Old 18-03-2023, 05:27   #1
Registered User
 
theBigKahuna's Avatar

Join Date: Jun 2018
Location: flexible
Boat: Leopard 40 Sailing Catamaran
Posts: 146
Cool In Bahamas: Is it our Fridge or House Bank... neither good option

Out the gate, my electrical knowledge base is not the best... I know that's a character flaw for a cruiser! Our situation is our new Vitrigo fridge (replaced in Dec) is showing a low voltage errror (1 red flash every 4 seconds). The quandry I have is at the same time our House bank mulitmeter never reads below 12.4 and the Inverter display not below 12.2. Any ideas / advice appreciated... Being in the Bahamas doesn't make either issue any easier.

Other notables:
- House Bank (3 Odessey Performance 4D-1300 AGMs) replaced 7/2019
- Error goes away when genset is run; but returns after turned off. Big Unless and I'm assuming. It's daylight and probably our solar panels (1500W) nudge things along.
- Error goes away under shore power
- By and large the fridge is keeping everything froze / chilled but we're seeing a bit of defraust melt down from time to time.

Praying not battery bank as we're over here 'till May.

Cheers!

jBrad
sv Fuzzy Logic ('15 Leopard Sailcat)
__________________
a pessimist says "it can't get any worse", an optimist says "yes it can!!"
theBigKahuna is offline   Reply With Quote
Old 18-03-2023, 05:31   #2
Registered User

Join Date: Mar 2012
Location: North Carolina
Boat: Seaward 22
Posts: 1,035
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

I'm far from an expert at this as I have a simple little boat. My first though is, what is the voltage at your fridge? You could have a voltage drop in the run from your batteries to the fridge.
ohdrinkboy is offline   Reply With Quote
Old 18-03-2023, 05:37   #3
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

That pretty much narrows it down actually.

It can really only be one of two things unless the refrigerator is malfunctioning.

Either you have corrosion between that refrigerator and the batteries, including whatever control panels and breakers you have between them.

OR….

Did you install the refrigerator? Or did a yard do it?

In either case, it sounds like maybe the wiring is too small. That can create a voltage drop as well. To fix the situation, rewire that refrigerator with quite a bit better and larger wires than you currently have. Double check with the manufacturer to see what they require for that wiring. And if it’s a long run, go up a little bit in thickness.


As a sanity check, if you can get in behind the refrigerator and put a voltmeter on the DC wiring that connects to the refrigerator, do that to see what you get and if it is low.

My post assumes that your batteries truly never go below 12.2. Definitely make sure of that. And make sure they’re not going below 12.2 when the refrigerator compressor is on. It doesn’t matter at other times.
Chotu is offline   Reply With Quote
Old 18-03-2023, 05:58   #4
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

OP: While checking for corrosion, undersized wire should be done, my first inclination is a weak house bank. Does the bank voltage increase to about 14.2V when charging and then reduce to about 13.6V?
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 18-03-2023, 06:16   #5
Registered User
 
theBigKahuna's Avatar

Join Date: Jun 2018
Location: flexible
Boat: Leopard 40 Sailing Catamaran
Posts: 146
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

Charlie, yes that's how the house bank reacts... currently working it's way up charging from solar (and flash is not occuring). OhDrinkBoy, yes, I'll check the voltage the next time we defrost (WAY more often than on land!!!). But Chotu, you reminded me of our install. The fridge was an 'inkind' swap. But (again, not being an electician) the new wire (12V) appeared larger than the existing and I should have paid attention!

It is funny though! I'd sailed my whole life, 16ft hobies, windsurfers, sunfish, lasers etc and love them all. Moving to a 40' cat didn't really change the sailing technique much. But what I didn't realize was we'd be a late bloomer diesel and 4 stroke mechanic, a PEX plumber and budding novice electrician. As always all you folks's input is always greatly appreciated/respected and we're so glad to have the cruisersforum platform to share knowledge.

Fair winds,
jBrad
__________________
a pessimist says "it can't get any worse", an optimist says "yes it can!!"
theBigKahuna is offline   Reply With Quote
Old 18-03-2023, 06:27   #6
Registered User
 
Bill O's Avatar

Join Date: Jul 2015
Boat: Bruce Bingham Christina 49
Posts: 3,328
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

jBrad,
We probably need more info to properly help.

With 1500W of solar you should be able to top off your house batteries daily (house bank = 3x 170ah = 510ah) During the day, what voltage are your batteries? (you mentioned 12.4V) Are you solar panels/chargers working? If so, would expect them to come up to 14.3+V.

How long are you running the gen? Assume the bats are getting charged when on, what bat V are you seeing when gen is on?

Unfortunately, could be the house bats failing after 4 yrs. There is a significant V drop at the fridge compressor when it starts up. If you are see 12.4 (low) on the house bank and have a 3% loss in your wire to the compressor, you could easily see <11.6V at the compressor on start up.
__________________
Bill O.
KB3YMH
https://phoenixketch.blogspot.com/
Bill O is offline   Reply With Quote
Old 18-03-2023, 06:30   #7
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

OP: So bank appears to be charging correctly. Next step would be to check the voltage, while the compressor is operating, at the battery terminals and compare it to the voltage reading at the load side of the breaker that serves the reefer and finally at the connection to the compressor.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 18-03-2023, 06:52   #8
Registered User

Join Date: May 2016
Location: Bradenton, FL https://share.garmin.com/seaseeker
Boat: Manta 42 Mk IV Catamaran
Posts: 160
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

To determine the problem:
1. Measure the battery voltage at the batteries with the low voltage warning going off.
2. Measure the voltage at the compressor with the low voltage warning going off.
If the voltage at the batteries is okay but the voltage at the compressor is low it is wiring, either too small wires or a bad connection. My bet is on a bad connection.

3. Put one probe from the voltmeter on the positive terminal of the battery, put the other probe on the positive post on the compressor. Write down the reading.

4. Put one probe from the voltmeter on the negative terminal of the battery, put the other probe on the negative post on the compressor. Write down the reading.

If the two reading are about the same your wires are too small.
If one number is larger than the other, that is the side with the bad connections.

Also be sure to check the drop across you circuit breaker, they go bad.
Avionics_Joe is online now   Reply With Quote
Old 18-03-2023, 07:00   #9
Registered User

Join Date: May 2016
Location: Bradenton, FL https://share.garmin.com/seaseeker
Boat: Manta 42 Mk IV Catamaran
Posts: 160
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

I am in the Bahamas, take a look at: https://share.garmin.com/seaseeker

And see it I am near you.


Quote:
Originally Posted by Avionics_Joe View Post
To determine the problem:
1. Measure the battery voltage at the batteries with the low voltage warning going off.
2. Measure the voltage at the compressor with the low voltage warning going off.
If the voltage at the batteries is okay but the voltage at the compressor is low it is wiring, either too small wires or a bad connection. My bet is on a bad connection.

3. Put one probe from the voltmeter on the positive terminal of the battery, put the other probe on the positive post on the compressor. Write down the reading.

4. Put one probe from the voltmeter on the negative terminal of the battery, put the other probe on the negative post on the compressor. Write down the reading.

If the two reading are about the same your wires are too small.
If one number is larger than the other, that is the side with the bad connections.

Also be sure to check the drop across you circuit breaker, they go bad.
Avionics_Joe is online now   Reply With Quote
Old 18-03-2023, 08:16   #10
Registered User
 
theBigKahuna's Avatar

Join Date: Jun 2018
Location: flexible
Boat: Leopard 40 Sailing Catamaran
Posts: 146
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

[QUOTE=Bill O;3756495]jBrad,
We probably need more info to properly help.

With 1500W of solar you should be able to top off your house batteries daily (house bank = 3x 170ah = 510ah) During the day, what voltage are your batteries? (you mentioned 12.4V) Are you solar panels/chargers working? If so, would expect them to come up to 14.3+V.

How long are you running the gen? Assume the bats are getting charged when on, what bat V are you seeing when gen is on?

Unfortunately, could be the house bats failing after 4 yrs. There is a significant V drop at the fridge compressor when it starts up. If you are see 12.4 (low) on the house bank and have a 3% loss in your wire to the compressor, you could easily see <11.6V at the compressor on start up.[/QUOTE
Just ran the genset for 1.5 hrs. and meter goes up to 14.31, in the 14s after 45 minutes or so. then down to ~13.65 and actually bouncing up to low 14s (solar is kicking in (The victron solar app is still showing us in Bulk mode though).

TBH, my MAJOR concerrn is the batterys or the Vitrigo fail while here... family visiting etc. So, the hope is we'll make it till June.

Offseason plan is already to replace Inverter and Charger as charger is inadequate (times out after 45-1hr and has to be reset) and battery bank very likely may be long in the tooth... This years boat kitty was pretty much eaten up w/ the solar and water maker, etc.

But, are going thru a bunch of the steps posted here so we can isolate the issue, which could very likely be power loss going to fridge and likely the issue is combination of 'all the above'.

Again, many many thanks and additional insights will definitely be factored in.

Cheers!
jBrad sv Fuzzy Logic
__________________
a pessimist says "it can't get any worse", an optimist says "yes it can!!"
theBigKahuna is offline   Reply With Quote
Old 18-03-2023, 09:04   #11
Registered User
 
Bill O's Avatar

Join Date: Jul 2015
Boat: Bruce Bingham Christina 49
Posts: 3,328
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

jBrad,
If you get a chance purchase an inexpensive Watt meter https://www.ebay.com/itm/36404132953...3ABFBMvMzT1t5h
and install just before compressor controller. They are helpful to record the low V when the compressor kicks in, total ah and shows the amp draw when compressor is running (this is helpful when recharging the refrigerant in a capillary system).

When they installed your new Vitrifrigo, did anyone add more refrigerant? If so, it maybe drawing too much current, which could also be part of the problem.

__________________
Bill O.
KB3YMH
https://phoenixketch.blogspot.com/
Bill O is offline   Reply With Quote
Old 18-03-2023, 10:17   #12
Registered User
 
Captain Bill's Avatar

Join Date: Apr 2008
Location: Punta Gorda, Fl
Boat: Endeavourcat Sailcat 44
Posts: 3,188
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

While your battery readings under load are not terribly concerning, I'm a bit concerned about your charging profiles. You said that your batteries went to float voltage after only 45 minutes of charging at absorption voltage. Having Many years of experience with AGMs before switching to LiFePO4 it seems to me that you have virtually no chance of getting your AGMs to 100% in 45 minutes. I'm not surprised the Victron is still reporting that it's in bulk. If you don't get your AGMs to 100% at least once or twice a week you will seriously affect their useful life. AGMs really don't like partial charge. If your routine is to bulk them up with the genset/charger in the mornings and let the solar take them to 100% then I don't see a problem, but on a 510ah bank they should not drop out of absorption until you are down to about 2.5 amps going into the batteries. 1500w of solar should have no trouble holding absorption voltage this time of year in the Bahamas. Except on the rare cloudy days in the Bahamas late winter/spring I was always able to reach absorption voltage by noon on 640w. Quite often it would take until 3:00 or 4:00 before the tailing current got down far enough to drop into float.



Do you get a lot of shadows on your solar array? My experience is that boats at anchor in the Bahamas are almost always facing east and this has a tendency to cast shadows on the solar arrays on the back of the boat until late in the morning even if the panels are mounted well behind the boom. I always pulled my boom well to port to avoid direct shadows on the panels in the morning. It also had the effect of shifting the stern slightly to starboard and causing the mast shadow to miss the solar panels much earlier in the day. It saved a lot of generators running.


Previous contributors have pretty much covered everything I would have to say about possible issues with your fridge.
Captain Bill is offline   Reply With Quote
Old 18-03-2023, 10:59   #13
Moderator
 
hpeer's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: Between Caribbean and Canada
Boat: Murray 33-Chouette & Pape Steelmaid-44-Safara-both steel cutters
Posts: 8,700
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

Going thru this myself at the moment.

I have wind and solar and all was just fine as long as the winds kept up. The wind genny kept my batteries up all night, no problem.

Then we hit low wind spell and the batteries are WAAAY low in the AM. The wind gunny masked the problem. The deep discharge punctuated it.

Oh the fun of sourcing batteries in Dominica.

GC-2 batteries, French. Last time they died, suddenly puffing up, was in Guadeloupe. I am afraid that during the covid period I was not on top of proper battery charging. So I blame myself for the short life.

Where exactly are you in Bahamas?
I would start calling around to source batteries, just in case. I hear importing takes time.
hpeer is offline   Reply With Quote
Old 18-03-2023, 12:02   #14
Registered User
 
chris mac's Avatar

Join Date: May 2015
Location: edmonton alberta
Boat: 1992 lagoon 42 tpi
Posts: 1,733
Re: In Bahamas: Is it our Fridge or House Bank... neither good option

Hey fuzzy logic, we have seen you around ( I'm on SV purrfect)
If we share an anchorage I would be happy to come try to help, so keep an eye out for us and I'll do the same. We are heading over to cat in the next day or two, not sure where you are at right now.
In terms of your battery, you mention the victron app. Go on there and check history. Depending on the app it might be a tab labeled "detailed". See what min and max have been on a day to day basis. That should tell us if the batteries are keeping up or not.
chris mac is offline   Reply With Quote
Old 18-03-2023, 15:07   #15
Registered User
 
theBigKahuna's Avatar

Join Date: Jun 2018
Location: flexible
Boat: Leopard 40 Sailing Catamaran
Posts: 146
Cool Re: In Bahamas: Is it our Fridge or House Bank... neither good option

Quote:
Originally Posted by chris mac View Post
Hey fuzzy logic, we have seen you around ( I'm on SV purrfect)
If we share an anchorage I would be happy to come try to help, so keep an eye out for us and I'll do the same. We are heading over to cat in the next day or two, not sure where you are at right now.
In terms of your battery, you mention the victron app. Go on there and check history. Depending on the app it might be a tab labeled "detailed". See what min and max have been on a day to day basis. That should tell us if the batteries are keeping up or not.
Hah! We, in turn, have been hearing you on the squaker! Yes, we'll keep an eye out for you! We're in Nassau and had been waiting for a window to get up to the Abacos, but Mother Nature is being a %#@$# (no disrespect intended!). Plan B's now heading to Shroud then the Staniel / Black Point Cays to await guests. It'd be outstanding to both run into you and get another set of eyes.

Fair Winds,

Brad sv Fuzzy Logic
__________________
a pessimist says "it can't get any worse", an optimist says "yes it can!!"
theBigKahuna is offline   Reply With Quote
Reply

Tags
Bahamas


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2x6v Deep cycle start bank and 2x12v regular house bank George_SD Electrical: Batteries, Generators & Solar 22 08-08-2021 23:46
House Bank or Genset-Engine Bank? BlueSovereign Electrical: Batteries, Generators & Solar 12 02-04-2019 08:45
Bahamas with neither USCG nor State documentation brownoarsman Rules of the Road, Regulations & Red Tape 34 23-02-2015 19:52
36vdc Motor Bank and 12vdc House Bank bobola Electrical: Batteries, Generators & Solar 24 22-12-2009 20:30

Advertise Here


All times are GMT -7. The time now is 12:53.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.