Old 11-03-2017, 15:52   #1
Registered User
 
Rowglide's Avatar

Join Date: Jan 2017
Location: Kingston, Ontario
Boat: Hans Christian 43
Posts: 382
Debating the wire size needs...LED

OK so here is the layout.
I have a pair of Signal Mate LED port /starboard nav lights. They are to be fed with a pair of wires (+,-) to the bowsprit. The actual distance is 38' so X2 for pos and neg... so 76 feet.
The Amperage is minuscule! The current draw is 0.100A at 12VDC per lamp so 0.200A.
Using standard "wire size chart".(I used the one from Blue Sea Systems) There is a 5 Amp minimum load shown on the charts. As Navigation lights, 3% voltage drop is max allowed.
at 76' that becomes #8AWG wires...? Am I missing something here? It seems to me that the relatively small amperages of LED lights need to be addressed.
Is there a formula that would allow me to calculate a more suitable wire size that would also be acceptable under ABYC standards?
Jim
Rowglide is offline   Reply With Quote
Old 11-03-2017, 16:10   #2
Registered User
 
Kelkara's Avatar

Join Date: Oct 2016
Location: Vancouver Island
Boat: Hullmaster 27
Posts: 1,063
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Rowglide View Post
Is there a formula that would allow me to calculate a more suitable wire size that would also be acceptable under ABYC standards?
The formula you're looking for is simply Ohm's law: V=IR.

V = 3% of 12V = 0.36V
I = 0.2A
R = V/I = 1.8 ohms.

This is the maximum allowable resistance of the wire in your circuit for a 3% voltage drop at 0.2A

Then it's a question of selecting a wire that has less than this resistance for a run of 76ft.

which according to this calculator: Wire Resistance Calculator & Table would be AWG23 wire ... which is too small for other reasons ... so basically you can get away with whatever boat appropriate wire that you have 76ft available.

discalaimer: I'm not an electrician.
Kelkara is offline   Reply With Quote
Old 11-03-2017, 16:15   #3
Registered User
 
DeepFrz's Avatar

Cruisers Forum Supporter

Join Date: Mar 2006
Location: Winnipeg
Boat: None at this time
Posts: 8,462
Re: Debating the wire size needs...LED

Blue Sea has an app that can help you with this. The size is 18 but Blue Sea recommend 16 gauge minimum unless inside a conduit or wire bundle.

The web app didn't seem to work for me but the Android app worked okay.
DeepFrz is offline   Reply With Quote
Old 11-03-2017, 16:45   #4
Registered User
 
Rowglide's Avatar

Join Date: Jan 2017
Location: Kingston, Ontario
Boat: Hans Christian 43
Posts: 382
Re: Debating the wire size needs...LED

Awesome,
Thanks
I hadn't seen that app anywhere, but now that I have it my life will be much easier. I am always willing to err on the side of safety, so 16AWG will be the wire of choice. Beats looking at 5A charts, that was just getting scary!
Jim
Rowglide is offline   Reply With Quote
Old 11-03-2017, 17:01   #5
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,561
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Rowglide View Post
OK so here is the layout.
I have a pair of Signal Mate LED port /starboard nav lights. They are to be fed with a pair of wires (+,-) to the bowsprit. The actual distance is 38' so X2 for pos and neg... so 76 feet.
The Amperage is minuscule! The current draw is 0.100A at 12VDC per lamp so 0.200A.
Using standard "wire size chart".(I used the one from Blue Sea Systems) There is a 5 Amp minimum load shown on the charts. As Navigation lights, 3% voltage drop is max allowed.
Is there a formula that would allow me to calculate a more suitable wire size that would also be acceptable under ABYC standards?
Jim
I've heard that the ABYC will at some point update their chart to add lower current values, since LEDs are becoming so common.

Anyway, all these charts start with knowing the resistance per length of different wire gauges.

According to this chart, here are a couple of sample values:

  • 16 AWG stranded: 4.03 ohms per 1000 ft => 0.00403 ohm per ft
  • 18 AWG stranded: 6.54 ohms per 1000 ft => 0.00654 ohm per ft

Back to your requirement: 200mA, 76 ft, less than 3% drop.

First thing I'm going to do is round up:
  • current to 0.5A, cos maybe you'll change the fixture down the road
  • length to 80 ft
3% of 12v is 0.36v. Ohms law says that if there's 0.5A of current, then you can find the resistance to produce that drop as:


E/I = 0.36/0.5 = 0.72 ohm


So the wire run must have less than 0.72 ohms to drop less than 3% of 12v.


80 ft of 18 AWG would drop 80 x 0.00654 = 0.5232 ohms...


So you could get away with 18 AWG. But there are other qualities of the wire to consider: how easy it is to pull and to crimp connectors on, how it will stand up to bumps and knocks, etc.


Myself I would use 16 AWG for this.

[ok so I type slower than everyone else ...]
Lake-Effect is offline   Reply With Quote
Old 11-03-2017, 17:29   #6
Registered User
 
Rowglide's Avatar

Join Date: Jan 2017
Location: Kingston, Ontario
Boat: Hans Christian 43
Posts: 382
Re: Debating the wire size needs...LED

16 it is! I agree, and besides with fat clumsy fingers like mine, handling slightly heavier wire will be easier.
Rowglide is offline   Reply With Quote
Old 12-03-2017, 09:29   #7
Registered User

Join Date: Nov 2013
Location: Homeport: Fair Haven, NY
Boat: 1993 Sabre 362 #113
Posts: 615
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Rowglide View Post
16 it is! I agree, and besides with fat clumsy fingers like mine, handling slightly heavier wire will be easier.
Not to be insensitive to my northern neighbor, but this is precisely the reason that 16 ga is the minimum. Smaller diameter wires are just too fragile for marine use unless they are in a cable, like a microphone cable, ethernet, or N2K.
Dave Lochner is offline   Reply With Quote
Old 12-03-2017, 09:37   #8
Registered User
 
S/V Alchemy's Avatar

Join Date: May 2008
Location: Nova Scotia until Spring 2021
Boat: Custom 41' Steel Pilothouse Cutter
Posts: 4,976
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Rowglide View Post
Awesome,
Thanks
I hadn't seen that app anywhere, but now that I have it my life will be much easier. I am always willing to err on the side of safety, so 16AWG will be the wire of choice. Beats looking at 5A charts, that was just getting scary!
Jim
Consider running 12 ga. to a breakered DC subpanel in the cabinetry in the saloon. Run all the saloon lights and the bow lights from here. Shorter total runs and the whole circuit is protected by whatever amperage breaker is appropriate. You just have to learn to switch on your nav lights from the middle of the boat.

I have always wondered why, on aft cockpit boats, the panels are all 3/4trs of the way aft. The logical place for the breakers is in the saloon, close to the mast, with equal runs fore and aft. The distance from the batteries can be compensated for by upsizing the cabling, but it's not nearly the problem it was with the phasing out of incandescents.
__________________
Can't sail? Read about our travels at https://alchemyonpassage.blogspot.com/. Can't sleep? Read www.alchemy2009.blogspot.com for fast relief. Can't read? Avoid www.volumesofsalt.blogspot.com, because it's just personal reviews of sea books.
S/V Alchemy is offline   Reply With Quote
Old 12-03-2017, 09:37   #9
Registered User

Join Date: Dec 2012
Boat: Jeanneau SO45.2
Posts: 386
Re: Debating the wire size needs...LED

In general (and as they say, "all generalizations are dangerous, including this one"), LED lights need so little current that you will be sizing wire for mechanical strength, and the ability to install terminations (lugs, connectors etc) rather than actual current-carrying capacity. #16 is good, 318 about as small as you'd want to handle, though you could go even smaller in a multi-conductor cable.
Redline452 is offline   Reply With Quote
Old 12-03-2017, 10:17   #10
Registered User

Join Date: May 2016
Location: Hanging out along the Gulf Coast
Boat: 81 Hunter Cherubini 27
Posts: 372
Images: 3
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Redline452 View Post
In general (and as they say, "all generalizations are dangerous, including this one"), LED lights need so little current that you will be sizing wire for mechanical strength, and the ability to install terminations (lugs, connectors etc) rather than actual current-carrying capacity. #16 is good, 318 about as small as you'd want to handle, though you could go even smaller in a multi-conductor cable.
Nailed it! Mechanical strength, crimps and terminations, and multi-conductor cabling. Oh, and use proper crimping tools with marine grade wire and terminations.
__________________
Cruising highly skilled Marine Electrician. Will work for beer, smokes and slip fees...and other important boat stuff
Teknishn is offline   Reply With Quote
Old 12-03-2017, 10:39   #11
Registered User

Join Date: Sep 2013
Location: San Francisco Bay
Boat: Chung Hwa Boat Builders, Magellan 36
Posts: 448
Re: Debating the wire size needs...LED

I find that crimping wire smaller than 16 gauge is very iffy even when doubling it. Go with 16 or larger
foufou is offline   Reply With Quote
Old 12-03-2017, 11:00   #12
Registered User

Join Date: Dec 2012
Boat: Jeanneau SO45.2
Posts: 386
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Redline452 View Post
In general (and as they say, "all generalizations are dangerous, including this one"), LED lights need so little current that you will be sizing wire for mechanical strength, and the ability to install terminations (lugs, connectors etc) rather than actual current-carrying capacity. #16 is good, 318 about as small as you'd want to handle, though you could go even smaller in a multi-conductor cable.
Aarrgh - the typo fairy strikes again. That's #18, not 318! .
The latter would be very very thin wire indeed, if it was a gauge.
Redline452 is offline   Reply With Quote
Old 12-03-2017, 11:14   #13
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Debating the wire size needs...LED

Quote:
Originally Posted by Rowglide View Post
OK so here is the layout.
I have a pair of Signal Mate LED port /starboard nav lights. They are to be fed with a pair of wires (+,-) to the bowsprit. The actual distance is 38' so X2 for pos and neg... so 76 feet.
The Amperage is minuscule! The current draw is 0.100A at 12VDC per lamp so 0.200A.
Using standard "wire size chart".(I used the one from Blue Sea Systems) There is a 5 Amp minimum load shown on the charts. As Navigation lights, 3% voltage drop is max allowed.
at 76' that becomes #8AWG wires...? Am I missing something here? It seems to me that the relatively small amperages of LED lights need to be addressed.
Is there a formula that would allow me to calculate a more suitable wire size that would also be acceptable under ABYC standards?
Jim
Jim,

I would not worry about wire size electrically. I would worry about the size needed for physical fatigue.
Cadence is offline   Reply With Quote
Old 12-03-2017, 11:47   #14
Registered User
 
SteveSails's Avatar

Join Date: Jan 2014
Location: St Michaels MD
Boat: F&C 44
Posts: 182
Re: Debating the wire size needs...LED

The 3% voltage drop rule is not critical with good quality LEDs like Signal Mate, they will work from 9V to 36V with constant brightness. The circuitry in the fixture maintains constant power so these LEDs actually draw more current at low voltage than higher voltages, just the opposite of an incandescent bulb. A #16 wire is adequate but what size breaker drives that wire? Reduce it to a 5Amp breaker or add a fuse to LED circuit.
SteveSails is offline   Reply With Quote
Old 12-03-2017, 12:33   #15
Marine Service Provider

Join Date: May 2011
Location: Cruising Mexico Currently
Boat: Gulfstar 50
Posts: 1,980
Re: Debating the wire size needs...LED

Also consider that the wire size should be large enough so that the breaker trips (at the source end) long before the small wire goes up in flames should there be a short somewhere along its length.

16 Gauge is the minimum size spec'ed by ABYC for that reason as well as the mechanical reasons noted.

As an example here are the resistances of 100' of various wire gauges taken from some random source (YMMV) along with the currents that would flow through that 100' loop at 12.8 volts.

18 gauge 0.639 ohms 20 amps
16 gauge 0.402 ohms 32 amps
14 gauge 0.253 ohms 50 amps
12 gauge 0.158 ohms 81 amps

So with a 100' loop of 18 gauge wire Shorted at one end and fed from a 10 amp breaker at the other we could expect the current through the loop to be limited to 20 amps by the wire resistance alone.

Looking at the A-series breaker Trip Delay Curve I see that it could take up to 20 seconds for a 10 amp breaker to trip when passing 20 amps. 20 seconds is plenty of time to start a fire....

With 16 gauge wire (and 32 amps) that same breaker would trip within 4 or 5 seconds and with 14 gauge wire and 50 amps that trip time would be 1 or 2 seconds. Of course those are worst case times with it more likely to trip in a shorter time.

When I first started to put in LED lighting I thought to use small gauge wire and use smaller breakers till this was pointed out to me. Now I tend to feed with 14 gauge for everything that doesn't need more current (I bought a 500' spool or was it 1000') and set the breaker size as needed. For small loads like LED in lockers I put a small inline fuse where the 14 gauge feed switches over to pigtails for the LEDs.
Attached Thumbnails
Click image for larger version

Name:	Toggle_CB.jpg
Views:	114
Size:	44.9 KB
ID:	142997  
evm1024 is offline   Reply With Quote
Reply

Tags
size


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Cruiser debating the Atlantic Coast of France, Spain, and Portugal Zoid Europe & Mediterranean 39 15-12-2016 13:37
St Martin Oyster Pond charter-debating provisioning options CEN Cooking and Provisioning: Food & Drink 9 20-10-2015 19:51
LED Wire Size Red Horse Electrical: Batteries, Generators & Solar 25 01-08-2014 22:53
debating about which watermaker style rebel heart Plumbing Systems and Fixtures 9 26-04-2013 08:15

Advertise Here


All times are GMT -7. The time now is 18:00.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.