Generator doesn't charge batteries

I have a 4-100 AH AGM house bank that is charged by the engine, 640 watts of solar, and shore power via the converter (charger). The 6kw genset runs well but is rarely used. On a 66 day trip this summer around the Great Lakes, I fired up the genset and noticed that it was not charging my batteries. It ran everything else as if I was on shore power. If I switch from shore power to genset, I lose the charging of the batteries. The converter breaker doesn't trip so all connections are the same - just the source is different. What could be causing this?

Any ideas?
__________________
- Mike
MGRodems is offline   Reply With Quote
Old 20-09-2021, 16:31   #2
Registered User
 
cr180's Avatar

Join Date: May 2015
Location: Chattanooga, Tn./New Smyrna Beach, Florida
Boat: 1980 Gulfstar 47 Sailmaster
Posts: 330
Re: Generator doesn't charge batteries

Interesting problem. Theoretically, the converter charger should function as long as the AC input voltage is above minimum input voltage prescribed by the vendor. Have you checked generator output voltage? I ask because mine was low and had to adjust generator speed (rpms) up to correct.
cr180 is offline   Reply With Quote
Old 20-09-2021, 21:31   #3
Registered User

Join Date: May 2010
Location: NW Washington State
Boat: Yankee Dolphin 24'
Posts: 244
Re: Generator doesn't charge batteries

One would think that 6KW would be enough to run any charger, however some chargers won't run if they don't think they can get enough current. Also, do the frequencies match?
tenchiki is offline   Reply With Quote
Old 21-09-2021, 03:43   #4
Registered User
 
MGRodems's Avatar

Join Date: Jan 2017
Location: Buffalo, NY & Chesapeake Bay
Boat: Irwin 43 MkIII
Posts: 77
Re: Generator doesn't charge batteries

Both the genset and the converter are original equipment (1988), but appear to function properly otherwise. I will check the voltage output on the genset next.
__________________
- Mike
MGRodems is offline   Reply With Quote
Old 21-09-2021, 08:38   #5
Registered User

Join Date: Sep 2015
Location: East Coast Florida
Boat: Chris Craft 38 Commander 1965
Posts: 482
Re: Generator doesn't charge batteries

Even without the onboard battery charger you should get some charging from the alternator on the generator if it has one - mine does.
If the genset is running and all other AC voltage items on the boat are running except the battery charger then I would expect it to be a break in the wiring or open circuit breaker. Also, on my installation there is a high amp inline DC breaker on the bulkhead near the batteries that gets tripped sometimes if the battery is way down and tries to charge (i think that is why). Anyway resetting it allows normal charging.

(1.) Check AC breaker to the Charger (does it turn on) and if not (2.) does it have power to it, (3.) check any DC breaker in the charging line to the battery, and (4.) see if there is an alternator on your genset.

If there is a break in either the AC line to the Charger or the DC line to the battery it could likely be possibly a wire crimp that has come loose or failed.
Squanderbucks is offline   Reply With Quote
Old 21-09-2021, 08:45   #6
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,740
Re: Generator doesn't charge batteries

Quote:
Originally Posted by Squanderbucks View Post
......
............................................

If the genset is running and all other AC voltage items on the boat are running except the battery charger then I would expect it to be a break in the wiring or open circuit breaker........................
.........................................

Yup, can't think of anything else.
Maybe it never did run the "battery charger" part of the system.
Or something that previously worked stopped doing so.

Who knows?
ONLY the skipper, at this point. Need to do some wire tracing, for starters. Or some DVM work. Asking us can't help, not the same as being there, is it?
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 21-09-2021, 09:07   #7
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Generator doesn't charge batteries

If it worked in the past and isn't now with the gen. running everything else, it's probably time for wire tracing. Remember to trace both not just the "hot". check the switch or relay whichever is applicable for burnt contacts.
Cadence is offline   Reply With Quote
Old 21-09-2021, 12:21   #8
Marine Service Provider

Join Date: May 2014
Location: Yucatan, Mexico
Boat: Molenmaker Dutch steel gaff-rigged ketch
Posts: 177
Images: 2
Re: Generator doesn't charge batteries

The generator's alternator should only be connected to it's cranking battery not house banks.

Quote:
Originally Posted by Squanderbucks View Post
Even without the onboard battery charger
you should get some charging from the alternator on the generator if it has one - mine does.
If the genset is running and all other AC voltage items on the boat are running except the battery charger then I would expect it to be a break in the wiring or open circuit breaker. Also, on my installation there is a high amp inline DC breaker on the bulkhead near the batteries that gets tripped sometimes if the battery is way down and tries to charge (i think that is why). Anyway resetting it allows normal charging.

(1.) Check AC breaker to the Charger (does it turn on) and if not (2.) does it have power to it, (3.) check any DC breaker in the charging line to the battery, and (4.) see if there is an alternator on your genset.

If there is a break in either the AC line to the Charger or the DC line to the battery it could likely be possibly a wire crimp that has come loose or failed.
__________________
Captain Ray Thackeray
International Rescue Group, disaster relief and humanitarian aid by sea.
Capt. Ray is offline   Reply With Quote
Old 21-09-2021, 13:50   #9
Registered User

Join Date: Feb 2015
Boat: Land bound, previously Morgan 462
Posts: 1,993
Re: Generator doesn't charge batteries

Quote:
Originally Posted by Capt. Ray View Post
The generator's alternator should only be connected to it's cranking battery not house banks.
Yes, your generator probably has a separate winding and rectifiers to produce about 14V at low current for maintaining the start battery. It’s a completely separate system from the main AC output.
Since know your charger works when you have the switch in SHORE position and connected to shore power, and all your other AC gear works when you run the generator, it seems the fault must not be in the switch or the wiring anywhere. Seems that the converter is connected to generator but is not getting the right AC voltage or frequency from the generator.
At least check the AC voltage of the generator with charger switched off and on and especially when battery charge state is low ( high current demand). You should have a permanently installed AC voltmeter but use a DVM also.
Many AC devices are tolerant of variations in frequency and voltage. Heaters, incandescent bulbs, stoves, toasters. What do you run that does work OK on the generator power? Did this problem only happen on your trip when the batteries were already discharged or does it happen even when batteries are fairly well charged already?
__________________
No shirt, no shoes, no problem!
waterman46 is offline   Reply With Quote
Old 22-09-2021, 00:16   #10
Registered User

Join Date: Aug 2013
Location: Guernsey, Channel Islands
Boat: Fisher 31, 9.4 M
Posts: 85
Re: Generator doesn't charge batteries

Quote:
Originally Posted by tenchiki View Post
One would think that 6KW would be enough to run any charger, however some chargers won't run if they don't think they can get enough current. Also, do the frequencies match?
Battery chargers don't think, they sense a low input voltage if they draw more current than the generator can supply.

What frequency do you expect from a DC generator?

The OP does not mention a charger, maybe he expects the 12 volt output from the generator to charge his batteries, but he needs a higher voltage from the battery charger.
AlanR is offline   Reply With Quote
Old 22-09-2021, 01:13   #11
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,734
Re: Generator doesn't charge batteries

Quote:
Originally Posted by Squanderbucks View Post
Even without the onboard battery charger you should get some charging from the alternator on the generator if it has one - mine does. .
It would only be charging the gen battery. Or the battery that starts the gen. Which is likly Not the house.
smac999 is offline   Reply With Quote
Old 22-09-2021, 06:45   #12
Registered User

Join Date: Apr 2018
Posts: 7
Re: Generator doesn't charge batteries

A few months ago I posted about the same problem on my Albin 28. The house and engine batteries charge fine on shore power but they do not charge if I am on generator power. However, I found that if I run my air conditioner (AC) while on generator power the charger will then charge the batteries normally. Sometimes I can stop the AC after about 10 minutes on the generator and the charger will continue charging other times it stops as soon as the AC turns off. I assume that the modified sine-wave from my small generator (NextGen 3.5 kw) is not compatible with the original onboard charger (ProTech 1230i) but is changed or modified by the AC running. My portable 15 amp Victron Blue Smart Charger works fine if I plug it into an outlet while the generator is running. I hope you can find an answer to your problem and post it.
hatchetjoe is offline   Reply With Quote
Old 22-09-2021, 07:09   #13
Registered User
 
MGRodems's Avatar

Join Date: Jan 2017
Location: Buffalo, NY & Chesapeake Bay
Boat: Irwin 43 MkIII
Posts: 77
Re: Generator doesn't charge batteries

Thanks for all of the great responses. I don't think it is the switch or wiring since I can switch the sources from shorepower to genset and back and get the charger to function properly when in the shore power position. I will check the voltage and play with the loads to see if I find anything out. I am currently not aboard or in the water since I just returned from a 66 day Great Lakes summer trip and had to haul out upon returning (no slip available), so it may take a while to figure it out.

Again, thanks for all of the responses.
__________________
- Mike
MGRodems is offline   Reply With Quote
Old 22-09-2021, 07:21   #14
Registered User
 
Captain Bill's Avatar

Join Date: Apr 2008
Location: Punta Gorda, Fl
Boat: Endeavourcat Sailcat 44
Posts: 3,202
Re: Generator doesn't charge batteries

Some battery chargers will not work if the power is "dirty" or the current is too far out of phase with the voltage. Depending on the type of voltage control on your genset this could be caused by a capacitor going bad. Resistance loads are usually not sensitive to this but electronics are. Most modern battery chargers are computer controlled and do not like power that doesn't meet their input specs and will not turn on. You didn't specify the brand of genset or the method of voltage regulation it uses, so it's hard to tell if this applies to your setup or not.
Captain Bill is offline   Reply With Quote
Old 22-09-2021, 08:37   #15
Registered User

Join Date: Nov 2012
Location: Steinhatchee, FL
Posts: 402
Re: Generator doesn't charge batteries

Quote:
Originally Posted by Captain Bill View Post
Some battery chargers will not work if the power is "dirty" or the current is too far out of phase with the voltage. Depending on the type of voltage control on your genset this could be caused by a capacitor going bad. Resistance loads are usually not sensitive to this but electronics are. Most modern battery chargers are computer controlled and do not like power that doesn't meet their input specs and will not turn on. You didn't specify the brand of genset or the method of voltage regulation it uses, so it's hard to tell if this applies to your setup or not.
I've seen generators with "dirty" power get "cleaner" when there is a little more load on them. Put a little more load on the generator and see if the battery charge starts working.
Be Free is offline   Reply With Quote
Reply

Tags
batteries, generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
400: Does My Generator Charge Stating Batteries? AZ_Zoner Lagoon Catamarans 17 30-07-2016 20:06
Charles marine battery charger doesn't work with inverter generator Joe from ny Electrical: Batteries, Generators & Solar 12 24-07-2016 18:50
air conditioning / ac on batteries, generator to maintain charge xluke Electrical: Batteries, Generators & Solar 17 17-07-2012 06:11
iPhone doesn't charge from boat battery rhr1956 Electrical: Batteries, Generators & Solar 7 01-03-2012 12:19
Use Portable Generator to Charge Batteries ? trimming out Electrical: Batteries, Generators & Solar 6 23-07-2011 08:38

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 22:21.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.