Help me troubleshoot - low solar voltage

So the situation is that I checked my battery monitor today and noticed the expected amp in were rather low for daylight hours when we should be in bulk state. I checked the individual mppt controllers and found that one of them was not on. It had not been working for the past two days.

The reason it reports is that the voltage coming in from the solar is too low. The controller is reporting 11v.


Steps I've taken so far:
Measured the voltage of the individual panels with a multimeter (both 40v)
Measured the voltage at the output of the MC4 style parallel splitter (40v)
Measured the voltage at the solar input of the mppt (11v)
Measured the voltage between the negative solar input at the mppt and the positive solar input before the circuit breaker (11v)

Now here is the funny thing... If I flip the circuit breaker...
Measured the voltage between the negative solar input at the mppt and the positive solar input before the circuit breaker (40v)


I don't understand how the voltage is changing when I flip the breaker open. Any insights?
ThereAndBack is offline   Reply With Quote
Old 08-05-2021, 10:02   #2
CLOD
 
sailorboy1's Avatar

Join Date: Jul 2007
Location: being planted in Jacksonville Fl
Boat: none
Posts: 20,616
Re: Help me troubleshoot - low solar voltage

Quote:
Originally Posted by ThereAndBack View Post

I don't understand how the voltage is changing when I flip the breaker open. Any insights?
When it happened to me it was a burnt MC4 connector. It still had a connection so there was voltage, it just would carry current.
__________________
Don't ask a bunch of unknown forum people if it is OK to do something on YOUR boat. It is your boat, do what you want!
sailorboy1 is online now   Reply With Quote
Old 13-05-2021, 13:16   #3
Registered User
 
ThereAndBack's Avatar

Join Date: Jun 2018
Boat: Voyage 430
Posts: 401
Re: Help me troubleshoot - low solar voltage

Sailorboy1 was actually spot on.

I also learned (and didn't understand previously), that the solar controls ground out the PV - to the Batt -. They're all tied together.

To help anyone attempting to diagnose this problem in the future. I found one MC4 connector that was a lot more difficult to separate than the others. That should have been the first clue, they should come apart easy.

Then I found physical evidence upon close inspection:


Notice the bubbled plastic indicating burning (caused by some resistance). I tried to get the thing apart but ended up just having to cut it off, and I was unable to pull the metal out of the MC4 connector presumably because it has melted to that point.

Thanks to sailorboy for nailing this issue.
ThereAndBack is offline   Reply With Quote
Reply

Tags
solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar - Unusual low battery voltage sunluvr Electrical: Batteries, Generators & Solar 7 27-07-2019 12:17
Low voltage vs higer voltage solar Singleprop Electrical: Batteries, Generators & Solar 11 06-07-2015 19:35
Troubleshoot low fresh water pressure eddy Plumbing Systems and Fixtures 12 23-04-2013 09:35
Low Voltage on Solar Panels Meck Electrical: Batteries, Generators & Solar 7 31-03-2011 17:03
Low Voltage Solar Panels SeaKing Electrical: Batteries, Generators & Solar 8 31-08-2010 12:52

Advertise Here


All times are GMT -7. The time now is 17:31.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.