Double Pole vs Single Pole Breaker

If you have a generator rated with a 40A single pole breaker wouldn't you change it to a 20A double pole breaker if you switch the generator to 240V output. Isn't a double pole breaker just two single pole breakers put together. Which means that any 120V loads on one leg can't go over 20A?
tuberider is offline   Reply With Quote
Old 13-02-2016, 05:18   #2
Registered User

Join Date: Jul 2015
Posts: 41
Re: Double Pole vs Single Pole Breaker

The simple answer... Yes your right.
A generator rated at 4800 watts would give you 40 amps at 120.
If it's equipped with the taps to change its output to 240 you would then need a 2 pole 20 amp breaker.
A two pole breaker may look like two singles connected together but most have an internal tie as well insuring both poles open during operation.

W = E x I x PF
dave948 is offline   Reply With Quote
Old 13-02-2016, 05:25   #3
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,261
Images: 241
Re: Double Pole vs Single Pole Breaker

More or less correct.
A single pole breaker is used with a typical 120v circuit, having one hot wire and one neutral wire.
However, a double pole breaker is used with a typical 240v circuit having two hot wires.
If there is a short circuit to either hot wire, both poles are ganged together (tie bar) so both trip together. Without the tie bar, it is possible to trip one side of the breaker while leaving the other hot.
A generator, rated at 4,800 Watts, will put out 40 Amps at 120 Volts, or 20 Amps at 240 Volts.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 13-02-2016, 05:34   #4
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Double Pole vs Single Pole Breaker

Without advocating dangerous practices...

In theory you have it about right... Double pole is two singles... and overloading either trips both....

Breakers don't care what voltage they see up to their rating... So... a 20A is going to trip over 20A @ 120v or 240v
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 13-02-2016, 05:55   #5
Registered User

Join Date: Jan 2012
Posts: 101
Re: Double Pole vs Single Pole Breaker

Thank you very much. this settled a discussion I've been having with a fellow employee. It started with you having to make sure the 120V load is well balanced because now you only have 20A at 120V per leg.
tuberider is offline   Reply With Quote
Old 13-02-2016, 06:14   #6
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Double Pole vs Single Pole Breaker

Quote:
Originally Posted by tuberider View Post
Thank you very much. this settled a discussion I've been having with a fellow employee. It started with you having to make sure the 120V load is well balanced because now you only have 20A at 120V per leg.

As hard as I tried to understand this...

I failed miserably !!!

Imma guess...

You have 240 per leg... as the "reference" is the other leg... 2 hot in 240, no neutral... You have 120 if your reference the neutral...
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 13-02-2016, 06:26   #7
Registered User
 
captjcook's Avatar

Join Date: Jul 2008
Location: Fort Lauderdale Florida
Boat: Northstar 1500, 35'
Posts: 318
Re: Double Pole vs Single Pole Breaker

Mdr...if you have "240" legs you get 480 volts. A double throw should never be used as a "twin" 120 volt breaker going different to different circuits. I don't comprehend term "balanced". Legs more commonly referred to as "phase"


Sent from my iPad using Cruisers Sailing Forum
captjcook is offline   Reply With Quote
Old 13-02-2016, 06:54   #8
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Double Pole vs Single Pole Breaker

Quote:
Originally Posted by captjcook View Post
Mdr...if you have "240" legs you get 480 volts. A double throw should never be used as a "twin" 120 volt breaker going different to different circuits. I don't comprehend term "balanced". Legs more commonly referred to as "phase"


Sent from my iPad using Cruisers Sailing Forum
I definitely understand....
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 13-02-2016, 07:26   #9
Registered User
 
Nicholson58's Avatar

Cruisers Forum Supporter

Join Date: Jan 2011
Location: Caribbean live aboard
Boat: Camper & Nicholson58 Ketch - ROXY Traverse City, Michigan No.668283
Posts: 6,517
Images: 84
Re: Double Pole vs Single Pole Breaker

Quote:
Originally Posted by HappyMdRSailor View Post
Without advocating dangerous practices...

In theory you have it about right... Double pole is two singles... and overloading either trips both....

Breakers don't care what voltage they see up to their rating... So... a 20A is going to trip over 20A @ 120v or 240v
PERFECT! I confirmed this with my electrical engineer at the office. Amps is Amps - volts don't matter up to the voltage rating. Ratings are typically 600 volts.

I always use two pole breakers so that the + & - are both interrupted. This isolates the devices totally. I have noted that devices that were so-isolated survived lightning strikes but single breaker systems did not. I have extended this practice also to two-pole on-off switches for all electronics - same observations.
Nicholson58 is offline   Reply With Quote
Old 13-02-2016, 12:21   #10
Registered User

Join Date: Jan 2012
Posts: 101
Re: Double Pole vs Single Pole Breaker

What I was trying to get at is that if you change out a 120v distribution panel that has a 40a single pole main breaker with a 120/240v panel with a 20a double pole main breaker you have to make sure the 120v loads are balanced. For example if you loaded up one 120v phase with 25a and the other 120v phase with 5a the double pole breaker would trip. Then you would lose 10a of power. By balancing each 120v circuit so neither one exceeds 20a you get the most out of your generator.
tuberider is offline   Reply With Quote
Old 13-02-2016, 15:20   #11
Registered User
 
captjcook's Avatar

Join Date: Jul 2008
Location: Fort Lauderdale Florida
Boat: Northstar 1500, 35'
Posts: 318
Re: Double Pole vs Single Pole Breaker

This is not true, I suggest you hire a qualified marine electrician for the installation to avoid a fire.


Sent from my iPad using Cruisers Sailing Forum
captjcook is offline   Reply With Quote
Old 13-02-2016, 15:53   #12
Registered User

Join Date: Jan 2012
Posts: 101
Re: Double Pole vs Single Pole Breaker

if limiting your load to less than 20a on a 20a breaker, how could that possibly cause a fire.
tuberider is offline   Reply With Quote
Old 16-02-2016, 05:51   #13
Moderator Emeritus
 
HappyMdRSailor's Avatar

Cruisers Forum Supporter

Join Date: May 2008
Location: Fort Lauderdale, FL
Boat: 48 Wauquiez Pilot Saloon
Posts: 5,975
Re: Double Pole vs Single Pole Breaker

Quote:
Originally Posted by tuberider View Post
What I was trying to get at is that if you change out a 120v distribution panel that has a 40a single pole main breaker with a 120/240v panel with a 20a double pole main breaker you have to make sure the 120v loads are balanced. For example if you loaded up one 120v phase with 25a and the other 120v phase with 5a the double pole breaker would trip. Then you would lose 10a of power. By balancing each 120v circuit so neither one exceeds 20a you get the most out of your generator.
I think you're confusing everybody with the term "phase" here... ALL of your loads are working off of "single phase" power regardless of voltage and reference.... hot to hot = 240 1ph, hot to neutral = 120 1ph...

Sure... make your 120v loads balanced for each breaker...

But it sounds like you now have 240v loads as well.... This will take some load from BOTH main breakers
__________________
In the harsh marine environment, something is always in need of repair...

Mai Tai's fix everything...
HappyMdRSailor is offline   Reply With Quote
Old 16-02-2016, 08:02   #14
Registered User

Join Date: Jan 2012
Posts: 101
Re: Double Pole vs Single Pole Breaker

Thank-you for the phase correction. My original premise was with 20a double pole breaker, one leg can't draw more than 20a.

Sent from my Nexus 7 using Cruisers Sailing Forum mobile app
tuberider is offline   Reply With Quote
Reply

Tags
single


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: Blue Sea 150amp DC Circuit Breaker Panel (Single) Opie91 Classifieds Archive 0 17-01-2016 12:53
Three pole breaker wiring HELP, and is it safe? AndDavRos Electrical: Batteries, Generators & Solar 6 08-11-2015 13:54
double the inverter double the wattage? drousy88 Electrical: Batteries, Generators & Solar 21 27-03-2013 08:26
single/double spreaders tommyh Monohull Sailboats 4 01-03-2013 10:01
Wiring Single Pole Single Throw (SPST) Rocker Switch with Light Patrick_DeepPlaya Marine Electronics 17 14-05-2011 19:42

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 16:41.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.