Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 09-05-2020, 15:17   #1
Registered User

Join Date: Nov 2010
Location: BC
Boat: O'Day 40
Posts: 1,084
Correct way to wire a water heater?

I had to get my boat surveyed for its insurance renewal.

One of the things the surveyor noted was that our Isotemp Spa water heater is not wired to a dedicated and labeled breaker.

Isotemp specifically say all internal connections are made at the factory and the supplied cable should be plugged in to a correctly installed socket.

We rarely plug it in as it is heated by the diesel hydronic system or the engine when motoring. I'm tempted to just cut the cord off but don't want to limit my options.

If it was in a house I'd say it needs to be connected within a suitable electrical box.

What is the normal solution on a boat?
__________________
Trying to make new mistakes.
bcboomer is offline   Reply With Quote
Old 09-05-2020, 15:27   #2
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,680
Re: Correct way to wire a water heater?

Normal is hard wired in from a breaker used to turn it off and on. AFAIK .
I dont know that I've seen one with a cord and plug. But I would think that a breaker at the plug box you plug it into would comply.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 09-05-2020, 15:58   #3
Registered User

Join Date: Nov 2010
Location: BC
Boat: O'Day 40
Posts: 1,084
Re: Correct way to wire a water heater?

Yes I was surprised to see a cord and instructions to not hard wire it.
It's certainly safer the way we use it and I'm not about to break into the heater wiring to change that. I suppose butt connectors in an electrical box near the heater and then to a breaker on the AC panel will meet their specs but it irks me that surveyors and insurance companies get fixated on ABYC.
__________________
Trying to make new mistakes.
bcboomer is offline   Reply With Quote
Old 09-05-2020, 16:05   #4
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Correct way to wire a water heater?

Why not install a dedicated receptacle/ breaker and plug in the water heater.

Frankly
Frankly is offline   Reply With Quote
Old 09-05-2020, 22:33   #5
Registered User

Join Date: Apr 2007
Location: Australia
Boat: Island Packet 40
Posts: 6,501
Images: 7
Re: Correct way to wire a water heater?

Different requirements for fixed versus portable equipment perhaps?
RaymondR is offline   Reply With Quote
Old 10-05-2020, 06:40   #6
Registered User

Community Sponsor

Join Date: Nov 2019
Location: South Carolina
Boat: Philip Rhodes Custom 71'
Posts: 192
Re: Correct way to wire a water heater?

Quote:
Originally Posted by bcboomer View Post
Yes I was surprised to see a cord and instructions to not hard wire it.
It's certainly safer the way we use it and I'm not about to break into the heater wiring to change that. I suppose butt connectors in an electrical box near the heater and then to a breaker on the AC panel will meet their specs but it irks me that surveyors and insurance companies get fixated on ABYC.
Unfortunately I'm suspecting that a majority of the ABYC specifications are dictated by lawyers paranoid of court challenges rather than by practical sailors.
Not to say that ultimate safety protection is not good but the average sailor has to balance cost and benefit.

Perhaps the $25 on rewiring a satisfactory heater could be spent on a backup float switch that has a much better chance of saving the whole boat rather than possibly getting a shock off a water heater.
__________________
Ann-Marie Foster
YANDINA is offline   Reply With Quote
Old 10-05-2020, 08:14   #7
Registered User
 
CaptTom's Avatar

Join Date: Apr 2004
Location: Southern Maine
Boat: Prairie 36 Coastal Cruiser
Posts: 3,252
Re: Correct way to wire a water heater?

First, disconnect the plug wires at the heater end. It should be simple to pull off the cover plate and unscrew the terminals. Now you're legal.

When time permits, run a new cable from a new, dedicated breaker in the breaker panel and hook it up directly to where you disconnected the plug. Now you're legal AND have one more option for hot water.

As a reminder, the breaker isn't just there to prevent a shock. It's there largely to protect the wire running from the panel to the heater. A short anywhere will cause it to overheat. Fire on a boat is bad. A GFCI breaker might be a good idea for a water heater, too. The cladding on the elements can corrode and create a shock hazard, not to mention the damage it'll do to the equipment.
CaptTom is online now   Reply With Quote
Old 10-05-2020, 08:36   #8
Registered User

Join Date: Jan 2020
Posts: 85
Re: Correct way to wire a water heater?

Possibly consider the following...
- The positive disconnect of the receptacle and plug protects any one working on the water heater no matter what happens elsewhere on the vessel.
- To comply with the survey report just make the receptacle a dedicated one with it's own circuit.
- Consider installing a ground fault device into that circuit somewhere.
Cheers,
Niall.
Niall leslie is offline   Reply With Quote
Old 10-05-2020, 08:47   #9
Registered User

Join Date: Nov 2010
Location: BC
Boat: O'Day 40
Posts: 1,084
Re: Correct way to wire a water heater?

Quote:
Originally Posted by Niall leslie View Post
Possibly consider the following...
- The positive disconnect of the receptacle and plug protects any one working on the water heater no matter what happens elsewhere on the vessel.
- To comply with the survey report just make the receptacle a dedicated one with it's own circuit.
- Consider installing a ground fault device into that circuit somewhere.
Cheers,
Niall.
That's probably the simplest. The AC is already protected by a GFCI.
Come to think of it, I could just put a label on the AC circuit breaker and be compliant.
__________________
Trying to make new mistakes.
bcboomer is offline   Reply With Quote
Old 10-05-2020, 09:01   #10
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,737
Re: Correct way to wire a water heater?

Why would you ever need to "open the heater connection at the heater end?"


Leave that as it is, and connect the other (loose) end properly, easiest as you note in #9!
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 10-05-2020, 09:50   #11
Registered User

Join Date: Nov 2010
Location: BC
Boat: O'Day 40
Posts: 1,084
Re: Correct way to wire a water heater?

Quote:
Originally Posted by CaptTom View Post
First, disconnect the plug wires at the heater end. It should be simple to pull off the cover plate and unscrew the terminals. Now you're legal.

As a reminder, the breaker isn't just there to prevent a shock. It's there largely to protect the wire running from the panel to the heater. A short anywhere will cause it to overheat. Fire on a boat is bad. A GFCI breaker might be a good idea for a water heater, too. The cladding on the elements can corrode and create a shock hazard, not to mention the damage it'll do to the equipment.
Pulling the cover off is tempting but the heater is really hard to get to and, besides, I don't know if the terminals are simple screws or permanently connected.
I don't see any GFCI breakers that could be installed in my panel. Consequently a dedicated standard breaker would be less safe than plugging into the existing GFCI wall socket.
__________________
Trying to make new mistakes.
bcboomer is offline   Reply With Quote
Old 10-05-2020, 10:49   #12
Registered User

Join Date: Feb 2006
Location: Eastern Caribbean for the 2020 season then east coast or Panama
Boat: Lagoon 470 cat
Posts: 700
Re: Correct way to wire a water heater?

What is the wattage of the heater. In my experience the requiremenet for a dedicated line is to prevent overloading a circuit. Like a separate circuit for a microwave in a house. They don't want that to be running on a "regular" kitchen circuit (15 amp) that also has a toaster, coffee pot, etc pluged into it.


Water heater elements I've seen are in the 1200-1500 watt range which takes it close to the limit for a 15 amp circuit.
Moontide is offline   Reply With Quote
Old 10-05-2020, 10:59   #13
Registered User

Join Date: Nov 2010
Location: BC
Boat: O'Day 40
Posts: 1,084
Re: Correct way to wire a water heater?

Quote:
Originally Posted by Moontide View Post
What is the wattage of the heater. In my experience the requiremenet for a dedicated line is to prevent overloading a circuit. Like a separate circuit for a microwave in a house. They don't want that to be running on a "regular" kitchen circuit (15 amp) that also has a toaster, coffee pot, etc pluged into it.


Water heater elements I've seen are in the 1200-1500 watt range which takes it close to the limit for a 15 amp circuit.
It's only 750 watts and plugging it in to the galley outlet pretty much guarantees no other accidental big loads. We use diesel for heat so no big loads anyway.
__________________
Trying to make new mistakes.
bcboomer is offline   Reply With Quote
Old 10-05-2020, 11:50   #14
Registered User

Join Date: Mar 2020
Posts: 35
Re: Correct way to wire a water heater?

Yandina. Really? The ABYC standards are dictated by a bunch of of attorneys covering their arses? Nothing worse than someone ignorant of they facts and making factual statements.
RigBig is offline   Reply With Quote
Old 11-05-2020, 14:23   #15
Registered User

Join Date: Jan 2016
Location: Beaufort, NC, USA
Boat: Ta Chiao 56
Posts: 753
Re: Correct way to wire a water heater?

Quote:
Originally Posted by CaptTom View Post
As a reminder, the breaker isn't just there to prevent a shock. It's there largely to protect the wire running from the panel to the heater.
The SOLE purpose of a circuit breaker is to prevent overload and resultant fire. A circuit breaker will do NOTHING to prevent shock or electrocution.
A GFCI WILL provide such protection, as long as it is installed properly.

On my boat, the water heater is plugged into a dedicated outlet, in the same lazarette location as the heater, which is controlled by one of the two circuit breakers on my AC panel. The other breaker controls the conveniece outlets.
Brewgyver is offline   Reply With Quote
Reply

Tags
heater, water


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
Correct gauge wire for solar panels mrybas Electrical: Batteries, Generators & Solar 12 28-05-2017 18:48
Correct size wire for 3GM Battery Bank? Gone2long Electrical: Batteries, Generators & Solar 23 16-01-2017 00:55
What's the Best Way to Connect a 4mm Wire to the Middle of a 6mm Wire? mischief Electrical: Batteries, Generators & Solar 11 07-11-2013 09:31
Correct Connection for 4-Way Battery Switch anglooff Electrical: Batteries, Generators & Solar 4 11-06-2010 08:55

Advertise Here


All times are GMT -7. The time now is 08:26.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.