Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by Rex Delay View Post
Is it acceptable to solder the ends of the multi strand wire rather than use captive rings? It seems that the rings are the main problem I am having.
No.

Have you tried a different brand of GFCI receptacle?

As someone else mentioned, one GFCI receptacle can protect an entire circuit if you install it as the first in a string of receptacles.

As far as the box being too small, I hesitate a bit to suggest this because you have to understand what you're doing, but depending on how the box was installed, you may be able to replace it with a deeper box. I had to do this to install one of the new receptacles with built in USB charging jacks. Another example of a fifteen minute job that takes two hours.


BTW: The box extenders that go on the front of a box are meant for use when the box is mounted too far in from the surface (drywall, paneling, etc. They may make the box deeper but the will stick out past the surface and look pretty silly. Any home center or electrical supply store will have boxes in several different depths. The extra depth is in the back.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 13-03-2016, 17:32   #17
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,206
Re: GFCI - Ground Fault Breaker

One thing I may have missed? Insure you have a good ground or a GFI is useless.
Cadence is offline   Reply With Quote
Old 13-03-2016, 18:46   #18
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by Cadence View Post
One thing I may have missed? Insure you have a good ground or a GFI is useless.
A GFCI will work without a ground. They operate on the difference between hot and neutral. GFCI's are allowed instead of a ground on a 2 wire system.
mitiempo is offline   Reply With Quote
Old 14-03-2016, 07:57   #19
Registered User

Join Date: Aug 2015
Location: Ontario Canada
Boat: Corbin 39
Posts: 67
Re: GFCI - Ground Fault Breaker

If you can find conveniant location to install first GFI receptical all downstream recepticals will be protected by first gfi receptical.
dmalcol1 is offline   Reply With Quote
Old 14-03-2016, 09:40   #20
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,206
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by mitiempo View Post
A GFCI will work without a ground. They operate on the difference between hot and neutral. GFCI's are allowed instead of a ground on a 2 wire system.
Interesting thanks. Probably well worth while on a boat since supplying a good ground can be suspect. What can you tell me about AFCI/GFCI ?
Cadence is offline   Reply With Quote
Old 14-03-2016, 13:30   #21
Registered User

Join Date: Apr 2013
Location: So Cal
Boat: Catalina 387
Posts: 967
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by Cadence View Post
Interesting thanks. Probably well worth while on a boat since supplying a good ground can be suspect. What can you tell me about AFCI/GFCI ?
It's one of the great reasons to have a GFCI. Any current goes 'somewhere else' it pops. Since that somewhere else may be through you, that's a good thing. Only way to upgrade 2-wire systems without pulling a real ground wire. It's fine to stick a GFCI as the first outlet and only run hot/neutral down the line (U.S. 110v)

Almost every circuit in my house is on a GFCI - when the kids were little I felt it added lots of safety. Every outlet is behind one too. (yup. Both circuits... )

AFCI is an arc detector. Since arcs can light fires an AFCI prevents that.
jeepbluetj is offline   Reply With Quote
Old 16-03-2016, 15:13   #22
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by Rex Delay View Post
I have been ordered by my insurance company to install GFCI in galley and head. Just tried in the galley and failed. There is just not enough room in the electrical box for the outlet and wires. Wires are supposed to be attached to captive rings on the plug but this cannot work due to space limitations. The ring connectors stick out the side and break off when trying to bend flat to go in the box. One option is to solder the ends of the multi strand wire and install as per house wiring. Is this acceptable practice?

Another option would to put a master Ground Fault breaker on the 110 volt system but how and where?
First, please be advised that a GFCI is not a breaker (current limiting device). It opens the circuit on a ground fault. It will not open the circuit on excess current from line to neutral. (The later is what a fuse or breaker is for.)

Despite some comments, installing an ELCI does not preclude the need for GFCI receptacles as specified. The ELCI give whole boat protection, but for a higher ground fault current than a GFCI.

Soldering stranded wires and inserting into a "gripping" terminal of a GFCI is our standard practice. If it is just a screw terminal, then a ring or flanged spade should be used to be compliant. If there is no room for the terminals, perhaps you need a deeper box? If the box is metal, this is a great opportunity to change it out for a water-tight plastic box.
ramblinrod is offline   Reply With Quote
Old 16-03-2016, 15:32   #23
Registered User

Join Date: Oct 2006
Location: Nanaimo, BC
Boat: Sceptre 36
Posts: 454
Re: GFCI - Ground Fault Breaker

I finally finished it. Used a Leviton slimline GFI as it is the thinnest I could find. Had to remove all excess wiring from the box as there was no room and then soldered the wire ends with just less than 2" sticking out of the box and then crammed it all in and it just fit. Insurance company now happy. Thank you all.
Rex Delay is offline   Reply With Quote
Old 16-03-2016, 15:55   #24
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,206
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by jeepbluetj View Post
It's one of the great reasons to have a GFCI. Any current goes 'somewhere else' it pops. Since that somewhere else may be through you, that's a good thing. Only way to upgrade 2-wire systems without pulling a real ground wire. It's fine to stick a GFCI as the first outlet and only run hot/neutral down the line (U.S. 110v)

Almost every circuit in my house is on a GFCI - when the kids were little I felt it added lots of safety. Every outlet is behind one too. (yup. Both circuits... )

AFCI is an arc detector. Since arcs can light fires an AFCI prevents that.
Guess I'm lucky. I just told the kids not to stick things in the plugs.

Must have worked. The eldest mad 56.
Cadence is offline   Reply With Quote
Old 16-03-2016, 16:09   #25
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by Cadence View Post
One thing I may have missed? Insure you have a good ground or a GFI is useless.
Incorrect, a GFCI works without reference to ground at all. They are equipped with a current sensor for both line and neutral. If there is a difference beyond the setpoint, the GFCI trips, disconnecting the receptacle from power.
ramblinrod is offline   Reply With Quote
Old 17-03-2016, 08:14   #26
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,206
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by ramblinrod View Post
Incorrect, a GFCI works without reference to ground at all. They are equipped with a current sensor for both line and neutral. If there is a difference beyond the setpoint, the GFCI trips, disconnecting the receptacle from power.
Someone already mentioned the GFCI and no ground required. Interesting since sometimes a ground is questionable either the vessel's or the marina's.
Cadence is offline   Reply With Quote
Old 17-03-2016, 13:45   #27
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: GFCI - Ground Fault Breaker

Quote:
Originally Posted by ramblinrod View Post
First, please be advised that a GFCI is not a breaker (current limiting device). It opens the circuit on a ground fault. It will not open the circuit on excess current from line to neutral. (The later is what a fuse or breaker is for.)

Despite some comments, installing an ELCI does not preclude the need for GFCI receptacles as specified. The ELCI give whole boat protection, but for a higher ground fault current than a GFCI.

Soldering stranded wires and inserting into a "gripping" terminal of a GFCI is our standard practice. If it is just a screw terminal, then a ring or flanged spade should be used to be compliant. If there is no room for the terminals, perhaps you need a deeper box? If the box is metal, this is a great opportunity to change it out for a water-tight plastic box.
Rod,
They do make some combination units. The most common in the marine market is the one made by Carling. The GFCI unit is added onto the breaker and trips the breaker when the leakage is detected, but it will also trip on over current. It's basically an ELCI turned down to the GFCI ma level. They are much more expensive then GFCI outlet thou and take an extra breaker space.
http://www.carlingtech.com/sites/def...CI_Catalog.pdf

The easiest and least expensive is to add a GFCI outlet upstream of the other outlets. If all else fails thou you could try one of the Inline GFCI modules I have seen them on a few production boats but they are expensive. http://www.gfcistore.com/30-amp-permanent-gfcis.html
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shore Power Problem - Ground Fault or Other Issue ? SailFastTri Electrical: Batteries, Generators & Solar 29 19-03-2017 20:51
Prosine 2 Ground Fault so34chi Electrical: Batteries, Generators & Solar 0 26-02-2015 19:40
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17
Ground fault protector problems tsl Electrical: Batteries, Generators & Solar 6 12-04-2013 15:51
source for RCBO? aka GFCI breaker Ryan Electrical: Batteries, Generators & Solar 1 11-08-2005 08:55

Advertise Here


All times are GMT -7. The time now is 21:46.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.