How do I handle 2 shore power inputs and a genset?

I'm looking to add an inverter charger to my boat. I have a Victron Multiplus Compact 12 | 2000 | 80 - 50. The boat has 2 shore power connections and one is labeled for the air conditioner. The boat also has a generator. The shore power inputs are both 110V 30 amp connections. The generator is also 110V.

The AC panel has 2 switches. You can see them labeled SHORE and GEN and AIR COND and GEN. Ideally I would like to wire my shore power and my genset to the AC input on the Multiplus via a AC transfer switch. That way when I'm on shore power, genset, or batteries the Multiplus would give me AC when needed. This would be easy with only one shore power line, but with 2 I don't know what to do.



Any suggestions on wiring the 2 110v shore power to the Multiplus?

Is there a way to parallel the 2 shore power inputs?

Should I just wire the shore power and genset into the transfer switch and operate the AIR COND by manually flipping the switch and turning on the genset? I don't plan on using the air conditioner unless the genset is running, since it would probably drain my battery too quickly.

Thanks,

Bobby
Attached Thumbnails
Click image for larger version

Name:	Panel.jpg
Views:	561
Size:	281.7 KB
ID:	278740  
blfinche is offline   Reply With Quote
Old 26-07-2023, 13:04   #2
Moderator
 
Jammer's Avatar

Join Date: Jan 2010
Location: Minnesota
Boat: Tartan 3800
Posts: 5,118
Re: How do I handle 2 shore power inputs and a genset?

You can't wire the second AC input to the multiplus because it only has one input.

If I recall correctly some of Victorn's larger inverter do have two inputs and two internal transfer switches to deal with this situation.

You can't parallel the shore power inputs for a variety of reasons.

You can wire the air conditioner as you describe, or wire it (in general terms) wtih a transfer switch to select either the inverter output or the 2nd shore power. That would allow you the choices of operating the AC from either the inverter, the generator (via the inverter) or the 1st shore power outlet (also via the inverter). You would need suitable overcurrent protection for all components.
__________________
The best part of an adventure is the people you meet.
Jammer is offline   Reply With Quote
Old 26-07-2023, 13:16   #3
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,265
Re: How do I handle 2 shore power inputs and a genset?

You have to choose an input for the Multiplus, see attached diagram where the three inputs are connected to a rotary selector switch.

If you need more power than one shore power connection can give, then I recommend to do what I did: convert one connection to a bigger one.

The first one at the top is a 120V 30A 3.6kW inlet with isolation transformer and the second one is a 120/240V 50A 12kW (which is massive) inlet with surge suppressor (Florida) and galvanic isolator.

And the third is the genset.
Attached Thumbnails
Click image for larger version

Name:	IMG_1375.jpg
Views:	159
Size:	284.2 KB
ID:	278743  
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 26-07-2023, 13:38   #4
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,601
Re: How do I handle 2 shore power inputs and a genset?

With a single Multiplus and 2 shore power legs, I'd plan to run one of the legs through the inverter and run the other directly to the panel. Then you have 1 side of the panel for inverter loads and the other for things you'd never want to run on the inverter (presumably the air conditioning).
rslifkin is online now   Reply With Quote
Old 26-07-2023, 14:30   #5
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,265
Re: How do I handle 2 shore power inputs and a genset?

Quote:
Originally Posted by rslifkin View Post
With a single Multiplus and 2 shore power legs, I'd plan to run one of the legs through the inverter and run the other directly to the panel. Then you have 1 side of the panel for inverter loads and the other for things you'd never want to run on the inverter (presumably the air conditioning).
So how to run air conditioning off inverter or even off the genset?
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 26-07-2023, 16:10   #6
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,601
Re: How do I handle 2 shore power inputs and a genset?

Quote:
Originally Posted by s/v Jedi View Post
So how to run air conditioning off inverter or even off the genset?

My suggestion presumes that you have at least some loads (such as A/C) that you don't ever want to run from the inverter. But looking at the panel in question, it appears that both panel legs can be transferred to generator power. So when both are transferred to generator power, 1 leg would go through the inverter, the other feeds directly from the generator.
rslifkin is online now   Reply With Quote
Old 27-07-2023, 01:04   #7
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,706
Re: How do I handle 2 shore power inputs and a genset?

The multi will go on shore power 1. After the shore / gen transfer switch on the panel. You said you want to add transfer switch. But it’s right in the picture…. You already have 2 transfer switches.

Shore 2 / gen stays separate as is. Feeding air con. You can not combine 2 shore plugs.

Shore 1, shore 2, inverter output neutrals must all stay separate.

Best done by someone who knows how to do it..,
smac999 is offline   Reply With Quote
Old 27-07-2023, 01:10   #8
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,706
Re: How do I handle 2 shore power inputs and a genset?

Quote:
Originally Posted by s/v Jedi View Post
So how to run air conditioning off inverter or even off the genset?

Air con won’t run off inverter. It will run off gen when air con transfer is on gen.

If he wants both shore inlets inverted . He needs 2 inverters.
smac999 is offline   Reply With Quote
Old 27-07-2023, 05:14   #9
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,265
Re: How do I handle 2 shore power inputs and a genset?

Quote:
Originally Posted by smac999 View Post
Air con won’t run off inverter. It will run off gen when air con transfer is on gen.

If he wants both shore inlets inverted . He needs 2 inverters.
I see. We run A/C off the inverter but that only makes sense for boats with big solar arrays.

I would still prefer a larger shore power inlet. Even when shore only provides 3.6kW and your peak loads are above that, the Multiplus does PowerAssist so it will work fine with a good house battery
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 27-07-2023, 05:26   #10
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,601
Re: How do I handle 2 shore power inputs and a genset?

Quote:
Originally Posted by s/v Jedi View Post
I see. We run A/C off the inverter but that only makes sense for boats with big solar arrays.

I would still prefer a larger shore power inlet. Even when shore only provides 3.6kW and your peak loads are above that, the Multiplus does PowerAssist so it will work fine with a good house battery

Yeah, the game changes a bit when you get to bigger boats where your ability to fit more battery and solar grows faster than your power demands. On smaller boats, you'll often have a few loads that just aren't practical to run on inverter power, so splitting things up is no big deal.
rslifkin is online now   Reply With Quote
Reply

Tags
power, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar/generator inputs and order Amart Electrical: Batteries, Generators & Solar 12 10-04-2022 15:03
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
Combining Wind and Solar Charge Inputs Target9000 Electrical: Batteries, Generators & Solar 17 25-11-2011 06:26
How to Handle USB GPS and NMEA to USB Inputs sailracer OpenCPN 16 16-04-2011 07:22
Switching Single Generator and Two Shore Power Inputs winds aloft Electrical: Batteries, Generators & Solar 8 20-08-2010 06:47

Advertise Here


All times are GMT -7. The time now is 06:17.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.