Re: Breaker sizing (Amps) in breaker panel

I think some of you are mixing house code and abyc code... 18awg isn't even allowed for power wires in a boat.

16 is min. I would run everything at 14 min

To answer question. Yes you size breakers to loads and what the device calls for in its manual . They can always be swapped later if you need to add a small load device down the road.
smac999 is offline   Reply With Quote
Old 25-04-2017, 11:42   #17
Registered User

Join Date: Jan 2017
Location: Sea of Cortez
Boat: Kelley-Peterson 46 cutter
Posts: 890
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by smac999 View Post
I think some of you are mixing house code and abyc code... 18awg isn't even allowed for power wires in a boat.

16 is min. I would run everything at 14 min

To answer question. Yes you size breakers to loads and what the device calls for in its manual . They can always be swapped later if you need to add a small load device down the road.
The question was about 18 gauge wire, and wire that small needs a low-amp fuse or breaker. I would use 5 amp - if I had any wire that small. I normally use 14 ga minimum size.

Breakers are to prevent overcurrent heat and fires. Over half of all boat fires are electrical, and fire is the most dangerous situation on a boat. Breakers must be sized to protect the wires, without regard to load. If a device needs a smaller breaker because a short can cause a fire within that device, then size the breaker to the device.
If you have 14 ga throughout your boat, your standard 15 amp breakers are correct unless an electronic device demands a smaller fuse (breaker).
KP44 is offline   Reply With Quote
Old 25-04-2017, 11:43   #18
Registered User

Join Date: Jul 2016
Location: Anguilla
Boat: CheoyLee Offshore 33
Posts: 644
Images: 1
Send a message via Skype™ to masonc
Re: Breaker sizing (Amps) in breaker panel

OCPD (breakers) are not designed to protect equipment, they are designed and rated to protect the conductors.
masonc is offline   Reply With Quote
Old 25-04-2017, 11:58   #19
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by masonc View Post
OCPD (breakers) are not designed to protect equipment, they are designed and rated to protect the conductors.
That is correct, but
For example I have a circuit I added last weekend, a 16ga wire running to the cockpit to power two LED lights on my Bimini, the LED's will draw less than 1 amp, the 16 ga wire can safely carry 25 amps (according to Blue seas circuit wizard app).
I used a 5 amp CB, cause if for any reason I draw more than that, I want it to trip and alert me that something is wrong.
I don't know maybe the light shorted out internally and could set the Bimini on fire?
There is logic to sizing the CB to the load and not just the conductor
a64pilot is offline   Reply With Quote
Old 25-04-2017, 12:31   #20
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by a64pilot View Post
That is correct, but
For example I have a circuit I added last weekend, a 16ga wire running to the cockpit to power two LED lights on my Bimini, the LED's will draw less than 1 amp, the 16 ga wire can safely carry 25 amps (according to Blue seas circuit wizard app).
I used a 5 amp CB, cause if for any reason I draw more than that, I want it to trip and alert me that something is wrong.
I don't know maybe the light shorted out internally and could set the Bimini on fire?
There is logic to sizing the CB to the load and not just the conductor
Absolutely! :thumb : A smoldering component is not going to worth a damn just because the wire was larger than required an was fused for the wire rating.
Don't take me wrong, I am a proponent of over sized wire if for nothing but line lose on a long run.
Cadence is offline   Reply With Quote
Old 26-04-2017, 04:12   #21
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,890
Images: 241
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by a64pilot View Post
... There is logic to sizing the CB to the load and not just the conductor
There is logic to DOWN-sizing the CB to the load and not just the conductor.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is online now   Reply With Quote
Old 26-04-2017, 07:30   #22
Registered User
 
Tasso's Avatar

Join Date: Apr 2017
Location: Newport RI
Boat: C&C 37/CB
Posts: 47
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by Cadence View Post
That's an excellent comment. You don't want the smallest wire to be the fuse.
I installed an in-line fuse with each of my LED fixtures as the pigtails on these were about 22ga. On older boats - lighting circuits had 15 amp breakers - with LED lighting you can reduce this if you like - as the current is reduced by 90%...

Wire size determines protection. Wire needs to be big enough to power connected equipment.

I often oversize wiring on circuits that run constantly - as on my 25 amp solar system I used 10ga and some 6ga wire to reduce loss... No need to increase the breaker size on these.
Tasso is offline   Reply With Quote
Old 26-04-2017, 11:49   #23
Registered User

Join Date: Nov 2015
Location: Fl
Boat: Wauquiez Hood 38
Posts: 1,187
Re: Breaker sizing (Amps) in breaker panel

I often fuse the load as close to the load as possible in addition to the appropriate sized CB or fuse for the wire at the source end. Works for me.
__________________
Keth

Boat Vinyl Lettering and Graphics
Bleemus is offline   Reply With Quote
Old 26-04-2017, 11:52   #24
Registered User

Join Date: Jul 2016
Location: Anguilla
Boat: CheoyLee Offshore 33
Posts: 644
Images: 1
Send a message via Skype™ to masonc
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by Bleemus View Post
I often fuse the load as close to the load as possible in addition to the appropriate sized CB or fuse for the wire at the source end. Works for me.
What's the point? If equipment needs fusing, it will have an equipment fuse.
masonc is offline   Reply With Quote
Old 26-04-2017, 12:22   #25
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: Breaker sizing (Amps) in breaker panel

A breaker can be a equipment protection device. The Thermal and Hydraulic Magnetic breakers used in boats are very similar to the same devices used as equipment protection devices in telecom equipment for instance.

Not all equipment that needs a protection device comes with it (many smaller pumps for instance).

Here is a breaker selection article from one of the marine breaker builders
http://airpax.sensata.com/pdfs/guidetoprotection.pdf
and another from the biggest marine breaker builder
http://www.carlingtech.com/sites/def...Protection.pdf

Both are technical but interesting.
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 26-04-2017, 12:26   #26
Registered User

Join Date: Nov 2015
Location: Fl
Boat: Wauquiez Hood 38
Posts: 1,187
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by masonc View Post
What's the point? If equipment needs fusing, it will have an equipment fuse.
True. Some things come with a fuse. Some dont. If they dont I will fuse it in relation to its draw as measured in use.
__________________
Keth

Boat Vinyl Lettering and Graphics
Bleemus is offline   Reply With Quote
Old 26-04-2017, 21:03   #27
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by Bleemus View Post
I often fuse the load as close to the load as possible in addition to the appropriate sized CB or fuse for the wire at the source end. Works for me.
That is a trouble shooting nightmare. Don't double fuse.
smac999 is offline   Reply With Quote
Old 27-04-2017, 04:04   #28
Registered User
 
Tasso's Avatar

Join Date: Apr 2017
Location: Newport RI
Boat: C&C 37/CB
Posts: 47
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by smac999 View Post
That is a trouble shooting nightmare. Don't double fuse.
Not sure how you'd install a nav system properly without doing this. I have a single breaker for "Nav" that goes to a sub-fuse panel holding individual fuses for each display, my GPS antenna and the NMEA 2000 backbone... These fuses will never fail unless something has gone seriously wrong. I also giggle the fuses from time to time to fight corrosion.
Tasso is offline   Reply With Quote
Old 27-04-2017, 04:51   #29
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by smac999 View Post
That is a trouble shooting nightmare. Don't double fuse.
Quite the contrary. One of the often overlooked functions of multiple object electrical systems is that of selectivity (isolating a problem electrical appliance when it develops trouble and leaving the remaining equipment operational). If I run a circuit up to my steering pedestal and then tap it for my AP, radar, and chartplotter, a problem with the AP trips the feeding breaker and I loose power to all three. Can always hand steer clear of the oncoming Aircraft Carrier. Three independent fuses at the pedestal solves this problem. Obviously three independent circuits would provide a similar function just a lot more wiring.
Frankly is offline   Reply With Quote
Old 28-04-2017, 05:30   #30
Registered User

Join Date: Nov 2015
Location: Fl
Boat: Wauquiez Hood 38
Posts: 1,187
Re: Breaker sizing (Amps) in breaker panel

Quote:
Originally Posted by Frankly View Post
Quite the contrary. One of the often overlooked functions of multiple object electrical systems is that of selectivity (isolating a problem electrical appliance when it develops trouble and leaving the remaining equipment operational). If I run a circuit up to my steering pedestal and then tap it for my AP, radar, and chartplotter, a problem with the AP trips the feeding breaker and I loose power to all three. Can always hand steer clear of the oncoming Aircraft Carrier. Three independent fuses at the pedestal solves this problem. Obviously three independent circuits would provide a similar function just a lot more wiring.
Exactly.
__________________
Keth

Boat Vinyl Lettering and Graphics
Bleemus is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
kyocera Solar Panel Volts no Amps deepthought Electrical: Batteries, Generators & Solar 28 04-06-2019 07:08
Solar amps in, consumption amps out, check my math please? Jarel Design Electrical: Batteries, Generators & Solar 24 26-04-2017 16:13
Amps v Amp hours v Amps/Hr StuM Electrical: Batteries, Generators & Solar 255 25-01-2016 14:21
Solar Panel Max Amps zboss Marine Electronics 17 16-08-2015 11:48
Sailboat Solar Panel Sizing silviris Electrical: Batteries, Generators & Solar 47 08-05-2013 15:51

Advertise Here


All times are GMT -7. The time now is 08:29.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.