I do quite well with DC systems and my like new/used panel has an AC side of course. I have attached a drawing of what the beakers look like on the inside of the panel.
I have run the #8/3 from to shore power in receptacle to the panel and thought I would run it by the powers to be here as to where I connect them. First note: The upper 3 breakers, labeled 1,2 and 3, have a single toggle. In other words, toggle to power on and all 3 close.
That being said, I am assuming that the black (hot) wire goes to the copper buss bar. White (neutral) goes to #2 breaker and the ground ties common to all device grounds. Is this right?
Attached Thumbnails
Click image for larger version

Name:	Aug_02_001.JPG
Views:	180
Size:	95.9 KB
ID:	44311  
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 02-08-2012, 16:40   #2
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Calling all AC Guru's

Ground should bypass breakers and connect direct to ground buss.

So Hot/black goes to one breaker (one connected via buss to lower breakers). White, neutral goes to second breaker and then to neutral buss. Ground goes direct to ground buss.
sailorchic34 is offline   Reply With Quote
Old 02-08-2012, 16:57   #3
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: Calling all AC Guru's

You have a three pole circuit breaker. Every circuit breaker has a load side and a line side. You need to id which is which and connect the incoming shore power legs (L1: black; L2: red and N: white) to the appropriate line sides of the three poles of the circuit breaker. To help in the id, the load of each pole will got to its respective bus bar; L1, L2 and N. As SailorChic above states, the safety ground wire does not go through a circuit breaker but goes directly to the safety ground bus, barring a galvanic isolator installation.

One note: DO NOT SCREW THIS UP. If your are the least bit unsure about what you are doing, find a qualified marine electrician and pay him/her for an hour's worth of education.I
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 02-08-2012, 17:40   #4
Registered User
 
ExRonin's Avatar

Join Date: May 2012
Posts: 23
This appears to be a standard 30A AC shore power breaker. Note "APPEARS", without actual part numbers we can't be sure. Per your drawing: Wiring would be Black (Hot) to 3, White (Neutral) to 2 and Green (Ground) to 1. Note, ground is not on the breaker per se, but is needed to detect reverse polarity on this arrangement. As Charlie say DO NOT, if you have any doubts, do this wiring yourself. Hire a qualified marine electrician. Mistakes here can have very bad consequences.
ExRonin is offline   Reply With Quote
Old 02-08-2012, 18:36   #5
Registered User
 
Roy M's Avatar

Join Date: Feb 2007
Location: Southwestern Yacht Club, San Diego, CA
Boat: Searunner 40 trimaran, WILDERNESS
Posts: 3,175
Images: 4
Re: Calling all AC Guru's

PLEASE, check out this website: Resources*—*Blue Sea Systems

Blue Sea makes electrical components of the highest quality, and they provide some of the best info available to folks regarding how things work and how they should be installed.

Specifically: http://bluesea.com/files/resources/i...tions/6637.pdf
Roy M is offline   Reply With Quote
Old 02-08-2012, 18:44   #6
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,475
Images: 5
Re: Calling all AC Guru's

Thanx evryone...as stated, I know green (ground) ties to all the grounds of outlets, charger and so on...and yes to a ground buss.
ExRonin, I agree the black (hot) goes to 3 but to the copper buss bar which goes to 3 via the red wire indicated on the diagram which is the direction of the flow to the the other side of the breaker. I think.
Then white goes to 2. I'm not clear however, how to tie the device whites in. A white wire from the other side of 2, to a neutral buss?
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 02-08-2012, 18:46   #7
Registered User
 
Roy M's Avatar

Join Date: Feb 2007
Location: Southwestern Yacht Club, San Diego, CA
Boat: Searunner 40 trimaran, WILDERNESS
Posts: 3,175
Images: 4
Re: Calling all AC Guru's

Celestialsailor: please see http://bluesea.com/files/resources/i...tions/6637.pdf
Roy M is offline   Reply With Quote
Old 02-08-2012, 18:56   #8
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Calling all AC Guru's

Correct on the white from other side of two to the neutral buss.

BTW I have a Blue Seas 120V panel on my boat. Good stuff.

BTW I assume that the panel with three main breakers is a 220V panel but with the 35' boat the OP has, he probably has a 30Amp 120V system..
sailorchic34 is offline   Reply With Quote
Old 02-08-2012, 19:00   #9
Registered User
 
ExRonin's Avatar

Join Date: May 2012
Posts: 23
Celestial, yes, the load side of neutral (white) goes to a separate neutral bus. Load wiring is as follows for each load. Black goes to the individual breaker for that load (fed by your copper bus from the main shore power breaker. It is then good practice to have two common bus bars, one for neutral (white) fed from the load side of the shore power neutral (your #2), and a second for grounds (green).
ExRonin is offline   Reply With Quote
Old 02-08-2012, 19:27   #10
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,475
Images: 5
Re: Calling all AC Guru's

Quote:
Originally Posted by sailorchic34 View Post
Correct on the white from other side of two to the neutral buss.

BTW I have a Blue Seas 120V panel on my boat. Good stuff.

BTW I assume that the panel with three main breakers is a 220V panel but with the 35' boat the OP has, he probably has a 30Amp 120V system..
You are correct that I am wiring 30A/120. My assumption was the #1 breaker was a feedback for reverse polarity but I could be wrong and is for 220AC. Which I will not use.
Thanx Roy M for the link. I think you specifically wanted me to read the "Test" portion of it which is a safe way of doing it before i through the switch to wake up the Monster...
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 02-08-2012, 19:30   #11
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,475
Images: 5
Re: Calling all AC Guru's

Quote:
Originally Posted by ExRonin View Post
Celestial, yes, the load side of neutral (white) goes to a separate neutral bus. Load wiring is as follows for each load. Black goes to the individual breaker for that load (fed by your copper bus from the main shore power breaker. It is then good practice to have two common bus bars, one for neutral (white) fed from the load side of the shore power neutral (your #2), and a second for grounds (green).
Great...I feel more confident now. Any recommendations on busses for neutral and ground? I"m thinking something enclosed the way I end up slithering around the boat.
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 02-08-2012, 19:41   #12
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Calling all AC Guru's

Well Ideally the buss bars are located behind the 120 panel, out of harms way. Here's a link to a nice buss bar. WM has them too.

Blue Sea Systems Busbars
sailorchic34 is offline   Reply With Quote
Old 02-08-2012, 19:46   #13
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,475
Images: 5
Re: Calling all AC Guru's

Thats what I had in mind and used similar with the DC. I epoxied wood behind the panel against the upper hull side, then screwed the buss to that. With the AC and the potential of touching it while working on the system, I will probably cover the busses with clear Tupperware.
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 02-08-2012, 19:52   #14
Moderator Emeritus
 
sailorchic34's Avatar

Cruisers Forum Supporter

Join Date: Feb 2011
Location: SF Bay Area
Boat: Islander 34
Posts: 5,486
Re: Calling all AC Guru's

Always good to protect them from the hot side. In a normal world its safe to touch the neutral and ground. On a boat, your never sure if the neutral will get hot with a reversed shore outlet. Its the hot legs that will light up your life if your in circuit.

BTW the reverse polarity led runs from hot to neutral, well really neutral to hot, so when the hot leg is on the neutral side the led lights.
sailorchic34 is offline   Reply With Quote
Old 02-08-2012, 20:43   #15
Registered User
 
Morganministry's Avatar

Join Date: Nov 2009
Location: Klamath River, California
Boat: Buccaneer 240
Posts: 169
Re: Calling all AC Guru's

Quote:
Originally Posted by Celestialsailor View Post
Great...I feel more confident now. Any recommendations on busses for neutral and ground? I"m thinking something enclosed the way I end up slithering around the boat.
The Neutral (White) wires will not have a charge as long as the connection isn't broken between the buss and the power supply. So a neutral buss doesn't need to be covered.

Scott
__________________
www.morganfamilyministry.com
Morganministry is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 13:40.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.