Entec EW-4200-D Voltage Adjust?

I have an Entec West EW-4200-D 4.2 kW generator. It starts and runs great, with a pretty steady 60 Hz output under various loads (drops maybe to 59.3 HZ fully loaded). The issue is the voltage. Under no load is at 109.5 volt, and if loaded up to 21 amp (out of 35 amp capacity) voltage drops to 104.3. Specified output is 120 VAC.

This is a huge issue as my battery charger's DC output to the batteries is greatly reduced (like cut in half or worse) with these low voltages. The charger wants to see 115 VAC or better for proper operation.

The manual says nothing about adjustment of voltage of the generator. Getting info from factory is an issue as Entec was sold some time ago to Mastry Engine Center, and no one there seems to know much about the Entec product (or at least no one I have talked to yet).

If anyone should happen to know the procedure for adjusting AC voltage output of the generator on these units, I would most appreciate your help.

Thanks
Dennis.G is offline   Reply With Quote
Old 11-12-2013, 17:23   #2
Registered User
 
glenn.225's Avatar

Join Date: Jan 2008
Location: Kingston, ON
Boat: Albin Vega 27'
Posts: 531
Re: Entec EW-4200-D Voltage Adjust?

A lot of gensets I have worked on have a voltage adjustment, screw or dial. It may be inside the panel. RPM will adjust hertz. There is a technical help here: Entec West Technical Request Form
__________________
Glenn
glenn.225 is offline   Reply With Quote
Old 11-12-2013, 17:42   #3
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Entec EW-4200-D Voltage Adjust?

Entec used the Mecc Alte Spa generators with an excitation capacitor on the excitation winding.


You should be able to test the winding and capacitor for spec, you might also have a look at the Mecc site for more info.

Also the engine is a Faryman so you can look to their site for governor adjustments.

A good gen mechanic or a marine electrician can most likely sort out what the real issues are.

It sounds as if your gov... setting maybe low, along with excitation issues. Your no load voltage should be at least 120 and hz about 62.

Lloyd

Quote:
Originally Posted by Dennis.G View Post
I have an Entec West EW-4200-D 4.2 kW generator. It starts and runs great, with a pretty steady 60 Hz output under various loads (drops maybe to 59.3 HZ fully loaded). The issue is the voltage. Under no load is at 109.5 volt, and if loaded up to 21 amp (out of 35 amp capacity) voltage drops to 104.3. Specified output is 120 VAC.

This is a huge issue as my battery charger's DC output to the batteries is greatly reduced (like cut in half or worse) with these low voltages. The charger wants to see 115 VAC or better for proper operation.

The manual says nothing about adjustment of voltage of the generator. Getting info from factory is an issue as Entec was sold some time ago to Mastry Engine Center, and no one there seems to know much about the Entec product (or at least no one I have talked to yet).

If anyone should happen to know the procedure for adjusting AC voltage output of the generator on these units, I would most appreciate your help.

Thanks
FlyingCloud1937 is offline   Reply With Quote
Old 11-12-2013, 17:47   #4
Registered User
 
Dennis.G's Avatar

Join Date: May 2011
Location: Sea of Cortez and the U.P. of Michigan
Boat: Celestial 48
Posts: 904
Re: Entec EW-4200-D Voltage Adjust?

Glenn: Thanks for reply. Under cover plate only some wires and a capacitor. No adjustable device seen. Also, the help link to Entec West seems to be broken (only get error on submit).
Dennis.G is offline   Reply With Quote
Old 11-12-2013, 18:00   #5
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Entec EW-4200-D Voltage Adjust?

2 pole MeccAlteSpa capacitor excited, You should have a name plate on the gen match it to the link I posted. It shows all the 2 pole capacitor gens with schematics and parts lists and specs.

Lloyd

Quote:
Originally Posted by FlyingCloud1937 View Post
Entec used the Mecc Alte Spa generators with an excitation capacitor on the excitation winding.


You should be able to test the winding and capacitor for spec, you might also have a look at the Mecc site for more info.

Also the engine is a Faryman so you can look to their site for governor adjustments.

A good gen mechanic or a marine electrician can most likely sort out what the real issues are.

It sounds as if your gov... setting maybe low, along with excitation issues. Your no load voltage should be at least 120 and hz about 62.

Lloyd
FlyingCloud1937 is offline   Reply With Quote
Old 12-12-2013, 06:31   #6
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: Entec EW-4200-D Voltage Adjust?

I agree with Lloyd that you should bump the rpm's to give 62Hz no load. This may be enough to increase the voltage back into spec.

If not, change the capacitor. It is a common inexpensive motor run capacitor - the only important information is the farad number printed on it. Look on the capacitor and something like 20uF or 40uF, etc should be printed on it. Just replace with same value and a voltage rating 250V or higher. Should cost $10-15 at any HVAC or motor supply place.

Don't touch the capacitor terminals without grounding or shorting them first.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 13-12-2013, 05:03   #7
Registered User

Join Date: Aug 2007
Location: In boat fixing' season I'm in a Maryland boat yard too close to Washington, DC ... except when I escape to home on the beach in Florida!
Boat: Prout Snowgoose 34
Posts: 175
Re: Entec EW-4200-D Voltage Adjust?

Dennis.G

Doug Jensen is Mastry's Entec specialist. His e-mail: djensen@mastry.com and his mobile telephone: Whoops … I might have the area code incorrect … but try it both ways: (386 or 863) 872-1473.

He is in charge of Mastry's Entec product and is based in Florida. He has been helpful to me and others. Be sure to let us know how it goes with you.

Roger
svtrio is offline   Reply With Quote
Old 28-12-2013, 12:49   #8
Registered User
 
Dennis.G's Avatar

Join Date: May 2011
Location: Sea of Cortez and the U.P. of Michigan
Boat: Celestial 48
Posts: 904
Re: Entec EW-4200-D Voltage Adjust?

Updating tathis issue:

I removed the capacitor and tested using a small meter with capacitance reading. This was non-conclusive, I think from meter not being designed to test large power type capacitors. I rode my bike all over La Paz, stopping at about a dozen places looking for a 20 MF capacitor with no luck. Finally got a friend to bring one down from Graingers in USA.

I did find a 25 MF capacitor and tried it out. Generator output shot up to 131 VAC. Didn't plug anything into that, but was interesting test.

When I did get the new capacitor (last night) installed, and started up generator, got 118 VAC and 60.0 Hz (no load) and 115 VAC 59.8 Hz when loaded about 60%.

I would like to crank up the Hz to 61 or 62 Hz at no load (to get a few more volts output), and figured out how to do it, but instructions recommend a special tool to avoid bending the adjustment screw, and as that is something I don't have I think I will resist the temptation for now.
Dennis.G is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 04:20.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.