Ahoy all, I have a Kohler generator, model 8CCO23, that the fuel solenoid will not draw in when the start switch is activated. It will run all day when I manually actuate the fuel control lever or "rig" a 12VDC directly to the fuel solenoid but I fear that applying a jumper for 12VDC will be bypassing the safety switch logic of the oil pressure, water temperature, and manifold Temperature.
I get 12.53 VDC up to the "C" relay but when I activate the start switch the voltage drops to 8.3 volts. Not enough to draw in the fuel solenoid to complete the start sequence

Thanks in advance for any ideas of the fix

Jeff
JSurr is offline   Reply With Quote
Old 03-05-2017, 04:56   #2
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Kohler Generator starting problem

Do you have three wires going to the solenoid? An earth, a pull, and a hold?

It possible for the pull side if the solenoid to have shorted. It's also possible that you've got high resistance electrical connections or a dirty relay contact somewhere in the system.
Sailmonkey is offline   Reply With Quote
Old 03-05-2017, 05:55   #3
Registered User

Join Date: May 2016
Location: Fla
Boat: Irwin MK III 43
Posts: 38
Re: Kohler Generator starting problem

There are only two wires coming from the fuel solenoid, a power and a ground Both have 0.00 resistance when checked for continuity. There are two relays in the system, both are new, both bench tested several times.
I have 8.3 VDC, dropped from 12.5 VDC, at the starter solenoid. I've had the alternator and new voltage regulator bench tested yesterday, both fine. The regulator putting out 14.8 volts and altenator 32amps. And the starter is newly replaced.
JSurr is offline   Reply With Quote
Old 07-06-2017, 22:31   #4
Registered User

Join Date: May 2016
Location: Fla
Boat: Irwin MK III 43
Posts: 38
Re: Kohler Generator starting problem

Discovered the problem. Turned out wrong relays were installed. The correct relays have an internal diode. Someone had installed the wrong relays and when I replaced them I used the same wrong part number. I looked at my buddy's Kohler generator and discovered the difference.
The correct relay is a Bosch 12-796-772
Same one that fits a 2003-2011 Saab 9-3 Fuel Pump Relay
NAPA Part number AR143
JSurr is offline   Reply With Quote
Reply

Tags
generator


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kohler generator warranty Russell7171 Electrical: Batteries, Generators & Solar 3 30-12-2013 11:02
Onan v Kohler 7kva/kvw diesel generator? nmit5903 Electrical: Batteries, Generators & Solar 4 01-12-2013 13:46
Kohler Generator Problem Dockhead Electrical: Batteries, Generators & Solar 16 13-05-2013 10:58
Major Generator Problems (Formerly Pink vs. Green Coolant for Kohler Genset?) Dockhead Engines and Propulsion Systems 39 29-06-2012 15:39

Advertise Here


All times are GMT -7. The time now is 17:18.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.