Old 15-07-2019, 10:25   #16
Registered User

Join Date: Nov 2018
Location: Panama
Boat: Norseman 447
Posts: 1,628
Re: Burned up capacitor on generator

Like many things, capacitors are theoretically simple, but not all are created equal. When you look at the “ratings” you will typically see just the capacitance and the maximum voltage. But there are a number of other “ratings" that you will only find if you can research a real manufacturer’s data sheet. Temperatures, equivalent series resistance, maximum current and a number of others. Just matching the capacitance and voltage ratings is not enough. For example, a "motor starting" capacitor only passes current while the motor is starting, ie very intermittent duty. A motor-running capacitor carries current whenever the motor is running. The former is unlikely to last long in the latter application.
Bycrick is offline   Reply With Quote
Old 17-07-2019, 06:53   #17
Registered User

Join Date: Apr 2019
Posts: 614
Re: Burned up capacitor on generator

Got the new cap in and all is well. One thing that I notice is that when the gen is started the hz display shows zero. As soon as I switch on a load like the water heater or battery charger it shoots up to 60 but I want to make sure that is normal.
crayiii is offline   Reply With Quote
Old 17-07-2019, 09:59   #18
Registered User

Join Date: Apr 2019
Posts: 614
Re: Burned up capacitor on generator

Also noticed that with a small load 30%, the voltage was reading about 130v. I didn't put anymore load on it to see if it dropped out of dear of freeing something. RPM is Rick solid at 3600 and the Hz was between 58 and 60.
crayiii is offline   Reply With Quote
Old 17-07-2019, 11:41   #19
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Burned up capacitor on generator

Quote:
Originally Posted by crayiii View Post
Got the new cap in and all is well. One thing that I notice is that when the gen is started the hz display shows zero. As soon as I switch on a load like the water heater or battery charger it shoots up to 60 but I want to make sure that is normal.


It’s not normal for mine, but then I have an electric water pump so it never is at zero load.
Before installing the pump, I don’t think I monitored Hz.
a64pilot is offline   Reply With Quote
Old 17-07-2019, 11:46   #20
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Burned up capacitor on generator

Quote:
Originally Posted by crayiii View Post
Also noticed that with a small load 30%, the voltage was reading about 130v. I didn't put anymore load on it to see if it dropped out of dear of freeing something. RPM is Rick solid at 3600 and the Hz was between 58 and 60.


You can trim the voltage by changing the uf rating of the Cap.
However I’d consider 125V normal, I know you said 130 and that’s a little high.

Page 2 gives you the allowable tolerances
https://www.pge.com/includes/docs/pd..._tolerance.pdf
a64pilot is offline   Reply With Quote
Old 17-07-2019, 12:17   #21
Registered User

Join Date: Apr 2019
Posts: 614
Re: Burned up capacitor on generator

Here's what I heard from the dealer:

On your boat, with everything set to on (aircon chargers water heaters) we had to crank up to 130 for the appliances not to shut down due to temporary low voltage.
All electric apparatus should be ok with voltage set between 110 and 140V.
Should you prefer to lower this voltage you will need a capacitor with slight lower capacitance.
crayiii is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator Capacitor sailorboy1 Electrical: Batteries, Generators & Solar 34 14-08-2018 05:00
What Does the Capacitor in a Generator Do? scoobert Electrical: Batteries, Generators & Solar 16 28-07-2013 03:21
Zener Diode or Capacitor with mcck Onan Control-o-Matic Genset? sdowney717 Electrical: Batteries, Generators & Solar 0 22-11-2011 09:02
Need a new capacitor in Panama Meck Electrical: Batteries, Generators & Solar 4 19-03-2011 18:38
Split Capacitor on Windlass Motor Terminals - Why? Zul Anchoring & Mooring 2 16-11-2009 08:14

Advertise Here


All times are GMT -7. The time now is 09:30.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.