Re: Fuse Sizing

In the illustration on the right, if both resistive loads are energized simultaneously the breaker will trip, opening the circuit (in most cases).

It is unclear to me what the author is trying to illustrate here. I simply don't know.

Mr. Casey has written for years for BoatUS, Sail magazine, International Marine, etc. Despite this, I am unable to locate any direct contact information, so we may never know what the author intended.

For the right side illustration, you could, per AYBC, provide a 60 amp breaker, and maybe not have nuisance trips (though I doubt it), or rethink the wire gauge to #8, along with a breaker/fuse at 70 amps and be protected (as well as having lower voltage drop). I would choose the latter.
redsky49 is offline   Reply With Quote
Old 12-06-2017, 15:50   #32
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Fuse Sizing

Quote:
Originally Posted by masonc View Post
The breaker size is determined by the cable, not the load. The cable is determined by the load.
No, as has been clarified many times above, if you plan a circuit to carry maximum X amps, but decide to use a heavier cable than what safety requires to reduce voltage drop, then it would make sense to size CP (and buss, connectors etc) to the smaller load rating.
john61ct is offline   Reply With Quote
Old 12-06-2017, 20:08   #33
Registered User

Join Date: Aug 2015
Posts: 474
Re: Fuse Sizing

Quote:
Originally Posted by john61ct View Post
No, as has been clarified many times above, if you plan a circuit to carry maximum X amps, but decide to use a heavier cable than what safety requires to reduce voltage drop, then it would make sense to size CP (and buss, connectors etc) to the smaller load rating.
Well the standards only quantify the maximum size circuit protection that can be employed for a given wire size/ampacity. Obviously you can decrease the breaker size if you aren't going to carry as much current.
boatbod is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Calculating House Bank DC Fuse size. Pelagic Electrical: Batteries, Generators & Solar 1 28-07-2008 02:05
Starter fuse for outboard... Allan S Engines and Propulsion Systems 2 11-05-2008 18:27
Fuse between Battery(s) and Selector Switch Chief Engineer Electrical: Batteries, Generators & Solar 27 14-01-2008 16:25
Voltage reading battery/fuse board seafox Electrical: Batteries, Generators & Solar 14 28-07-2007 17:52
Fuse Protection Ted Beyer Electrical: Batteries, Generators & Solar 5 17-05-2005 10:07

Advertise Here


All times are GMT -7. The time now is 23:22.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.