Re: ELCI / Isolation Transformer.

What make/model is the surge suppressor you detail in your drawing?

Quote:
Originally Posted by s/v Jedi View Post
Attached my “gold standard” AC power reference diagram. It is comprehensive but you can just pick what you need from it and ignore other parts.

It has a 30A 120V 60Hz shore power with isolation transformer that can use an adapter to connect to 16A 230V 50Hz shore power. The transformer in this diagram always outputs 230/240V so when 120V 30A is put in, 240V 15A will come out. See how it breaks the ground conductor from shore? That is the most important part of it. The output then goes to your “shore/gen” selector switch.

There’s also the popular 120/240V 50A 60Hz shore power connection. This one is 12kW which makes for a very big isolation transformer so instead I used a galvanic isolator. I also added a surge suppressor to reduce the risk of damage from lightning strikes etc.

The part about a battery charger on shore power and an inverter for the power used aboard is done a little differently (more costly) in this diagram: it has two inverter/chargers of the same type. To get one to just invert for use of it’s output aboard, you flip the input breaker to the OFF position. The other one does the charging so on the outputs you use the unit that is inverting, not the one that is charging. This diagram allows to change things by turning switches instead of rewiring. Also, it uses 230/240V throughout and only creates 120V in the distribution groups. This is only of interest for US boats with 120V outlets.
bglad is offline   Reply With Quote
Old 28-12-2020, 14:37   #32
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: ELCI / Isolation Transformer.

Quote:
Originally Posted by CharlieJ View Post
@goboatingnow
It should be noted that the ABYC Standards and the ISO Standards are being homogenized. This is a long process, but the end result will be universal standards worldwide for the recreational boating market.

BTW: Though not mentioned in the verbiage, ISO 13297 Small craft -Electrical systems Alternating current installations Figure D.3 clearly shows an electrostatic screen between the primary and secondary windings and connected to the shore safety ground. It is not connected to the isolation xfmr case. Note that Appendix D is "Informative".


Which year version are you referencing
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 28-12-2020, 15:16   #33
Registered User

Join Date: Dec 2020
Posts: 26
Re: ELCI / Isolation Transformer.

[QUOTE=CharlieJ;3308093]@mimijane #29


You will be compliant with ABYC if you can install the iso. xfmr. within 10', measured along the conductor, from the shore power inlet. In this case, no ELCI is required.
/QUOTE]


Hi Charlie,


Yes, but I would believe this would require an IT that complies with AYBC standards (As noted the Victron units don't have the shield). One can purchase a medical transformer that meets this requirement (example: http://catalog.triadmagnetics.com/As...M240-10400.pdf) , but it's not encapsulated so it still doesn't meet E11.7.



I'm pretty sure the Carling 120/240VAC are for split phase installations and expects the 240VAC line-line voltage to run the current sense module part. Maybe I'm just looking for something that doesn't exist.



Cheers,
Mark
mimijane is offline   Reply With Quote
Old 28-12-2020, 21:30   #34
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,425
Re: ELCI / Isolation Transformer.

Quote:
Originally Posted by CharlieJ View Post
@s/v Jedi #24


I will explain how the ABYC develops the Standards with a quote from the Standards:



The ABYC Staff has 16 paid staff members across five departments: Admin, Education, Technical, Membership and Marketing.

The Standards are developed in accordance with the quote above. Membership on the individual PTCs is based on expertise and experience and membership is closely monitored so that all market segments are represented. For example, the Electrical PTC is comprised of boatbuilders, equipment manufacturers, surveyors, USCG, UL, consulting engineers, working marine electricians, etc. These members are all volunteers...about 300 total volunteers across all the 70+ Standards.

I am disappointed in your comment as it comes from someone with an excellent technical background who has voluntarily shared his expertise on this forum over 11k times.

I again invite you, and anybody else that wants to improve the Standards, to join the applicable Standards' mailing list and participate.
I won’t. I do not believe in volunteering for something that is used commercially. Before I retired I volunteered a significant amount of time for organizations related to my work area; it’s not something to take lightly.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 28-12-2020, 21:33   #35
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,425
Re: ELCI / Isolation Transformer.

Quote:
Originally Posted by bglad View Post
What make/model is the surge suppressor you detail in your drawing?
Progressive.
Attached Thumbnails
Click image for larger version

Name:	C3FBCBD3-AB40-4D4B-BFF0-14711482A26D.jpg
Views:	106
Size:	434.6 KB
ID:	229578  
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 29-12-2020, 06:05   #36
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,560
Re: ELCI / Isolation Transformer.

@s/v Jedi #34

Quote:
I won’t. I do not believe in volunteering for something that is used commercially. Before I retired I volunteered a significant amount of time for organizations related to my work area; it’s not something to take lightly.
I obviously will not change your mind about applying your technical knowledge to a wider audience by codifying it in the ABYC Standards. But I have to leave you with two thoughts:
1. In the USA, a non-profit organization (which the ABYC is) is just that, "non-profit". Your objection to contributing your knowledge to a "commercial" endeavor is strange. But it is absolutely your decision.
2. You object to volunteering as it is "...not something to take lightly." And yet you have posted on this site more than 11k times which certainly appears to be volunteering to me.
Oh well, one man's logic is another man's folly.

I am sorry you won't make the effort to improve the Standards...your expertise would have been welcomed and you would have made a positive impact.

"Better to light a candle than to curse the darkness."
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 29-12-2020, 06:08   #37
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,560
Re: ELCI / Isolation Transformer.

@goboatingnow #32

I am referring to ISO 13297-2012.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 29-12-2020, 06:42   #38
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: ELCI / Isolation Transformer.

Quote:
Originally Posted by CharlieJ View Post
@goboatingnow #32

I am referring to ISO 13297-2012.


Hmm. I see no reference to the drawing you mention in 2012 or later Ones either
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 29-12-2020, 08:44   #39
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,560
Re: ELCI / Isolation Transformer.

@goboatingnow #38

Page 21 of the document.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 29-12-2020, 13:01   #40
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: ELCI / Isolation Transformer.

Quote:
Originally Posted by CharlieJ View Post
@goboatingnow #38



Page 21 of the document.


I’m sorry to be so dense, my copy does not go beyond page 16 ( Annex D)
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 29-12-2020, 13:09   #41
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: ELCI / Isolation Transformer.

Ah I see the 2012 version has two extra annex’s , afaik they have been removed from the standard in subsequent years.

Irrespective the screen shown is not part of the actual spec
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 30-12-2020, 05:30   #42
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,560
Re: ELCI / Isolation Transformer.

goboatingnow#41
Quote:
Irrespective the screen shown is not part of the actual spec
As I noted in #28 above.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 30-12-2020, 06:03   #43
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,425
Re: ELCI / Isolation Transformer.

Quote:
Originally Posted by CharlieJ View Post
@s/v Jedi #34

I obviously will not change your mind about applying your technical knowledge to a wider audience by codifying it in the ABYC Standards. But I have to leave you with two thoughts:
1. In the USA, a non-profit organization (which the ABYC is) is just that, "non-profit". Your objection to contributing your knowledge to a "commercial" endeavor is strange. But it is absolutely your decision.
2. You object to volunteering as it is "...not something to take lightly." And yet you have posted on this site more than 11k times which certainly appears to be volunteering to me.
Oh well, one man's logic is another man's folly.

I am sorry you won't make the effort to improve the Standards...your expertise would have been welcomed and you would have made a positive impact.

"Better to light a candle than to curse the darkness."
Okay, another attempt to explain this: you are/represent a commercial business that uses the ABYC recommendations and information. You ask me to volunteer my time and effort to make that data better even though it has only negative effect for me (even less time for family, friends, socializing). Life is too short for that, sorry. I have done my share of contributing to the advance of mankind

Here on CF and FB I can directly help others, or at least point out the regular BS so that fellow sailors aren’t getting in more trouble than they already are and I can do it whenever I have sometime for it.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 20-02-2021, 23:10   #44
Registered User
 
mdsilvers's Avatar

Join Date: Mar 2009
Boat: Antares 44i - Field Trip
Posts: 120
Re: ELCI / Isolation Transformer.

I've been researching an EFCI/ELCI issue I'm having with my Victron Isolation transformer. I'm pulling my hair out trying to find the issue.

I am trying to figure out if I am chasing real issues or one based on the setup of my installation.

I have installed the Victron 3600 isolation transformer. The output of the transformer goes to a 30m Amp .1s breaker (photo attached).

Every time I turn on the unit and flip on my control panel's power, the GFCI trips.

If I remove the jumper (picture), it does not trip and works fine.

I don't want to 'fix' a problem incorrectly. I have tried to track down a ground fault but can't seem to find one. I noticed from a photo that another boat owner - Jedi - has a similar setup. He is using 120v in and 120v out - but the jumpers were not on J33 & J21.

The manual states to have this jump 'on' for GFCIs to function correctly.

I've hit a wall on this. Any advice from others would be appreciated.

Thanks.
Attached Thumbnails
Click image for larger version

Name:	Breaker.jpg
Views:	65
Size:	403.7 KB
ID:	232955   Click image for larger version

Name:	Victron Install.jpg
Views:	82
Size:	444.1 KB
ID:	232956  

__________________
Mark

https://svfieldtrip.blogspot.com
mdsilvers is offline   Reply With Quote
Old 21-02-2021, 04:26   #45
Registered User

Join Date: Dec 2012
Location: Jacksonville, Florida
Posts: 80
Re: ELCI / Isolation Transformer.

Just curious. You are using 230/240 in and 110/120 out?

Quote:
Originally Posted by mdsilvers View Post
I've been researching an EFCI/ELCI issue I'm having with my Victron Isolation transformer. I'm pulling my hair out trying to find the issue.

I am trying to figure out if I am chasing real issues or one based on the setup of my installation.

I have installed the Victron 3600 isolation transformer. The output of the transformer goes to a 30m Amp .1s breaker (photo attached).

Every time I turn on the unit and flip on my control panel's power, the GFCI trips.

If I remove the jumper (picture), it does not trip and works fine.

I don't want to 'fix' a problem incorrectly. I have tried to track down a ground fault but can't seem to find one. I noticed from a photo that another boat owner - Jedi - has a similar setup. He is using 120v in and 120v out - but the jumpers were not on J33 & J21.

The manual states to have this jump 'on' for GFCIs to function correctly.

I've hit a wall on this. Any advice from others would be appreciated.

Thanks.
bglad is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
ELCI and isolation transformers Cyrus Safdari Electrical: Batteries, Generators & Solar 0 11-09-2020 07:19
ELCI and isolation transformers Cyrus Safdari Electrical: Batteries, Generators & Solar 0 11-09-2020 07:18
ELCI and Isolation Transformer gpeacock Electrical: Batteries, Generators & Solar 12 29-04-2014 09:27
ELCI and Isolation Transformer Microship Electrical: Batteries, Generators & Solar 20 19-08-2010 15:54
Isolation transformer Pa La O La Construction, Maintenance & Refit 11 12-08-2008 13:14

Advertise Here


All times are GMT -7. The time now is 05:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.