Balmar XT170 case ground alternator - grounding

Hello,

I have just recently installed new Balmar XT170 alternator,
replacing old Hitachi on my 4JH5E Yanmar engine.

This particular alternator is case grounded, non-isolated version.
Initially, I was thinking that this will simplify my installation by
not requiring separate ground cable. Now I am thinking it was a mistake.

I am simply afraid, that in case of any problems with a ground path
through mounting foot and adjuster assembly on top of alternator,
I will potentially run through a lot of problems, including burning diodes,
when the electrical load suddenly disappears.

Moreover, case grounding depends on proper connection between
engine block and batteries. This is the wire bolted on bell house of the engine,
and in my case is sized properly for starter motor intermittent use,
but not for charging large house bank with continuous 170 Amps for hours.
So I will need to replace this wire too.


So, as a safety measure, I would like to run separate ground wire,
assuring proper connection between alternator and negative side
of electrical system.

But here is a problem: where do I attach ground wire to the case of alternator:

The whole case is cover with paint, and the only threaded wholes are either
tiny (M5 thread), or have already their purpose (temperature sensor)
Friend of mine suggested using M10 bolt securing foot of the alternator,
which maybe an option, but there is no contact surface between
power lug and the case of alternator due to sliding spacer needed to mount
the foot securely without stressing the alternator assembly.

I am leaning toward sanding some of the paint around one of those existing
M5 holes, and bolting a proper ground power lug into that place.

Or, should I just stop worrying, and assume that ground current will always
flow through the case (all 170 Amps of it), and not worry about it at all?

Any advice?

Przemek
S/V Festina Lente
Attached Thumbnails
Click image for larger version

Name:	EE24025B-AC9A-4223-B477-76A19BB518C5.jpg
Views:	7003
Size:	299.3 KB
ID:	228426  
karwas is offline   Reply With Quote
Old 10-12-2020, 15:59   #2
Marine Service Provider
 
Scott Berg's Avatar

Join Date: Jul 2011
Location: Aboard
Boat: Seaton 60' Ketch
Posts: 1,341
Re: Balmar XT170 case ground alternator - grounding

Attach the ground to the pivot bolt or an unused lock bolt fitting
__________________
Scott Berg
WAØLSS
SV CHARDONNAY
Scott Berg is offline   Reply With Quote
Old 10-12-2020, 22:52   #3
Registered User

Join Date: Aug 2011
Location: San Francisco, US
Boat: Bénéteau, Oceanis 45
Posts: 8
Images: 2
Re: Balmar XT170 case ground alternator - grounding

Quote:
Originally Posted by Scott Berg View Post
Attach the ground to the pivot bolt or an unused lock bolt fitting
I will consider one of unused lock bolt fittings on the upper flange (not shown on the picture I've posted), but pivot bolt in the foot, would rather be not the best option IMHO,
because the power lug will rest on small surface of the split spacer sitting
in the hole of the foot of the alternator.
karwas is offline   Reply With Quote
Old 10-12-2020, 23:22   #4
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,067
Re: Balmar XT170 case ground alternator - grounding

Quote:
Originally Posted by karwas View Post
Hello,

I have just recently installed new Balmar XT170 alternator,
replacing old Hitachi on my 4JH5E Yanmar engine.

This particular alternator is case grounded, non-isolated version.
Initially, I was thinking that this will simplify my installation by
not requiring separate ground cable. Now I am thinking it was a mistake.

I am simply afraid, that in case of any problems with a ground path
through mounting foot and adjuster assembly on top of alternator,
I will potentially run through a lot of problems, including burning diodes,
when the electrical load suddenly disappears.

Moreover, case grounding depends on proper connection between
engine block and batteries. This is the wire bolted on bell house of the engine,
and in my case is sized properly for starter motor intermittent use,
but not for charging large house bank with continuous 170 Amps for hours.
So I will need to replace this wire too.


So, as a safety measure, I would like to run separate ground wire,
assuring proper connection between alternator and negative side
of electrical system.

But here is a problem: where do I attach ground wire to the case of alternator:

The whole case is cover with paint, and the only threaded wholes are either
tiny (M5 thread), or have already their purpose (temperature sensor)
Friend of mine suggested using M10 bolt securing foot of the alternator,
which maybe an option, but there is no contact surface between
power lug and the case of alternator due to sliding spacer needed to mount
the foot securely without stressing the alternator assembly.

I am leaning toward sanding some of the paint around one of those existing
M5 holes, and bolting a proper ground power lug into that place.

Or, should I just stop worrying, and assume that ground current will always
flow through the case (all 170 Amps of it), and not worry about it at all?

Any advice?

Przemek
S/V Festina Lente
Balmar think the case grounding is sufficient (presumably).

Upgrade the engine ground cable if you believe it is insufficient; what size is it ATM?

I can't imagine any circumstance where the case ground could suddenly go open circuit due to the mounting bolts.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 11-12-2020, 02:35   #5
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,890
Images: 241
Re: Balmar XT170 case ground alternator - grounding

What you are proposing is just an auxiliary negative ground path, so anything you provide will be an improvement over just the case ground.
FWIW: The current carrying capacity, of an M5 bolt, is roughly 50 - 75 Amps, when used on a circuit breaker or terminal strip.
This is a case of bigger is better.


According to Carling (Cct Breakers)
8-32 screw terminals are rated up to 30 amps;
10-32 (near = M5) screw terminals are rated up to 50 amps.
Carling E-Series circuit breakers also offer 1/4-20 screw terminals, which are rated to a maximum of 100 amps.
And F-Series breakers offer 3/8-16 screw terminals rated up to 700 amps.
https://www.carlingtech.com/circuit-termination
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 11-12-2020, 09:45   #6
Registered User

Join Date: Apr 2012
Posts: 353
Re: Balmar XT170 case ground alternator - grounding

Quote:
Originally Posted by GordMay View Post
What you are proposing is just an auxiliary negative ground path, so anything you provide will be an improvement over just the case ground.
FWIW: The current carrying capacity, of an M5 bolt, is roughly 50 - 75 Amps, when used on a circuit breaker or terminal strip.
This is a case of bigger is better.


According to Carling (Cct Breakers)
8-32 screw terminals are rated up to 30 amps;
10-32 (near = M5) screw terminals are rated up to 50 amps.
Carling E-Series circuit breakers also offer 1/4-20 screw terminals, which are rated to a maximum of 100 amps.
And F-Series breakers offer 3/8-16 screw terminals rated up to 700 amps.
https://www.carlingtech.com/circuit-termination

I think you are missing a key contact point for cables terminated by terminal bolts. The major current flow is via the terminal to terminal contact. The mounting screw is only used to clamp the terminals together. That's why terminal makers get away with SS and mild steel bolts in their terminals and not more conductive copper/brass derived materials.
If those steel bolts are not correctly pasivated and torqued they will very quickly produce power loss and heat at the junction. There is a current crop of industrial batteries with 8 MM SS bolts uses as terminals extending from the lead post of the battery. A small amount of corrosion on the flat lead surface of the post is a major issue on industrial equipment where they are used.
Good luck with your vessel!
oleman is offline   Reply With Quote
Old 11-12-2020, 10:27   #7
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,554
Re: Balmar XT170 case ground alternator - grounding

You can (very carefully) drill and tap that candidate hole for a larger bolt. Just don't drill through into anything vital. If you do that in situ drill very slowly and vacuum up the tailings. It would be better to dis-assemble the alternator to do this. And remove the paint under where the terminal will go.
stormalong is online now   Reply With Quote
Old 11-12-2020, 11:23   #8
Registered User
 
Ween's Avatar

Join Date: Jul 2020
Location: Bahamas now
Boat: Valiant 42
Posts: 95
Re: Balmar XT170 case ground alternator - grounding

If you ask Balmar they will tell you mount a ground to one of the unused mounting holes at the top. I know ;-)
Ween is offline   Reply With Quote
Old 11-12-2020, 12:34   #9
Registered User

Join Date: Feb 2015
Posts: 58
Re: Balmar XT170 case ground alternator - grounding

Why don’t you sand the paint off at the temp sensor position, put ground lug against case, then temp sensor lug on top of that?
Copper lug has good thermal transfer.
12 v is from lug to case, not through the stud.
knotnline is offline   Reply With Quote
Old 11-12-2020, 13:30   #10
Registered User

Join Date: Jul 2016
Location: Atlantic Highlands, NJ
Boat: Swallowed the anchor
Posts: 983
Re: Balmar XT170 case ground alternator - grounding

Quote:
Originally Posted by Ween View Post
If you ask Balmar they will tell you mount a ground to one of the unused mounting holes at the top. I know ;-)
^^^This^^^
kenbo is offline   Reply With Quote
Old 16-12-2020, 07:10   #11
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,891
Re: Balmar XT170 case ground alternator - grounding

I am not impressed with a new 170 amp alternator without a grounding post. Balmar must have been taken over by the marketing department.

They probably count on the fact that you will not be able to pull more than 100 amps out of it with a single v belt.
donradcliffe is offline   Reply With Quote
Old 16-12-2020, 08:39   #12
Registered User

Join Date: Jul 2016
Location: Atlantic Highlands, NJ
Boat: Swallowed the anchor
Posts: 983
Re: Balmar XT170 case ground alternator - grounding

Quote:
Originally Posted by donradcliffe View Post
I am not impressed with a new 170 amp alternator without a grounding post. Balmar must have been taken over by the marketing department.

They probably count on the fact that you will not be able to pull more than 100 amps out of it with a single v belt.
And you won't get 170A out of it for long either. No miracles in that alternator, it's still small case and the only safe way to get more amperage is more, larger wires in the stator and that means more mass and a larger case. But I'm sure it appeals to the buy high amp and derate crowd.
kenbo is offline   Reply With Quote
Old 16-12-2020, 09:01   #13
Registered User
 
MARC D's Avatar

Join Date: Oct 2009
Location: Canada
Boat: Shopping...
Posts: 309
Re: Balmar XT170 case ground alternator - grounding

For about the same application, I was recommended by a Balmar tech to use 6 series alternator instead of XT170 as this one was more intended for GM gas engines.

6 series alt. have dedicated negative post.
__________________
Sur le même bateau, l'homme de terre et l'homme de mer ont deux buts différents. Le but du premier est d'arriver, le but du deuxième est de repartir.
La terre nous tire vers le passé, la mer les pousse vers le futur.- Albert Londres, 1927
MARC D is offline   Reply With Quote
Old 13-11-2021, 02:06   #14
Registered User

Join Date: Jan 2020
Location: Plymouth UK
Boat: Beneteau Oceanis 45
Posts: 11
Re: Balmar XT170 case ground alternator - grounding

Extending an older post. I am thinking of the same alternator on a Yanmar 4JH5E. Did you resolve the negative ground? My existing Valeo is rated to 120Ah but only delivering 40Ah at 2000revs. Have installed a Balmar Ext Smart Reg ARS-5 but hasn't improved performance. Think my pos cable rating should accommodate higher amps and sizing of the XT170 fits the Yanmar block. The Balmar 200 does not. Existing Valeo alternator has a lighter weight negative cable attached to rear casing. But the engine block ground connection has a more substantial cable nowhere near as thick/AWG rating as the pos cable. Had not thought through the fact that case ground means the engine black ground cable (back to battery etc) would need to be the same rating as the pos, although in my current OEM set up presumably this is currently spec's for 120 Ah anyway.. How did you resolve your neg/ground install and also importantly what level of Ah delivery is the XT170 giving you now?
UK Ade is offline   Reply With Quote
Old 13-11-2021, 05:08   #15
Registered User

Join Date: Apr 2013
Posts: 35
Re: Balmar XT170 case ground alternator - grounding

Okay so what you are referring to as a case ground is in fact the 12 volt negative return path to the battery. At the risk of being flamed (I don’t care) there is no ground connection in your circuit. There is a positive and a negative path from the source. Although in this instance the alternator becomes a source when operating. If you think the bolts holding your alternator to the engine block are not of sufficient capacity to carry the charging current go ahead and add another wire to the block or direct to the battery. It won’t matter much. The path from the engine block to the battery is a different matter. If this was spec’d for example to carry a charging current from the battery of around 75 amps then you may need to increase it. I doubt it, if as like most production boats(?) this circuit also carries the starting current from the battery.
Put an ammeter clamp on the negative to the battery when it is at low charge state and run the engine at WOT. This will tell you if you need to update the cable. And I wouldn’t expect the reading to be anywhere close to 170 amps.
__________________
Consume, be silent, die
Davidla is offline   Reply With Quote
Reply

Tags
alternator, balmar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
[SOLD] Balmar Regulator, 100A Alternator & 35A alternator JimJohnston General Classifieds (no boats) 0 07-10-2018 19:36
Externally Rectifying Balmar small case alternators SoonerSailor Electrical: Batteries, Generators & Solar 1 23-08-2018 03:41
DC Negative Grounding to grounding plate - Isolated shaft Thistle1969 Electrical: Batteries, Generators & Solar 17 27-09-2015 04:51
Balmar 614 regulator / Balmar Alternator help Strait Shooter Electrical: Batteries, Generators & Solar 16 25-08-2015 13:08
For Sale: Dry Case Waterproof Phone, Camera & MP3 Case - NEW off-the-grid Classifieds Archive 2 11-07-2012 14:58

Advertise Here


All times are GMT -7. The time now is 09:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.