Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 27-08-2022, 06:14   #31
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by RaymondR View Post
I could be wrong, I learned a lot of this stuff a long time ago and my memory is not what it once was.

You can have a transformer with centre taps on either primary or secondary coils with them still fully isolated from each other. My understanding of whats known as an autotransformer is one in which the primary and secondary share a coil and therefor there is no isolation possible.

However if you have a separate isolation transformer between the shore power transformer and an autotransformer in the boats circuits then you will have isolation between shore and vessel power and the presence of the autotransformer would not introduce DC to the shore power circuit or trip the RCD.
When you look at my diagram, you find the auto transformers (I use two) all the way at the right, where the distribution breakers are. Everything that is to the left of it, is 240V only, without any Neutral. This makes for a simple, powerful setup.

Attached a diagram of these Victron auto transformers. L1 and L2 are the inputs as well as outputs. There is one winding with a center tap, which becomes the Neutral. There is a grounding relay in case one needs a grounded Neutral.

The beauty of this setup is that when at the distribution panel loads are balanced over L1 and L2, the transformer does nothing, carries no current. Only when an imbalance occurs, the transformer handles it and of course L1 and L2 fed into it are always perfectly balanced, optimizing inverter and genset capacity. The transformers I use are rated for 32A.

All the way in the left side of the diagram you see the shore power input, which uses an isolation transformer.
Attached Thumbnails
Click image for larger version

Name:	20BDFE7B-7667-4DC7-94E4-BC8C0FF22CE8.jpeg
Views:	36
Size:	66.2 KB
ID:	263511   Click image for larger version

Name:	B0559E20-BD19-4C63-B953-50CCE8D1117A.jpg
Views:	64
Size:	340.9 KB
ID:	263512  

__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 27-08-2022, 07:00   #32
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by s/v Jedi View Post
You mean like this: https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1

Same ones are sold by Blue Sea Systems for much more $$$ but they probably are better quality. I have been using the cheaper ones and they work fine, although I don’t switch much, maybe two times a year (leave marina to go cruising, then come back in marina from cruising)

I have 3 inputs so a bigger switch that I couldn’t find on Amazon, so my next source is eBay or AliExpress (often the same sellers).
That will do exactly what I need and the price is great thank you
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 27-08-2022, 08:01   #33
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: Jedi AC power diagram: updated version 3

Now that this thread became active again, let me update it. I already posted the latest diagram above, which is basically the same as in the OP but much nicer done after I got the software for it.

Attached here are the two panels that I designed to go with it. First is the main panel, which holds the input selector switch and the breakers for the inverter/chargers as well as the bypass breaker. I also added power monitors for each input. These also count kWh so you can check the marina bill

The second panel is for the distribution breakers. As you can see, I ended up with only two distribution groups. Each group can select input independently from the other with the rotary switches.

Note how I aligned breakers and used colors to make it easy to work with. Also note how I divided loads over the groups. Remember that these groups, when they support 120V, needs separate auto transformers.

The reason that I have separate panels is that I am limited to a maximum of 8” height for them.
Attached Thumbnails
Click image for larger version

Name:	91E2563E-560C-43E6-9D54-3D0559FA9485.jpg
Views:	66
Size:	264.5 KB
ID:	263518   Click image for larger version

Name:	895AF5C9-760E-4242-A1A8-7C76746B7AD8.jpg
Views:	46
Size:	230.4 KB
ID:	263519  

__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 27-08-2022, 08:16   #34
Registered User

Join Date: Mar 2009
Location: Annapolis, MD
Boat: Southerly 480
Posts: 533
Images: 1
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by s/v Jedi View Post
Now that this thread became active again, let me update it. I already posted the latest diagram above, which is basically the same as in the OP but much nicer done after I got the software for it.

Attached here are the two panels that I designed to go with it. First is the main panel, which holds the input selector switch and the breakers for the inverter/chargers as well as the bypass breaker. I also added power monitors for each input. These also count kWh so you can check the marina bill

The second panel is for the distribution breakers. As you can see, I ended up with only two distribution groups. Each group can select input independently from the other with the rotary switches.

Note how I aligned breakers and used colors to make it easy to work with. Also note how I divided loads over the groups. Remember that these groups, when they support 120V, needs separate auto transformers.

The reason that I have separate panels is that I am limited to a maximum of 8” height for them.
Where did you get the panels made?
shimari is offline   Reply With Quote
Old 27-08-2022, 11:59   #35
Registered User

Join Date: Dec 2021
Location: Pacific North West, Unites States
Boat: Deerfoot 62
Posts: 10
Re: Jedi AC power diagram: updated version 3

Do you use GFCI outlets for the 120v/240v distribution, and do they work?
Are you able to detect L1 to equipment case ground faults in the loads after the 120v/240v distribution?

I'm asking as you have an AC ground for the cases of the IT/Inverters/AT but I imagine that the ground is not physically linked to the AT neutrals.
Alex A is offline   Reply With Quote
Old 27-08-2022, 12:59   #36
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by shimari View Post
Where did you get the panels made?
Front Panel Express (Google them for link). You design the panels yourself using their free CAD software, send the files in and they send you the panels in a couple of days
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 27-08-2022, 13:04   #37
Registered User

Join Date: Aug 2019
Location: New England
Boat: Building myself... FTW
Posts: 185
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by s/v Jedi View Post
The beauty of this setup is that when at the distribution panel loads are balanced over L1 and L2, the transformer does nothing, carries no current. Only when an imbalance occurs, the transformer handles it and of course L1 and L2 fed into it are always perfectly balanced, optimizing inverter and genset capacity. The transformers I use are rated for 32A.
Could I restate this as?

only when L1 and L2 are carrying alternating current does the transformer kick-in
bdgWesternMass is offline   Reply With Quote
Old 27-08-2022, 16:19   #38
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by bdgWesternMass View Post
Could I restate this as?

only when L1 and L2 are carrying alternating current does the transformer kick-in
No, only when the current on L1 is different from the current on L2, then (only) the difference is handled by the transformer.

So when L1 does 20A and L2 does 22A then the auto transformer sees 2A.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 27-08-2022, 19:42   #39
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by Alex A View Post
Do you use GFCI outlets for the 120v/240v distribution, and do they work?
Are you able to detect L1 to equipment case ground faults in the loads after the 120v/240v distribution?

I'm asking as you have an AC ground for the cases of the IT/Inverters/AT but I imagine that the ground is not physically linked to the AT neutrals.
Being behind an isolation transformer, one can use double pole breakers and do away with all ground conductors. But this brings in the case ground faults:

When one appliance develops a case ground fault, the metal housing becomes energized by one of the two poles. This is not a problem because it is what is done on purpose with a grounded neutral. The difference is when another appliance also develops a ground fault but from the other pole. In theory one can touch one appliance with one hand and the other appliance with the other hand and be electrocuted.

This is why I recommend to install the ground conductor to all outlets, inverters etc. Even though it would be of near zero possibility, with the ground conductor installed, you simply trigger the breaker as soon as the second case ground fault occurs and this problem is eliminated.

The only reasons for alarming on the first ground fault is for applications where power supply is a critical necessity, like hospitals, navy ships etc. When they are able to detect the first case ground fault, they can fix that, which improves power availability. For sailboats the DC power is used for all critical systems like bilge pumps, autopilot etc. so we don’t need this.

For detecting the first case ground fault, additional equipment is required.

GFCI outlets will work as regular outlets but don’t provide any benefit over regular outlets because the danger from ground as a return path is eliminated because the ground return oath has been eliminated. Without that danger, you don’t need the safety anymore.
But when the boat is hauled out and connected to shore power, it stops being a boat and may require a grounded neutral, in which case the isolation transformer comes with a jumper to provide that and you have gfci outlets etc.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 29-08-2022, 14:33   #40
Registered User

Join Date: Dec 2021
Location: Pacific North West, Unites States
Boat: Deerfoot 62
Posts: 10
Re: Jedi AC power diagram: updated version 3

Sorry, another question: Do you have a connection between your AC ground and DC system?
Alex A is offline   Reply With Quote
Old 29-08-2022, 17:31   #41
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: Jedi AC power diagram: updated version 3

Quote:
Originally Posted by Alex A View Post
Sorry, another question: Do you have a connection between your AC ground and DC system?
No, AC ground is exactly as shown in the diagram.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
wiring diagram for autohelm3000... NOT the ST version! centerline General Sailing Forum 3 07-01-2015 09:16
Updated to New Version - Lost Old Tracks?? obelisk OpenCPN 20 14-03-2014 02:32
30 Amp Shore Power Receptacle Wiring Diagram Needed sdowney717 Electrical: Batteries, Generators & Solar 6 24-08-2011 09:08
Final version: Jedi's whole wheat & rye bread recipe s/v Jedi Cooking and Provisioning: Food & Drink 0 25-02-2011 10:28

Advertise Here


All times are GMT -7. The time now is 23:28.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.