Galvanic Isolator or Iso Transformer - To Bond or Not ?

I have a 43 ft Bene and am looking for opinions on the above. I am leaning towards the galv isolator due to price, size, and weight considerations, but have no experience with this. I have bronze thru-hulls for the most part which are not currently bonded. The only zinc is on the prop shaft and I do not have a genset or inverter. Thanks.
CHM is offline   Reply With Quote
Old 28-01-2012, 07:34   #2
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,439
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Galvanic isolators can fail and leave you without a ground on board - a potentially fatal problem. Or fail closed and fail to protect your boat.

I think the isolation transformer is a much better solution, but much more expensive, heavier, and bulkier, plus will limit the amount of current from shore power.

There is a third solution -- just don't leave the boat plugged in. Have you thought about that? If you have solar or a wind gennie, why leave your boat plugged in when you're not on board? That might be the best solution of all.
Dockhead is offline   Reply With Quote
Old 28-01-2012, 08:30   #3
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,831
Images: 241
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Here’s a good analysis of GI’s & IT’s:
SmartGauge Electronics - Isolation Transformers or Galvanic Isolator? 1/2
SmartGauge Electronics - Isolation Transformers or Galvanic Isolator 2/2

About Fail-Safe GI’s - Excerpted from ABYC A-8
“Fail Safe Galvanic Isolator – An isolator that, if after meeting all other criteria of this standard, meets the requirements of an effective ground-fault current path when subjected to the test conditions in A-28.14, Table 2.
NOTE: The device may not continue to provide galvanic isolation in the event of a failure. “

“28.6.1 The galvanic isolator shall be equipped with an integral or external status monitor that provides an audible or visible indication of failure.
Exception: Fail-Safe galvanic isolators
28.6.2 The monitor shall alert when tested between the wiring terminals on the isolator as a result of the following conditions:
28.6.2.1 the isolator fails to conduct above 2.5 volts DC in both directions or if the isolator fails to open below 1.0 volt DC in both directions, or
28.6.2.2 the shorted or open condition of current carrying components in the ground path.

More ➥ http://deimarine.com/deimarine/sites..._liability.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 28-01-2012, 08:44   #4
CHM
Registered User
 
CHM's Avatar

Join Date: Dec 2011
Location: Ponce Inlet, FL
Boat: Beneteau Moorings 432
Posts: 241
Images: 1
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Thanks for the quick replies. I read through the above links already as well as the ABYC section 11 standards - well I am on page 50 or so. I already do not have the shore power connected while I am away from the boat and have a wind generator on board. In fact, the boat is currently in the yard on stands. I recently purchased the boat and am trying to balance the ABYC ideals with reality. I never want to be the one responsible for unsafe conditions which could injure someone. I will likely leave things be for now and go with the isolation transformer when the time comes when I need shore power for an extended period. I am actually looking for folks who have this equipment in a similar vessel. I am not sure where I would install an IT. It looks like they mostly mount to a bulkhead, but thats a lot of weight! The shore power inlet is on the aft starboard cabin bulkhead just above the panel in the aft starboard berth. Installing an IT there looks feasible, but would certainly infringe on space and likely generate some heat. A galvanic isolator with an indicator might be a reasonable alternative. What about the bonding question?
CHM is offline   Reply With Quote
Old 28-01-2012, 08:56   #5
Moderator Emeritus
 
nigel1's Avatar

Cruisers Forum Supporter

Join Date: Oct 2009
Location: Manchester, UK
Boat: Beneteau 473
Posts: 5,595
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Quote:
Originally Posted by CHM View Post
What about the bonding question?
I have a Bene 473 According to dealer, the boat was originally delivered with only a prop zinc, which accordding to him last about 3 months

The PO fitted a hull anode, and I have also fitted a shaft anode. Also in the process of fitting bushes to the prop shaft, which will then connect direct to the hull anode. Although the prop shaft has a solid coupling to the gear box, I have been advised that continuity can be lost with the shaft turning, the oil in the gear box isolating the prop shaft.
As for the through hulls, only two on my boat are bonded, the cooling water">engine cooling water inlet, and the water inlet to the prop shaft seal This was factory fitted.
Boat is 10 yrs old with no sign of corrosion on the though hulls.

If your concerned, best get a boat electrician to check the boat over when back in the water.

Oh, and +1 to disconnecting from shore power when not needed
__________________
Nigel
Beneteau 473
Manchester, UK
nigel1 is offline   Reply With Quote
Old 28-01-2012, 09:59   #6
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,886
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

If you're in fresh water and worried about safety, forget the galvanic isolator. Install one of these

Double Pole Residual Current Circuit Breaker ( RCBO-ELCI )

Then break the connection between the AC green wire and the boat DC ground which is the reason you need a galvanic isolater in first place.
donradcliffe is offline   Reply With Quote
Old 28-01-2012, 10:09   #7
Registered User

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40 (sold). Still have a Hobie 20
Posts: 2,953
Images: 7
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

The one you referenced and E-02 all say IF bonding, IF cathodic protection, IF galvanic isolator, IF isolation transformer, is installed...

So these are not ABYC requirements. Not saying that these are bad or good ideas, just if you're worried about following the standard, the standard does not require any of the above.

John

Quote:
Originally Posted by CHM View Post
Thanks for the quick replies. I read through the above links already as well as the ABYC section 11 standards - well I am on page 50 or so. I already do not have the shore power connected while I am away from the boat and have a wind generator on board. In fact, the boat is currently in the yard on stands. I recently purchased the boat and am trying to balance the ABYC ideals with reality. I never want to be the one responsible for unsafe conditions which could injure someone. I will likely leave things be for now and go with the isolation transformer when the time comes when I need shore power for an extended period. I am actually looking for folks who have this equipment in a similar vessel. I am not sure where I would install an IT. It looks like they mostly mount to a bulkhead, but thats a lot of weight! The shore power inlet is on the aft starboard cabin bulkhead just above the panel in the aft starboard berth. Installing an IT there looks feasible, but would certainly infringe on space and likely generate some heat. A galvanic isolator with an indicator might be a reasonable alternative. What about the bonding question?
cal40john is offline   Reply With Quote
Old 29-01-2012, 08:22   #8
Sponsoring Vendor

Community Sponsor

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 414
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Quote:
Originally Posted by Dockhead View Post
Galvanic isolators can fail and leave you without a ground on board - a potentially fatal problem. Or fail closed and fail to protect your boat.
We have sold thousands of Galvanic Isolators over a period of about 14 years. EVERY one has unconditonal warranty. So far there has only been one return under warranty and it was a severe lightning strike victim.

Certainly an isolation transformer is preferable especially if you get one with voltage taps. On our boat we use shore power anywhere from about 80 volts to 430. But there is too much paranoia on the reliability of galvanic isolators, they are extremely reliable.
Andina Marie is offline   Reply With Quote
Old 29-01-2012, 10:38   #9
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

But without a remote monitor you don't know if it has failed or not.
mitiempo is offline   Reply With Quote
Old 29-01-2012, 10:42   #10
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

The standard European method is as seen in the Beneteau, thats is no continuous bonding, hence a galvanic isolator or even a traffo isnt as common as in US systems, with continous bonding.

I wouldnt install either just check the thru-hulls as in Europe DNZ brass is more common then bronze and thats whats youll have.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 29-01-2012, 10:49   #11
Registered User

Join Date: Sep 2011
Location: port aransas
Boat: departure 35
Posts: 116
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

My boat doesn't have a galvanic isolator, yet, but if it had I probably wouldn't have gotten my lights knocked out a few days ago. My shore power breaker is in the back underneath the hatch in the cockpit. I had to lean over in there to get something and my head touched it lighting me up good. I found out the third ground wire isn't even there between the shore power inlet and breaker so I became the ground. This is my project this week. The surveyor completely missed it all too. Make sure you have good grounds! At least now I know why my shaft zinc last so long.
rrranch is offline   Reply With Quote
Old 29-01-2012, 13:27   #12
Sponsoring Vendor

Community Sponsor

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 414
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Quote:
Originally Posted by mitiempo View Post
But without a remote monitor you don't know if it has failed or not.
That is very true from a theoretical "liabilility for ABYC" standpoint but look at the practical side of owning a boat. If you are sufficiently paranoid and have money to burn there are hundreds of things on a boat you can monitor. But in the practical world you allocate your budget on itmes with the highest ROI.

To meet the full requirements of the ABYC monitoring specification it would double the cost of the isolator. Especially considering the requirement of a "Remote monitor visible to the boat operator" DUH you don't use shore power when operating a boat.

So if you are going to spend $100 on monitoring something I can think of dozens of things much more important than a galvanic isolator. How about a raw water exit temperature? A second level bilge alarm? A remote indicator on Racor filter pressure?

Considering we have had one failure in over 2,000 isolators in 14 years that calculates to a life expectancy of 1 failure every 28,000 years. I know that figure is meaningless due to insufficient data but you get the message.

Spend your monitoring dollars where they are practical and NEEDED and not to allay the paranoia of ABYC who only require it so they can't be sued if it fails and they didn't require it.
Andina Marie is offline   Reply With Quote
Old 01-02-2012, 07:20   #13
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Quote:
Spend your monitoring dollars where they are practical and NEEDED and not to allay the paranoia of ABYC who only require it so they can't be sued if it fails and they didn't require it.
As a member of two of the committees that write the Standards, this comment (emphasis added) is the author's opinion and, not what the ABYC is about.

Charlie
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 01-02-2012, 07:34   #14
Sponsoring Vendor

Community Sponsor

Join Date: Dec 2003
Location: South Carolina
Boat: Philip Rhodes Custom
Posts: 414
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

Quote:
Originally Posted by CharlieJ View Post
As a member of two of the committees that write the Standards, this comment (emphasis added) is the author's opinion and, not what the ABYC is about.

Charlie
Oh I understand and agree fully, Charlie, and the work ABYC does is very valuable. But it seems to be the "bible" and written to cover all contingencies. I fear the motives are often influenced by the real paranoia of being sued if someone died because ABYC forgot to require a monitor.

From a real life practical approach, I stick by my statement that unless you have unlimited funds you should budget them where they will give the best return on investment.

Many of us rely on a "bible" to guide our life but very few follow it to the letter. I applaud the standards and having a reference is of great value but each individual can decide what to incorporate and what to wish for.

Spending $100 to monitor a component with a MTBF of over 1,000 years compared to things like navigation and safety is sometimes hard to justify.
Andina Marie is offline   Reply With Quote
Old 01-02-2012, 08:00   #15
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,230
Re: Galvanic Isolator or Iso Transformer? To Bond or not?

You should buy and install an IT. An IT is *much* safer because it is in fact a safety device that not only protects the boat but also the people.

A GI is a device that *tries* to protect the boat while *trying* not to lower the safety of people aboard too much.

Also, when an IT fails you loose power. When a GI fails you loose protection.

I don't think it's wise to ridicule safety provisions that are there to guard against possible failures of GI. Especially not when you sell GI's and thus depend on them for your livelihood... although, after selling thousands of them that shouldn't matter much anymore.

ciao!
Nick.
s/v Jedi is offline   Reply With Quote
Reply

Tags
galvanic isolator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heads Up - Victron Isolation Transformer s/v Jedi Electrical: Batteries, Generators & Solar 115 04-06-2023 06:46
Isolation Transformer: Victron vs Mastervolt vs Charles wilsodf Electrical: Batteries, Generators & Solar 87 07-07-2016 12:33
Pacific Islands Visas ? Bond Required ? dennisail Pacific & South China Sea 5 14-01-2012 23:29
Neighbor dumping raw AC into water?...what to do? 2nd Dog Watch Marine Electronics 211 04-01-2012 05:56
Galvanic Corrosion of Chain Galvanizing wsmurdoch Anchoring & Mooring 0 22-08-2011 11:17

Advertise Here


All times are GMT -7. The time now is 11:24.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.