Old 06-07-2018, 18:52   #1
Registered User

Join Date: Jun 2016
Location: Phoenix/Puerto Penasco
Boat: Between boats--currently shopping
Posts: 107
Help! Generator and Shore power AC breakers tripping under load

Hi All,

Totally bumfuzzled here in Fajardo. I am having an AC system problem. Onboard I have an northern lights Jennie and a dual 30/120 shore power setup.

When I hook up the shore power, the shore power available light on the AC panel lights up indicating power avail. However, as soon as I try any load, the breaker at the power cord (EFCI) trips.

Ditto with the generator. As soon as any load is placed on the circuit the EFCI for the generator pops.

To me, that means that that the problem must be downstream of those 2 breakers since the same problem happens with different sources.

Hours of research online seems to suggest this might be a ground/neutral fault in the panel but I have no idea how to find and troubleshoot.

Can someone please point me in a troubleshooting direction??

THANKS!
AZ Parothead is offline   Reply With Quote
Old 06-07-2018, 19:32   #2
Registered User

Join Date: Dec 2015
Location: Nanaimo BC
Boat: modified Spray 56' oa
Posts: 378
Re: Help! Generator and Shore power AC breakers tripping under load

Is this an existing system that has recently failed or new wiring?
topmast is offline   Reply With Quote
Old 06-07-2018, 19:47   #3
Registered User
 
Dsanduril's Avatar

Join Date: Aug 2011
Location: Petersburg, AK
Boat: Outremer 50S
Posts: 4,229
Re: Help! Generator and Shore power AC breakers tripping under load

Open (turn off) every breaker on the AC panel. Pull the plug on every AC connected device. Turn on the AC (either Gen or shore). Sounds like at this point you get "AC Available" light? Close one breaker. EFCI trip? If not, try to run whatever is connected to that breaker. If it doesn't trip re-open breaker and wash/rinse/repeat with each breaker one at a time.

If you've already gone that far and have trips with more than one load then it has to be in the common neutral wiring. EFCI is expecting the same current in the hot and neutral legs. If it doesn't see it then some current must be going elsewhere. Working from the point where the shore power and gen power cables meet, check the neutral and all connections from there to the AC panel. Likely one is somehow broken/damaged.
Dsanduril is offline   Reply With Quote
Old 07-07-2018, 06:45   #4
Registered User

Join Date: Jun 2016
Location: Phoenix/Puerto Penasco
Boat: Between boats--currently shopping
Posts: 107
Re: Help! Generator and Shore power AC breakers tripping under load

Quote:
Originally Posted by topmast View Post
Is this an existing system that has recently failed or new wiring?


Existing. No changes to wiring.
AZ Parothead is offline   Reply With Quote
Old 07-07-2018, 06:48   #5
Registered User

Join Date: Jun 2016
Location: Phoenix/Puerto Penasco
Boat: Between boats--currently shopping
Posts: 107
Re: Help! Generator and Shore power AC breakers tripping under load

Quote:
Originally Posted by Dsanduril View Post
Open (turn off) every breaker on the AC panel. Pull the plug on every AC connected device. Turn on the AC (either Gen or shore). Sounds like at this point you get "AC Available" light? Close one breaker. EFCI trip? If not, try to run whatever is connected to that breaker. If it doesn't trip re-open breaker and wash/rinse/repeat with each breaker one at a time.

If you've already gone that far and have trips with more than one load then it has to be in the common neutral wiring. EFCI is expecting the same current in the hot and neutral legs. If it doesn't see it then some current must be going elsewhere. Working from the point where the shore power and gen power cables meet, check the neutral and all connections from there to the AC panel. Likely one is somehow broken/damaged.


Thanks! I’ve already tried your first suggestion so I’m on to the second. Will report back.
AZ Parothead is offline   Reply With Quote
Old 07-07-2018, 09:04   #6
Registered User

Join Date: May 2015
Location: Baltimore, Maryland USA
Boat: Herreshoff Cat Ketch 38, Halvorsen 32 Gourmet Cruiser
Posts: 16
Re: Help! Generator and Shore power AC breakers tripping under load

Um... have tried replacing the gfci breaker? They do go bad. Think of them as the old distributor caps found on older British sports cars. Don't get them wet; damp doesn't work too well either.
I get many calls in a week of customers complaining of the gfci/arc fault combo breakers tripping with little to no provocation. I generally suggest replacing with an arc fault only breaker and a new gfci receptacle. Don't know the code requirements in your jurisdiction, but eliminating as many gfci trip points is a good place to start. Arc fault good! Ground fault bad.
GuerrillaCamper is offline   Reply With Quote
Old 07-07-2018, 15:48   #7
Registered User

Join Date: Dec 2012
Location: Mannum, Australia
Boat: Houseboat, 60ft.
Posts: 290
Re: Help! Generator and Shore power AC breakers tripping under load

I had a very similar problem on my houseboat.
The combo inverter/charger sees both shore & Genny power as AC power so when it was installed initially both were fed through contactors that have a lockout bit mounted between them so only one or the other can be engaged at any time.
One contactor failed & wouldn't drop out due to a loose/dirty wire connection.
More over heating caused further damage and on it goes.
Good luck chasing it!
BruceS is offline   Reply With Quote
Reply

Tags
generator, loa, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
PERKINS 4108 LOW RPM UNDER LOAD...help! avazquez Engines and Propulsion Systems 53 17-10-2020 11:41
Shore GFI tripping troubleshooting US1Fountain Electrical: Batteries, Generators & Solar 14 24-02-2018 15:29
DC circuit breaker tripping on Kohler generator JSurr Electrical: Batteries, Generators & Solar 6 15-06-2017 23:35
Shore Power Circuit Breaker Tripping Often FollowingCs Electrical: Batteries, Generators & Solar 35 13-03-2017 18:29
Battery Charger, Shore Power and Generator? motion30 Electrical: Batteries, Generators & Solar 13 20-06-2009 14:02

Advertise Here


All times are GMT -7. The time now is 05:35.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.