Old 28-05-2013, 15:41   #1
Registered User
 
mrybas's Avatar

Join Date: May 2010
Location: East Coast USA or out cruising
Boat: Lock Crowther 150
Posts: 665
Confused on Wire Gauge from Panels to Charge Controller

Hi,
I am adding two Sunpower 245's in parallel to my 12V electrical system. It is roughly 30' one way from the panel to the charge controller (OutBack Flex 60). The panel is rated at 40.5 volts. I should be looking at a wire gauge chart for 40.5Vs, not 12V, right?
Here is my math: 2 x 245W panels= 490W
490W/40.5V=12 Amps
One way distance 30' x2= 60'

According to a wire gauge calculator website @ 3% loss I need 8G wire. Does this sound correct?

From the charge controller to the batteries is 15'. This voltage would be stepped down to 12V.
490W/12V=40.8 Amps
15' x 2= 30'
@ 3% loss, I would need 4G wire.

Does this sound correct?
mrybas is offline   Reply With Quote
Old 28-05-2013, 17:40   #2
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,461
Re: Confused on Wire Gauge from Panels to Charge Controller

Well, you are approximately correct and there is nothing unsafe about your wire sizes. Is your panel rated at 40.5 V at its maximum power point (Vmp)? I would have thought that the voltage would be lower and the current higher. It is the current at the maximum power point (Imp) that you should size your wiring from the panel to the controller. Take the Imp and double it for two panels and use that in your calculations.

Make sure that you put a fuse or circuit breaker near the battery sized for 50 amps. There is no need (contrary to a lot of bad advice on this site) for another fuse at the panels. 8 gauge wire is plenty big to handle all of the current that the panels can put out.

David
djmarchand is offline   Reply With Quote
Old 28-05-2013, 17:52   #3
Registered User
 
mrybas's Avatar

Join Date: May 2010
Location: East Coast USA or out cruising
Boat: Lock Crowther 150
Posts: 665
Re: Confused on Wire Gauge from Panels to Charge Controller

Quote:
Originally Posted by djmarchand View Post
Well, you are approximately correct and there is nothing unsafe about your wire sizes. Is your panel rated at 40.5 V at its maximum power point (Vmp)? I would have thought that the voltage would be lower and the current higher. It is the current at the maximum power point (Imp) that you should size your wiring from the panel to the controller. Take the Imp and double it for two panels and use that in your calculations.

Make sure that you put a fuse or circuit breaker near the battery sized for 50 amps. There is no need (contrary to a lot of bad advice on this site) for another fuse at the panels. 8 gauge wire is plenty big to handle all of the current that the panels can put out.

David
Hi David,
The Vmpp is 40.5V. The Imp is 6.05A. So I need to size for 6.05A @ 40.5V, right?
Attached Files
File Type: pdf SunPower 245.pdf (547.0 KB, 59 views)
mrybas is offline   Reply With Quote
Old 28-05-2013, 18:11   #4
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,371
Re: Confused on Wire Gauge from Panels to Charge Controller

Quote:
Originally Posted by mrybas View Post
Hi David,
The Vmpp is 40.5V. The Imp is 6.05A. So I need to size for 6.05A @ 40.5V, right?
No, you just need to size for 6A times 2 (panels) = 12A. Voltage has no meaning for determining cable diameter as long as the cable insulation value is high enough (but that is 600V normally so fine).

12A with 3% voltage drop puts you at AWG6, but only just so you could get away with AWG8 with may be 4-5% voltage drop.

If you have no other panels connected yet, you could go for a series connection of the two panels which gives 6A @ 81V. Your controller can take that and the required cable goes down to AWG8.



s/v Jedi is offline   Reply With Quote
Old 28-05-2013, 18:39   #5
Moderator Emeritus
 
David M's Avatar

Cruisers Forum Supporter

Join Date: Sep 2007
Location: Eastern Tennessee
Boat: Research vessel for a university, retired now.
Posts: 10,406
Re: Confused on Wire Gauge from Panels to Charge Controller

Jedi is correct. You gauge wire for the current, the run, the percentage drop and sometimes the temperature. The insulation must be rated for the voltage and the type of environment.
__________________
David

Life begins where land ends.
David M is offline   Reply With Quote
Old 28-05-2013, 19:50   #6
Registered User
 
mrybas's Avatar

Join Date: May 2010
Location: East Coast USA or out cruising
Boat: Lock Crowther 150
Posts: 665
Re: Confused on Wire Gauge from Panels to Charge Controller

Ahhhh, it all makes sense now. Thanks for the help!
mrybas is offline   Reply With Quote
Old 28-05-2013, 19:56   #7
Registered User
 
mrybas's Avatar

Join Date: May 2010
Location: East Coast USA or out cruising
Boat: Lock Crowther 150
Posts: 665
Re: Confused on Wire Gauge from Panels to Charge Controller

Quote:
Originally Posted by s/v Jedi View Post
If you have no other panels connected yet, you could go for a series connection of the two panels which gives 6A @ 81V. Your controller can take that and the required cable goes down to AWG8.
[/IMG]
Yes, it is just the two panels. Is it correct that the two panels wired in series makes them more susceptible to the effects of shading? They are mounted on top of the bimini, so its fairly clear, except for a backstay and mast shadow.
mrybas is offline   Reply With Quote
Old 28-05-2013, 22:57   #8
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Confused on Wire Gauge from Panels to Charge Controller

Quote:
Originally Posted by David M View Post
Jedi is correct. You gauge wire for the current, the run, the percentage drop and sometimes the temperature. The insulation must be rated for the voltage and the type of environment.
Quote:
Originally Posted by s/v Jedi View Post
No, you just need to size for 6A times 2 (panels) = 12A. Voltage has no meaning for determining cable diameter as long as the cable insulation value is high enough (but that is 600V normally so fine).

12A with 3% voltage drop puts you at AWG6, but only just so you could get away with AWG8 with may be 4-5% voltage drop.

If you have no other panels connected yet, you could go for a series connection of the two panels which gives 6A @ 81V. Your controller can take that and the required cable goes down to AWG8.




I'm sorry, but you are both wrong.

The percentage of voltage drop, is in fact related to the Volts in the circuit.

A 24 volt circuit with a 12 amp load, # 6 wire, with a run of 30 feet one way is 1.22%

A 12 volt circuit with a 12 amp load, # 6 wire, with a run of 30 feet one way is 2.44% double what the 24 volt % drop is.

A 48 volt circuit with a 12 amp load, # 6 wire, with a run of 30 feet one way is .69% half what 24 volt % drop is.



Lloyd
FlyingCloud1937 is offline   Reply With Quote
Old 28-05-2013, 23:11   #9
Registered User
 
rebel heart's Avatar

Join Date: Oct 2005
Posts: 6,185
Images: 3
Re: Confused on Wire Gauge from Panels to Charge Controller

I don't think his 12v panels are going to push at 48 volts.
rebel heart is offline   Reply With Quote
Old 29-05-2013, 04:32   #10
Registered User
 
mrybas's Avatar

Join Date: May 2010
Location: East Coast USA or out cruising
Boat: Lock Crowther 150
Posts: 665
Re: Confused on Wire Gauge from Panels to Charge Controller

Quote:
Originally Posted by rebel heart View Post
I don't think his 12v panels are going to push at 48 volts.
No, but close.... Vmpp= 40.5V. This is from the panels to the charge controller, before its stepped down to 12V by the charge controller.
mrybas is offline   Reply With Quote
Old 29-05-2013, 04:53   #11
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,371
Quote:
Originally Posted by FlyingCloud1937 View Post

I'm sorry, but you are both wrong.

The percentage of voltage drop, is in fact related to the Volts in the circuit.

A 24 volt circuit with a 12 amp load, # 6 wire, with a run of 30 feet one way is 1.22%

A 12 volt circuit with a 12 amp load, # 6 wire, with a run of 30 feet one way is 2.44% double what the 24 volt % drop is.

A 48 volt circuit with a 12 amp load, # 6 wire, with a run of 30 feet one way is .69% half what 24 volt % drop is.

Lloyd
Ah, the mad scientist, telling us we're wrong again

Mr Ohm dictates us that the voltage drop over the wire equals the wire resistance times the current, regardless of voltage of the source. Mr Ohm does not allow for opinion being different than his law

When we operate the panels at a higher voltage, the current goes down (again Mr Ohm) and with it the voltage drop.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 29-05-2013, 05:42   #12
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Not to mention that the power loss , which is actually stuff thrown away , is I squared R


Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 29-05-2013, 07:04   #13
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 364
Re: Confused on Wire Gauge from Panels to Charge Controller

Currant does not necessarily go down with higher voltage. Size your wires based on the demand of your controller. Use a wire chart for the distance.
Zil is offline   Reply With Quote
Old 29-05-2013, 08:01   #14
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,371
Re: Confused on Wire Gauge from Panels to Charge Controller

Quote:
Originally Posted by Zil View Post
Currant does not necessarily go down with higher voltage. Size your wires based on the demand of your controller. Use a wire chart for the distance.
It does for solar panels which is the topic here.
s/v Jedi is offline   Reply With Quote
Reply

Tags
panels


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 21:00.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.