Generator Field Capacitor

We have a 8.5KW Paguro Generator that we’ve been fighting to keep running since it was new. It currently has 200 hours on it and I have to replace the 35uf field capacitor about every 10 hours of run time. So basically every 6 months or so.

I’m wondering if there are high quality brands of run capacitors we should be buying to help with this issue. Are there good brands we should focus on?

Also, the capacitor is mounted inside the very tight sound enclosure. I’m wondering if I should extend the two wires and try mounting the capacitor outside the enclosure.

Does anyone have advice around this?
crayiii is offline   Reply With Quote
Old 07-08-2022, 20:10   #2
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Generator Field Capacitor

Your best bet is to extend and mount outside. Heat kills caps.
Sailmonkey is offline   Reply With Quote
Old 09-08-2022, 06:18   #3
Registered User
 
phorvati's Avatar

Join Date: Jan 2006
Location: Rhode Island
Boat: Tayana FD-12
Posts: 1,200
Images: 6
Re: Generator Field Capacitor

Do you have cap specs? Not paguro part number, but rather capacitor manufacturer part number....rybicon,nichicon are the two that make shitty electrolytics that tend to fail early.
phorvati is offline   Reply With Quote
Old 09-08-2022, 06:32   #4
Registered User

Join Date: Apr 2019
Posts: 614
Re: Generator Field Capacitor

Quote:
Originally Posted by phorvati View Post
Do you have cap specs? Not paguro part number, but rather capacitor manufacturer part number....rybicon,nichicon are the two that make shitty electrolytics that tend to fail early.
It’s a Paguro generator. They just say 30uf 440v. I have been burning up the Titan Pro caps pretty quickly. I just extended the wires by 6 feet and mounted it outside the enclosure into an air conditioned area. I’m hoping the extending wires don’t cause an issue but after a few hours it’s still running okay.
crayiii is offline   Reply With Quote
Old 09-08-2022, 06:36   #5
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Generator Field Capacitor

Sounds like too high a ripple current issue.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 09-08-2022, 15:03   #6
Registered User

Join Date: Apr 2019
Posts: 614
Re: Generator Field Capacitor

Quote:
Originally Posted by goboatingnow View Post
Sounds like too high a ripple current issue.
I’ll be honest, I’m not sure what that means.

Here is how the unit is operated (it has 200 hours on it).

It’s started with zero load and then after a minute or so, load is added. We can only run the unit to 60% load max but it’s usually around 50%.

It runs at 3600 RPM, 60-61 Hz, and voltage is between 120 and 121.

When we shut it down, we remove all loads and the meter reads 0%, then we shut it down after about a minute running with no load.
crayiii is offline   Reply With Quote
Old 09-08-2022, 15:10   #7
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Generator Field Capacitor

Quote:
Originally Posted by crayiii View Post
I’ll be honest, I’m not sure what that means.

Here is how the unit is operated (it has 200 hours on it).

It’s started with zero load and then after a minute or so, load is added. We can only run the unit to 60% load max but it’s usually around 50%.

It runs at 3600 RPM, 60-61 Hz, and voltage is between 120 and 121.

When we shut it down, we remove all loads and the meter reads 0%, then we shut it down after about a minute running with no load.
if there is high frequency current spikes , you can find that the ESR of the caps is too high ( Equivalent series resistance) equally if there is a DC component that can affect things

this causes caps to heat up , and fail even though their "label" ratings suggest they are within spec

you might consder a high quality one like https://connect.kemet.com:7667/gatew...274AC35400AA0J

This is a metallised film type and way better then cheaper electrolytic types often used , far more tolerant of excess circumstances
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 09-08-2022, 15:21   #8
Registered User

Join Date: Apr 2019
Posts: 614
Re: Generator Field Capacitor

Quote:
Originally Posted by goboatingnow View Post
if there is high frequency current spikes , you can find that the ESR of the caps is too high ( Equivalent series resistance) equally if there is a DC component that can affect things

this causes caps to heat up , and fail even though their "label" ratings suggest they are within spec
The loads are as follows:

4 Dometic air conditioners
1 Quick water heater
2 Cristec battery chargers
1 Splendide clothes washer (rarely run)

Plug in AC consumers are run through the inverter.

One thing that I just thought of is that even though we rarely run the washer/dryer, it does power up when the generator is started which means it is on (just in standby) when we shut the generator off.

Thinking about this, does that mean that field capacitor is trying to maintain 120 volts as the generator shuts down because of the tiny amount of current the washer is using? Maybe I should **** the breaker off for the washer.
crayiii is offline   Reply With Quote
Old 09-08-2022, 15:22   #9
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,614
Re: Generator Field Capacitor

Quote:
Originally Posted by crayiii View Post
It’s a Paguro generator. They just say 30uf 440v. I have been burning up the Titan Pro caps pretty quickly. I just extended the wires by 6 feet and mounted it outside the enclosure into an air conditioned area. I’m hoping the extending wires don’t cause an issue but after a few hours it’s still running okay.


This is probably un needed advice because you’ve changed a few but that capacitor is live and remains so for a while after shutdown so the remote mounting of it should be in an insulated box. You seem to be using a very good brand of capacitor already so I can’t offer a better recommendation. I’m interested to see how this issue resolves.
Pete.
skipperpete is offline   Reply With Quote
Old 09-08-2022, 15:27   #10
Registered User

Join Date: Apr 2019
Posts: 614
Re: Generator Field Capacitor

Quote:
Originally Posted by skipperpete View Post
This is probably un needed advice because you’ve changed a few but that capacitor is live and remains so for a while after shutdown so the remote mounting of it should be in an insulated box. You seem to be using a very good brand of capacitor already so I can’t offer a better recommendation. I’m interested to see how this issue resolves.
Pete.
Agreed! I always short them out with an insulated tool before handling. At the moment it is just zip tied to a bulkhead way out of the way but I’ll do a permanent safe mount if this corrects the issue.

One thing that I just found out is the Titan Pro caps are made in China and the Titan HD are made in the US. I don’t know if that has anything to do with quality or not but there is definitely a difference in price.
crayiii is offline   Reply With Quote
Old 09-08-2022, 15:30   #11
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Generator Field Capacitor

the capacitor on a generator is there to dampen fast transients and help regulate the output , if you have a deficient generator or rapidly dynamic loads, you can exceed the capacitors ratings

titan pro is an established brand, I think its now made in china, and I believe its a aluminium electrolytic type, personally as I mentioned Id use metallized film types. electrolytics are much more sensitive to heat ( internal or ambient ) so if there is significant heat in their original mounting space, moving them will help
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 09-08-2022, 16:08   #12
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,614
Re: Generator Field Capacitor

Quote:
Originally Posted by crayiii View Post
Agreed! I always short them out with an insulated tool before handling. At the moment it is just zip tied to a bulkhead way out of the way but I’ll do a permanent safe mount if this corrects the issue.



One thing that I just found out is the Titan Pro caps are made in China and the Titan HD are made in the US. I don’t know if that has anything to do with quality or not but there is definitely a difference in price.


Does your genset have twin capacitors? I just took a look at the Volpi/paguro in google images and the 8.5’s have 2 side by side on the control box. I’ve had a bit to do with Volpi gensets but not for AC problems, just engine issues. These engines need to be maintained carefully, clean fuel, regular oil changes and frequent inspection of the cooling water circuits. Some folks just never open up the sound shell until something goes wrong ( raw water leaks , hose and harness chafing,loose belts, mixer elbow, exhaust connection etc) and they’re very hard to work on especially after a raw water leak in that tight sealed sound shell.
skipperpete is offline   Reply With Quote
Old 09-08-2022, 21:47   #13
Registered User

Join Date: Apr 2019
Posts: 614
Re: Generator Field Capacitor

Quote:
Originally Posted by skipperpete View Post
Does your genset have twin capacitors? I just took a look at the Volpi/paguro in google images and the 8.5’s have 2 side by side on the control box. I’ve had a bit to do with Volpi gensets but not for AC problems, just engine issues. These engines need to be maintained carefully, clean fuel, regular oil changes and frequent inspection of the cooling water circuits. Some folks just never open up the sound shell until something goes wrong ( raw water leaks , hose and harness chafing,loose belts, mixer elbow, exhaust connection etc) and they’re very hard to work on especially after a raw water leak in that tight sealed sound shell.
It’s a 9000 and has a single cap. I’ve though about replacing the 30uf cap with three 10uf caps in parallel to see if that helps.

This is the second engine as the first was replaced under warranty after 221 hours. We maintain it the best we can with frequent inspections and annual oil changes (we do maybe 100 hours a year).

We’re on our third temp sensor and second water pump already.
crayiii is offline   Reply With Quote
Old 09-08-2022, 22:25   #14
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,614
Re: Generator Field Capacitor

Well you’re not alone with the issues that the little LDW experiences. I’m yet to see one of the common rail versions but I believe kohler has em in their newer gensets
The basic engine is solid, pistons,
block , crank all seem to last but Lombardini dropped the ball with the fuel system, hard to service and adjust and depressingly difficult finding a tech who has the tools and knowhow to get smooth power output.
skipperpete is offline   Reply With Quote
Old 10-08-2022, 06:55   #15
Registered User

Join Date: Apr 2019
Posts: 614
Re: Generator Field Capacitor

Quote:
Originally Posted by skipperpete View Post
Well you’re not alone with the issues that the little LDW experiences. I’m yet to see one of the common rail versions but I believe kohler has em in their newer gensets
The basic engine is solid, pistons,
block , crank all seem to last but Lombardini dropped the ball with the fuel system, hard to service and adjust and depressingly difficult finding a tech who has the tools and knowhow to get smooth power output.
Initially, we had a heck of a time getting a steady RPM. It surged like heck which, obviously, it’s really bad for maintaining 60 hz.

We ended up installing a Facet Dura-Lift fuel pump that is way way overkill but it solved the issue.
crayiii is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacing generator run capacitor with aircons cap crayiii Electrical: Batteries, Generators & Solar 6 12-09-2019 08:07
Burned up capacitor on generator crayiii Electrical: Batteries, Generators & Solar 20 17-07-2019 12:17
Generator Capacitor sailorboy1 Electrical: Batteries, Generators & Solar 34 14-08-2018 05:00
What Does the Capacitor in a Generator Do? scoobert Electrical: Batteries, Generators & Solar 16 28-07-2013 03:21
Split Capacitor on Windlass Motor Terminals - Why? Zul Anchoring & Mooring 2 16-11-2009 08:14

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 14:45.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.