Old 21-11-2020, 16:21   #1
Registered User

Join Date: Mar 2012
Location: Vancouver Island
Boat: 37' Tollycraft Sedan
Posts: 41
Generator AC output wiring

I am installing a used Northern Lights 673 6kw generator. 6kw at 120 volts works out to 50 amps and that's the size of the breaker I have on the generator side of the gen / shore power switch. That means 6 gauge wire and that's what was run to the old 7.5 Onan but it is very stiff. My plan was to put a terminal strip near the generator and tie down the existing wires to one side and continue on with new more flexible cable.

My problem is - and I thought this when I first laid eyes on the generator - the control box is very crowded and there's not much room for 3 #6 wires. Would it be permissible to run two 10/3 cables for the short distance (~6 ft) to the terminal strip? It's about 15 ft the rest of the way to the panel.

#6 is 26251 CMs and 2 x #6 is 20766 or the equivalent of a #7 wire.
Perdiem is offline   Reply With Quote
Old 21-11-2020, 16:47   #2
Registered User

Join Date: Oct 2019
Location: Kennebunk ME
Boat: Owner built 60’ Aluminum Expedition Yacht.
Posts: 1,854
Re: Generator AC output wiring

I’m confused as to the plan but concerned about the condition of the wire.
The condition of the insulation is very important. Some cable is stiffer than others but I’ve seen cable exposure to heat, oil or diesel turn stiff which in some cases means the protection is compromised.
If you can post some photos or a little hand drawn diagram, I’m sure it will help.
Happy trails to you.
Mark and the manatees
Manateeman is offline   Reply With Quote
Old 21-11-2020, 21:41   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Generator AC output wiring

no 10/3 is for 30a. (sorry just noticed you said two of them, but still no)

6awg marine wire is very flexible

make sure you have a breaker on the output of the gen. either internal or directly outside it

and make sure the ground and neutral get connected together inside the gen if it does not come with it pre jumpered.
smac999 is offline   Reply With Quote
Old 22-11-2020, 04:55   #4
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,881
Images: 241
Re: Generator AC output wiring

Quote:
Originally Posted by Perdiem View Post
... Would it be permissible to run two 10/3 cables for the short distance (~6 ft) to the terminal strip?...
... #6 is 26251 CMs and 2 x #6 is 20766 or the equivalent of a #7 wire.
Not under the National Electrical Code (North America).
NEC Section 310.4 permits conductors that are at least 1/0 AWG or larger to be connected in parallel, if these parallel conductors are electrically joined at both ends to form a single conductor, where the circular-mil areas of these conductors are added together, to provide the total cross-sectional area, for the overall size of the parallel conductors (as you’ve calculated).
All of the paralleled conductors, in each phase, neutral or grounded set, must be the same length and be made from the same conductor material. They must be the same circular mil area and have the same type of insulation.
There are exceptions to this (1/0 min), which don’t apply to your application.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 22-11-2020, 11:07   #5
Registered User

Join Date: Apr 2012
Posts: 353
Re: Generator AC output wiring

AWG 6 ANCOR marine wire is not very rigid.

Could be a good opportunity to upgrade your wiring.
My opinion is based on Ancor PN 111910 which is AWG 8 but 6 is very similar.
oleman is offline   Reply With Quote
Old 22-11-2020, 11:56   #6
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Generator AC output wiring

Quote:
Originally Posted by GordMay View Post
Not under the National Electrical Code (North America).
NEC Section 310.4 permits conductors that are at least 1/0 AWG or larger to be connected in parallel, if these parallel conductors are electrically joined at both ends to form a single conductor, where the circular-mil areas of these conductors are added together, to provide the total cross-sectional area, for the overall size of the parallel conductors (as you’ve calculated).
All of the paralleled conductors, in each phase, neutral or grounded set, must be the same length and be made from the same conductor material. They must be the same circular mil area and have the same type of insulation.
There are exceptions to this (1/0 min), which don’t apply to your application.
Is the NEC still published in a little book with yellow covers?
Cadence is offline   Reply With Quote
Old 22-11-2020, 13:07   #7
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,881
Images: 241
Re: Generator AC output wiring

Quote:
Originally Posted by oleman View Post
AWG 6 ANCOR marine wire is not very rigid...
Indeed.


What you want to use is tinned copper boat cable, with type 3 stranding (or class K or M).
I recommend wire and cables by Pacer Group or Ancor Products (but there are others):
Pacerhttps://www.pacergroup.net/
Ancorhttps://www.ancorproducts.com/en
Genuine Deals https://www.genuinedealz.com/ (made by Pacer),

An excellent explanation, all about UL 1426 Boat Cable, BC 5W2.
Boat cable ~ Ocean Navigator
https://www.oceannavigator.com/boat-cable/
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 22-11-2020, 13:44   #8
Registered User

Join Date: Mar 2012
Location: Vancouver Island
Boat: 37' Tollycraft Sedan
Posts: 41
Re: Generator AC output wiring

Thanks guys - I kind of figured as much about using 2 x #10 instead of a #6. Just to be clear, the boat's existing wiring is old nonmarine 6/3 that is fairly stiff due to having fewer strands. The insulation is still good and the copper is still shiny when I remove the insulation (obviously not tinned).

I am using new Ancor 6/3 to go from the terminal strip into the generator and I am still at a loss to see how those three big wires will fit into the control box and tie down on the #10 screws.

I will look at a friend's this week and see how they did it. It is a 5kw so probably #8 wires but it will be similar.
Gregg
Perdiem is offline   Reply With Quote
Reply

Tags
generator, wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator output wiring Question pwilletts Electrical: Batteries, Generators & Solar 2 27-02-2017 12:04
Wiring ammeter to monitor solar output BozSail Electrical: Batteries, Generators & Solar 11 22-07-2014 05:17
wiring solar output sailorboy1 Electrical: Batteries, Generators & Solar 55 01-04-2013 16:24
AC Generator with Low Output Voltage- Engine running slow jonmhammond Electrical: Batteries, Generators & Solar 4 23-02-2012 03:38
Alternator Output Wiring idearat Electrical: Batteries, Generators & Solar 28 28-12-2010 18:48

Advertise Here


All times are GMT -7. The time now is 07:19.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.