in info you'd like to know but I agree the FullRiver spec sheet has a lot of info.
dougweibel is offline   Reply With Quote
Old 10-03-2021, 05:45   #11
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,562
Re: Am I pushing my bank too hard?

Quote:
Originally Posted by dougweibel View Post
That doesn't seem like useful information. How can one get current at 0.5% of bank capacity at absorption voltage if all chargers have already switched to float voltage before that low current is reached.

Ideally, the point when chargers drop to float is controllable. I know the Victron solar controllers (with new-ish firmware) can switch based on end amps. And if you have their battery monitor networked to the controllers (either via VE.Smart or though a GX device with DVCC), it can use the amps sensed by the battery monitor for the change, which accounts for multiple controllers as well as loads.
rslifkin is offline   Reply With Quote
Old 10-03-2021, 06:18   #12
Registered User

Join Date: Feb 2017
Location: Occasionally in Colorado. Generally live-aboard. Eastern Caribbean last winter. Nova Scotia and Newfoundland hopefully this summer.
Boat: Antares 44i
Posts: 789
Re: Am I pushing my bank too hard?

Quote:
Originally Posted by rslifkin View Post
Ideally, the point when chargers drop to float is controllable. I know the Victron solar controllers (with new-ish firmware) can switch based on end amps. And if you have their battery monitor networked to the controllers (either via VE.Smart or though a GX device with DVCC), it can use the amps sensed by the battery monitor for the change, which accounts for multiple controllers as well as loads.
Good point. I've got two Victron solar controller, one older on some smaller panels and one new on larger panels. I checked on the newer and you have to open the 'expert settings'. The default tail current is 2.0 Amps which would be only 0.25% in my application, so pretty low already. You can change the max absorption time up from a default of 6 hours but that seems unnecessary as I do transition from absorption to float.
dougweibel is offline   Reply With Quote
Old 10-03-2021, 06:29   #13
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,541
Re: Am I pushing my bank too hard?

[QUOTE=dougweibel;3361512 You can change the max absorption time up from a default of 6 hours but that seems unnecessary as I do transition from absorption to float.[/QUOTE]

you don't fully get it and appear to want to disagree with people providing the answer to your question

Doesn't matter what your charger/controller does, all that matters is how much current the batteries accept at absorption voltage. If the current at absorption does not drop to whatever you manufacturer says equals fully charged then you aren't 100% charged. Doesn't matter if a battery monitor or smart gauge says you are of that the charger/controller went into float. People mistakenly believe they are at 100% when they are 99% partial state of charge.

There are lots of threads about this if you really what to understand. But I have lots of cruisers who don't and still get about the same life because battery life on an off grid cruising boat never matches the factory use life.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Old 10-03-2021, 06:49   #14
Registered User

Join Date: Feb 2017
Location: Occasionally in Colorado. Generally live-aboard. Eastern Caribbean last winter. Nova Scotia and Newfoundland hopefully this summer.
Boat: Antares 44i
Posts: 789
Re: Am I pushing my bank too hard?

Perhaps I don't get it but I fail to see how.

I fully understand using the criteria of absorption current falling to a certain level as a criteria for determining 100% SoC. My charge controller is currently programmed to switch from absorption to float at a current that is ~0.25% of the bank Ah capacity. The manufacturer, in a spec sheet cited in this thread as being a pretty good spec sheet, gives no guidance on what current level should be used to conclude absorption. Paul L suggests a range of 1.0% to 0.05%, a range that spans a factor of 20. I am well within that range. Are you suggesting I need to be lower in that range? Why?
dougweibel is offline   Reply With Quote
Old 10-03-2021, 07:56   #15
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,541
Re: Am I pushing my bank too hard?

Quote:
Originally Posted by dougweibel View Post
Are you suggesting I need to be lower in that range? Why?
I am 100% positive I posted what to use for your batteries to determine 100% charge.

I am now unsubscribing to this threads that has been fully answered.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Living on the HOOK sailboat W.Coast,Fla is it hard or they pushing people into marina videorov Our Community 50 15-12-2018 07:14
Advice Needed On Pushing Stuffing Box Hose Onto Shaft macbeth Plumbing Systems and Fixtures 6 24-04-2013 21:10
Pushing My Envelope While 'Kroozing' Locally CalebD The Sailor's Confessional 6 14-10-2009 17:25
Be Careful Pushing VHF Buttons JusDreaming The Sailor's Confessional 4 08-08-2009 07:53

Advertise Here


All times are GMT -7. The time now is 15:46.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.