Heres my situation. I have a 1 year old Trojan FLA 220ah battery bank and a slightly older interstate 220ah FLA bank. They both go from 100+% to 25% in 10 min with a 7 amp load.

Loads are: fridge draws 4-5 amps, laptop (12v charger) draws 2-3 amps, wifi draws 1/2 amp or less.

I've ruled out connection issues. Everything is pointing to the batteries being sulfated.

To desulfate i want to be able to use whats powered in my 12v panel, but that wouldn't be good for desulfication process.

So here's my possible solution that i'd like your opinions on.

While on shore power, how about replacing the battery power to the panel with a DC power supply that runs off the inverter? This is rated for 30amps, roughly 4x what i use.

https://www.amazon.com/MegaWatt-S-35.../dp/B00JZBE97U

It would be a permanent install with a switch to toggle between battery power and power supply power.

I would use this for about 8 hours a month.


Thoughts?

Thanks in advance everyone.
Rugger is offline   Reply With Quote
Old 26-07-2018, 02:01   #2
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,713
Re: DC power supply to power 12v DC panel instead of batteries

if your 220ah bank can't handle a 7a load for 10 mins. you need new ones. don't even waste your time on them. they should last 30 hours. if your problem was they only lasted 20 hours instead of 30. then maybe I'd spend time on them.
smac999 is offline   Reply With Quote
Old 26-07-2018, 02:57   #3
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,603
Images: 21
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by Rugger View Post
I have a 1 year old Trojan FLA 220ah battery bank and a slightly older interstate 220ah FLA bank. They both go from 100+% to 25% in 10 min with a 7 amp load.
What exactly have you done to them to reach this point in a year?
Pete7 is offline   Reply With Quote
Old 26-07-2018, 03:44   #4
Registered User
 
StuM's Avatar

Cruisers Forum Supporter

Join Date: Nov 2013
Location: Port Moresby,Papua New Guinea
Boat: FP Belize Maestro 43 and OPBs
Posts: 12,891
Re: DC power supply to power 12v DC panel instead of batteries

Those batteries are stuffed. Almost certainly because of an inadequate charging system.



Replace them.
But before you do, tell us how you have been charging them. There are plenty of people here who can advise on an appropriate charging regime.
StuM is offline   Reply With Quote
Old 26-07-2018, 03:45   #5
Registered User

Join Date: Dec 2008
Location: Oriental, NC
Boat: Mainship Pilot 34
Posts: 1,461
Re: DC power supply to power 12v DC panel instead of batteries

I agree that the batteries ae dead and all the equalization in the world won't revive them, so replace.


Also in my experience, if you charge your batteries fully at least every other day, there will be no need for equalization. Equalization is a technique to put moderate sulfates back into solution after standing discharged for significant time. Once the sulfates begin to reduce capacity significantly, the batteries are toast.


So replace the batteries and keep them fully charged and don't worry about equalization.



David
djmarchand is offline   Reply With Quote
Old 26-07-2018, 04:26   #6
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: DC power supply to power 12v DC panel instead of batteries

Beyond what everyone has already said about the batteries being complete toast.

How do you propose to run this power supply (that will be fine for your intended application) off of the inverter if the batteries are disconnected?
Sailmonkey is offline   Reply With Quote
Old 26-07-2018, 05:07   #7
cruiser

Join Date: Dec 2006
Posts: 405
Re: DC power supply to power 12v DC panel instead of batteries

Only a year or so old! Maybe they are sulphated due to erratic charging. Maybe they are finished but suggest removing them to a safe well ventilated area, connect each to a 3 to 4 Amp charger at say 14.5volts minimum for a day or so. (Check water levels first!)
I think you may be pleasantly surprised...

Here is an old but good article re batteries...
https://iceking.ca/icetechblog/Sulfated_Batteries.pdf

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems
OzePete is offline   Reply With Quote
Old 26-07-2018, 07:25   #8
Registered User

Join Date: Aug 2015
Location: Saint Petersburg, FL
Posts: 57
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by Pete7 View Post
What exactly have you done to them to reach this point in a year?
They have been on the 20ish yer old Heart Interface charger the whole time. I've desulfated them once or twice.

topped off the water with distilled every 30 to 45 days.
Rugger is offline   Reply With Quote
Old 26-07-2018, 07:46   #9
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,679
Re: DC power supply to power 12v DC panel instead of batteries

FIRST: Charge the batteries long and well with a shore type charger. Near the end of that charge cycle feel each battery for heat. If one is very hot ... it's shorted inside and it's drawing the others down. I have had this occur twice on boats with relatively new batteries.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 26-07-2018, 07:49   #10
Registered User

Join Date: Aug 2015
Location: Saint Petersburg, FL
Posts: 57
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by StuM View Post
Those batteries are stuffed. Almost certainly because of an inadequate charging system.



Replace them.
But before you do, tell us how you have been charging them. There are plenty of people here who can advise on an appropriate charging regime.
The 20ish year old charger has supposedly been managing the charging. The setup should be fine. The default setup on the system is whats needed for these batteries so its fine.

Hooked up to shore power whole time with the exception of day sails and an overnight.
Rugger is offline   Reply With Quote
Old 26-07-2018, 07:53   #11
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by Rugger View Post
The 20ish year old charger has supposedly been managing the charging. The setup should be fine. The default setup on the system is whats needed for these batteries so its fine.
Then what is your explanation for banks that should last at least 6 years, maybe 12+ when cared for meticulously, failing in less than a year?

You need a decent ammeter and a new battery, then use the knowledgeable people here, to find out what is wrong with your system(s).

IMO charging will indeed turn out to be the issue.
john61ct is offline   Reply With Quote
Old 26-07-2018, 07:54   #12
Registered User

Join Date: Aug 2015
Location: Saint Petersburg, FL
Posts: 57
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by Sailmonkey View Post
Beyond what everyone has already said about the batteries being complete toast.

How do you propose to run this power supply (that will be fine for your intended application) off of the inverter if the batteries are disconnected?
Thanks for pointing out an error in my post. I meant to say the DC power supply would run off of shore power rather than the inverter.
Rugger is offline   Reply With Quote
Old 26-07-2018, 07:58   #13
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by Rugger View Post
So here's my possible solution that i'd like your opinions on.

While on shore power, how about replacing the battery power to the panel with a DC power supply that runs off the inverter? This is rated for 30amps, roughly 4x what i use.
An inverter produces AC power from DC usually batteries.

The power supply produces DC from AC.

Makes no sense to run the latter from the former, going in circles, huge inefficiency losses.

Just run the PS off your shore power.

But none of this is a "solution" to your fundamental problem of your batteries getting murdered.

Solve that first.
john61ct is offline   Reply With Quote
Old 26-07-2018, 07:59   #14
Moderator
 
Jammer's Avatar

Join Date: Jan 2010
Location: Minnesota
Boat: Tartan 3800
Posts: 5,165
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by Rugger View Post
So here's my possible solution that i'd like your opinions on.

While on shore power, how about replacing the battery power to the panel with a DC power supply that runs off the inverter? This is rated for 30amps, roughly 4x what i use.

https://www.amazon.com/MegaWatt-S-35.../dp/B00JZBE97U

Yes, you can do that. Yes, it will work.


But if your batteries have failed, there is no way to bring them back from the dead. No amount of Dr. McGellan's Snake Oil Liniment. No amount of Prof. Eggerston's magnetic resonance ultrasonic battery charger. You got a losing hand, read 'em and weep.


My batting average in diagnosing electrical problems over the internet is basically zero. Someone who knows what they're doing is going to have to get on your boat, test stuff, figure out what went wrong, and fix it, and then you're going to have to buy new batteries.
Jammer is offline   Reply With Quote
Old 26-07-2018, 08:31   #15
Registered User

Join Date: Aug 2015
Location: Saint Petersburg, FL
Posts: 57
Re: DC power supply to power 12v DC panel instead of batteries

Quote:
Originally Posted by john61ct View Post
Then what is your explanation for banks that should last at least 6 years, maybe 12+ when cared for meticulously, failing in less than a year?

You need a decent ammeter and a new battery, then use the knowledgeable people here, to find out what is wrong with your system(s).

IMO charging will indeed turn out to be the issue.
The reason for the post was to see if the power supply would work for powering the panel so i could still have my 12v devices working while i move on to troubleshooting the charging/battery system.

The previous owner indeed got 7 to 9 years out of batteries with this setup. I talk to him frequently. Everything in this system is (or was) super high quality when purchased. The ammeters included.

https://photos.app.goo.gl/nQJfvQfpiCNGMhXL6

The plan was to get the panel powered and disconnected from the batteries so I can do 3-4 desulfate cycles on one of the banks to see if i could breathe some life back into them.

When or if that doesnt work, tackle the issue of what is killing the batteries.
Rugger is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
negative power supply and 12v negative battery supply same thing? er9 Marine Electronics 8 02-03-2016 08:06
Need 12V stable power supply for WIFI router SFH Marine Electronics 20 09-06-2015 17:50
Refrigerator 12v/110v power supply J. Nikitaridis Marine Electronics 12 24-02-2015 10:15
Can I still get 12V from two 12V batteries in series Mikado Electrical: Batteries, Generators & Solar 26 29-10-2014 18:48
12V Charger as Power Supply Hugh Walker Electrical: Batteries, Generators & Solar 10 11-02-2012 05:59

Advertise Here


All times are GMT -7. The time now is 17:56.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.