Hooking up my new (to me) boat to shore power and plugging things in resulted in it tripping the circuit breaker, usually on the boat's main AC board but sometimes at the shore pedestal (see attached pics).. I think I've ruled out a DC leak from batteries on board (it still trips with all batteries disconnected). I've also tested the Galvanic Isolator and the results are within range: 1.284v and 1.266v

But, with the Galvanic Isolator completely disconnected I can plug in appliances without it tripping. There doesn't seem to be an self-test function on it which, from my understanding could cause the tripping.

I've reached my limit of where Internet research has brought me and not sure what to do next, although it seems to be working the Galvanic Isolator seems to be at least part of the problem. Any ideas of what I should do next?

P.S. Sometimes it would take multiple minutes with just a phone charger plugged in to trip, sometimes I'd have to add an extra appliance to make it trip and sometimes it would trip immediately something was plugged in.
Attached Thumbnails
Click image for larger version

Name:	20220723_191003.jpg
Views:	61
Size:	444.3 KB
ID:	264758   Click image for larger version

Name:	20220916_093227.jpg
Views:	41
Size:	421.4 KB
ID:	264759  

Intifada is offline   Reply With Quote
Old 21-09-2022, 07:11   #2
Registered User

Community Sponsor

Join Date: Nov 2019
Location: South Carolina
Boat: Philip Rhodes Custom 71'
Posts: 192
Re: Circuit Breaker Tripping (Galvanic Isolator)

You probably have the neutral and the ground connected together in the breaker box. First thing to do is remove that.
__________________
Ann-Marie Foster
YANDINA is offline   Reply With Quote
Old 22-09-2022, 20:17   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Circuit Breaker Tripping (Galvanic Isolator)

when you test with the galvanic isolator out, are you connecting the 2 green cables back together to reconnect the boats ground? or leaving them off, so you no longer have a ground.

I'm guessing the later. try with them connected back. if it trips again then it's not the isolator, it's just the fact that you disconnected the ground to the dock
smac999 is offline   Reply With Quote
Reply

Tags
galvanic isolator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Engine circuit breaker tripping Mickeyrouse Engines and Propulsion Systems 51 02-09-2020 12:26
DC circuit breaker tripping on Kohler generator JSurr Electrical: Batteries, Generators & Solar 6 15-06-2017 23:35
Shore Power Circuit Breaker Tripping Often FollowingCs Electrical: Batteries, Generators & Solar 35 13-03-2017 18:29
Keep tripping main 20 amp circuit breaker Popatop Electrical: Batteries, Generators & Solar 8 26-08-2015 13:09
Windlass keeps tripping circuit breaker MinorI Electrical: Batteries, Generators & Solar 36 19-01-2015 19:32

Advertise Here


All times are GMT -7. The time now is 15:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.