Double or triple tapping 110 breakers?

I know in houses, if you double tap a breaker, you fail inspection but what about on boats? I am replacing a Blue Seas 110 breaker panel and some breakers were double and even triple tapped. I am sure this was done at the factory. What is the correct way to connect several wires to one breaker? If it were a house, i would wire nut them in a larger box but no wire nuts on the boat for me.



Also, what is the best way to clean a slightly corroded tin plated bus bar?
Sailorman Ed is offline   Reply With Quote
Old 18-09-2023, 18:13   #2
Registered User

Join Date: Jan 2023
Posts: 1,800
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by Sailorman Ed View Post
I know in houses, if you double tap a breaker, you fail inspection but what about on boats? I am replacing a Blue Seas 110 breaker panel and some breakers were double and even triple tapped. I am sure this was done at the factory. What is the correct way to connect several wires to one breaker? If it were a house, i would wire nut them in a larger box but no wire nuts on the boat for me.



Also, what is the best way to clean a slightly corroded tin plated bus bar?
For corroded bus bars, replace. Once the plating is compromised, there is no going back. If they are corroded, they are likely getting wet with salt water. Fix that too.

Definitely no wire nuts! There are household breakers with terminals specifically designed to double tap, but of course that does not guarantee your inspector will approve...

My memory is that the ABYC limits the number of connections on a single terminal to five. I believe that applies to both AC and DC. On any installation I do, I never do more than two power connections under one screw or nut. Sometimes--like on battery terminals--I will have a third measurement connection for voltage or temperature on top.

For entertainment, I have attached before and after photos. Before as the factory in France wired the 220V AC panel, and after I fixed it...
Attached Thumbnails
Click image for larger version

Name:	dsc_1805.jpg
Views:	230
Size:	323.0 KB
ID:	281187   Click image for larger version

Name:	DSC_1824(0).jpg
Views:	244
Size:	235.6 KB
ID:	281188  

SailingHarmonie is offline   Reply With Quote
Old 18-09-2023, 18:15   #3
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,339
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by Sailorman Ed View Post
I know in houses, if you double tap a breaker, you fail inspection but what about on boats? I am replacing a Blue Seas 110 breaker panel and some breakers were double and even triple tapped. I am sure this was done at the factory. What is the correct way to connect several wires to one breaker? If it were a house, i would wire nut them in a larger box but no wire nuts on the boat for me.



Also, what is the best way to clean a slightly corroded tin plated bus bar?
I wire my breakers to terminal strips (DIN rail or US style)

Assuming it’s copper under the tin: use a maroon scotchpad to clean it up, then brush on liquid tin: https://www.amazon.com/MG-Chemicals-.../dp/B081KRTZ4S
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 19-09-2023, 06:05   #4
Registered User
 
Sailorman Ed's Avatar

Join Date: Jun 2010
Boat: Gemini 105Mc+
Posts: 940
Images: 15
Send a message via Skype™ to Sailorman Ed
Re: Double or triple tapping 110 breakers?

Jedi, I have seen pics of your wiring, very nice. I actually had liguid Tin in my Amazon shopping cart. I'll get a scotchbirte pad.
'
Harmonie - I am surprised that you could add multiple connectors but thanks.
Ed
Sailorman Ed is offline   Reply With Quote
Old 19-09-2023, 07:07   #5
JBP
Registered User
 
JBP's Avatar

Join Date: Sep 2016
Location: Lake Erie, PA
Boat: Jeanneau Tonic 23
Posts: 544
Re: Double or triple tapping 110 breakers?

In house wiring, a "double tap" usually means two circuits on one breaker which is bad. In boats having two circuits on one breaker is still bad, for example cabin lights plus nav instruments on one breaker. However that does not mean you can't have two wires on one breaker, for example a cabin light wire running forward and a cabin light wire running aft is essentially one cabin lights circuit.
To avoid connecting too many wires to one screw, a terminal block is usually used for positive wires. A bus bar can be used to declutter negative wires.
JBP is offline   Reply With Quote
Old 19-09-2023, 08:56   #6
Registered User

Join Date: Nov 2017
Location: Portland, Oregon USA
Boat: Island Packet, Packet Cat 35
Posts: 1,016
Re: Double or triple tapping 110 breakers?

As a former home inspector. The reason double tapping is bad is that you cannot get the screw down tight enough to make a perfect connection which leads to microscopic arcing and if left long enough could lead to fire. Any competent inspector should see if they are double tap designed and if so, give it a pass.

I've not waded through the ABYC guidelines but I would suspect that double tapping is a no no. And, it's found on virtually every used boat out there.
Cpt Mark is online now   Reply With Quote
Old 19-09-2023, 08:58   #7
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,653
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by Cpt Mark View Post
As a former home inspector. The reason double tapping is bad is that you cannot get the screw down tight enough to make a perfect connection which leads to microscopic arcing and if left long enough could lead to fire. Any competent inspector should see if they are double tap designed and if so, give it a pass.

I've not waded through the ABYC guidelines but I would suspect that double tapping is a no no. And, it's found on virtually every used boat out there.
As long as there is adequate screw length, that shouldn't be an issue with properly sized and aligned ring terminals (as used on a boat), right? Home breakers are often designed to accept a bare wire connection which is a different story.
rslifkin is online now   Reply With Quote
Old 19-09-2023, 09:13   #8
Registered User

Join Date: Nov 2017
Location: Portland, Oregon USA
Boat: Island Packet, Packet Cat 35
Posts: 1,016
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by rslifkin View Post
As long as there is adequate screw length, that shouldn't be an issue with properly sized and aligned ring terminals (as used on a boat), right? Home breakers are often designed to accept a bare wire connection which is a different story.
In theory that makes sense. But, again, I haven't looked at the ABYC.

A very long time ago there was a company called Zinser who manufactured breaker panels for homes. They are long out of business but their panels are still found and need replacing. When they manufactured them the breakers slid in and locked as they should. However, there was the tiniest of gaps in there that lead to arcing which ate away the metal creating bigger arcing etc. It was many years before the houses caught fire because of this. I've only seen 1 of these panels but I could hear from a long way away.
Cpt Mark is online now   Reply With Quote
Old 19-09-2023, 10:59   #9
Registered User
 
Turtle Blues's Avatar

Join Date: Aug 2015
Location: Chesapeake Bay
Boat: 30' Ericson / 42' Golden Star / Yard full of trailer boats
Posts: 193
Re: Double or triple tapping 110 breakers?

Breakers are intentionally supplied with short screws to prevent this. If someone triple tapped one hopefully they replaced the screw which I do not recommend.
The accepted installation would be a single wire to a terminal strip with proper jumpers installed to power the additional circuits.
Turtle Blues is offline   Reply With Quote
Old 20-09-2023, 05:48   #10
Registered User

Join Date: Nov 2015
Boat: R&C Leopard 40
Posts: 926
Re: Double or triple tapping 110 breakers?

ABYC has a 4 terminals per terminal stud, with highest ampacity at the bottom working your way from largest to smallest.

There is also a rule that an AC motor has to have it's own individual over current or thermal protection device.

I can't find anything else, but that doesn't mean there isn't any.
__________________
-Chris
FlyingScot is offline   Reply With Quote
Old 23-09-2023, 18:13   #11
Registered User
 
Sailorman Ed's Avatar

Join Date: Jun 2010
Boat: Gemini 105Mc+
Posts: 940
Images: 15
Send a message via Skype™ to Sailorman Ed
Re: Liquid Tin coating on bussbars

Quote:
Assuming it’s copper under the tin: use a maroon scotchpad to clean it up, then brush on liquid tin: https://www.amazon.com/MG-Chemicals-.../dp/B081KRTZ4S
So I followed Jedi's suggestion, used the maroon scotchpad, then the salt and vinegar cleaner, then the Liquid Tin. Not perfect but substantially better. I also treated an old bare copper bussbar that was in remarkably good condition and it cleaned up very well with the salt vinegar solution and the tin looks the best here. I couldn't immerse the small double one so I tried just covered with a paper towel but the results were not good.


Tomorrow I am going to try the same process on the ends of wires.
Attached Thumbnails
Click image for larger version

Name:	Before.jpg
Views:	80
Size:	242.9 KB
ID:	281367   Click image for larger version

Name:	after vinagar cleaning.jpg
Views:	88
Size:	256.4 KB
ID:	281368  

Click image for larger version

Name:	with Liquid Tin.jpg
Views:	90
Size:	293.4 KB
ID:	281369  
Sailorman Ed is offline   Reply With Quote
Old 23-09-2023, 18:47   #12
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,301
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by Sailorman Ed View Post
I know in houses, if you double tap a breaker, you fail inspection but what about on boats? I am replacing a Blue Seas 110 breaker panel and some breakers were double and even triple tapped. I am sure this was done at the factory. What is the correct way to connect several wires to one breaker? If it were a house, i would wire nut them in a larger box but no wire nuts on the boat for me.



Also, what is the best way to clean a slightly corroded tin plated bus bar?
A few statements here about what people think ABYC might say ... I'm not getting into that argument so PM me an email address and I'll send you a copy of the Standards and you can see for yourself what the they actually say, which is quite different.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 23-09-2023, 19:27   #13
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,339
Re: Liquid Tin coating on bussbars

Quote:
Originally Posted by Sailorman Ed View Post
So I followed Jedi's suggestion, used the maroon scotchpad, then the salt and vinegar cleaner, then the Liquid Tin. Not perfect but substantially better. I also treated an old bare copper bussbar that was in remarkably good condition and it cleaned up very well with the salt vinegar solution and the tin looks the best here. I couldn't immerse the small double one so I tried just covered with a paper towel but the results were not good.

Tomorrow I am going to try the same process on the ends of wires.
Yours were pretty bad the black stuff is zinc oxide, to get rid of all that you may be better off sanding it to bare copper.

You can also brush it on with a small brush or even Q-tip. It’s nice stuff, right?
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 02-10-2023, 07:00   #14
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 586
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by SailingHarmonie View Post
For corroded bus bars, replace. Once the plating is compromised, there is no going back. If they are corroded, they are likely getting wet with salt water. Fix that too.

Definitely no wire nuts! There are household breakers with terminals specifically designed to double tap, but of course that does not guarantee your inspector will approve...

My memory is that the ABYC limits the number of connections on a single terminal to five. I believe that applies to both AC and DC. On any installation I do, I never do more than two power connections under one screw or nut. Sometimes--like on battery terminals--I will have a third measurement connection for voltage or temperature on top.

For entertainment, I have attached before and after photos. Before as the factory in France wired the 220V AC panel, and after I fixed it...
Looks like they got aa "deal" on brown wire...
sinnerman is offline   Reply With Quote
Old 02-10-2023, 10:30   #15
Registered User

Join Date: Sep 2017
Location: Langley, WA
Boat: Nordic 44
Posts: 2,555
Re: Double or triple tapping 110 breakers?

Quote:
Originally Posted by sinnerman View Post
Looks like they got aa "deal" on brown wire...
Brown is the European equivalent of black for AC wiring in the USA.

Once all the wiring is done a coat of Boeshield will prevent corrosion. BUT do it after all the terminals are in place and tight. You don't want the Boesheild under the terminals.
stormalong is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double pole circuit breakers for each circuit ayates Electrical: Batteries, Generators & Solar 9 04-01-2021 10:34
Double Pole Breakers on Metal Boats? msponer Electrical: Batteries, Generators & Solar 29 28-12-2011 14:00
Tapping for Mast and Boom Screws SvenG Construction, Maintenance & Refit 17 21-12-2010 13:21
Canvas Snaps with #10 Self-Tapping Threads thinwater Deck hardware: Rigging, Sails & Hoisting 0 02-08-2010 05:23
Tapping into Raymarine Power Cable nelson.peter Marine Electronics 7 01-06-2009 14:05

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 14:19.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.