Old 17-06-2018, 15:03   #31
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Generator AVR

Let us know what transpires if you will, many of us have Cap regulated generators.
a64pilot is offline   Reply With Quote
Old 18-06-2018, 04:32   #32
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,686
Re: Generator AVR

turns out you can't add an AVR to a brushless alternator, so now I'll research the capacitor
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-06-2018, 06:27   #33
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,686
Re: Generator AVR

So the generator people I’m communicating with say not to change the capacitor value or there will be damage.

For those that have changed the value what/where did you find that this was ok?
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-06-2018, 08:37   #34
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Generator AVR

Quote:
Originally Posted by sailorboy1 View Post
So the generator people I’m communicating with say not to change the capacitor value or there will be damage.

For those that have changed the value what/where did you find that this was ok?
When my unit was shipped with 31.5mf and the service manual calls for 35mf. Service tech also said to stick with 31.5mf. When I measured 26mf on the original after 2 years, the unit was running low no-load voltage, I figured going over by 10-12% wouldn't hurt, and 35mf raised the no-load voltage from 120VAC (with new 31.5mf) to 126VAC (with 35mf).

It appears your unit calls for 31.5mf, and there is only one capacitor as you have a 2-pole alternator (mine is 4-pole, 2 capacitors, 1800rpm). I would not try more then 35mf. It's best if you can measure it, then you'll know. I've gotten junk from Ebay labeled 35mf and measured 50mf.

There are just run capacitors (not start capacitors). Use at least 400V (or 450V) rated, they will last longer.

Measure the physical size of the one you have and match it.
DotDun is offline   Reply With Quote
Old 19-06-2018, 15:30   #35
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,686
Re: Generator AVR

yes mine does call for the 31.5, I wonder what it really is and if they call for something in the US service manual

BTW - I don't think I've ever seen 120V for my generator even when it was new.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-06-2018, 15:34   #36
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Generator AVR

Quote:
Originally Posted by sailorboy1 View Post
yes mine does call for the 31.5, I wonder what it really is and if they call for something in the US service manual

BTW - I don't think I've ever seen 120V for my generator even when it was new.


I’m thinking you may need one of these.....measures capacitance.

https://m.grainger.com/mobile/produc...180619223333:s
Sailmonkey is offline   Reply With Quote
Old 19-06-2018, 15:41   #37
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,686
Re: Generator AVR

Quote:
Originally Posted by Sailmonkey View Post
I’m thinking you may need one of these.....measures capacitance.

https://m.grainger.com/mobile/produc...180619223333:s
I think I have one but since never have needed to measure capacitance I doubt I would have taken note. It measures hertz and I hadn't noted that till I want to do it.

What I really need is my generator to make the correct voltage when loaded more than 50% so I can use the full capacity!!!!!
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-06-2018, 15:43   #38
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: Generator AVR

Quote:
Originally Posted by Sailmonkey View Post
I’m thinking you may need one of these.....measures capacitance.

https://m.grainger.com/mobile/produc...180619223333:s
This is what I have and it works as advertised.....a little cheaper....plus infrared temp


http://www.testequipmentdepot.com/ex...iAAEgIAH_D_BwE
DotDun is offline   Reply With Quote
Old 19-06-2018, 15:48   #39
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Generator AVR

Quote:
Originally Posted by sailorboy1 View Post
I think I have one but since never have needed to measure capacitance I doubt I would have taken note. It measures hertz and I hadn't noted that till I want to do it.



What I really need is my generator to make the correct voltage when loaded more than 50% so I can use the full capacity!!!!!


I’d then measure the cap, send a photo of the less than spec value to the distributor.......then replace the cap with a correct value cap.
Sailmonkey is offline   Reply With Quote
Old 19-06-2018, 17:01   #40
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,686
Re: Generator AVR

So, how many people reading this thread have chnged their capacity to one with a higher value, what was the value, how long have you ran your generator with the higher cap.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 19-06-2018, 17:28   #41
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Generator AVR

I’ve replaced a lot of caps that said they were value X and when measured were value X-Y. Capacitors, especially cheap ones mounted sideways in a hot area, have a finite lifespan. It may be that your cap value is correct, just that the cap has been degraded.

I’ve replaced one cap with a larger value (5uf) to increase voltage by a few volts. That particular generator is 10 years older but lives an easy life of less than 5 hours per year use.
Sailmonkey is offline   Reply With Quote
Old 19-06-2018, 17:33   #42
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator AVR

Well, you know I have.
Actually I’m at spec now. When I looked it was a low, I assumed during manufacture they would change uf value to meet spec, I guess mine was a little high.
I just looked in spares, what was in there was a 35 uf plus or minus 5% it says on the cap.
What I’m running is a 40 uf, which I think is spec.
I didn’t know a Fluke 115 would measure a capacitor, anyone know how to do it, I’m looking at mine and it’s not apparent.
a64pilot is offline   Reply With Quote
Old 19-06-2018, 17:38   #43
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Generator AVR

OK I learned something new.
The old cap which says 35 uf on it measured 30.7 uf. Likely why the generator doesn’t work with it, ya think?
The new 40 I have in spares measures 40.3.
a64pilot is offline   Reply With Quote
Old 19-06-2018, 17:39   #44
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Generator AVR

Quote:
Originally Posted by a64pilot View Post
OK I learned something new.
The old cap which says 35 uf on it measured 30.7 uf. Likely why the generator doesn’t work with it, ya think?
The new 40 I have in spares measures 40.3.


Hey, lookee there!
Sailmonkey is offline   Reply With Quote
Old 19-06-2018, 18:59   #45
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,686
Re: Generator AVR

Anyone have a good source for these capacitors? Ordering anything for me is a PITA and I would prefer to order ahead and not need a $20 part than have to sit around waiting on it.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Portable Inverter Generator or Reg. Generator? Hatch Liveaboard's Forum 54 15-06-2017 23:05
Generator vs Inverter Generator (Genset) Jon4399 Electrical: Batteries, Generators & Solar 30 11-01-2011 09:13
Portable Generator vs Solar Panels or Wind Generator Sweet As Electrical: Batteries, Generators & Solar 120 16-09-2010 18:27
Any way to convert a DC Generator to an AC Generator? Latitude9.5 Engines and Propulsion Systems 13 06-04-2007 11:06

Advertise Here


All times are GMT -7. The time now is 08:42.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.