Disconnecting panels under load

I’ve read that panels should not be disconnected under load, and therefore should be covered with a towel before disconnecting in daylight , e.g. to store or reposition. I would appreciate advice from more experienced users on this point. Is it a problem, and if so is there a better approach than covering with a towel?

Thanks, R. Andrew
rha9 is offline   Reply With Quote
Old 13-11-2021, 16:43   #2
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,296
Re: Disconnecting panels under load

Quote:
Originally Posted by rha9 View Post
I’ve read that panels should not be disconnected under load, and therefore should be covered with a towel before disconnecting in daylight , e.g. to store or reposition. I would appreciate advice from more experienced users on this point. Is it a problem, and if so is there a better approach than covering with a towel?

Thanks, R. Andrew
Disconnect between panel and controller - no problem
Disconnect at battery - PROBLEM
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 14-11-2021, 08:08   #3
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Disconnecting panels under load

Why is it a problem disconnecting at the battery. ?
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 14-11-2021, 08:18   #4
Registered User

Join Date: Oct 2021
Posts: 589
Re: Disconnecting panels under load

Panels get disconnected under load all the time. It is the primary protection feature in power plants. The code requires that the disconnecting not cause damage. The risk is more to the disconnecting means, it must be designed to disconnect DC under load and quench the ensuing arc. Disconnecting by unplugging an MC4 connector under load will damage the connector. Disconnecting with a properly rated DC load-break switch not a problem.

To Boatpoker’s comment, the risk of disconnecting at the battery side is similar to the risk to alternators - the collapsing field in the controller power electronics might cause damage when their output is disconnected under load.
HeywoodJ is offline   Reply With Quote
Old 14-11-2021, 08:47   #5
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Disconnecting panels under load

Again why. An alternator is a very specific case ( And one that alternator manufacturers could easily solve if they bothered )

In my case there is no such stipulation , I can disconnect anywhere I like

An mppt controller is essentially a switched mode power supply , there is no issue disconnecting its output.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 14-11-2021, 08:56   #6
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Disconnecting panels under load

Quote:
Originally Posted by goboatingnow View Post
Again why. An alternator is a very specific case ( And one that alternator manufacturers could easily solve if they bothered )

In my case there is no such stipulation , I can disconnect anywhere I like

An mppt controller is essentially a switched mode power supply , there is no issue disconnecting its output.
Well before I added my panels and MPPT controller, neither the manual nor the internet told me I couldn't disconnect at any point so I did a few times at the battery and so far nothing blew up or caught on fire.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 14-11-2021, 09:07   #7
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,515
Re: Disconnecting panels under load

Arcing contacts doesn't do them any good. Especially with DC circuits. DC doesn't have that nice waveform that goes thru zero Amps many times a second. Its that zero crossing that helps AC switches blow out the arc.
So, its best practice to switch off loads at the lower current branches, rather than at the source of much higher currents. So, if there is no big current, then it doesn't matter where you shut it down. If there is a large current, even the larger Batt switches will eventually complain about it.

This is why 125V DC rated circuit breakers are so expensive.

Here is a question. How does China Grid and Hydro Quebec shut off their 1MV
and 735kV DC transmission lines?
team karst is online now   Reply With Quote
Old 14-11-2021, 09:18   #8
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Disconnecting panels under load

Ah here turning off a 50A or 100A solar feed ( assuming you have 1200W ) is no biggie. Arcing might occur but the switch is built to withstand it. You’re not looking for 100,000 operations in 50 secs
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 14-11-2021, 09:42   #9
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,515
Disconnecting panels under load

Oh. Solar panels, not power panels. In that case, i’ll have start over. Thinking here about a towel over an electrical panel to fix an arc flash issue. 🤯

I disconnect my SOLAR controllers from the house batts sometimes. No ill effects. Even with current flowing.
team karst is online now   Reply With Quote
Old 14-11-2021, 09:47   #10
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,925
Re: Disconnecting panels under load

Most controllers instruct you to connect the battery first. Some will withstand ignoring that instruction, so will not. I looked for the controller I cooked when the battery got unplugged, but I have binned it. It showed serious signs of overheating.
donradcliffe is offline   Reply With Quote
Old 14-11-2021, 09:54   #11
Registered User

Join Date: Oct 2021
Posts: 589
Re: Disconnecting panels under load

Quote:
Originally Posted by goboatingnow View Post
Again why. An alternator is a very specific case ( And one that alternator manufacturers could easily solve if they bothered )

In my case there is no such stipulation , I can disconnect anywhere I like

An mppt controller is essentially a switched mode power supply , there is no issue disconnecting its output.
Yes, and most SMPS have a flyback system to prevent the damage that might occur when disconnecting under load. Serving inductive loads this is much more a problem than straight resistive loads. The mechanism is nearly identical to what happens in alternators, however, any decent power supply can deal with it. As could any reasonably designed alternator with a couple of extra dollars worth of components. The problem comes in with cheap/poorly designed systems where the flyback isn’t present or isn’t adequate. Hence “might”.

In all cases, much better to just tell the controller to shut down than to disconnect on either side, that way you don’t have to disconnect under load.
HeywoodJ is offline   Reply With Quote
Old 14-11-2021, 10:34   #12
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Disconnecting panels under load

Quote:
Originally Posted by HeywoodJ View Post
Yes, and most SMPS have a flyback system to prevent the damage that might occur when disconnecting under load. Serving inductive loads this is much more a problem than straight resistive loads. The mechanism is nearly identical to what happens in alternators, however, any decent power supply can deal with it. As could any reasonably designed alternator with a couple of extra dollars worth of components. The problem comes in with cheap/poorly designed systems where the flyback isn’t present or isn’t adequate. Hence “might”.

In all cases, much better to just tell the controller to shut down than to disconnect on either side, that way you don’t have to disconnect under load.
It’s simpler then that , an alternator is a big inductor , smps isnt, especially modern high frequency.

But I agree with what you say. A few bucks and alternators could easily design out the disconnect issue
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 14-11-2021, 12:11   #13
Senior Cruiser
 
skipmac's Avatar

Cruisers Forum Supporter

Join Date: Oct 2007
Location: 29° 49.16’ N 82° 25.82’ W
Boat: Pearson 422
Posts: 16,306
Re: Disconnecting panels under load

Quote:
Originally Posted by team karst View Post
Here is a question. How does China Grid and Hydro Quebec shut off their 1MV and 735kV DC transmission lines?
Don't know if they still do it this way but years ago a friend that worked with HV systems told me they used switches that were armed with some kind of cartridge, like a shotgun shell (without the shot of course) and the switches were blown open. The shell blew the switch open so fast that it eliminated or at least reduced the arcing.
__________________
The water is always bluer on the other side of the ocean.
Sometimes it's necessary to state the obvious for the benefit of the oblivious.
Rust is the poor man's Loctite.
skipmac is offline   Reply With Quote
Old 14-11-2021, 12:41   #14
Registered User
 
Steve_C's Avatar

Join Date: Apr 2009
Location: La Rochelle, France
Boat: L42
Posts: 530
Re: Disconnecting panels under load

Most Distribution and Transmission Lines use OCB's (Oil Circuit Breakers) to open and quench the Arc. In some cases the switches open inside of gas. It all depends on if the switch is design to open under load (load-Break) or just open circuit voltage.
__________________
_________________
Steve
www.svfreebird.com
Steve_C is offline   Reply With Quote
Old 14-11-2021, 13:03   #15
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,515
Re: Disconnecting panels under load

At around 100 kV ac and above, SF6 breakers have dominated modern installs.
I’ve not worked with the EHV dc systems directly. But, I suspect faults are managed on the ac/ pre-rectifier areas. Breaking a million volts dc at many tens of thousands of amps is really difficult.
team karst is online now   Reply With Quote
Reply

Tags
loa, panels


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Disconnecting Solar Panel Under Load Triton318 Electrical: Batteries, Generators & Solar 16 06-05-2015 06:34
disconnecting battery charging monte Electrical: Batteries, Generators & Solar 7 15-11-2014 14:34
Disconnecting internal voltage regulator on Yanmar alternator svstrider Electrical: Batteries, Generators & Solar 4 25-06-2012 03:52
When Temporarily Disconnecting Shrouds . . . off-the-grid Deck hardware: Rigging, Sails & Hoisting 7 13-12-2010 17:25
Dual Batt Charger: Will disconnecting one output damage it? AaronJ Electrical: Batteries, Generators & Solar 2 26-10-2009 03:04

Advertise Here


All times are GMT -7. The time now is 14:22.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.